[bldg-sim] CHP energy cost summary
    Baker, Kristopher 
    kbaker at syska.com
       
    Mon Jan 17 13:32:25 PST 2005
    
    
  
Peter,
 
The ES-F report summarizes just the blocks and ratchet components of the
utility rate structure.  If they aren't matching, then you have some
non-block costs included in the definition of the utility structure.
 
For example, 
 
"XXX" = UTILITY-RATE    
   TYPE             = ELECTRICITY
   MONTH-CHGS       = ( 110 )
   ENERGY-CHG       = 0.01836
   DEMAND-CHGS      = ( 3.84 )
   BLOCK-CHARGES    = ( "On Peak Summer", "Intermediate Summer", 
         "Off Peak Summer", "On Peak Winter", "Intermediate Winter", 
         "Off Peak Winter", "Demand Gen Summer", "Demand Gen Winter" )
   DEMAND-INTERVAL  = 30
  
With monthly energy usage of 22,476 kWh and 81.2 kW, the total energy
costs are $1750, but the ES-F reports $915.  This is due the $110
monthly charge, the additional $0.01836/kwh fixed consumption charge
($413 = 0.01836 * 22476), and the additional 3.84/kW fixed demand charge
($312 = 3.84 * 81.2). Thus, the ES-E total of $1750 = 110 + 413 + 312 +
915 
 
Hope this makes sense.
 
KB
Kristopher S. Baker
Sustainability Specialist
LEED(r) Accredited Professional
Syska Hennessy Group, Inc.
 
 
11350 Random Hills Road,
Suite 750
Fairfax, VA 22030
Tel: 703.383.9383
Email:kbaker at syska.com <mailto:dcallan at syska.com>  
http://www.syska.com <http://www.syska.com/>  
 
 
________________________________
From: postman at gard.com [mailto:postman at gard.com] On Behalf Of Peter
Simmonds
Sent: Monday, January 17, 2005 3:18 PM
To: bldg-sim at gard.com
Subject: [bldg-sim] CHP energy cost summary
 
Does anyone have any experience with utility rate applications for
electricity? We are simulating the cost comparison of building having a
traditional chilled water plant and boilers against a plant having three
cogeneration units providing heat for an absorption chiller. The results
shown in report ES-E do not match report ES-F. The total charges should
be the same or am I missing something?
 
Peter Simmonds Ph.D.
Associate
IBE Consulting Engineers
14130 Riverside Drive Suite 201
Sherman Oaks, CA 91423
p:   (818) 377-8220
f:    (818) 377-8230
m:  (818) 219-1284
IDEAS FOR THE BUILT ENVIRONMENT <BLOCKED::http://www.ibece.com/> 
This e-mail message, including any attachments, is for the sole use of
the intended recipient(s) and may contain confidential and privileged
information. Any unauthorized review, use, disclosure, or distribution
is prohibited. If you are not the intended recipient, please contact the
sender by reply e-mail and destroy all copies of the original message.
 
 
 
==================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM
------------------
ATTACHMENT REMOVED
------------------
    
    
More information about the Bldg-sim
mailing list