[Bldg-sim] Appendix G - Fan power
Tyler Thumma
tyler at energyopportunities.com
Tue Mar 8 10:14:08 PST 2011
That is correct. This issue has been fixed in the updated spreadsheet
attached.
Tyler Thumma, EIT, LEED AP
Energy Opportunities, Inc/a 7group Company
1200 E Camping Area Rd, Wellsville, PA 17365
thumma at sevengroup.com
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Rosenberg,
Michael I
Sent: Tuesday, March 08, 2011 12:38 PM
To: jtorres-coto at mbo1.com; 'Sami, Vikram';
'bldg-sim at lists.onebuilding.org'
Subject: Re: [Bldg-sim] Appendix G - Fan power
A word of caution if you are using this 2007 tab of this spreadsheet.
The pressure credit is being calculated for the entire supply fan cfm.
It should only be calculated for the design airflow through the device.
While these two airflows can be the same, often they are not.
Mike
__________________________
Michael Rosenberg, CEM, LEED AP
Senior Research Scientist
ENERGY & ENVIRONMENT DIRECTORATE
Pacific Northwest National Laboratory
2032 Todd Street
Eugene, OR 97405
(541) 844-1960
michael.rosenberg at pnl.gov <mailto:michael.rosenberg at pnl.gov>
www.pnl.gov <http://www.pnl.gov/>
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Jorge
Torres-Coto
Sent: Tuesday, March 08, 2011 8:29 AM
To: 'Sami, Vikram'; 'bldg-sim at lists.onebuilding.org'
Subject: Re: [Bldg-sim] Appendix G - Fan power
Yes that is correct, the dot means multiplication.
The Excel calculator will come in very handy (credit to 7 Group)
Jorge E. Torres Coto
4830 Viewridge Ave.
San Diego, CA 92123
p 858.751.0933
f 858.751.0937
c 858.688.6088
________________________________
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Sami,
Vikram
Sent: Tuesday, March 08, 2011 8:11 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Appendix G - Fan power
Does the dot in the equation indicate multiplication? So should the
equation read CFMS X 0.0013 + A?
The reason I am confused is that they use X in other places.
Thanks in advance
We've moved! Please note our new address.
Vikram Sami, LEED AP BD+C
Sustainable Design Analyst
1315 Peachtree St. NE, Atlanta, GA 30309
t: 404-443-7462 f: 404.892.5823 e: vikram.sami at perkinswill.com
www.perkinswill.com <http://www.perkinswill.com/>
Perkins+Will. Ideas + buildings that honor the broader goals of society
Perkins+Will is carbon neutral. Learn more about our 2030 Challenge
Estimating + Evaluation <http://2030e2.perkinswill.com/> tool for
fossil fuel free buildings
This email and any files transmitted with it are confidential and
intended solely for the addressee. If you are not the named addressee
you should not disseminate, distribute, copy, or alter this email.
________________________________
No virus found in this message.
Checked by AVG - www.avg.com
Version: 10.0.1204 / Virus Database: 1497/3490 - Release Date: 03/08/11
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110308/47e5abeb/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1226 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110308/47e5abeb/attachment.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 14532 bytes
Desc: image002.gif
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110308/47e5abeb/attachment.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 47671 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110308/47e5abeb/attachment-0001.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: 7group Appendix G Fan Power Calculator.xls
Type: application/vnd.ms-excel
Size: 130560 bytes
Desc: 7group Appendix G Fan Power Calculator.xls
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110308/47e5abeb/attachment.xls>
More information about the Bldg-sim
mailing list