> I have seen some discussion on how to separate fan power from EER on the
> various list-serves, but never seen an explicit description of exactly how
> to go about it. Below are my calculation methodologies and I'm hoping to
> generate some thumbs up/thumbs down discussion and clarification:
>
> From ASHRAE 90.1 Users manual formula G-A:
>
> EER = (Net Cooling [BTU/h]) / (Total Input Power [W])
>
> = ((Gross Cooling - Supply Fan Power) [Btu/h]) / (Total Input Power
> [W])
>
> Definitions
>
> Total Input Power: Includes supply and condenser fan power, and condenser
> power
>
> Supply Fan Power [btu h ] : this is the heat rejected by the fan to the
> supply air stream. If 100% of the fan power is eventually converted to
> heat, then this is 3,413 X Supply Fan KW.
>
>
> To Calculate the EER, minus the fan, do the following:
>
> Break Total Input Power into Supply Fan Power and condenser fan and
> compressor power
>
> I'll use the following abbreviations for subsequent formulas to minimize
> typing:
>
> GC : Gross Cooling [btu/h]
> SPb: Supply Fan Power [btu/h]
> SPw: Supply Fan Power [w]
> CP: Compressor Power [w]
>
> For an Appendix G baseline model, we have GC, SPb, SPw, and EER. So, from
> formula G-A, we solve for CP::
>
> CP + SPw = (GC - SPb) / EER
>
> CP = (GC - SPb) / EER - SPw
>
> Now, we can determine the EER, excluding the fan power so:
>
> Modified EER = GC / CP
>
> A few things to discuss:
>
> 1. Is this really appropriate for systems where the fan power is
> calculated using the G.3.1.2.9 guidelines?
>
> 2. What is done when the requirements for cooling system efficiency is
> listed as a SEER instead of an EER? Is there an acceptable conversion
> factor for use in these calculations?
>
> 3. I this methodology what is intended? ASHRAE Appendix G, and even the
> User's Manual is extremely brief of this.
>
> Thanks,
>
> --
> Karen
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100426/f3b465e7/attachment.htm>
More information about the Bldg-sim
mailing list