[Bldg-sim] TRNSYS: LIGHTING

Fred Betz fbetz at aeieng.com
Tue May 1 08:15:14 PDT 2012


Francesco,

Yes, you’d have to export the geometry from sketchup into a format that radiance can read such as .3ds.

One concern is that the TRNSYS model won’t have all the internal geometry that Radiance expects such as light shelves, etc. Adjusting geometry within Radiance is very complex as its all based on editing a text file.

Therefore, create a separate copy of your TRNSYS Sketchup model, and then add any objects that have an effect on lighting (trees, other buildings, etc. ). Then export to .3ds so that can be imported into Radiance.

Good luck.

Fred


Fred Betz  PhD., LEED AP
Sustainable Systems Analyst



AEI | AFFILIATED ENGINEERS, INC.
5802 Research Park Blvd. | Madison, WI  53719

P: 608.236.1175 | F: 608.238.2614
fbetz at aeieng.com<mailto:fbetz at aeieng.com>  |  www.aeieng.com<http://www.aeieng.com/>



From: francesco.passerini at inwind.it [mailto:francesco.passerini at inwind.it]
Sent: Tuesday, May 01, 2012 10:10 AM
To: Fred Betz; bldg-sim at lists.onebuilding.org
Subject: R: RE: [Bldg-sim] TRNSYS: LIGHTING


Hello Fred

Thank you for your message.

Do you use the same geometrical model for TRNSYS and Radiance, e.g. a model created with Google SketchUp?

Best Regards

Francesco Passerini


----Messaggio originale----
Da: fbetz at aeieng.com<mailto:fbetz at aeieng.com>
Data: 01/05/2012 16.27
A: "francesco.passerini at inwind.it<mailto:francesco.passerini at inwind.it>"<francesco.passerini at inwind.it<mailto:francesco.passerini at inwind.it>>, "bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>"<bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>>
Ogg: RE: [Bldg-sim] TRNSYS: LIGHTING
Francesco,

I don’t believe TRNSYS can model daylighting, but I would email the TRNSYS list to be sure, trnsys-users at cae.wisc.edu<mailto:trnsys-users at cae.wisc.edu>.

What we do is model the daylighting using Radiance/Daysim, and then integrate those results into TRNSYS by adjusting the artificial lighting schedule.

In general it is difficult to model ASHRAE 90.1 system types in TRNSYS, but doable. Also, I would discourage you from modeling more than 20-30 zones as it gets cumbersome in TRNSYS.

We typically use TRNSYS to design complex systems, and then adjust other software such as eQuest to match for compliance modeling. Sometimes an exceptional calculation is required when the changes are just too much for eQuest.

Our experience is that model reviewers don’t understand TRNSYS as it doesn’t provide “canned” reports like TRACE or eQuest that are familiar to them.

Good luck.

Fred


Fred Betz  PhD., LEED AP
Sustainable Systems Analyst



AEI | AFFILIATED ENGINEERS, INC.
5802 Research Park Blvd. | Madison, WI  53719

P: 608.236.1175 | F: 608.238.2614
fbetz at aeieng.com<mailto:fbetz at aeieng.com>  |  www.aeieng.com<http://www.aeieng.com/>



From: francesco.passerini at inwind.it<mailto:francesco.passerini at inwind.it> [mailto:francesco.passerini at inwind.it]
Sent: Monday, April 30, 2012 11:26 AM
To: bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Subject: [Bldg-sim] TRNSYS: LIGHTING

Hello.
I attended a course about TRNSYS v.17 and probably my research group will buy it. Our idea is to use TRNSYS for simulations according to ASHRAE 90.1 annex G (LEED certification refers to that method).
Can TRNSYS v.17 calculate the internal illuminance? It would be useful to model lighting control systems, e.g. if the artificial lighting is switched off when solar lighting provides a determined level of internal illuminance (lux).
Best Regards