Type2 models a differential temperature controller. It's control
decision is based on the difference between two values no matter what
the magnitudes of those values are. A typical thermostat makes a control
decision by comparing the magnitude of two values (not just the
difference). While you can use a type2 to model a thermostat, I think it
would be easier in your case to use Type108 (Controllers: 5-Stage Room
thermostat.)
Regards,
David
On 12/7/2012 05:36, Talib Ahmadu wrote:
> Dear all,
> I want to create a control for a multizone building cooling model
> using type 2d. I have used an absorption chiller, type 107. I want the
> chiller on when the temperature in the zones exceed 24C and off when
> the temperature falls below 19C. These are my inputs.
> Upper input value= Tzone
> Lower input value=0
> Upper dead band=24
> Lower bead band=19
> I tried this for a single zone but it didnt seem to work well. I have
> 9 zones in the building, my problem is how to connect all zone
> temperatures to Upper input value.
> Please i need to know if this strategy is correct and how i can
> connect all zone temperatures. Suggestions will be appreciated. Thanks
> Talib.
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20121207/e8b70271/attachment-0005.htm>
More information about the TRNSYS-users
mailing list