Chiara, 

I don't have to look much farther than the data file. You have used a
comma for the decimal point and not '.' TRNSYS numbers must use the
decimal point. Please update your file and try again. 

Jeff 

---
Jeff Thornton
President - TESS LLC
22 N. Carroll Street, Madison WI USA 53703
Office: (608) 274-2577 Fax: (608) 278-1475
www.tess-inc.com
E-Mail: thornton at tess-inc.com

On 05/17/2018 4:35 pm, chiara pinto wrote: 

> I Jeff, 
> 
> here there is the project and the input file. I haven't the design capacity and the design power so i normalizd on the maximus value for each variable (capacity, power and flow rates). I'm using a black box approach so i have only real values. 
> 
> Thank you for your help. 
> 
> Best regard, 
> 
> Chiara 
> 
> Inviato da Posta [2] per Windows 10 
> 
> -------------------------
> 
> DA: TRNSYS-users <trnsys-users-bounces at lists.onebuilding.org> per conto di Jeff Thornton via TRNSYS-users <trnsys-users at lists.onebuilding.org>
> INVIATO: Thursday, May 17, 2018 11:19:59 PM
> A: trnsys-users at lists.onebuilding.org
> CC: Jeff Thornton
> OGGETTO: Re: [TRNSYS-users] R: R: I: strange output for type 927 
> 
> Chiara, 
> 
> It looks like the data file that you supplied to Type 927 is horribly wrong...LOL Type 927 requires a specially formatted file that contains the NORMALIZED performance (ratio of capacity to design capacity and ration of power to design power) at a combination of source and load temperatures and flow rates. It looks like maybe the file you are using isn't normalized. Please send us your project and data files and we can verify. 
> 
> Jeff 
> 
> ---
> Jeff Thornton
> President - TESS LLC
> 22 N. Carroll Street, Madison WI USA 53703
> Office: (608) 274-2577 Fax: (608) 278-1475
> www.tess-inc.com
> E-Mail: thornton at tess-inc.com
> 
> On 05/17/2018 11:28 am, chiara pinto via TRNSYS-users wrote: 
> 
> Hi Jeff, 
> 
> i took your advice and i saw the trace file .lst, that i sent you annexed to this e-mail. So the type 927 seems to be off but i don't understand why. How can i turn it on? I know that this question seems to be stupid but is my firt project in trnsys and i can't use very well yet. 
> 
> Thanks for your help. 
> 
> Best regards, 
> 
> Chiara 
> 
> Inviato da Posta [2] per Windows 10 
> 
> -------------------------
> 
> DA: TRNSYS-users <trnsys-users-bounces at lists.onebuilding.org> per conto di chiara pinto via TRNSYS-users <trnsys-users at lists.onebuilding.org>
> INVIATO: Thursday, May 17, 2018 6:25:32 PM
> A: Jeff Thornton; TRNSYS users mailing list at OneBuilding.org
> CC: chiara pinto
> OGGETTO: [TRNSYS-users] R: I: strange output for type 927 
> 
> Hi Jeff, 
> 
> i took your advice and i saw the trace file .lst, that i sent you annexed to this e-mail. So the type 927 seems to be off but i don't understand why. How can i turn it on? I know that this question seems to be stupid but is my firt project in trnsys and i can't use very well yet. 
> 
> Thanks for your help. 
> 
> Best regards, 
> 
> Chiara 
> 
> Inviato da Posta [2] per Windows 10 
> 
> -------------------------
> 
> DA: Jeff Thornton <thornton at tess-inc.com>
> INVIATO: Wednesday, May 16, 2018 2:59:02 AM
> A: TRNSYS users mailing list at OneBuilding.org
> CC: chiara pinto
> OGGETTO: Re: [TRNSYS-users] I: strange output for type 927 
> 
> Chiara, 
> 
> If you have no heat transfer from the heat pump that means the device is off. And if the device is off then the outlet temperature is set to the inlet temperature. So if you're seeing a large outlet temperature it means that you are giving the model a large inlet temperature. I suggest you review the TRACE command in TRNSYS and use it to figure out what may be going wrong with your simulation. 
> 
> Jeff - TESS
> 
> Sent from my iPhone 
> 
> On May 15, 2018, at 1:40 PM, chiara pinto via TRNSYS-users <trnsys-users at lists.onebuilding.org> wrote:
> 
> Inviato da Posta [2] per Windows 10 
> 
> DA: chiara pinto via TRNSYS-users
> INVIATO: lunedì 14 maggio 2018 20:17
> A: trnsys-users at lists.onebuilding.org
> CC: chiara pinto
> OGGETTO: [TRNSYS-users] strange output for type 927 
> 
> Hi everyone, 
> 
> i'm using type 927 to simulate a water to water heatpump. I have write the input file and i have modify the input schedule in trnsys, but ,when i run the simulation , i have strange value: for example my oulet load temperature= 1.6*10^8 and this is not normal. I have the same problem if i use the input file that trnsys give me as example with its default values. 
> 
> One other problem is that the heat pump seems to be off because heat transfer to load end heat transfer from source are zero. There is a type to impose that heat pump had to be on from 8.00 am to 17.00 pm? 
> 
> I really don't understand where the problem is. 
> 
> Has anyone a solution for this problem? 
> 
> Thanks for your help, 
> 
> Best regards, 
> 
> Chiara 
> 
> Inviato da Posta [2] per Windows 10 
> 
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org [1] 
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org [1] 
> 
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org [1]
 

Links:
------
[1]
http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
[2] https://go.microsoft.com/fwlink/?LinkId=550986
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20180517/7bfabf0f/attachment.htm>


More information about the TRNSYS-users mailing list