Can does not mean you will have an accurate model.  All too often the
questions are about what can or what must I do and not about what is best to
do.

 

From: Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of
Leonard Sciarra via Bldg-sim
Sent: Thursday, December 15, 2016 1:05 PM
To: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] LEED project - maximum limit allowed to simplified
wall azimuth.

 

Julian – 

 

The text is written to include 45 degrees.  So if they are 45 degrees, then
you can make it a square, although the exception was intended for curved
surfaces.

 

Hope this helps.

                                                                      
Leonard Sciarra, AIA, ASHRAE, LEED ap+ 
Senior Associate 
+1 312.577.6580 Direct 
+1 312.456.0123 Main 
+1 847.345.5619 Mobile 
                                                                      
Gensler 
11 East Madison Street
Suite 300 
Chicago, Illinois 60602 
USA

 

 <http://www.gensler.com/> Gensler.com |  <http://www.gensleron.com/> Blog |
<http://www.facebook.com/GenslerDesign> Facebook |
<http://www.twitter.com/GenslerOnCities> Twitter |
<http://www.youtube.com/GenslerTV> YouTube

 

What’s ahead for design and our clients?

Find out here:  <http://www.gensler.com/doc/gensler-design-forecast-2016>
Gensler Design Forecast 2016

 

From: Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of
via Bldg-sim
Sent: Thursday, December 15, 2016 11:17 AM
To: bldg-sim at lists.onebuilding.org <mailto:bldg-sim at lists.onebuilding.org> 
Subject: [Bldg-sim] LEED project - maximum limit allowed to simplified wall
azimuth.

 

Hello,

 

Does anyone know how to interpret “no more than 45 degrees” of exception 5.b
- table G3.1 (90.1-2007/2010/2013) ? : 

 

5.  Building Envelope

All components of the building envelope in the proposed design shall be
modeled as shown on architectural drawings or as built for existing building
envelopes. 

 

Exceptions:

b. Exterior surfaces whose azimuth orientation and tilt differ by no more
than 45 degrees and are otherwise the same may be described as either a
single surface or by using multipliers.

 

Because “no more than 45 degree” include 45 degree, does the exception still
apply if the azimuth of two walls is exactly 45 degrees? 

In other words, considering a LEED project, can a perfect octagonal building
shape be modeled as a square building (as long as they have the same floor
area and the 8 walls have a similar construction) ?

 

Thanks

 

Julien

____________________________________________________________________

Julien Dutel, ing., CEM, CMVP.

Direction des secteurs résidentiel, institutionnel et des affaires

Bureau de l'efficacité et de l'innovation énergétiques

Ministère de l'Énergie et des Ressources naturelles

5700, 4e Avenue Ouest, B-406

Québec (Québec)  G1H 6R1

Téléphone : 418 627-6379, poste 8060

Téléphone sans frais : 1 877 727-6655

Télécopieur : 418 643-5828

 <mailto:julien.dutel at mern.gouv.qc.ca> julien.dutel at mern.gouv.qc.ca

mern.gouv.qc.ca

 

 

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20161216/03d1ae2e/attachment-0001.html>


More information about the Bldg-sim mailing list