Hi Hür,
You can set a variable cooling set temperature by defining an Input in TYPE 56
e.g. Y_summer (1:summer, 0:winter).
The set temperature can be set in the cooling type manager, use the option "input" and define the
set temperature as 2*Y_summer+22.
Furthermore you need to define Y_summer (e.g. depending on the variable "time") in an equation
in the Simulation Studio and pass it to TYPE 56.
Best
__________________________________________________________________________________________________
Jochen Lam
TRNSYS Software Team
Transsolar Energietechnik GmbH
Curiestraße 2
70563 Stuttgart
Fax: +49 711 67976-11
Email: jlam at transsolar.com<mailto:jlam at transsolar.com>
Web: www.trnsys.de<http://www.trnsys.de>
Von: trnsys-users-bounces at cae.wisc.edu [mailto:trnsys-users-bounces at cae.wisc.edu] Im Auftrag von hür bütün
Gesendet: Dienstag, 23. Juli 2013 12:46
An: trnsys-users at cae.wisc.edu
Betreff: [TRNSYS-users] Seasonal cooling
Hello,
How can I set seasonal cooling for type56b building . I would like to set the cooling target temperature to 22 in winter period and 24 in summer period.
Thanks,