A word of caution if you are using this 2007 tab of this spreadsheet. The pressure credit is being calculated for the entire supply fan cfm. It should only be calculated for the design airflow through the device. While these two airflows can be the same, often they are not.
Mike
__________________________
Michael Rosenberg, CEM, LEED AP
Senior Research Scientist
ENERGY & ENVIRONMENT DIRECTORATE
Pacific Northwest National Laboratory
2032 Todd Street
Eugene, OR 97405
(541) 844-1960
michael.rosenberg at pnl.gov<mailto:michael.rosenberg at pnl.gov>
www.pnl.gov<http://www.pnl.gov/>
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Jorge Torres-Coto
Sent: Tuesday, March 08, 2011 8:29 AM
To: 'Sami, Vikram'; 'bldg-sim at lists.onebuilding.org'
Subject: Re: [Bldg-sim] Appendix G - Fan power
Yes that is correct, the dot means multiplication.
The Excel calculator will come in very handy (credit to 7 Group)
Jorge E. Torres Coto [cid:image001.jpg at 01CBDD74.8C8AC2C0]
4830 Viewridge Ave.
San Diego, CA 92123
p 858.751.0933
f 858.751.0937
c 858.688.6088
[cid:image002.gif at 01CBDD74.8C8AC2C0]
________________________________
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Sami, Vikram
Sent: Tuesday, March 08, 2011 8:11 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Appendix G - Fan power
Does the dot in the equation indicate multiplication? So should the equation read CFMS X 0.0013 + A?
The reason I am confused is that they use X in other places.
[cid:image003.jpg at 01CBDD74.8C8AC2C0]
Thanks in advance
We've moved! Please note our new address.
Vikram Sami, LEED AP BD+C
Sustainable Design Analyst
1315 Peachtree St. NE, Atlanta, GA 30309
t: 404-443-7462 f: 404.892.5823 e: vikram.sami at perkinswill.com<mailto:vikram.sami at perkinswill.com> www.perkinswill.com<http://www.perkinswill.com/>
Perkins+Will. Ideas + buildings that honor the broader goals of society
Perkins+Will is carbon neutral. Learn more about our 2030 Challenge Estimating + Evaluation<http://2030e2.perkinswill.com/> tool for fossil fuel free buildings
This email and any files transmitted with it are confidential and intended solely for the addressee. If you are not the named addressee you should not disseminate, distribute, copy, or alter this email.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110308/94fa77ef/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1226 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110308/94fa77ef/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.gif
Type: image/gif
Size: 14532 bytes
Desc: image002.gif
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110308/94fa77ef/attachment.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 47671 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110308/94fa77ef/attachment-0001.jpg>
More information about the Bldg-sim
mailing list