[Bldg-sim] Is there a point to "virtual partitions"?
Cheney
chenyu73 at gmail.com
Wed Jan 26 08:52:00 PST 2011
Hello Chris,
It is not a cultural nuance and I use virtual partitions almost everyday.
Why? I have to employ it when
1. I need to setup different internal loads for a space with multi-zone,
such as big open office (you mentioned it in your own definition);
2. I need to simulate displacement ventilation in a space (I will put the
virtual partitions horizontally though to separate occupied and stratified
spaces)
3. I need to define stack effect in some spaces
4. Some other reasons...
>
> --
>
Regards,
Cheney
LinkedIN @ http://ca.linkedin.com/pub/yu-cheney-chen/27/637/72b
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110126/69ef5c62/attachment.htm>
More information about the Bldg-sim
mailing list