[Bldg-sim] LEED project - maximum limit allowed to simplified wall azimuth.

Jim Dirkes via Bldg-sim bldg-sim at lists.onebuilding.org
Fri Dec 16 06:43:01 PST 2016


We are on the same page.

A friend once said (probably quoting someone else), "Become good, then
better, then best. After that, set a new standard for 'best'."

On Fri, Dec 16, 2016 at 9:20 AM, Andrew S. Hoover via Bldg-sim <
bldg-sim at lists.onebuilding.org> wrote:

> Agree with everything you say below.  Reasonably achievable is probably
> the best, lol.  Just wanted to emphasize getting reasonably achievable is
> the goal not just getting done.
>
>
>
> *From:* Jim Dirkes [mailto:jim at buildingperformanceteam.com]
> *Sent:* Friday, December 16, 2016 8:47 AM
> *To:* Andrew S. Hoover <andyhoover at thebestconsultant.com>
> *Cc:* bldg-sim at lists.onebuilding.org
>
> *Subject:* Re: [Bldg-sim] LEED project - maximum limit allowed to
> simplified wall azimuth.
>
>
>
> Andrew,
>
> Not trying to be difficult here, but it might be better to substitute
> "reasonable" or "representative" for "accurate". From a certain perspective
> none of our energy models are accurate. Especially for Appendix G
> comparisons of new building designs, there are so many variables which are
> not known with high confidence!
>
>
>
> What's the infiltration rate - really?
>
> What is the occupancy or lighting or plug load diversity - really?
>
> What is the part load performance - as installed?
>
> etc.
>
>
>
> I'm always glad to learn of research which quantifies the impact of topics
> about which I have a gut check, but don't have time to actually
> investigate.  The paper Nick cited would be one of them. Those ASHRAE
> people are also pretty good at doing their homework when writing standards
> such as 90.1, too.
>
>
>
> I ALWAYS attempt to input the best available information, using a good
> understanding of building science, physics and heat transfer. Nonetheless,
> I also realize that there are dozens of variables that will not match with
> actual operation.
>
>
>
> p.s., I used 16 facets for my last round tower just to be more confident :)
>
> [image: Inline image 2]
>
>
>
>
>
>
>
> On Fri, Dec 16, 2016 at 6:12 AM, Andrew S. Hoover via Bldg-sim <
> bldg-sim at lists.onebuilding.org> wrote:
>
> Can does not mean you will have an accurate model.  All too often the
> questions are about what can or what must I do and not about what is best
> to do.
>
>
>
> *From:* Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] *On
> Behalf Of *Leonard Sciarra via Bldg-sim
> *Sent:* Thursday, December 15, 2016 1:05 PM
> *To:* bldg-sim at lists.onebuilding.org
> *Subject:* Re: [Bldg-sim] LEED project - maximum limit allowed to
> simplified wall azimuth.
>
>
>
> Julian –
>
>
>
> The text is written to include 45 degrees.  So if they are 45 degrees,
> then you can make it a square, although the exception was intended for
> curved surfaces.
>
>
>
> Hope this helps.
>
>
> *Leonard Sciarra, AIA, ASHRAE, LEED ap+ *
> Senior Associate
> +1 312.577.6580 <(312)%20577-6580> Direct
> +1 312.456.0123 <(312)%20456-0123> Main
> +1 847.345.5619 <(847)%20345-5619> Mobile
>
> *Gensler *
> 11 East Madison Street
> Suite 300
> Chicago, Illinois 60602
> USA
>
>
>
> Gensler.com <http://www.gensler.com/> | Blog <http://www.gensleron.com/>
>  | Facebook <http://www.facebook.com/GenslerDesign> | Twitter
> <http://www.twitter.com/GenslerOnCities> | YouTube
> <http://www.youtube.com/GenslerTV>
>
>
>
> What’s ahead for design and our clients?
>
> Find out here: *Gensler Design Forecast 2016*
> <http://www.gensler.com/doc/gensler-design-forecast-2016>
>
>
>
> *From:* Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org
> <bldg-sim-bounces at lists.onebuilding.org>] *On Behalf Of *via Bldg-sim
> *Sent:* Thursday, December 15, 2016 11:17 AM
> *To:* bldg-sim at lists.onebuilding.org
> *Subject:* [Bldg-sim] LEED project - maximum limit allowed to simplified
> wall azimuth.
>
>
>
> Hello,
>
>
>
> Does anyone know how to interpret “no more than 45 degrees” of exception
> 5.b - table G3.1 (90.1-2007/2010/2013) ? :
>
>
>
> *5.  Building Envelope*
>
> All components of the building envelope in the proposed design shall be
> modeled as shown on architectural drawings or as built for existing
> building envelopes.
>
>
>
> *Exceptions:*
>
> b. Exterior surfaces whose azimuth orientation and tilt differ by no more
> than 45 degrees and are otherwise the same may be described as either a
> single surface or by using multipliers.
>
>
>
> Because “no more than 45 degree” include 45 degree, does the exception
> still apply if the azimuth of two walls is exactly 45 degrees?
>
> In other words, considering a LEED project, can a perfect octagonal
> building shape be modeled as a square building (as long as they have the
> same floor area and the 8 walls have a similar construction) ?
>
>
>
> Thanks
>
>
>
> Julien
>
> ____________________________________________________________________
>
> *Julien Dutel,* ing., CEM, CMVP*.*
>
> *Direction des secteurs **résidentiel, institutionnel et des affaires*
>
> *Bureau de l'efficacité et de l'innovation énergétiques*
>
> *Ministère de l'Énergie et des Ressources naturelles*
>
> 5700, 4e Avenue Ouest, B-406
>
> Québec (Québec)  G1H 6R1
>
> Téléphone : 418 627-6379 <(418)%20627-6379>, poste 8060
>
> Téléphone sans frais : 1 877 727-6655 <(877)%20727-6655>
>
> Télécopieur : 418 643-5828 <(418)%20643-5828>
>
> julien.dutel at mern.gouv.qc.ca
>
> *mern.gouv.qc.ca <http://mern.gouv.qc.ca>*
>
>
>
>
>
>
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>
>
>
> --
>
> James V Dirkes II, PE, BEMP, LEED AP
> CEO/President
> The Building Performance Team Inc.
> 1631 Acacia Dr, GR, Mi 49504
>
> Direct: 616.450.8653 <(616)%20450-8653>
> jim at buildingperformanceteam.com
>
> Website <http://buildingperformanceteam.com>l  LinkedIn
> <https://www.linkedin.com/pub/jim-dirkes/7/444/413> | May 2016 ASHRAE
> Journal article on energy modeling
> <http://buildingperformanceteam.com/bpt-insights-blog/item/73-modeled-performance-isn-t-actual-performance>
>
> All people should seek Truth, and seek it with love's reckless passion.
> Without that passion, difficulties seem insurmountable and soon erode the
> search. Society often regards intensity of conviction as dangerous, when it
> should be cherished so long as it continues to demonstrate love.
>
>
>
>
>
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>


-- 

James V Dirkes II, PE, BEMP, LEED AP
CEO/President
The Building Performance Team Inc.
1631 Acacia Dr, GR, Mi 49504

Direct: 616.450.8653
jim at buildingperformanceteam.com

Website <http://buildingperformanceteam.com>l  LinkedIn
<https://www.linkedin.com/pub/jim-dirkes/7/444/413> | May 2016 ASHRAE
Journal article on energy modeling
<http://buildingperformanceteam.com/bpt-insights-blog/item/73-modeled-performance-isn-t-actual-performance>

All people should seek Truth, and seek it with love's reckless
passion. Without that passion, difficulties seem insurmountable and
soon erode the search. Society often regards intensity of conviction
as dangerous, when it should be cherished so long as it continues to
demonstrate love.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20161216/42ab4f9d/attachment-0001.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 22121 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20161216/42ab4f9d/attachment-0003.jpg>


More information about the Bldg-sim mailing list