[Bldg-sim] Exceptions to G3.1.1, and how you model them?

Cheney chenyu73 at gmail.com
Mon Nov 1 09:35:49 PDT 2010


Hi James,

LEED CIR allows projects to demonstrate substantial energy savings for
well-designed HVAC system serving high process load spaces based on the
exception to G3.1.1. So the premise is "high occupancy or process load"
spaces, such as server rooms, natatoriums, before it comes to the benchmark
of 10 btu/h-ft2. Therefore, I guess your storage rooms, stairs, mechanical
rooms should not be modeled separately.

Regards,

Cheney

I guess your storage rooms, stairs, mechanical rooms, lobbies, etc. should
not be

On Mon, Nov 1, 2010 at 5:12 AM, James Hansen <JHANSEN at ghtltd.com> wrote:

>  I was interested to see if anyone would share how they model the
> exception to G3.1.1 in ASHRAE 90.1-2007 (or 04).  This is the part that says
> when you have a baseline building with system 5-8, you’re supposed to model
> system 3 or 4 for any spaces that “have occupancy or process loads or
> schedules that differ significantly from the rest of the building.”  It goes
> on to say that basically the peak thermal loads must differ by 10 Btu /
> h-ft2 or more from the average of the other spaces, or that schedules must
> differ by more than 40 full load hours per week, for this exception to
> apply.
>
>
>
> I’ve had reviewers question certain rooms that I’ve put on separate PSZ-AC
> systems, and so I’ve sort of defaulted to putting almost all rooms on the
> main systems (5-8).   However, in looking at some of my recent models,
> depending on interior loads and climate, the actual peak cooling load on a
> square foot basis varies anywhere from 5-20 btu / h-ft2 range for offices.
> So this means there is a big difference between those models with 5 btu /
> h-ft2 peak and those with 20.  For the models with 5, almost every space in
> the building is going to be within +/- 10 btu/h-ft2 of that average.
> However, those buildings that average around 20 will have many rooms that
> are < 10 btu/h-ft2 peak (ie any internal space whose light + plug load
> density is < 3.0 W / sq ft).
>
>
>
> *To use a simple example as a question:  if your particular office
> building averaged 20 btuh / h-ft2 peak cooling load, would you model a
> separate PSZ-AC system for a core bathroom, whose peak cooling load is only
> 3 btu/h-ft2?*
>
>
>
> There are lots of rooms where I question whether I should do a separate
> PSZ-AC/HP system (storage rooms, stairs, mechanical rooms, lobbies, etc).  I
> can see where these meet the 10 Btu/h-ft2 delta exception.
>
>
>
> So does everyone really model a bunch of PSZ-AC systems based specifically
> on the average peak thermal loads of the building?
>
>
>
> I’m thinking out loud, but if I had an office building that averaged on the
> low side (5 Btu/h-ft2) for cooling peaks, it seems pretty easy to have a
> perimeter conference room that exceeded 15 Btu / h-ft2 peak.  Seems like an
> exhaustive process to confirm this delta for every room in a model to
> determine whether it needs its own system…
>
>
>
> Sorry for the long email.  Thanks!
>
>
>
> *GHT Limited
> **James Hansen**, PE, LEED AP*
>
> *Senior Associate***
>
> 1010 N. Glebe Rd, Suite 200
>
> Arlington, VA  22201-4749
>
> 703-338-5754 (Cell)
>
> 703-243-1200 (Office)
>
> 703-276-1376 (Fax)
>
> www.ghtltd.com
>
> * *
>
>
>
> ------------------------------
> The information contained in this communication is confidential, may be
> privileged, and is intended only for the use of the addressee.  It is the
> property of GHT Limited.  Unauthorized use, disclosure or copying of this
> communication or any part thereof is strictly prohibited and may be
> unlawful.  If you have received this communication in error, please notify
> me immediately by return e-mail or by e-mail to ght at ghtltd.com, and
> destroy this communication and all copies thereof, including all
> attachments.  Thank you.
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20101101/a73daf0f/attachment.htm>


More information about the Bldg-sim mailing list