[Bldg-sim] Exceptions to G3.1.1, and how you model them?
James Hansen
JHANSEN at ghtltd.com
Mon Nov 1 12:46:42 PDT 2010
Thanks Cheney, but I'm not sure I follow your email. I've already
determined that, for example, a core bathroom could easily have a peak
load that is 10 Btu/hr-ft2 less than the peak average of the rest of my
spaces. Same goes for stairs, storage rooms, etc. So doesn't 90.1
REQUIRE that I model these separately?
What CIR are you referencing?
From: Cheney [mailto:chenyu73 at gmail.com]
Sent: Monday, November 01, 2010 12:36 PM
To: James Hansen
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Exceptions to G3.1.1, and how you model them?
Hi James,
LEED CIR allows projects to demonstrate substantial energy savings for
well-designed HVAC system serving high process load spaces based on the
exception to G3.1.1. So the premise is "high occupancy or process load"
spaces, such as server rooms, natatoriums, before it comes to the
benchmark of 10 btu/h-ft2. Therefore, I guess your storage rooms,
stairs, mechanical rooms should not be modeled separately.
Regards,
Cheney
I guess your storage rooms, stairs, mechanical rooms, lobbies, etc.
should not be
On Mon, Nov 1, 2010 at 5:12 AM, James Hansen <JHANSEN at ghtltd.com> wrote:
I was interested to see if anyone would share how they model the
exception to G3.1.1 in ASHRAE 90.1-2007 (or 04). This is the part that
says when you have a baseline building with system 5-8, you're supposed
to model system 3 or 4 for any spaces that "have occupancy or process
loads or schedules that differ significantly from the rest of the
building." It goes on to say that basically the peak thermal loads must
differ by 10 Btu / h-ft2 or more from the average of the other spaces,
or that schedules must differ by more than 40 full load hours per week,
for this exception to apply.
I've had reviewers question certain rooms that I've put on separate
PSZ-AC systems, and so I've sort of defaulted to putting almost all
rooms on the main systems (5-8). However, in looking at some of my
recent models, depending on interior loads and climate, the actual peak
cooling load on a square foot basis varies anywhere from 5-20 btu /
h-ft2 range for offices. So this means there is a big difference
between those models with 5 btu / h-ft2 peak and those with 20. For the
models with 5, almost every space in the building is going to be within
+/- 10 btu/h-ft2 of that average. However, those buildings that average
around 20 will have many rooms that are < 10 btu/h-ft2 peak (ie any
internal space whose light + plug load density is < 3.0 W / sq ft).
To use a simple example as a question: if your particular office
building averaged 20 btuh / h-ft2 peak cooling load, would you model a
separate PSZ-AC system for a core bathroom, whose peak cooling load is
only 3 btu/h-ft2?
There are lots of rooms where I question whether I should do a separate
PSZ-AC/HP system (storage rooms, stairs, mechanical rooms, lobbies,
etc). I can see where these meet the 10 Btu/h-ft2 delta exception.
So does everyone really model a bunch of PSZ-AC systems based
specifically on the average peak thermal loads of the building?
I'm thinking out loud, but if I had an office building that averaged on
the low side (5 Btu/h-ft2) for cooling peaks, it seems pretty easy to
have a perimeter conference room that exceeded 15 Btu / h-ft2 peak.
Seems like an exhaustive process to confirm this delta for every room in
a model to determine whether it needs its own system...
Sorry for the long email. Thanks!
GHT Limited
James Hansen, PE, LEED AP
Senior Associate
1010 N. Glebe Rd, Suite 200
Arlington, VA 22201-4749
703-338-5754 (Cell)
703-243-1200 (Office)
703-276-1376 (Fax)
www.ghtltd.com <http://www.ghtltd.com/>
________________________________
The information contained in this communication is confidential, may be
privileged, and is intended only for the use of the addressee. It is
the property of GHT Limited. Unauthorized use, disclosure or copying of
this communication or any part thereof is strictly prohibited and may be
unlawful. If you have received this communication in error, please
notify me immediately by return e-mail or by e-mail to ght at ghtltd.com
<mailto:ght at ghtltd.com> , and destroy this communication and all copies
thereof, including all attachments. Thank you.
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
The information contained in this communication is confidential, may be privileged, and is intended only for the use of the addressee. It is the property of GHT Limited. Unauthorized use, disclosure or copying of this communication or any part thereof is strictly prohibited and may be unlawful. If you have received this communication in error, please notify me immediately by return e-mail or by e-mail to ght at ghtltd.com, and destroy this communication and all copies thereof, including all attachments. Thank you.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20101101/cbe427c7/attachment.htm>
More information about the Bldg-sim
mailing list