[TRNSYS-users] Active Layer - Problem
David BRADLEY
d.bradley at tess-inc.com
Fri May 6 11:58:34 PDT 2011
Florian,
I have seen that behavior as well; what it comes down to is the time
base that you have selected in TRNBuild. If the wall transfer function
coefficients are computed based on 1-hour intervals then you are going
to see some discrete behavior if your timestep gets too far away from
your time base. It is best to have your time step and your time base
match but that isn't practical. Try generating the wall coefficients
with a 0.25 hour time base and see if that helps.
Best,
David
On 5/4/2011 02:36, Stift Florian wrote:
>
> Dear TRNSYS-users,
>
> I am simulating a room with an active layer in the separating wall.
>
> I tried to change the simulation timestep to 1 min. to get more exact
> results.
>
> What I realized is, that the output started to show discrete results
> in an hour interval.
>
> My Question: Could it be that TRNSYS has a limitation in the active
> layer system, to solve it in one hour timesteps only?
>
> Can I change this somehow?
>
> Thanks for your help,
>
> Florian
>
> *FLORIAN STIFT, DI(FH)*
>
> Energy Department
>
> Sustainable Building Technologies
>
> *AIT Austrian Institute of Technology *
>
> Österreichisches Forschungs- und Prüfzentrum Arsenal Ges.m.b.H.
>
> Giefinggasse 2 | 1210 Vienna | Austria
>
> T +43(0) 50550-6277 | M +43(0) 664 815 79 46 | F +43(0) 50550-6613
>
> florian.stift at ait.ac.at <mailto:florian.stift at ait.ac.at>__|
> _http://www.ait.ac.at _
>
> FN: 165088b HG Wien | UID: ATU46577208 This email and any attachments
> thereto, is intended only for use by the addressee(s) named herein and
> may contain legally privileged and/or confidential information. If you
> are not the intended recipient, please notify the sender by return
> e-mail or by telephone and delete this message from your system and
> any printout thereof. Any unauthorized use, reproduction, or
> dissemination of this message is strictly prohibited. Please note that
> e-mails are susceptible to change. Österreichisches Forschungs- und
> Prüfzentrum Arsenal Ges.m.b.H. shall not be liable for the improper or
> incomplete transmission of the information contained in this
> communication, nor shall it be liable for any delay in its receipt.
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20110506/d6a6b036/attachment-0005.htm>
More information about the TRNSYS-users
mailing list