This is one of my favorite peeves with DOE2.1E. in a VAVS or PVAVS the
heating coil does not work if you specify COOL-CONTROL = WARMEST. In
practice an actual VAV system with a heating coil will maintain the minimum
supply T. This is not a problem in California where the code for the
systems portion of DOE2.1E was developed. If you set COOL-CONTROL =
CONSTANT or COOL-CONTROL = RESET and define an outdoor temperature reset
schedule then the heating coil works as expected. I have not been able to
convince anyone to fix the code for COOL-CONTROL = WARMEST and I have been
trying for a number of years.
The work around is to define a PREHEAT-T at a couple of degrees below the
MIN-SUPPLY-T. There tends to be more heating and cooling with this work
around than you would expect but it is better than using COOL-CONTROL =
CONSTANT.
I wonder if this problem has been fixed in DOE2.2?
>In modeling a PVAVS system in DOE2.1E, I can't get the main heating coil to
>be recognized. I have entered a "HEAT-SET-T" (greater than the
>"MIN-SUPPLY-T") in "system control" and specified the heating coil capacity,
>however, the only heating I'm getting is from the baseboards. I've worked
>around this problem before by distributing my main coil capacity into the
>preheat, reheat and/or baseboard. Any opinions on the best work-around for
>this problem?
>
>James Campbell CEM, BEP
>Geo-Marine Inc.
>
>
>
>======================================================
>You received this e-mail because you are subscribed
>to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
>from this mailing list send a blank message to
>BLDG-SIM-UNSUBSCRIBE at GARD.COM
Chris Jones, P.Eng.
14 Oneida Avenue
Toronto, ON M5J2E3
Tel. 416 203-7465
Fax. 416 946-1005
======================================================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
More information about the Bldg-sim
mailing list