Hi Karen,<br><br>How are you?? Well, I trust. I will look at your calcs as soon as I can but I must go watch the PORTLAND TRAILBLAZERS (go BLAZERS!!) win! I hope!! The game is starting right now.<br><br>Sorry in advance to any/all Suns fans (just kidding). You know the Trailblazers are all we have here in Portland and we are FANS!<br>
<br>Carol!!<br><br><br><br><div class="gmail_quote">On Mon, Apr 26, 2010 at 2:07 PM, Karen Walkerman <span dir="ltr"><<a href="mailto:kwalkerman@gmail.com">kwalkerman@gmail.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin: 0pt 0pt 0pt 0.8ex; border-left: 1px solid rgb(204, 204, 204); padding-left: 1ex;">
<div>Hello,<br></div><div><br></div><div>I have seen some discussion on how to separate fan power from EER on the various list-serves, but never seen an explicit description of exactly how to go about it.  Below are my calculation methodologies and I'm hoping to generate some thumbs up/thumbs down discussion and clarification:</div>


<div><br></div><div>From ASHRAE 90.1 Users manual formula G-A:</div><div><br></div><div>EER = (Net Cooling [BTU/h]) / (Total Input Power [W])</div><div><br></div><div>     = ((Gross Cooling - Supply Fan Power) [Btu/h]) / (Total Input Power [W])</div>


<div><br></div><div>Definitions</div><div><br></div><div>Total Input Power:  Includes supply and condenser fan power, and condenser power</div><div><br></div><div>Supply Fan Power [btu h ] : this is the heat rejected by the fan to the supply air stream.  If 100% of the fan power is eventually converted to heat, then this is 3,413 X Supply Fan KW.</div>


<div><br></div><div><br></div><div>To Calculate the EER, minus the fan, do the following:</div><div><br></div><div>Break Total Input Power into Supply Fan Power and condenser fan and compressor power</div><div><br>
</div><div>I'll use the following abbreviations for subsequent formulas to minimize typing:</div><div><br></div><div>GC : Gross Cooling [btu/h]</div><div>SPb: Supply Fan Power [btu/h]</div><div>SPw: Supply Fan Power [w]</div>

<div>CP: Compressor Power [w]</div><div><br></div><div>For an Appendix G baseline model, we have GC, SPb, SPw, and EER.  So, from formula G-A, we solve for CP::</div><div><br></div><div>CP + SPw = (GC - SPb) / EER</div><div>

<br></div><div>CP = (GC - SPb) / EER - SPw</div><div><br></div><div>Now, we can determine the EER, excluding the fan power so:</div><div><br></div><div>Modified EER = GC / CP</div><div><br></div><div>A few things to discuss:</div>

<div><br></div><div>1.  Is this really appropriate for systems where the fan power is calculated using the G.3.1.2.9 guidelines?</div><div><br></div><div>2.  What is done when the requirements for cooling system efficiency is listed as a SEER instead of an EER?  Is there an acceptable conversion factor for use in these calculations?</div>

<div><br></div><div>3.  I this methodology what is intended?  ASHRAE Appendix G, and even the User's Manual is extremely brief of this.</div><div><br></div><div>Thanks,</div><div><br></div><div>--</div><div>Karen</div>


<br>_______________________________________________<br>
Bldg-sim mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br><div style="visibility: hidden; display: inline;" id="avg_ls_inline_popup"></div><style type="text/css">#avg_ls_inline_popup {  position:absolute;  z-index:9999;  padding: 0px 0px;  margin-left: 0px;  margin-top: 0px;  width: 240px;  overflow: hidden;  word-wrap: break-word;  color: black;  font-size: 10px;  text-align: left;  line-height: 13px;}</style>