David,
Thanks for pointing that out - there is a typo in the paper. The formula
should read
QSOL + QEQU + QPPL = (M*CP + UABLD) x (TDES - TBAL)
The software uses the correct formula though. At this point we (Lord
Aeck Sargent & The Rocky Mountain Institute) use this as a schematic
design tool on quite a few projects, and find its quite useful. The plan
is to ultimately make this available freely (I would like to make it
work with the new TMY3 files before I start giving it away though).
Once again - thanks for pointing out the typo - sharp eyes (sharper than
mine when I was typing out the paper at 2am).
Vikram Sami, LEED AP
Direct Phone 404-253-1466 | Direct Fax 404-253-1366
LORD, AECK & SARGENT ARCHITECTURE
1201 Peachtree Street NE, Suite 300, Atlanta, GA 30361
Responsive Design * Technological Expertise * Exceptional Service
www.lordaecksargent.com
Please don't print this email unless you really have to.
In the United States, we use enough office paper each year to build a
10-foot high wall that's 6,815 miles long or two and a half times the
distance from New York to Los Angeles.
~ Wisconsin Department of Natural Resources, "Recycling Facts and
Figures," PUBL CE-163, 2002.
________________________________
From: David Bryan [mailto:DBryan at AmerIndian.com]
Sent: Friday, May 09, 2008 2:16 PM
To: Vikram Sami
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Balance point temperature for houses
Vikram -
The balance point tool looks extremely useful during the building design
stages when it wpould be much more practical than a detailed energy
model.
I look forward to its availability.
Do you intend it to be for commercial as well as residential buildings?
In that case it would need a way to input code-required minimum
ventilation rates with some heat exchange options.
The formula Qint = M*Cp UAbld x (Tdes-Tbal) looks odd. Maybe I don't
understand the units, but should that be Qint = (M/hr*Cp + UAbld) x
(Tdes-Tbal)?
Thanks,
Dave Bryan
AIA, LEED
AmerINDIAN Architecture
Suite 100, 475 Cleveland Avenue North
Saint Paul, Minnesota, 55104 USA
651-644-1586 phone
651-644-7172 fax
dbryan at amerindian.com
www.amerindian.com
<http://www.amerindian.com/> <http://www.amerindian.com/>
Vikram Sami wrote:
I have been working on developing an analysis tool that extends
the
building passive envelope season based on a dynamic balance
point
analysis (see attached)
Vikram Sami, LEED AP
Direct Phone 404-253-1466 | Direct Fax 404-253-1366
LORD, AECK & SARGENT ARCHITECTURE
1201 Peachtree Street NE, Suite 300, Atlanta, GA 30361
Responsive Design * Technological Expertise * Exceptional
Service
www.lordaecksargent.com
Please don't print this email unless you really have to.
In the United States, we use enough office paper each year to
build a
10-foot high wall that's 6,815 miles long or two and a half
times the
distance from New York to Los Angeles.
~ Wisconsin Department of Natural Resources, "Recycling Facts
and
Figures," PUBL CE-163, 2002.
-----Original Message-----
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of
Chris
Balbach
Sent: Wednesday, May 07, 2008 11:27 AM
To: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Balance point temperature for houses
Dr. Abaza :
The TREAT (Targeted Residential Energy Analysis Tool) whole
building
energy simulation software package can determine a building's
balance
point (both heating and cooling) given the building description.
One can
construct a 'simple' model of a typical house in about 15
minutes, and
TMY2 weather files for all 50 states are included for driving
the model.
It would be pretty simple to make some parametric runs varying
both
climate and envelope /infiltration to produce a range of balance
point
temps. We have found both insulation levels and air infiltration
(tightness of the envelope) often have the greatest effect on
the
balance point of a given structure, along with the temperature
setpoints
used for heating and cooling. Significant internal gains, of
course, can
also drive the balance points.
A 30 day fully functional version (free download) of the TREAT
software
is available from http://www.treatsoftware.com
Best,
_Chris
Chris Balbach, PE, CEM
Vice President of Research and Development
124 Brindley Street, Suite 4, Ithaca, NY 14850
ph: (607)-327-1647
http://www.psdconsulting.com
http://www.treatsoftware.com
Michael Blasnik wrote:
In my experience from analyzing utility usage data with
a floating
balance point, the typical effective heating balance
point in US homes
will usually be in the range of 54F - 62F (for true
heating climates).
Newer homes are usually closer to the low end of the
scale while older
homes are on the higher end. Electrically heated homes
tend to be on
the lower end but it's not clear how much of that
difference is the
effects of vintage/thermal integrity vs. lower
thermostat set points
or zoning.
There may be some published results in ACEEE summer
study proceedings,
but I can't recall any specific reference.
Michael Blasnik
----- Original Message ----- From: "Abaza Hussein"
<ahussein at spsu.edu> <mailto:ahussein at spsu.edu>
To: <equest-users at lists.onebuilding.org>
<mailto:equest-users at lists.onebuilding.org> ;
<bldg-sim at lists.onebuilding.org>
<mailto:bldg-sim at lists.onebuilding.org>
Sent: Tuesday, May 06, 2008 3:52 PM
Subject: [Bldg-sim] Balance point temperature for houses
Could you please help. Is there any recent data
or survey about the
balance point temperature of homes in the US. Is
the 65F still
applicable?
I appreciate any input.
Dr. H. Abaza
ECU
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank
message to
BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
________________________________
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080509/6aa40df6/attachment.htm>
More information about the Bldg-sim
mailing list