<div dir="ltr">If your building has two distinct uses (say, data center and office), I would have two different baselines, one for each. Follow App G as if they were each standalone buildings -- So for example, if each "baseline" system is all 7 floors, I would have two system type 8's. <div><br><div>Then, within those baseline systems, if you still have deviant zones, you could potentially pulll them out as separate PSZs, but I will bet that most of the deviation goes away.</div></div><div><br></div><div>I have used this strategy for many mixed use buildings under LEED (dorm/dining hall, hotel/office, Multifamily etc.), but it would be a good idea to run it past your reviewer if you have that luxury.</div><div><br></div><div>Good luck!</div></div><div class="gmail_extra"><br clear="all"><div><div class="gmail_signature"><div dir="ltr"><div><div dir="ltr"><div><div dir="ltr"><div><div dir="ltr"><div dir="ltr"><div dir="ltr"><b>Elizabeth Gillmor <font size="1">PE, BEMP, LC, LEED AP</font></b><div><br></div><div><span style="font-size:large;background-color:rgb(255,255,255)"><b><font color="#38761d" face="arial, helvetica, sans-serif">e n e r g e t i c s </font></b></span><b><font color="#38761d" face="arial, helvetica, sans-serif" size="2">consulting engineers, llc</font></b></div><div><font size="2" style="background-color:rgb(255,255,255)" color="#666666"><a href="http://energetics-eng.com" target="_blank">energetics-eng.com</a></font></div><div><span style="font-size:small;background-color:rgb(255,255,255)"><font color="#666666">c 303.619.0091</font></span><br></div></div></div></div></div></div></div></div></div></div></div></div>
<br><div class="gmail_quote">On Tue, Oct 13, 2015 at 10:49 AM, Veronica Ochoa <span dir="ltr"><<a href="mailto:veronica.ochoa@hurleypalmerflatt.com" target="_blank">veronica.ochoa@hurleypalmerflatt.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"><div lang="EN-GB" link="blue" vlink="purple"><div><p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d">Jim, thanks for your prompt response. <u></u><u></u></span></p><p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"><u></u> <u></u></span></p><p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d">The average peak load for my systems is as follows:<u></u><u></u></span></p><p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d">Level -2: 578 W/m2<u></u><u></u></span></p><p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d">Level -1: 392 W/m2<u></u><u></u></span></p><p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d">Level 0: 186 W/m2<u></u><u></u></span></p><p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d">Level 1: 83 W/m2<u></u><u></u></span></p><p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"><u></u> <u></u></span></p><p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d">Of the rooms in each system only 6 zones are within the 31W/m2 difference, therefore meeting the Sys8 criteria. The rest of the zones differ from the average cooling loads by anything from 50 W/m2 to 1,200 W/m2, leaving 44 zones to fall under the System#4 (B) exception. My question is if I should have Sys#4 created for each zone, therefore ending up with 44 System#4’s which seems a bit excessive and if I could simplify this by creating a system per floor or per different setpoint groups?<u></u><u></u></span></p><p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"><u></u> <u></u></span></p><p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d">Thanks again,<u></u><u></u></span></p><p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"><u></u> <u></u></span></p><table width="500" border="0"><colgroup><col></colgroup><tbody><tr><td><p style="FONT-FAMILY:Arial"><span style="FONT-SIZE:11pt;FONT-FAMILY:Arial">Veronica Ochoa</span></p></td></tr><tr><td><p style="FONT-FAMILY:Arial"><span style="FONT-SIZE:11pt;FONT-FAMILY:Arial">Consultant</span></p></td></tr></tbody></table><table style="WIDTH:170.15pt" cellspacing="0" cellpadding="0" width="227" border="0"><colgroup><col width="227"></colgroup><tbody><tr><td style="WIDTH:170.15pt;PADDING-BOTTOM:0cm;PADDING-TOP:0cm;PADDING-LEFT:0cm;PADDING-RIGHT:0cm" width="227" nowrap><p class="MsoNormal" style="FONT-FAMILY:Arial"><b><span style="FONT-SIZE:19.5pt;COLOR:#00aeef">hurleypalmerflatt</span></b></p></td></tr><tr><td style="WIDTH:170.15pt;PADDING-BOTTOM:0cm;PADDING-TOP:0cm;PADDING-LEFT:0cm;PADDING-RIGHT:0cm" valign="top" width="227" nowrap><p class="MsoNormal" style="FONT-FAMILY:Arial;TEXT-ALIGN:right;MARGIN-RIGHT:9.85pt" align="right"><b><i><span style="FONT-SIZE:9pt;FONT-FAMILY:"Arial","sans-serif";COLOR:#00aeef">building</span></i></b><span style="FONT-SIZE:9pt;FONT-FAMILY:"Arial","sans-serif";COLOR:#00aeef"> </span><b><span style="FONT-SIZE:9pt;FONT-FAMILY:"Arial","sans-serif";COLOR:#7dc242">sustainability</span></b></p></td></tr></tbody></table><table width="500" border="0"><colgroup><col width="30"><col></colgroup><tbody><tr><td width="30"><p style="FONT-SIZE:10pt;FONT-FAMILY:Arial"><b>d:</b></p></td><td><p style="FONT-SIZE:10pt;FONT-FAMILY:Arial"><a href="tel:%2B44%2020%207535%203750" value="+442075353750" target="_blank">+44 20 7535 3750</a></p></td></tr><tr><td width="30"><p style="FONT-SIZE:10pt;FONT-FAMILY:Arial"><b>t:</b></p></td><td><p style="FONT-SIZE:10pt;FONT-FAMILY:Arial"><a href="tel:%2B44%2020%207535%203100" value="+442075353100" target="_blank">+44 20 7535 3100</a></p></td></tr><tr><td width="30"><p style="FONT-SIZE:10pt;FONT-FAMILY:Arial"><b>e:</b></p></td><td><p style="FONT-SIZE:10pt;FONT-FAMILY:Arial"><a href="mailto:veronica.ochoa@hurleypalmerflatt.com" target="_blank">veronica.ochoa@hurleypalmerflatt.com</a></p></td></tr></tbody></table><table><colgroup><col></colgroup><tbody><tr><td><p style="FONT-FAMILY:Arial;MARGIN:6pt 0cm"><span style="font-size:9pt">View</span><span style="font-size:9pt;font-family:"Arial","sans-serif""> company email disclaimer at: <a href="http://www.hurleypalmerflatt.com/disclaimer.html" target="_blank"><font color="#0000ff">http://www.hurleypalmerflatt.com/</font></a></span><span style="font-size:9pt"><a href="http://www.hurleypalmerflatt.com/disclaimer.html" target="_blank"><font color="#0000ff">disclaimer</font></a></span><span style="font-size:9pt;font-family:"Arial","sans-serif""><a href="http://www.hurleypalmerflatt.com/disclaimer.html" target="_blank"><font color="#0000ff">.html</font></a></span></p><p style="MARGIN:6pt 0cm;font-family:Arial"><span style="font-size:9pt"><span style="font-size:10pt"><b><span style="font-size:10pt;color:#7dc242"><span style="font-family:Webdings">P</span> Please</span></b></span><span style="FONT-SIZE:10pt;FONT-FAMILY:"Arial","sans-serif""><b><span style="FONT-SIZE:10pt;FONT-FAMILY:"Arial","sans-serif";COLOR:#7dc242"> consider the environment before printing this </span></b></span><span style="font-size:10pt"><b><span style="font-size:10pt;color:#7dc242">email</span></b></span><span style="FONT-SIZE:10pt;FONT-FAMILY:"Arial","sans-serif""><b><span style="FONT-SIZE:10pt;FONT-FAMILY:"Arial","sans-serif";COLOR:#7dc242">.</span></b></span></span></p></td></tr></tbody></table><p class="MsoNormal"><b><span lang="EN-US" style="font-size:10.0pt;font-family:"Tahoma","sans-serif"">From:</span></b><span lang="EN-US" style="font-size:10.0pt;font-family:"Tahoma","sans-serif""> Jim Dirkes [mailto:<a href="mailto:jim@buildingperformanceteam.com" target="_blank">jim@buildingperformanceteam.com</a>] <br><b>Sent:</b> 13 October 2015 17:38<br><b>To:</b> Veronica Ochoa<br><b>Cc:</b> <a href="mailto:bldg-sim@lists.onebuilding.org" target="_blank">bldg-sim@lists.onebuilding.org</a><br><b>Subject:</b> Re: [Bldg-sim] ASHRAE systems exception B interpretation<u></u><u></u></span></p><p class="MsoNormal"><u></u> <u></u></p><div><div><p class="MsoNormal"><span style="font-size:18.0pt;color:#b45f06">Veronica,<u></u><u></u></span></p></div><div><p class="MsoNormal"><span style="font-size:18.0pt;color:#b45f06">I'm not sure if I understand your problem, but the exceptions for non-predominant HVAC sytems are based on<u></u><u></u></span></p></div><div><div><p class="MsoNormal"><span style="font-size:18.0pt;color:#b45f06">"Peak thermal loads that <b><u>differ </u></b>by xx W/m2 or more from the average of other spaces..."<u></u><u></u></span></p></div><div><p class="MsoNormal"><span style="font-size:18.0pt;color:#b45f06"><u></u> <u></u></span></p></div><div><p class="MsoNormal"><span style="font-size:18.0pt;color:#b45f06">Thus, if all zones are 30 W/m2, they should be modeled with the normal Baseline HVAC. If, however, one or more zones is 15W/m2 or 50 W/m2, you have justification for using Systems #3 or #4.<u></u><u></u></span></p></div></div></div><div><p class="MsoNormal"><u></u> <u></u></p><div><p class="MsoNormal">On Tue, Oct 13, 2015 at 11:37 AM, Veronica Ochoa <<a href="mailto:veronica.ochoa@hurleypalmerflatt.com" target="_blank">veronica.ochoa@hurleypalmerflatt.com</a>> wrote:<u></u><u></u></p><div><div><p class="MsoNormal">Hi,<u></u><u></u></p><p class="MsoNormal"> <u></u><u></u></p><p class="MsoNormal">I’m modelling a data center with 50 thermal zones for LEED EAp2/c1 purposes. The baseline system determined based on area and building type is system 8. However when doing the load deviation average to determine suitability for System 4 (under exception B), all but 6 zones are greater than the 31 W/m2 of the averaged cooling load per system/floor. This means that I will have 6 zones (2.5% of total area) as system 8 and 44 zones as system 4. Do I need to follow the exception that says that each zone served by System 4 should be modelled as one zone per system?? I find this a bit too much… I was wondering if you can simplify this by grouping similar spacetypes by setpoints or floors and reduce the number of systems. <u></u><u></u></p><p class="MsoNormal"> <u></u><u></u></p><p class="MsoNormal">Also, in the preliminary submission 100% of the zones were submitted as system 4, but this was noted by the USGBC reviewer as an error (as it was based on the average of the entire building not per system). As it has been now corrected and only 2.5% of the zones will be system 8, we are estimating the difference will be negligible. Would a narrative explaining this suffice? Has anyone been in this situation and how did you approach it? <u></u><u></u></p><p class="MsoNormal"> <u></u><u></u></p><p class="MsoNormal">Many thanks in advance for your help,<u></u><u></u></p></div><table border="0" cellpadding="0" width="500" style="width:375.0pt"><tbody><tr><td style="padding:.75pt .75pt .75pt .75pt"><p><span style="font-size:11.0pt;font-family:"Arial","sans-serif"">Veronica Ochoa</span><span style="font-family:"Arial","sans-serif""><u></u><u></u></span></p></td></tr><tr><td style="padding:.75pt .75pt .75pt .75pt"><p><span style="font-size:11.0pt;font-family:"Arial","sans-serif"">Consultant</span><span style="font-family:"Arial","sans-serif""><u></u><u></u></span></p></td></tr></tbody></table><p class="MsoNormal"><span><u></u> <u></u></span></p><table border="0" cellspacing="0" cellpadding="0" width="227" style="width:170.15pt"><tbody><tr><td width="227" nowrap style="width:170.15pt;padding:0cm 0cm 0cm 0cm"><p class="MsoNormal"><b><span style="font-size:19.5pt;font-family:"Arial","sans-serif";color:#00aeef">hurleypalmerflatt</span></b><span style="font-family:"Arial","sans-serif""><u></u><u></u></span></p></td></tr><tr><td width="227" nowrap valign="top" style="width:170.15pt;padding:0cm 0cm 0cm 0cm"><p class="MsoNormal" align="right" style="margin-right:9.85pt;text-align:right"><b><i><span style="font-size:9.0pt;font-family:"Arial","sans-serif";color:#00aeef">building</span></i></b><span style="font-size:9.0pt;font-family:"Arial","sans-serif";color:#00aeef"> </span><b><span style="font-size:9.0pt;font-family:"Arial","sans-serif";color:#7dc242">sustainability</span></b><span style="font-family:"Arial","sans-serif""><u></u><u></u></span></p></td></tr></tbody></table><p class="MsoNormal"><span><u></u> <u></u></span></p><table border="0" cellpadding="0" width="500" style="width:375.0pt"><tbody><tr><td width="30" style="width:22.5pt;padding:.75pt .75pt .75pt .75pt"><p><b><span style="font-size:10.0pt;font-family:"Arial","sans-serif"">d:</span></b><span style="font-size:10.0pt;font-family:"Arial","sans-serif""><u></u><u></u></span></p></td><td style="padding:.75pt .75pt .75pt .75pt"><p><span style="font-size:10.0pt;font-family:"Arial","sans-serif""><a href="tel:%2B44%2020%207535%203750" target="_blank">+44 20 7535 3750</a><u></u><u></u></span></p></td></tr><tr><td width="30" style="width:22.5pt;padding:.75pt .75pt .75pt .75pt"><p><b><span style="font-size:10.0pt;font-family:"Arial","sans-serif"">t:</span></b><span style="font-size:10.0pt;font-family:"Arial","sans-serif""><u></u><u></u></span></p></td><td style="padding:.75pt .75pt .75pt .75pt"><p><span style="font-size:10.0pt;font-family:"Arial","sans-serif""><a href="tel:%2B44%2020%207535%203100" target="_blank">+44 20 7535 3100</a><u></u><u></u></span></p></td></tr><tr><td width="30" style="width:22.5pt;padding:.75pt .75pt .75pt .75pt"><p><b><span style="font-size:10.0pt;font-family:"Arial","sans-serif"">e:</span></b><span style="font-size:10.0pt;font-family:"Arial","sans-serif""><u></u><u></u></span></p></td><td style="padding:.75pt .75pt .75pt .75pt"><p><span style="font-size:10.0pt;font-family:"Arial","sans-serif""><a href="mailto:veronica.ochoa@hurleypalmerflatt.com" target="_blank">veronica.ochoa@hurleypalmerflatt.com</a><u></u><u></u></span></p></td></tr></tbody></table><p><a href="https://retrofit.architectsjournal.co.uk/shortlist-2015" target="_blank"><span style="font-family:"Arial","sans-serif";border:solid windowtext 1.0pt;padding:0cm;text-decoration:none"><img border="0" width="600" height="120" src="cid:image001.jpg@01D105DF.7AB47DF0" alt="Description: Image removed by sender."></span></a><span style="font-family:"Arial","sans-serif""><br></span><a href="http://www.hurleypalmerflatt.com/" target="_blank"><span style="font-family:"Arial","sans-serif";border:solid windowtext 1.0pt;padding:0cm;text-decoration:none"><img border="0" width="30" height="30" src="cid:image002.jpg@01D105DF.7AB47DF0" alt="Description: Image removed by sender. HPFWebsite"></span></a><span style="font-family:"Arial","sans-serif""> </span><a href="https://uk.linkedin.com/company/hurleypalmerflatt" target="_blank"><span style="font-family:"Arial","sans-serif";border:solid windowtext 1.0pt;padding:0cm;text-decoration:none"><img border="0" width="30" height="30" src="cid:image002.jpg@01D105DF.7AB47DF0" alt="Description: Image removed by sender. LinkedIn"></span></a><span style="font-family:"Arial","sans-serif""> </span><a href="https://twitter.com/hpf_group" target="_blank"><span style="font-family:"Arial","sans-serif";border:solid windowtext 1.0pt;padding:0cm;text-decoration:none"><img border="0" width="30" height="30" src="cid:image002.jpg@01D105DF.7AB47DF0" alt="Description: Image removed by sender. Twitter"></span></a><span style="font-family:"Arial","sans-serif""> </span><a href="https://plus.google.com/105591062940781402373" target="_blank"><span style="font-family:"Arial","sans-serif";border:solid windowtext 1.0pt;padding:0cm;text-decoration:none"><img border="0" width="30" height="30" src="cid:image002.jpg@01D105DF.7AB47DF0" alt="Description: Image removed by sender. GooglePlus"></span></a><span style="font-family:"Arial","sans-serif""> </span><a href="https://www.flickr.com/photos/127827710@N02/" target="_blank"><span style="font-family:"Arial","sans-serif";border:solid windowtext 1.0pt;padding:0cm;text-decoration:none"><img border="0" width="30" height="30" src="cid:image002.jpg@01D105DF.7AB47DF0" alt="Description: Image removed by sender."></span></a><span style="font-family:"Arial","sans-serif""> </span><a href="https://www.facebook.com/hurley.palmer.flatt?ref=hl" target="_blank"><span style="font-family:"Arial","sans-serif";border:solid windowtext 1.0pt;padding:0cm;text-decoration:none"><img border="0" width="30" height="30" src="cid:image002.jpg@01D105DF.7AB47DF0" alt="Description: Image removed by sender. Facebook"></span></a><span style="font-family:"Arial","sans-serif""> </span><a href="http://www.youtube.com/user/hurleypalmerflatt" target="_blank"><span style="font-family:"Arial","sans-serif";border:solid windowtext 1.0pt;padding:0cm;text-decoration:none"><img border="0" width="30" height="30" src="cid:image002.jpg@01D105DF.7AB47DF0" alt="Description: Image removed by sender. YouTube"></span></a><span style="font-family:"Arial","sans-serif""><u></u><u></u></span></p><table border="0" cellpadding="0"><tbody><tr><td style="padding:.75pt .75pt .75pt .75pt"><p style="margin-right:0cm;margin-bottom:6.0pt;margin-left:0cm"><span style="font-size:9.0pt;font-family:"Arial","sans-serif"">View company email disclaimer at: <a href="http://www.hurleypalmerflatt.com/disclaimer.html" target="_blank">http://www.hurleypalmerflatt.com/</a><a href="http://www.hurleypalmerflatt.com/disclaimer.html" target="_blank">disclaimer</a><a href="http://www.hurleypalmerflatt.com/disclaimer.html" target="_blank">.html</a></span><span style="font-family:"Arial","sans-serif""><u></u><u></u></span></p><p style="margin-right:0cm;margin-bottom:6.0pt;margin-left:0cm"><b><span style="font-size:10.0pt;font-family:Webdings;color:#7dc242">P</span></b><b><span style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#7dc242"> Please consider the environment before printing this email.</span></b><span style="font-family:"Arial","sans-serif""><u></u><u></u></span></p></td></tr></tbody></table></div><p class="MsoNormal" style="margin-bottom:12.0pt"><br>_______________________________________________<br>Bldg-sim mailing list<br><a href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a><br>To unsubscribe from this mailing list send a blank message to <a href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a><u></u><u></u></p></div><p class="MsoNormal"><br><br clear="all"><u></u><u></u></p><div><p class="MsoNormal"><u></u> <u></u></p></div><p class="MsoNormal">-- <u></u><u></u></p><div><div><div><div><div><div><div><div><div><div><div><div><div><div><div><div><p class="MsoNormal">James V Dirkes II, PE, BEMP, LEED AP<br>CEO/President<br>The Building Performance Team Inc.<br>1631 Acacia Dr, GR, Mi 49504<br><br>Direct: <a href="tel:616.450.8653" value="+16164508653" target="_blank">616.450.8653</a><br><a href="mailto:jim@buildingperformanceteam.com" target="_blank">jim@buildingperformanceteam.com</a><br><br><a href="http://buildingperformanceteamcom" target="_blank">Website </a>l <a href="https://www.linkedin.com/pub/jim-dirkes/7/444/413" target="_blank">LinkedIn</a><u></u><u></u></p><p style="margin-bottom:6.0pt;text-autospace:none"><span style="font-size:10.0pt;font-family:"Calibri","sans-serif";color:blue">“…happiness is the joy produced in us by truth. To be truly happy means coming to know how things really are, experiencing …reality in its ultimate root…<br>What matters more to one’s happiness than getting more freedom and power is the end toward which we order whatever freedom and power we have. Unless we order ourselves to the truth, more freedom and more power will bring only more unhappiness, examples of which abound.</span><u></u><u></u></p></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div><br>_______________________________________________<br>
Bldg-sim mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org" rel="noreferrer" target="_blank">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br></div>