[bldg-sim] DOE2.1E - PVAVS main heating coil
hamnmegs at ozemail.com.au
hamnmegs at ozemail.com.au
Fri Jan 14 18:49:40 PST 2005
In 2.2 you can specify HEAT-CONTROL = COLDEST (in addition to HEAT-SET-T) which I believe will give you what you want. Main heating coil will temper air to the point where it can still cool the warmest zone and then trim heaters / reheaters / baseboards will do the rest. It's een a while since I worked with 2.1E so not sure if same control is available.
Regards,
Graham
>
> From: Chris Jones <cj at cr-jay.ca>
> Date: 15/01/2005 5:08:42
> To: <bldg-sim at gard.com>
> Subject: [bldg-sim] DOE2.1E - PVAVS main heating coil
>
> This is one of my favorite peeves with DOE2.1E. in a VAVS or PVAVS the
> heating coil does not work if you specify COOL-CONTROL = WARMEST. In
> practice an actual VAV system with a heating coil will maintain the minimum
> supply T. This is not a problem in California where the code for the
> systems portion of DOE2.1E was developed. If you set COOL-CONTROL =
> CONSTANT or COOL-CONTROL = RESET and define an outdoor temperature reset
> schedule then the heating coil works as expected. I have not been able to
> convince anyone to fix the code for COOL-CONTROL = WARMEST and I have been
> trying for a number of years.
>
> The work around is to define a PREHEAT-T at a couple of degrees below the
> MIN-SUPPLY-T. There tends to be more heating and cooling with this work
> around than you would expect but it is better than using COOL-CONTROL =
> CONSTANT.
>
> I wonder if this problem has been fixed in DOE2.2?
>
>
> >In modeling a PVAVS system in DOE2.1E, I can't get the main heating coil to
> >be recognized. I have entered a "HEAT-SET-T" (greater than the
> >"MIN-SUPPLY-T") in "system control" and specified the heating coil capacity,
> >however, the only heating I'm getting is from the baseboards. I've worked
> >around this problem before by distributing my main coil capacity into the
> >preheat, reheat and/or baseboard. Any opinions on the best work-around for
> >this problem?
> >
> >James Campbell CEM, BEP
> >Geo-Marine Inc.
> >
> >
> >
> >======================================================
> >You received this e-mail because you are subscribed
> >to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
> >from this mailing list send a blank message to
> >BLDG-SIM-UNSUBSCRIBE at GARD.COM
>
>
> Chris Jones, P.Eng.
> 14 Oneida Avenue
> Toronto, ON M5J2E3
> Tel. 416 203-7465
> Fax. 416 946-1005
>
>
> ======================================================
> You received this e-mail because you are subscribed
> to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
> from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at GARD.COM
>
>
This message was sent through MyMail http://www.mymail.com.au
======================================================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
More information about the Bldg-sim
mailing list