Omar, 
If it is a standing seam roof with thermal spacer blocks (between the structure and roof system) you would take the first row, where it says 'none' in the first column then interpolate between the R-11.2 and R-16.8.  If it is a metal roof without thermal spacer blocks, then there is no default assembly and you would need some tested data of the assembly.

                                                                                                          
Leonard Sciarra 
Senior Associate 
+1 (312) 577.6580 Direct 

Gensler 
11 East Madison Street
Suite 300 
Chicago IL 60602 


-----Original Message-----
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of omoltay at mimtarch.com
Sent: Saturday, December 18, 2010 5:10 PM
To: equest-users at lists.onebuilding.org
Cc: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Using Table A2.3

Dear All,

In calculating the U-values for my proposed model, I am trying to use Table A2.3 for metal roofs. If I have an insulation with R-14 (applied continously), which values do I have to select to interpolate? The table just does not make sense to me as I do not understand the relationship between the left portion and the right portion.

Thanks in advance,

Omer Moltay
Mimta Ltd.