[Bldg-sim] Is there a point to "virtual partitions"?

Mehta, Gaurav Gaurav.Mehta at stantec.com
Wed Jan 26 08:58:00 PST 2011


Chris,

Please see the responses below.

Gaurav Mehta, LEED® AP BD+C
Sustainable Building Analyst
Stantec
1932 First Avenue Suite 307
Seattle WA 98101
Ph: (206) 770-7779
Fx: (206) 770-5941
Gaurav.Mehta at stantec.com
stantec.com<http://www.stantec.com>

The content of this email is the confidential property of Stantec and should not be copied, modified, retransmitted, or used for any purpose except with Stantec's written authorization. If you are not the intended recipient, please delete all copies and notify us immediately.

ü Please consider the environment before printing this email.

From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Chris Yates
Sent: Wednesday, January 26, 2011 8:29 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Is there a point to "virtual partitions"?

Hello,

Virtual partition: a transparent partition with no mass and no thermal resistance.  If the simulation employs an air flow network it may also be considered as a hole allowing air to pass through the partition. Usually used to define a perimeter zone. (BTW this isn't quoting any source, just what I understand!)

I feel I may be describing a cultural nuance of energy modelling in the UK. So I'd like to ask the following:

 *   Do engineers in countries apart from the UK use "virtual partitions"?
I use them all the time, especially when defining a large space (such as an open office or a gymnasium). I divide the zone into perimeter (~15 feet or approx. 5 m beyond external wall) and core zone. There is no actual partition but only a virtual partition which I have created. The reason for this division is that the perimeter zones experience external loads as well as internal loads, whereas the core zones experience only the internal loads.

 *   What benefits do virtual partitions have over physical partitions?
The virtual partitions allow for heat transfer through convection between the perimeter and the adjacent core zone. If it is defined as an internal partition, then the heat transfer will be through conduction which is not true for the actual space as there is no actual partition. Additionally, if the internal partition is defined with thermal mass, it can add some thermal lag as well and the zone then might peak at a different time than it would without the lag.
Any other comments will be gratefully received.

Many thanks
--

Chris Yates C Eng MCIBSE

Building Physics Consultant

Tel:   +447960731576

Email: chris.malcolm.yates at gmail.com<mailto:chris.malcolm.yates at gmail.com>

Skype: christopher.m.yates
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110126/4dd53f93/attachment.htm>


More information about the Bldg-sim mailing list