[Bldg-sim] Occupancy

Nick Caton ncaton at smithboucher.com
Wed Dec 8 14:35:21 PST 2010


The topic is kind of broad but I'll take a swing:

 

-          The ideal "100% occupied" figures and scheduling to use are
those describing actual occupancy in an existing/future building.  In
the real world, energy modelers generally can't get ahold of this
information for new construction.  Real-world scheduling may be readily
available for schools and the like, however.

 

-          The best "100% occupied" occupancy numbers in lieu of "real
world" would be those already used to develop the HVAC design loads - at
the minimum you know the modeled equipment capacities/airflows will be
sufficient for the resultant interior/ventilation loads.  Your architect
may or may not be the person to talk to to get this information.

 

-          When the mechanical designer's ventilation/occupancy figures
aren't handy either... a fire plan's space/exit capacity figures, while
inflated to a worst case for life safety purposes, might be okay in a
pinch if you don't have time to develop your own figures, but given
time...

 

-          ...I would sooner develop my own numbers (play the part of
the missing ME) using the furniture plans and occupancy density figures
(P/1000SF) per ASHRAE Std 62/62.1.  Such figures are often built into
load calc and energy modeling programs for the user's convenience, and
those are a good starting point to refine/round using other resources at
hand.

 

90.1 Appendix G is (thankfully) fairly simple and "hands-off" when it
comes to how occupancy/scheduling should be handled.  As long as
everything is identical between baseline and proposed, everyone on the
reviewer side should be happy, so the means by which we approximate
maximum occupancies and hourly fractional scheduling is pretty much up
to the modelers.  This is one of those "self-policing" approaches within
90.1:  Skewing the occupancy/scheduling too far in either direction is
not in the best interest for a LEED model, as you will either (A) have
an overly-vacant building with fewer loads for your more-efficient
systems to handle, decreasing the building performance %, or (B) have an
over-occupied building resulting in loads that cause unmet hours the
proposed equipment capacities can't handle.

 

~Nick



 

 

NICK CATON, E.I.T.

PROJECT ENGINEER

Smith & Boucher Engineers

25501 west valley parkway

olathe ks 66061

direct 913 344.0036

fax 913 345.0617

www.smithboucher.com 

 

From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Peter
Simmonds
Sent: Wednesday, December 08, 2010 3:02 PM
To: Brian Tysoe; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Occupancy

 

This is a very important point that is often forgotten in simulation
modeling. The computer is a strange object and if you tell the computer
to put one occupant for every 100ft2, then is does just that and the
related ventilation air and cooling (or heating).

I usually request the architect provide me with the occupation
calculations for the elevators and cafeteria and also the Fire Marshall
rating for building occupancy. These numbers are typically around 70% of
the simulation program occupants. The occupancy density in the program
and therefore be adjusted to match this.

How this could be interpreted in 90.1 I will leave up to any following
discussions?

 

Peter Simmonds, Ph.D. 
Senior Associate
Head of the Advanced Technology Group
IBE Consulting Engineers
14130 Riverside Drive, Suite 201
Sherman Oaks, CA 91423 
p: (818) 377-8220 x246 m: (818) 219-1284 f: (818) 377-8230

www.ibece.com <http://www.ibece.com/> 
Ideas for the built environment

This e-mail message, including any attachments, is for the sole use of
the intended recipient(s) and may contain confidential and privileged
information. Any unauthorized review, use, disclosure, or distribution
is prohibited. If you are not the intended recipient, please contact the
sender by reply e-mail and destroy all copies of the original message.

From: Brian Tysoe [mailto:BTysoe at mcw.com] 
Sent: Wednesday, December 08, 2010 6:50 AM
To: 'bldg-sim at lists.onebuilding.org'
Subject: [Bldg-sim] Occupancy

 

Hello all,

 

I have a question about occupancy schedules for energy models.

 

Generally the owner will provide peak occupancy numbers on a
room-by-room basis; and a peak overall occupancy number for the entire
building. Inevitably the room-by-room numbers will add up to
significantly more than the overall building number.

 

Which numbers should be used for the energy model? Would you use the
room-by-room number and scale them down with the occupancy schedule
based on the overall occupancy?

 

Obviously, this has a significant impact on the results.

 

Thanks,

 

 

Brian Tysoe M.A.Sc., P.Eng., LEED AP 

Mechanical Engineer 

 

MCW Consultants Ltd. <http://www.mcw.com> 

600-156 Front Street West 
Toronto, ON M5J 2L6 
Phone 416-598-2920 
Fax 416-598-5394 

 

This e-mail may be privileged and confidential. Any unauthorized use is
strictly prohibited. If you received this e-mail in error, please
contact the sender directly. 

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20101208/dab12848/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20101208/dab12848/attachment.jpeg>


More information about the Bldg-sim mailing list