<div>My understanding is that the statement will apply beyond system 1-2. Whenever a HVAC system is defined in EER, it is necessary to separate supply fan energy from cooling energy. </div>
<div> </div>
<div>Supply fan energy = (gross cooling - net cooling)/3.413 </div>
<div> </div>
<div>and </div>
<div> </div>
<div>COP = gross cooling /[(total input power - fan power) x 3.413] </div>