[Bldg-sim] ASHRAE 90.1 Window to Wall area definition
Jim Dirkes
jim at buildingperformanceteam.com
Thu Oct 15 11:19:12 PDT 2015
You people rock. I got way smarter in 5 minutes of reading your posts than
5 hours of scouring references.
On Thu, Oct 15, 2015 at 2:06 PM, Elizabeth Gillmor <
elizabeth at energetics-eng.com> wrote:
> That is a great point. Appendix G is different from the prescriptive
> requirements.
>
> The prescriptive requirements (and thus Energy Cost Budget method) allow
> you to count below-grade conditioned walls as per section 5.5.4.5 as part
> of your "gross wall area", while Appendix G specifically says above-grade
> walls only.
>
>
> *Elizabeth Gillmor PE, BEMP, LC, LEED AP*
>
> *e n e r g e t i c s **consulting engineers, llc*
> energetics-eng.com
> c 303.619.0091
>
> On Thu, Oct 15, 2015 at 11:38 AM, Shaun Martin <
> smartin at shaunmartinconsulting.com> wrote:
>
>> Page 213 of 90.1-2010 says “above-grade”
>>
>>
>>
>> Shaun
>>
>>
>>
>> Shaun Martin LEED-AP, BEMP
>>
>> Principal
>>
>> Shaun Martin Consulting
>>
>> #90 – 425 Carrall Street
>>
>> Vancouver, BC V6B 6E3
>>
>> p. 604-789-1095
>>
>>
>>
>>
>>
>>
>>
>> *From:* Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] *On
>> Behalf Of *Jones, Christopher
>> *Sent:* Thursday, October 15, 2015 10:15 AM
>> *To:* bldg-sim at lists.onebuilding.org
>> *Subject:* [Bldg-sim] ASHRAE 90.1 Window to Wall area definition
>>
>>
>>
>> I know this question has been asked before but I could not find a related
>> thread.
>>
>>
>>
>> 90.1 states that the WWR is based on the gross wall area and the
>> definition of gross wall area includes below ground walls as well as above
>> ground walls.. Including the below grade walls can make a significant
>> difference in the WWR for typical urban high rise buildings with a number
>> of below grade parking floors.
>>
>>
>>
>> Can someone confirm that the WWR calculation is based on above grade wall
>> area plus below grade wall area?
>>
>>
>>
>>
>>
>> [image: cid:image003.png at 01D09C46.E75BA0D0]
>>
>> *Christopher Jones,* P.Eng.
>> Senior Engineer
>>
>>
>>
>> *WSP Canada Inc.*
>>
>> 2300 Yonge Street, Suite 2300
>>
>> Toronto, ON M4P 1E4
>> T +1 416-644-4226
>>
>> F +1 416-487-9766
>>
>> C +1 416-697-0056
>>
>>
>>
>> www.wspgroup.com
>>
>>
>> ------------------------------
>>
>>
>> You are receiving this communication because you are listed as a current
>> WSP contact. Should you have any questions regarding WSP’s electronic
>> communications policy, please consult our Anti-Spam Commitment
>> www.wspgroup.com/casl. For any concern or if you believe you should not
>> be receiving this message, please forward this message to us at
>> caslcompliance at wspgroup.com so that we can promptly address your
>> request. This message is intended only for the use of the individual or
>> entity to which it is addressed, and may contain information which is
>> privileged, confidential, proprietary or exempt from disclosure under
>> applicable law. If you are not the intended recipient or the person
>> responsible for delivering the message to the intended recipient, you are
>> strictly prohibited from disclosing, distributing, copying or in any way
>> using this message. If you have received this communication in error,
>> please notify the sender, and destroy and delete any copies you may have
>> received.
>>
>> WSP provides professional land surveying services through the following
>> entities: WSP Surveys (AB) Limited Partnership and WSP Surveys (BC) Limited
>> Partnership
>>
>> _______________________________________________
>> Bldg-sim mailing list
>> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
>> To unsubscribe from this mailing list send a blank message to
>> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>>
>>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
--
James V Dirkes II, PE, BEMP, LEED AP
CEO/President
The Building Performance Team Inc.
1631 Acacia Dr, GR, Mi 49504
Direct: 616.450.8653
jim at buildingperformanceteam.com
Website <http://buildingperformanceteamcom>l LinkedIn
<https://www.linkedin.com/pub/jim-dirkes/7/444/413>
“…happiness is the joy produced in us by truth. To be truly happy means
coming to know how things really are, experiencing …reality in its ultimate
root…
What matters more to one’s happiness than getting more freedom and power is
the end toward which we order whatever freedom and power we have. Unless we
order ourselves to the truth, more freedom and more power will bring only
more unhappiness, examples of which abound.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20151015/92c7fbf4/attachment-0001.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 6574 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20151015/92c7fbf4/attachment-0003.png>
More information about the Bldg-sim
mailing list