[BLDG-SIM] ERV energy use in eQuest and economizers
Brandon Nichols
BrandonN at Hargis.biz
Tue Sep 11 16:35:04 PDT 2007
Karen,
What do you mean by floating hours -- system off? Perhaps your
schedules are not assigned correctly.
Here's a post with an enthalpy wheel I simulated recently that works as
expected...
http://elcca-exchange.blogspot.com/2007/08/equest-latent-heat-recovery.h
tml
Hope that helps!
Brandon Nichols, PE, LEED(r) AP
Mechanical
HARGIS ENGINEERS
600 Stewart Street
Suite 1000
Seattle, WA 98101
www.hargis.biz
d | 206.436.0400 c | 206.228.8707
o | 206.448.3376 f | 206.448.4450
_____
From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of Karen
Walkerman
Sent: Tuesday, September 11, 2007 6:41 AM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] ERV energy use in eQuest and economizers
Ok, so I have just noticed:
A comparison between the SS-M report of the baseline (no erv) and ERV
models shows that the ERV uses a little more fan energy for heating and
cooling modes (this seems reasonable) and then a HUGE amount more during
floating hours.
This is what I have input (through a parametric run) for ERV's
ERV-RECOVER-TYPE = ENTHALPY-WHEEL
ERV-RUN-CTRL = WHEN-MIN-OA
ERV-CAP-CTRL = MODULATE-HX
ERV-FANS = HVAC-SUPPLY/RETURN
ERV-FAN-EFF = 0.9
ERV-MOTOR-CLASS = PREMIUM
ERV-OA-KW/FLOW = 8.5e-005
ERV-FROST-CTRL = USE-CAP-CTRL
ERV Model:
REPORT- SS-M Building HVAC Fan Elec Energy
WEATHER FILE- Burlington VT TMY2
------------------------------------------------------------------------
---------------------------------------------------------
FAN ELECTRIC FAN ELECTRIC FAN ELECTRIC FAN ELECTRIC
ENERGY DURING ENERGY DURING ENERGY DURING ENERGY DURING
HEATING COOLING HEATING-COOLING FLOATING
MONTH (KWH) (KWH) (KWH) (KWH)
JAN 2031.042 24.259 0.000 1134.069
FEB 1699.503 24.384 0.000 1097.507
MAR 1441.447 64.325 0.000 1964.537
APR 632.728 129.451 0.000 3292.951
MAY 174.217 444.731 0.000 4805.784
JUN 58.014 617.355 0.000 4853.930
JUL 16.702 868.591 0.000 4656.523
AUG 11.749 860.175 0.000 4763.009
SEP 73.569 408.324 0.000 5260.542
OCT 256.301 198.773 0.000 4641.178
NOV 899.911 41.370 0.000 2216.153
DEC 1603.912 20.847 0.000 1417.681
------------- ------------- --------------- -------------
ANNUAL 8899.124 3702.583 0.000 40093.965
************************************************************************
******************
Baseline Model:
REPORT- SS-M Building HVAC Fan Elec Energy
WEATHER FILE- Burlington VT TMY2
------------------------------------------------------------------------
---------------------------------------------------------
FAN ELECTRIC FAN ELECTRIC FAN ELECTRIC FAN ELECTRIC
ENERGY DURING ENERGY DURING ENERGY DURING ENERGY DURING
HEATING COOLING HEATING-COOLING FLOATING
MONTH (KWH) (KWH) (KWH) (KWH)
JAN 1458.496 14.424 0.000 0.140
FEB 1220.828 14.370 0.000 0.018
MAR 1023.469 36.366 0.000 0.258
APR 457.305 72.241 0.000 1.313
MAY 144.202 235.738 0.000 0.450
JUN 52.800 327.834 0.000 0.000
JUL 16.527 467.251 0.000 0.000
AUG 11.605 452.370 0.000 0.000
SEP 63.427 214.222 0.000 0.069
OCT 206.193 101.587 0.000 0.777
NOV 633.372 23.710 0.000 1.893
DEC 1101.974 13.247 0.000 0.000
------------- ------------- --------------- -------------
ANNUAL 6390.089 1973.342 0.000 4.919
On 9/11/07, Karen Walkerman < kwalkerman at gmail.com> wrote:
Ok, so there have been a couple post recently asking about
energy savings from ERV's in eQuest. The concern is that there is some
reduction in cooling and heating energy use, but a significant increase
in fan energy use.
Here's my thought: in the baseline case, the only energy
expended with respect to ventilation air is the energy required to heat
and cool the outdoor air, but the fan energy to move the ventilation air
through ductwork is not represented. (If someone knows where to put
this number, or how to represent it, please let me know). Any other
thoughts/suggestions out there?
I am trying to get to the bottom of this as well, because so
far, according to eQuest, installing an ERV has not made much sense.
Also, is there a way to turn off the airside economizer? I'm
modeling a building with heat pumps. There is an ERV for ventilation,
but no economizer.
Thanks,
~Karen~
--
Karen Walkerman
Second Law Consulting
802-238-0980
kwalkerman at gmail.com
--
Karen Walkerman
Second Law Consulting
802-238-0980
kwalkerman at gmail.com
===========================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20070911/4cd8d5a3/attachment.htm>
More information about the Bldg-sim
mailing list