Chiara,

  That is a bad default value. The scale factor should be set to 1.

kind regards,

  David



On 05/08/2018 13:43, chiara pinto via TRNSYS-users wrote:
>
> Hi everyone,
>
> i’m using type 927 to simulate a water to water heat pump but when i 
> start the simulation an error like this occurs:
>
> TRNSYS Message  126 : The referenced Unit has a bad imput value
> Reported information : Input # 7, Reported Problem. The scale factor 
> must be above 0.
>
> The problem is that i have not changed this parameter and it is equal 
> to 0.
>
> Has anyone experienced this problem and knows how to fix it?
>
> Best regards,
>
> Chiara
>