Some things of the top of my head:<br><br>-try to find out the actual occupancies, lighting and equipment power densities (if you don't know them use ASHRAE values)<br>-make sure you are using the correct reheat delta T
<br>-correct heat recovery effectiveness<br>-as mentioned earlier, check the thermo setpt temps and the setbacks. also make sure you are taking into account the time when the school is on break.<br>-in addition to the OA% make sure you are supplying the correct amount of makeup air as well. (again if you don't know them refer to ASHRAE for minimum air flow rates)
<br>-im assuming you have the actual drawings, but if you don't make sure you inputted the correct external wall and the glazing performance values.<br><br>Good luck,<br><br>Steve Mignogna<br>Atelier Ten<br><br><div class="gmail_quote">
On Nov 23, 2007 3:21 PM, Seun Odukomaiya <<a href="mailto:oodukoma@purdue.edu">oodukoma@purdue.edu</a>> wrote:<br><blockquote class="gmail_quote" style="border-left: 1px solid rgb(204, 204, 204); margin: 0pt 0pt 0pt 0.8ex; padding-left: 1ex;">
<div link="blue" vlink="purple" lang="EN-US">
<div>
<p>Guys,</p>
<p>I am overwhelmed with the response to my post about needing
help with an eQuest calibration. I can't tell you how much I appreciate
all your willingness to help. I will try some of the things that were
suggested. In the mean time, here is some more information about my eQuest
model:</p>
<p> </p>
<p>Location: Indianapolis, Indiana</p>
<p>Air-Side HVAC: Single-Zone Reheat with chilled water coil,
electric heating coil, and heat recovery</p>
<p>Water-Side HVAC: Chilled water loop with screw compressor</p>
<p> </p>
<p>It is my understanding that with a reheat system, the
cooling coil is supposed to overcool the incoming air to achieve the needed
dehumidification. When this happens, the heating coil is then supposed to
reheat the temperature back up to the zone setpoint. Is this correct? If this
is the case, shouldn't the heating coil have to do more work? My humidity
setpoint is 45% RH. Also, is there a different way to model a steam humidifier
in eQuest besides the "humidistat" option. It seems limited in
terms of input parameters.</p>
<p> </p>
<p>I have matched the model's heating element capacity
(kW) to that of the actual building. I will try some of your suggestions, such
as decreasing internal loads, and increasing outside air %. Again, thank you so
much, and I will keep you posted on any progress</p>
<p> </p>
<p>Seun Odukomaiya</p>
<p>Mechanical Engineering Technology</p>
<p>Purdue University</p>
</div>
<pre>You received this e-mail because you are subscribed
to the <a href="mailto:BLDG-SIM@GARD.COM" target="_blank">BLDG-SIM@GARD.COM</a> mailing list. To unsubscribe
from this mailing list send a blank message to
<a href="mailto:BLDG-SIM-UNSUBSCRIBE@GARD.COM" target="_blank">BLDG-SIM-UNSUBSCRIBE@GARD.COM</a>
</pre></div>
</blockquote></div><br><br clear="all"><br>-- <br>Steve Mignogna<br>Atelier Ten