[TRNSYS-users] Evaporative cooling system modelling inside a building (Type 56)
Jeff Thornton
thornton at tess-inc.com
Tue Feb 12 11:02:11 PST 2013
<I would like to introduce an evaporative cooling system (Misting
system) inside my building (Type 56) to test it's effect and analyze
it's performance. How is it possible to implement that machine so as to
detect the climatic improvement provided and also the possible change in
the humidity ratio within the building.>
You would connect the
temperature and RH from the building zone to an evaporative cooler
(fogger) model (TESS HVAC Library has one) and then connect the outputs
from the evaporative cooler model back to the building zone through a a
"Ventilation" stream for the zone.
Jeff
---
Jeff Thornton
_President - TESS LLC_
_22 N. Carroll Street, Madison WI USA 53703_
_Office: (608) 274-2577 Fax: (608) 278-1475_
_www.tess-inc.com_
_E-Mail: thornton at tess-inc.com_
On 02/11/2013 11:04 am, Mohamed Adel
wrote:
> Hello,
>
> Best Regards
>
> Mohamed Adel
> M.Sc. Ing.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20130212/a87ffa22/attachment-0005.htm>
More information about the TRNSYS-users
mailing list