Hi Karen,

My understanding is that the statement will apply beyond system 1-2.
Whenever a HVAC system is defined in EER, it is necessary to separate supply
fan energy from cooling energy.

Supply fan energy = (gross cooling - net cooling)/3.413

and

COP = gross cooling /[(total input power - fan power) x 3.413]

Does it make sense?


Regards,

Cheney