[BLDG-SIM] Thanks for help with eQuest calibration
Steve Mignogna
smignogna at gmail.com
Fri Nov 23 18:13:50 PST 2007
Some things of the top of my head:
-try to find out the actual occupancies, lighting and equipment power
densities (if you don't know them use ASHRAE values)
-make sure you are using the correct reheat delta T
-correct heat recovery effectiveness
-as mentioned earlier, check the thermo setpt temps and the setbacks. also
make sure you are taking into account the time when the school is on break.
-in addition to the OA% make sure you are supplying the correct amount of
makeup air as well. (again if you don't know them refer to ASHRAE for
minimum air flow rates)
-im assuming you have the actual drawings, but if you don't make sure you
inputted the correct external wall and the glazing performance values.
Good luck,
Steve Mignogna
Atelier Ten
On Nov 23, 2007 3:21 PM, Seun Odukomaiya <oodukoma at purdue.edu> wrote:
> Guys,
>
> I am overwhelmed with the response to my post about needing help with an
> eQuest calibration. I can't tell you how much I appreciate all your
> willingness to help. I will try some of the things that were suggested. In
> the mean time, here is some more information about my eQuest model:
>
>
>
> Location: Indianapolis, Indiana
>
> Air-Side HVAC: Single-Zone Reheat with chilled water coil, electric
> heating coil, and heat recovery
>
> Water-Side HVAC: Chilled water loop with screw compressor
>
>
>
> It is my understanding that with a reheat system, the cooling coil is
> supposed to overcool the incoming air to achieve the needed
> dehumidification. When this happens, the heating coil is then supposed to
> reheat the temperature back up to the zone setpoint. Is this correct? If
> this is the case, shouldn't the heating coil have to do more work? My
> humidity setpoint is 45% RH. Also, is there a different way to model a steam
> humidifier in eQuest besides the "humidistat" option. It seems limited in
> terms of input parameters.
>
>
>
> I have matched the model's heating element capacity (kW) to that of the
> actual building. I will try some of your suggestions, such as decreasing
> internal loads, and increasing outside air %. Again, thank you so much, and
> I will keep you posted on any progress
>
>
>
> Seun Odukomaiya
>
> Mechanical Engineering Technology
>
> Purdue University
>
> You received this e-mail because you are subscribed
> to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
> from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at GARD.COM
>
>
--
Steve Mignogna
Atelier Ten
======================================================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20071123/587fc38c/attachment.htm>
More information about the Bldg-sim
mailing list