[Bldg-sim] Baseline System type exceptions
Cheney
chenyu73 at gmail.com
Wed Oct 26 16:05:46 PDT 2011
Hi,
*1. I doubt you can understand exception b in this manner. My understanding
is that this exception should only be applied to individual rooms which may
need individual HVAC system due to its 'abnormal' thermal loads or schedules
other than the space at the same floor, for example, server rooms, telecom
rooms, small laboratory spaces, auditoriums and security rooms among office
spaces.*
*2. Probably you should further clarify how you can get 50 btu/h-sqft for
perimeter zones and 10 btu/h-sqft for inner zones. Is this 10 btu/h-sqft
heating peak load for inner zones?*
Regards,
Cheney
LinkedIN @ http://ca.linkedin.com/pub/yu-cheney-chen/27/637/72b
On Wed, Oct 26, 2011 at 2:45 PM, Dahlstrom, Aaron
<ADahlstrom at in-posse.com>wrote:
> If the only distinguishing feature driving the load is envelope, and the
> zones are on the same system in the design, I think I would keep them all on
> System 7 in the baseline.****
>
> ** **
>
> I tend to use G3.1.1 exception b only when there is a good argument for why
> the building would be designed that way.****
>
> Very unlikely that a 7-story office building would use single zone
> air-cooled systems for either core or interior zones on each floor.****
>
> ** **
>
> For additional certainty on the approach you could try an administrative
> request to USGBC or informal interpretation request to ASHRAE 90.1
> committee.****
>
> ** **
>
> *Aaron Dahlstrom , PE, LEED® AP*****
>
> *In P**o**sse* – A subsidiary of *AKF*| 1500 Walnut Street, Suite 1414,
> Philadelphia, PA 19102 ****
>
> d: 215-282-6753| m: 267-507-5470| In Posse: 215-282-6800| AKF:
> 215-735-7290****
>
> e: ADahlstrom at in-posse.com | in posse web: www.in-posse.com | akf web:
> www.akfgroup.com****
>
> ****
>
> ****
>
> ****
>
> *From:* bldg-sim-bounces at lists.onebuilding.org [mailto:
> bldg-sim-bounces at lists.onebuilding.org] *On Behalf Of *bldgsim bldgsim
> *Sent:* Wednesday, October 26, 2011 5:24 PM
> *To:* bldg-sim at lists.onebuilding.org
> *Subject:* [Bldg-sim] Baseline System type exceptions****
>
> ** **
>
> I have an office building that I'm trying to model per ASHRAE 90.1-2007
> appendix G, with 5 core zones and 5 perimeter zones for a total of 10 zones
> (it has way more than 10 zones but to make it simpler we'll say 10). Because
> the office building is heated with natural gas and is more than 5 stories it
> is Baseline system 7. This office building has a lot of glass that isn't the
> best performance glazing. Therefore the load on the 5 perimeter zones is 50
> btu/h-sqft and the load on the 5 core zones is 10 btu/h-sqft, for an average
> of 30 btu/h-sqft. ASHRAE 90.1-2007 G3.1.1 exception b states that:
>
> "If the baseline HVAC system type is 5, 6, 7, or 8, use separate
> single-zone systems conforming with the requirements of System 3 or System 4
> (depending on building heating source) for any spaces that have occupancy or
> process loads or schedules that differ significantly from the rest of the
> building. *Peak thermal loads that differ by 10 Btu/h-ft2 or more from the
> average of other spaces served by the system* or schedules that differ by
> more than 40 equivalent full-load hours per week from other spaces served by
> the system are considered to differ significantly."
>
> Since all my spaces vary by 10 btu/h-sqft for the average (30 btu/h-sqft)
> I'm curious what to do. I can see a few options so far, but I want to know
> what your experience has been.****
>
> - Put all the zones in the building on system 3, because they all vary
> by 10 btu/h-sqft from the average.****
> - Put all the perimeter zones on system 3, making the core zones fall
> within a 10 btu/h-sqft average.****
> - Put all the core zones on system 3, making the perimeter zones fall
> within a 10 btu/h-sqft average.****
> - Put a few of either the core or perimeter zones on system 3 until the
> average of the others falls within range, but how do I pick which zones?
> ****
>
> Any ideas?****
>
> This e-mail may contain information that is confidential, privileged or
> otherwise protected from disclosure. If you are not an intended recipient of
> this e-mail, do not duplicate or redistribute it by any means. Please delete
> it and any attachments and notify the sender that you have received it in
> error. Unintended recipients are prohibited from taking action on the basis
> of information in this e-mail. E-mail messages may contain computer viruses
> or other defects, may not be accurately replicated on other systems, or may
> be intercepted, deleted or interfered without the knowledge of the sender or
> the intended recipient. If you are not comfortable with the risks associated
> with e-mail messages, you may decide not to use e-mail to communicate with
> In Posse.
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20111026/8b566ac3/attachment.htm>
More information about the Bldg-sim
mailing list