[Bldg-sim] 90.1 - lighting - Additional interior lighting power using non-mandatory control
Elizabeth Gillmor
elizabeth at energetics-eng.com
Mon Nov 23 10:17:32 PST 2015
Lighting Power Under Control = the total lighting power (W) that is
controlled by whatever control factor is applicable.
Control Factor is a unitless percentage. However, how you use it is going
to depend on what protocol you are following. Appendix G and Energy Cost
Budget Method both treat CF differently from the prescriptive code.
Prescriptive code uses Control Factor as an additional allowance to your
baseline. Appendix G and Energy Cost Budget Method do not; instead you
would have the option to either model controls directly (such as with
daylighting controls), or to apply the Control Factor as a % LPD reduction
to your Proposed Lighting Power Under Control (using only the watts
controlled by that particular control strategy).
So if I was an electrical engineer filling out COMCheck for the
prescriptive code, I would use Answer B above. But neither would be
correct for Appendix G or code compliance energy modeling.
Cheers,
Elizabeth
*Elizabeth Gillmor PE, BEMP, LC, LEED AP*
*e n e r g e t i c s **consulting engineers, llc*
energetics-eng.com
c 303.619.0091
On Mon, Nov 23, 2015 at 10:47 AM, <Julien.Dutel at mern.gouv.qc.ca> wrote:
> Hello,
>
>
>
> Does anybody have to deal with section 9.6.3 from 90.1 - 2013 :
> “Additional interior lighting power using non-mandatory control”? I find it
> unclear ( it’s pretty much the same section than section 9.6.2 c in the
> 2010 version).
>
>
>
> It says that :
>
> Additional Interior Lighting Power Allowance =
>
> Lighting Power Under Control x Control Factor
>
>
>
> 1) I have a hard time to figure it out what is “Lighting Power Under
> Control”, is it a power or a surface ?
>
> According to section 9.6.3 it is a power: “the total input watts of all
> lamps being controlled” by specific control, but according to example 9-MM
> of 90.1 – 2013 User’s Manual, it’s much more the surface (in m2 or ft2)
> lighted by all lamps being controlled by specific control.
>
>
>
> 2) What is “Control Factors”, a unitless factor or a LPD in W/m2 ?
>
> According to section 9.6.3 it’s a unitlessfactor, but according to example
> 9-MM of 90.1 – 2013 User’s Manual, it’s much more a LPD (see note).
>
>
>
> 3) In a theoretical
> <https://www.google.ca/search?espv=2&biw=1219&bih=745&q=theoretical&spell=1&sa=X&ved=0ahUKEwiTzuDniafJAhVBkh4KHQD2AQsQBQgYKAA>
> example following section 9.6.3 of 90.1-2013 what should be the power
> allowance for an 550 ft2 open office in which there is a 150 ft2 with a
> manual diming control (Control Factor = 0.05 according to table 9.6.3 and
> maximum LPD for an open office is 0.98 W/ft2 LPD according to section
> 9.6.1) ? Is it answer A, B, or another one ?
>
> [image: 400 ft2 500 W installed ,150 ft2 180 W inst.]
>
>
>
>
>
>
>
>
>
>
>
> A) Power allowance = (550 ft2 x 0.98 W/ft2) + (150 ft2 x 0.98 W/ft2 x 0.05)
> = 539 + 7.35 = 546.35 W
>
> B) Power allowance = (550 ft2 x 0.98 W/ft2) + (180 W x 0.05) = 539 +
> 9 = 548 W
>
>
>
> Note about example 9-MM of 90.1 – 2013 User’s Manual: this example is full
> of mistakes.
>
> · It refers to example 9-JJ instead of 9-LL
>
> · The answer mentions an allowance without control of 450,000 W,
> so with a 500,000 ft2 open office that’s mean a 0.90 W/ft2 LPD. But with
> the space-by-space method section 9.6.1 allows a 0.98 W/ft2 LPD, so the
> allowance without control should be 459,184 W
>
> · The use of the control factors is unclear
>
>
>
>
>
> Any help on that would be appreciated
>
> Thanks,
>
>
>
>
>
>
>
> *Julien Dutel,* ing., CEM, CMVP*.*
>
> Direction des secteurs résidentiel, institutionnel et des affaires
>
> Bureau de l'efficacité et de l'innovation énergétiques
>
> Ministère des Ressources naturelles
>
> 5700, 4e Avenue Ouest, B-406
>
> Québec (Québec) G1H 6R1
>
> Téléphone : 418 627-6379, poste 8060
>
> Téléphone sans frais : 1 877 727-6655
>
> Télécopieur : 418 643-5828
>
> http://www.efficaciteenergetique.mrn.gouv.qc.ca
>
>
>
> *AVIS DE CONFIDENTIALITÉ*
>
> *Ce message est confidentiel. Il est à l'usage exclusif du destinataire
> ci-dessus. Si vous n'êtes pas le destinataire visé ou une personne
> autorisée à lui remettre cette communication, vous êtes par la présente
> avisé qu'il est expressément interdit* *de le diffuser, de le distribuer,
> de le reproduire,* *d'en dévoiler la teneur ou de prendre quelque mesure
> fondée sur l'information qui y est contenue. S’il vous a été envoyé par
> erreur, veuillez en informer immédiatement l'expéditeur par téléphone au
> 418 627-6379 <418%20627-6379> et détruire ce message ainsi que toute copie
> de celui-ci.*
>
> *P* Devez-vous vraiment imprimer ce courriel? Si oui, pensez
> l’imprimer recto-verso!
>
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20151123/59416d3d/attachment-0001.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 2098 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20151123/59416d3d/attachment-0003.png>
More information about the Bldg-sim
mailing list