[Bldg-sim] ASHRAE systems exception B interpretation
Elizabeth Gillmor
elizabeth at energetics-eng.com
Tue Oct 13 10:55:21 PDT 2015
If your building has two distinct uses (say, data center and office), I
would have two different baselines, one for each. Follow App G as if they
were each standalone buildings -- So for example, if each "baseline" system
is all 7 floors, I would have two system type 8's.
Then, within those baseline systems, if you still have deviant zones, you
could potentially pulll them out as separate PSZs, but I will bet that most
of the deviation goes away.
I have used this strategy for many mixed use buildings under LEED
(dorm/dining hall, hotel/office, Multifamily etc.), but it would be a good
idea to run it past your reviewer if you have that luxury.
Good luck!
*Elizabeth Gillmor PE, BEMP, LC, LEED AP*
*e n e r g e t i c s **consulting engineers, llc*
energetics-eng.com
c 303.619.0091
On Tue, Oct 13, 2015 at 10:49 AM, Veronica Ochoa <
veronica.ochoa at hurleypalmerflatt.com> wrote:
> Jim, thanks for your prompt response.
>
>
>
> The average peak load for my systems is as follows:
>
> Level -2: 578 W/m2
>
> Level -1: 392 W/m2
>
> Level 0: 186 W/m2
>
> Level 1: 83 W/m2
>
>
>
> Of the rooms in each system only 6 zones are within the 31W/m2 difference,
> therefore meeting the Sys8 criteria. The rest of the zones differ from the
> average cooling loads by anything from 50 W/m2 to 1,200 W/m2, leaving 44
> zones to fall under the System#4 (B) exception. My question is if I should
> have Sys#4 created for each zone, therefore ending up with 44 System#4’s
> which seems a bit excessive and if I could simplify this by creating a
> system per floor or per different setpoint groups?
>
>
>
> Thanks again,
>
>
>
> Veronica Ochoa
>
> Consultant
>
> *hurleypalmerflatt*
>
> *building* *sustainability*
>
> *d:*
>
> +44 20 7535 3750
>
> *t:*
>
> +44 20 7535 3100
>
> *e:*
>
> veronica.ochoa at hurleypalmerflatt.com
>
> View company email disclaimer at: http://www.hurleypalmerflatt.com/
> <http://www.hurleypalmerflatt.com/disclaimer.html>disclaimer
> <http://www.hurleypalmerflatt.com/disclaimer.html>.html
> <http://www.hurleypalmerflatt.com/disclaimer.html>
>
> *P Please** consider the environment before printing this **email**.*
>
> *From:* Jim Dirkes [mailto:jim at buildingperformanceteam.com]
> *Sent:* 13 October 2015 17:38
> *To:* Veronica Ochoa
> *Cc:* bldg-sim at lists.onebuilding.org
> *Subject:* Re: [Bldg-sim] ASHRAE systems exception B interpretation
>
>
>
> Veronica,
>
> I'm not sure if I understand your problem, but the exceptions for
> non-predominant HVAC sytems are based on
>
> "Peak thermal loads that *differ *by xx W/m2 or more from the average of
> other spaces..."
>
>
>
> Thus, if all zones are 30 W/m2, they should be modeled with the normal
> Baseline HVAC. If, however, one or more zones is 15W/m2 or 50 W/m2, you
> have justification for using Systems #3 or #4.
>
>
>
> On Tue, Oct 13, 2015 at 11:37 AM, Veronica Ochoa <
> veronica.ochoa at hurleypalmerflatt.com> wrote:
>
> Hi,
>
>
>
> I’m modelling a data center with 50 thermal zones for LEED EAp2/c1
> purposes. The baseline system determined based on area and building type is
> system 8. However when doing the load deviation average to determine
> suitability for System 4 (under exception B), all but 6 zones are greater
> than the 31 W/m2 of the averaged cooling load per system/floor. This means
> that I will have 6 zones (2.5% of total area) as system 8 and 44 zones as
> system 4. Do I need to follow the exception that says that each zone served
> by System 4 should be modelled as one zone per system?? I find this a bit
> too much… I was wondering if you can simplify this by grouping similar
> spacetypes by setpoints or floors and reduce the number of systems.
>
>
>
> Also, in the preliminary submission 100% of the zones were submitted as
> system 4, but this was noted by the USGBC reviewer as an error (as it was
> based on the average of the entire building not per system). As it has been
> now corrected and only 2.5% of the zones will be system 8, we are
> estimating the difference will be negligible. Would a narrative explaining
> this suffice? Has anyone been in this situation and how did you approach
> it?
>
>
>
> Many thanks in advance for your help,
>
> Veronica Ochoa
>
> Consultant
>
>
>
> *hurleypalmerflatt*
>
> *building* *sustainability*
>
>
>
> *d:*
>
> +44 20 7535 3750
>
> *t:*
>
> +44 20 7535 3100
>
> *e:*
>
> veronica.ochoa at hurleypalmerflatt.com
>
> [image: Description: Image removed by sender.]
> <https://retrofit.architectsjournal.co.uk/shortlist-2015>
> [image: Description: Image removed by sender. HPFWebsite]
> <http://www.hurleypalmerflatt.com/> [image: Description: Image removed by
> sender. LinkedIn] <https://uk.linkedin.com/company/hurleypalmerflatt> [image:
> Description: Image removed by sender. Twitter]
> <https://twitter.com/hpf_group> [image: Description: Image removed by
> sender. GooglePlus] <https://plus.google.com/105591062940781402373> [image:
> Description: Image removed by sender.]
> <https://www.flickr.com/photos/127827710@N02/> [image: Description: Image
> removed by sender. Facebook]
> <https://www.facebook.com/hurley.palmer.flatt?ref=hl> [image:
> Description: Image removed by sender. YouTube]
> <http://www.youtube.com/user/hurleypalmerflatt>
>
> View company email disclaimer at: http://www.hurleypalmerflatt.com/
> <http://www.hurleypalmerflatt.com/disclaimer.html>disclaimer
> <http://www.hurleypalmerflatt.com/disclaimer.html>.html
> <http://www.hurleypalmerflatt.com/disclaimer.html>
>
> *P** Please consider the environment before printing this email.*
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>
>
>
> --
>
> James V Dirkes II, PE, BEMP, LEED AP
> CEO/President
> The Building Performance Team Inc.
> 1631 Acacia Dr, GR, Mi 49504
>
> Direct: 616.450.8653
> jim at buildingperformanceteam.com
>
> Website <http://buildingperformanceteamcom>l LinkedIn
> <https://www.linkedin.com/pub/jim-dirkes/7/444/413>
>
> “…happiness is the joy produced in us by truth. To be truly happy means
> coming to know how things really are, experiencing …reality in its ultimate
> root…
> What matters more to one’s happiness than getting more freedom and power
> is the end toward which we order whatever freedom and power we have. Unless
> we order ourselves to the truth, more freedom and more power will bring
> only more unhappiness, examples of which abound.
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20151013/6ea1db08/attachment-0001.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1175 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20151013/6ea1db08/attachment-0006.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 344 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20151013/6ea1db08/attachment-0007.jpg>
More information about the Bldg-sim
mailing list