[TRNSYS-users] Error: generating shading/insolation matrix
Joke De Beuckelaer
joke.d at vkgroup.be
Wed May 18 23:42:04 PDT 2011
Thanks a lot! You saved my day if that is the problem :-)
I don't know if it's still necessary, but normally the original idf file was attached in the last mail. But it's about 3MB so I don't know if you received it or if it is too big.
Greetings,
Joke De Beuckelaer
project engineer mep
VK HEALTHCARE | BUILDINGS | INDUSTRY | INFRA
Value by design
VK ENGINEERING Avenue Clemenceaulaan 87, 1070 Bruxelles Brussel, Belgium
t +32 2 414 07 77 f +32 2 414 04 98 m +32 473 97 01 50 e joke.d at vkgroup.be w www.vkgroup.be
-----Oorspronkelijk bericht-----
Van: Marion Hiller [mailto:hiller at transsolar.com]
Verzonden: donderdag 19 mei 2011 8:39
Aan: Joke De Beuckelaer
CC: TRNSYS-users
Onderwerp: AW: RE: Re: [TRNSYS-users] Error: generating shading/insolation matrix
Dear Joke,
in Trnsys3d the surfaces (walls, window and shaders) have arbitrary
names composed by numbers and characters. The import converts them to
unique surface ID numbers without changing existing already converted
surface IDs. In Version 17.00.0018 the import had a bug when there where
no characters in the automatic generated name of trnsys3D.
This bug is fixed in the current version 17.00.0019. in order to solve
your problem, please contact your distributor for a free update.
Kind Regards,
Marion
P.S. I received two emails with attachments but the original IDF file
doesn't seem to be included.
Dipl.-Ing. Marion Hiller
TRANSSOLAR: KlimaEngineering - Technologien für energieeffizientes Bauen
und Nutzerkomfort in Gebäude
Munich - New York - Stuttgart + 49.711.67976.0
Transsolar Energietechnik GmbH, Curiestrasse 2, 70563 Stuttgart
Amtsgericht Stuttgart - HRB 23347, Steuernummer 99073/00911, USt-IdNr.:
DE152272639
Geschäftsführer: Dipl.Ing. Matthias Schuler, Dipl.Ing. Thomas Auer,
Dipl.Phys. Stefan Holst, Prof. Dipl.-Ing. Bleicher
-----Ursprüngliche Nachricht-----
Von: Joke De Beuckelaer [mailto:joke.d at vkgroup.be]
Gesendet: Donnerstag, 19. Mai 2011 08:09
An: Marion Hiller
Cc: TRNSYS-users
Betreff: RE: Re: [TRNSYS-users] Error: generating shading/insolation
matrix
Dear Marion,
It's strange that the error occurs because the surface number>999. When
I deleted all the shading except 1 rectangle, the same error occurred.
Or is this number (999) with the surfaces of the model included?
In attachment you can find the original idf file. Normally I've send all
my files already, didn't you receive them?
I'm working with Trnsys version 17.00.0018.
Thanks a lot already for all your help and I hope you can find the
problem,
Kind regards,
Joke De Beuckelaer
project engineer mep
VK HEALTHCARE | BUILDINGS | INDUSTRY |
INFRA
Value by design
VK ENGINEERING Avenue Clemenceaulaan 87, 1070 Bruxelles Brussel,
Belgium
t +32 2 414 07 77 f +32 2 414 04 98 m +32 473 97 01 50 e
joke.d at vkgroup.be w www.vkgroup.be
-----Oorspronkelijk bericht-----
Van: Marion Hiller [mailto:hiller at transsolar.com]
Verzonden: dinsdag 17 mei 2011 13:27
Aan: Joke De Beuckelaer
CC: TRNSYS-users
Onderwerp: AW: Re: [TRNSYS-users] Error: generating shading/insolation
matrix
Joke,
the error message is due to too surface numbers > 999. The surface
number can't be written in the log file (artsmetiers7_shd.log) and ***
are written instead.
*** Notice at time : 0.000000
Orientation of wall SURF=***: azimuth angle= 180.00°, slope= 90.00°
Orientation of wall SURF=***: azimuth angle= 0.00°, slope= 0.00°
In order to see why the surface numbers are so high (starting with
3993 instead of 1) I need to need the original *.idf and check the
import function.
With what version of TRNSYS17 are you working? I have in mind that we
fixed such a bug created by the import.
Kind regards,
Marion
-----Ursprüngliche Nachricht-----
Von: Joke De Beuckelaer [mailto:joke.d at vkgroup.be]
Gesendet: Donnerstag, 12. Mai 2011 08:58
An: duffy at tess-inc.com; trnsys-users at cae.wisc.edu
Betreff: Re: [TRNSYS-users] Error: generating shading/insolation matrix
_______________________________________________
TRNSYS-users mailing list
TRNSYS-users at cae.wisc.edu
https://mailman.cae.wisc.edu/listinfo/trnsys-users
VISIT US AT REALTY SUBSCRIBE FOR THE VK-COCKTAIL AT REALTY
<mailto:marketing at vkgroup.be?SUBJECT=vk-cocktail>
****DISCLAIMER****
This communication is confidential and for the sole useof the addressee.
If you are not the intended recipient,
please immediately notify the sender by e-mail at the address shown and
then delete it from your system
without copying, disclosing or forwarding its contents. Thank you.
VISIT US AT REALTY SUBSCRIBE FOR THE VK-COCKTAIL AT REALTY<mailto:marketing at vkgroup.be?SUBJECT=vk-cocktail>
****DISCLAIMER****
This communication is confidential and for the sole useof the addressee. If you are not the intended recipient,
please immediately notify the sender by e-mail at the address shown and then delete it from your system
without copying, disclosing or forwarding its contents. Thank you.
More information about the TRNSYS-users
mailing list