[TRNSYS-users] Problem with Dry Fluid Cooler (type 511)

maxence.bureau at cofely-gdfsuez.com maxence.bureau at cofely-gdfsuez.com
Wed Apr 10 01:20:39 PDT 2013


Hello,

I would like to use a type 511 (HVAC Library (TESS) - Dry Fluid Cooler), but it doesn't work.

When the value of input 2 (fluid flow rate) is higher than 0, the simulation doesn't work and an error message appear ("TRNSYS errors : one error was found in the deck...").

I have this error message in "list file" :
"*** Fatal Error at time   :         0.125000
    Generated by Unit     :    10
    Generated by Type     :   511
    Message               : The dry cooler model was unable to correctly calculate the number of transfer units (NTU) for the design condition.  Please check the design conditions carefully."

I tested the type with the defaults design conditions, but it was the same error message. I think there is a problem with input 2.

Please find attached my ".tpf" file.
Thank you for your help.

Sincerely,

Maxence BUREAU
Ingénieur de Recherche
______________________________________________________________________
[cid:image001.jpg at 01CE35D1.B01AB3A0]


Centre de recherche Cylergie
L'Orée d'Ecully - Bât. C - Chemin de la Forestière
69130 - ECULLY
tel. +33472860980 - fax +33478433959
mailto:maxence.bureau at cofely-gdfsuez.com
www.cofely-gdfsuez.fr<http://www.cofely-gdfsuez.fr>

Before printing, think about the environment / Avant d'imprimer, pensez à l'environnement
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20130410/659f04fa/attachment-0005.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 6840 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20130410/659f04fa/attachment-0005.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Test_Dry_Cooler.tpf
Type: application/octet-stream
Size: 179384 bytes
Desc: Test_Dry_Cooler.tpf
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20130410/659f04fa/attachment-0005.obj>
-------------- next part --------------



Before printing, think about the environment / Avant d'imprimer, pensez a l'environnement 

GDF SUEZ Mail Disclaimer: http://www.gdfsuez.com/disclaimer/disclaimer-fr.html



More information about the TRNSYS-users mailing list