Ok, so I have just noticed:

A comparison between the SS-M report of the baseline (no erv) and ERV models
shows that the ERV uses a little more fan energy for heating and cooling
modes (this seems reasonable) and then a HUGE amount more during floating
hours.

This is what I have input (through a parametric run) for ERV's

   ERV-RECOVER-TYPE = ENTHALPY-WHEEL
   ERV-RUN-CTRL     = WHEN-MIN-OA
   ERV-CAP-CTRL     = MODULATE-HX
   ERV-FANS         = HVAC-SUPPLY/RETURN
   ERV-FAN-EFF      = 0.9
   ERV-MOTOR-CLASS  = PREMIUM
   ERV-OA-KW/FLOW   = 8.5e-005
   ERV-FROST-CTRL   = USE-CAP-CTRL


ERV Model:

REPORT- SS-M Building HVAC Fan Elec
Energy                                                  WEATHER FILE-
Burlington   VT TMY2
---------------------------------------------------------------------------------------------------------------------------------


         FAN ELECTRIC    FAN ELECTRIC    FAN ELECTRIC      FAN ELECTRIC
         ENERGY DURING   ENERGY DURING   ENERGY DURING     ENERGY DURING
            HEATING         COOLING      HEATING-COOLING     FLOATING
 MONTH      (KWH)            (KWH)            (KWH)            (KWH)




  JAN      2031.042           24.259             0.000        1134.069

  FEB      1699.503           24.384             0.000        1097.507

  MAR      1441.447           64.325             0.000        1964.537

  APR       632.728          129.451             0.000        3292.951

  MAY       174.217          444.731             0.000        4805.784

  JUN        58.014          617.355             0.000        4853.930

  JUL        16.702          868.591             0.000        4656.523

  AUG        11.749          860.175             0.000        4763.009

  SEP        73.569          408.324             0.000        5260.542

  OCT       256.301          198.773             0.000        4641.178

  NOV       899.911           41.370             0.000        2216.153

  DEC      1603.912           20.847             0.000        1417.681
         -------------   -------------   ---------------   -------------

  ANNUAL   8899.124         3702.583             0.000       40093.965


******************************************************************************************

Baseline Model:

REPORT- SS-M Building HVAC Fan Elec
Energy                                                  WEATHER FILE-
Burlington   VT TMY2
---------------------------------------------------------------------------------------------------------------------------------


         FAN ELECTRIC    FAN ELECTRIC    FAN ELECTRIC      FAN ELECTRIC
         ENERGY DURING   ENERGY DURING   ENERGY DURING     ENERGY DURING
            HEATING         COOLING      HEATING-COOLING     FLOATING
 MONTH      (KWH)            (KWH)            (KWH)            (KWH)




  JAN      1458.496           14.424             0.000           0.140

  FEB      1220.828           14.370             0.000           0.018

  MAR      1023.469           36.366             0.000           0.258

  APR       457.305           72.241             0.000           1.313

  MAY       144.202          235.738             0.000           0.450

  JUN        52.800          327.834             0.000           0.000

  JUL        16.527          467.251             0.000           0.000

  AUG        11.605          452.370             0.000           0.000

  SEP        63.427          214.222             0.000           0.069

  OCT       206.193          101.587             0.000           0.777

  NOV       633.372           23.710             0.000           1.893

  DEC      1101.974           13.247             0.000           0.000
         -------------   -------------   ---------------   -------------

  ANNUAL   6390.089         1973.342             0.000           4.919












On 9/11/07, Karen Walkerman <kwalkerman at gmail.com> wrote:
>
> Ok, so there have been a couple post recently asking about energy savings
> from ERV's in eQuest.  The concern is that there is some reduction in
> cooling and heating energy use, but a significant increase in fan energy
> use.
>
> Here's my thought:  in the baseline case, the only energy expended with
> respect to ventilation air is the energy required to heat and cool the
> outdoor air, but the fan energy to move the ventilation air through ductwork
> is not represented.  (If someone knows where to put this number, or how to
> represent it, please let me know).  Any other thoughts/suggestions out
> there?
>
> I am trying to get to the bottom of this as well, because so far,
> according to eQuest, installing an ERV has not made much sense.
>
> Also, is there a way to turn off the airside economizer?  I'm modeling a
> building with heat pumps.  There is an ERV for ventilation, but no
> economizer.
>
> Thanks,
> ~Karen~
>
> --
> Karen Walkerman
> Second Law Consulting
> 802-238-0980
> kwalkerman at gmail.com
>



-- 
Karen Walkerman
Second Law Consulting
802-238-0980
kwalkerman at gmail.com


======================================================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20070911/74c686f4/attachment.htm>


More information about the Bldg-sim mailing list