[TRNSYS-users] Problem of temperature decrease
Augustin CUQ
augustin.cuq at gmail.com
Tue May 24 01:14:57 PDT 2011
Dear trnsys-users,
I have made a simple model, with a two rooms building. The regulation device
is as simple as the model: when the temperature is lower than the
instruction one , the heating signal is put to 1; else, it remains equal to
0.
When the heating signal is put to 1, the temperature of the concerned room
increases logically. When the signal becomes equal to 0, temperature go down
very fast during two time steps. Then, a little increase of the temperature
can be observed (but there is no reason why...).
The little increase I previously mentioned can be observed changing the
heating device by the TRNSys Building heating type manager (after the same
number of time step).
I tried to modify the time step, the radiative part of the heating device,
the power of the heating device, the walls composition but nothing has
changed...
Can anyone explain to me why those phenomenons are observed?
Thanks in advance.
Please find attached some results of the simulation... It can, for instance,
be observed between the simulation times 14.75hr and 18.75hr
--
Augustin CUQ
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20110524/1f52121a/attachment-0001.htm>
-------------- next part --------------
TIME Top_Room1 Top_Room2 Text Heat_Sign_Room1 Heat_Sign_Room2 Tcons_1 Tcons_2 Total Power for Room1 Total Power for Room2 Temp_diff 1 Temp_diff 2
1 19.13 19.21 -5.4 - - 16 16 - - 3.13 3.21
1.25 19.16 19.17 -5.4 - - 16 16 - - 3.16 3.17
1.5 19.15 19.18 -5.4 - - 16 16 - - 3.15 3.18
1.75 19.14 19.16 -5.9 - - 16 16 - - 3.14 3.16
2 18.88 18.93 -5.9 - - 16 16 - - 2.88 2.93
2.25 18.79 18.85 -5.9 - - 16 16 - - 2.79 2.85
2.5 18.81 18.87 -5.9 - - 16 16 - - 2.81 2.87
2.75 18.8 18.86 -6.1 - - 16 16 - - 2.8 2.86
3 18.59 18.67 -6.1 - - 16 16 - - 2.59 2.67
3.25 18.51 18.6 -6.1 - - 16 16 - - 2.51 2.6
3.5 18.53 18.62 -6.1 - - 16 16 - - 2.53 2.62
3.75 18.52 18.61 -6.3 - - 16 16 - - 2.52 2.61
4 18.32 18.42 -6.3 - - 16 16 - - 2.32 2.42
4.25 18.24 18.36 -6.3 - - 16 16 - - 2.24 2.36
4.5 18.26 18.38 -6.3 - - 16 16 - - 2.26 2.38
4.75 18.25 18.37 -6.4 - - 16 16 - - 2.25 2.37
5 18.05 18.18 -6.4 - - 16 16 - - 2.05 2.18
5.25 17.98 18.12 -6.4 - - 16 16 - - 1.98 2.12
5.5 17.99 18.14 -6.4 - - 16 16 - - 1.99 2.14
5.75 17.97 18.11 -7 - - 16 16 - - 1.97 2.11
6 17.76 17.92 -7 - - 16 16 - - 1.76 1.92
6.25 17.69 17.85 -7 - - 16 16 - - 1.69 1.85
6.5 17.7 17.87 -7 - - 16 16 - - 1.7 1.87
6.75 17.65 17.82 -8.4 - - 16 16 - - 1.65 1.82
7 17.42 17.61 -8.4 - - 16 16 - - 1.42 1.61
7.25 17.35 17.55 -8.4 - - 16 16 - - 1.35 1.55
7.5 17.37 17.56 -8.4 - - 16 16 - - 1.37 1.56
7.75 17.28 17.47 -10.9 - - 16 16 - - 1.28 1.47
8 17.03 17.24 -10.9 - - 16 16 - - 1.03 1.24
8.25 17.09 20.42 -10.9 - 1 16 19 - 32 046.67 1.09 1.42
8.5 17.05 18.81 -10.9 - - 16 19 - - 1.05 -0.19
8.75 17.1 20.05 -10.3 - 1 16 19 - 32 046.67 1.1 1.05
9 16.94 19.39 -10.3 - - 16 19 - - 0.94 0.39
9.25 16.86 17.45 -10.3 - - 16 19 - - 0.86 -1.55
9.5 16.98 21.19 -10.3 - 1 16 19 - 32 046.67 0.98 2.19
9.75 17.03 19.48 -7.6 - - 16 19 - - 1.03 0.48
10 16.87 17.75 -7.6 - - 16 19 - - 0.87 -1.25
10.25 16.86 21.51 -7.6 - 1 16 19 - 32 046.67 0.86 2.51
10.5 16.84 19.69 -7.6 - - 16 19 - - 0.84 0.69
10.75 16.85 17.83 -6.1 - - 16 19 - - 0.85 -1.17
11 16.81 21.66 -6.1 - 1 16 19 - 32 046.67 0.81 2.66
11.25 16.72 19.88 -6.1 - - 16 19 - - 0.72 0.88
11.5 16.69 17.96 -6.1 - - 16 19 - - 0.69 -1.04
11.75 16.78 21.71 -5.7 - 1 16 19 - 32 046.67 0.78 2.71
12 16.65 20.31 -5.7 - - 16 19 - - 0.65 1.31
12.25 16.57 18.54 -5.7 - - 16 19 - - 0.57 -0.46
12.5 16.67 22.23 -5.7 - 1 16 19 - 32 046.67 0.67 3.23
12.75 16.67 20.47 -4.8 - - 16 19 - - 0.67 1.47
13 16.53 18.69 -4.8 - - 16 19 - - 0.53 -0.31
13.25 16.55 22.45 -4.8 - 1 16 19 - 32 046.67 0.55 3.45
13.5 16.52 20.62 -4.8 - - 16 19 - - 0.52 1.62
13.75 16.5 18.73 -4.1 - - 16 19 - - 0.5 -0.27
14 16.5 22.55 -4.1 - 1 16 19 - 32 046.67 0.5 3.55
14.25 20.01 20.79 -4.1 1 - 19 16 32 046.67 - 1.01 4.79
14.5 18.32 18.8 -4.1 - - 19 16 - - -0.68 2.8
14.75 19.68 19.38 -4.2 1 - 19 16 32 046.67 - 0.68 3.38
15 19.14 19.34 -4.2 - - 19 16 - - 0.14 3.34
15.25 17.16 19.39 -4.2 - - 19 16 - - -1.84 3.39
15.5 21.13 19.45 -4.2 1 - 19 16 32 046.67 - 2.13 3.45
15.75 19.3 19.4 -4.7 - - 19 16 - - 0.3 3.4
16 17.44 19.12 -4.7 - - 19 16 - - -1.56 3.12
16.25 21.49 19.12 -4.7 1 - 19 16 32 046.67 - 2.49 3.12
16.5 19.68 19.11 -4.7 - - 19 16 - - 0.68 3.11
16.75 18.45 19.24 -6.4 - - 19 16 - - -0.55 3.24
17 21.81 18.91 -6.4 1 - 19 16 32 046.67 - 2.81 2.91
17.25 19.62 18.7 -6.4 - - 19 16 - - 0.62 2.7
17.5 17.55 18.7 -6.4 - - 19 16 - - -1.45 2.7
17.75 21.47 18.74 -7.2 1 - 19 16 32 046.67 - 2.47 2.74
18 20.07 18.51 -7.2 - - 19 16 - - 1.07 2.51
18.25 18.05 18.4 -7.2 - - 16 16 - - 2.05 2.4
18.5 18.46 18.42 -7.2 - - 16 16 - - 2.46 2.42
18.75 18.38 18.42 -7.2 - - 16 16 - - 2.38 2.42
19 18.11 18.2 -7.2 - - 16 16 - - 2.11 2.2
19.25 18 18.12 -7.2 - - 16 16 - - 2 2.12
19.5 18.02 18.14 -7.2 - - 16 16 - - 2.02 2.14
19.75 18.07 18.19 -5.7 - - 16 16 - - 2.07 2.19
20 17.84 18.01 -5.7 - - 16 16 - - 1.84 2.01
20.25 17.73 17.93 -5.7 - - 16 16 - - 1.73 1.93
20.5 17.75 17.95 -5.7 - - 16 16 - - 1.75 1.95
20.75 17.76 17.96 -5.3 - - 16 16 - - 1.76 1.96
21 17.55 17.78 -5.3 - - 16 16 - - 1.55 1.78
21.25 17.46 17.71 -5.3 - - 16 16 - - 1.46 1.71
21.5 17.48 17.73 -5.3 - - 16 16 - - 1.48 1.73
21.75 17.49 17.74 -4.9 - - 16 16 - - 1.49 1.74
22 17.29 17.57 -4.9 - - 16 16 - - 1.29 1.57
22.25 17.22 17.5 -4.9 - - 16 16 - - 1.22 1.5
22.5 17.23 17.52 -4.9 - - 16 16 - - 1.23 1.52
22.75 17.24 17.53 -4.6 - - 16 16 - - 1.24 1.53
23 17.05 17.36 -4.6 - - 16 16 - - 1.05 1.36
23.25 16.98 17.3 -4.6 - - 16 16 - - 0.98 1.3
23.5 17 17.32 -4.6 - - 16 16 - - 1 1.32
23.75 16.98 17.31 -4.8 - - 16 16 - - 0.98 1.31
24 16.8 17.14 -4.8 - - 16 16 - - 0.8 1.14
24.25 16.73 17.08 -4.8 - - 16 16 - - 0.73 1.08
24.5 16.74 17.1 -4.8 - - 16 16 - - 0.74 1.1
24.75 16.73 17.08 -5 - - 16 16 - - 0.73 1.08
25 16.55 16.92 -5 - - 16 16 - - 0.55 0.92
25.25 16.49 16.86 -5 - - 16 16 - - 0.49 0.86
25.5 16.5 16.88 -5 - - 16 16 - - 0.5 0.88
25.75 16.5 16.88 -4.9 - - 16 16 - - 0.5 0.88
26 16.33 16.72 -4.9 - - 16 16 - - 0.33 0.72
26.25 16.26 16.66 -4.9 - - 16 16 - - 0.26 0.66
26.5 16.28 16.67 -4.9 - - 16 16 - - 0.28 0.67
26.75 16.28 16.68 -4.7 - - 16 16 - - 0.28 0.68
27 16.12 16.52 -4.7 - - 16 16 - - 0.12 0.52
27.25 16.05 16.47 -4.7 - - 16 16 - - 0.05 0.47
27.5 16.07 16.48 -4.7 - - 16 16 - - 0.07 0.48
27.75 16.05 16.47 -5 - - 16 16 - - 0.05 0.47
28 15.88 16.31 -5 - - 16 16 - - -0.12 0.31
28.25 19.32 16.33 -5 1 - 16 16 32 046.67 - 3.32 0.33
28.5 17.62 16.31 -5 - - 16 16 - - 1.62 0.31
28.75 15.44 16.26 -5 - - 16 16 - - -0.56 0.26
29 19.64 16.21 -5 1 - 16 16 32 046.67 - 3.64 0.21
29.25 17.9 16.13 -5 - - 16 16 - - 1.9 0.13
29.5 15.73 16.09 -5 - - 16 16 - - -0.27 0.09
29.75 19.68 16.15 -5.6 1 - 16 16 32 046.67 - 3.68 0.15
30 18.36 15.99 -5.6 - - 16 16 - - 2.36 -0.01
30.25 16.47 19.09 -5.6 - 1 16 16 - 32 046.67 0.47 3.09
30.5 16.86 17.45 -5.6 - - 16 16 - - 0.86 1.45
30.75 16.72 15.49 -5.7 - - 16 16 - - 0.72 -0.51
31 16.61 19.39 -5.7 - 1 16 16 - 32 046.67 0.61 3.39
31.25 16.49 17.64 -5.7 - - 16 16 - - 0.49 1.64
31.5 16.46 15.71 -5.7 - - 16 16 - - 0.46 -0.29
31.75 16.55 19.44 -5.5 - 1 16 16 - 32 046.67 0.55 3.44
32 16.33 18.05 -5.5 - - 16 16 - - 0.33 2.05
32.25 16.34 19.54 -5.5 - 1 16 19 - 32 046.67 0.34 0.54
32.5 16.31 18.41 -5.5 - - 16 19 - - 0.31 -0.59
32.75 16.36 19.53 -4.7 - 1 16 19 - 32 046.67 0.36 0.53
33 16.21 18.9 -4.7 - - 16 19 - - 0.21 -0.1
33.25 16.2 20.12 -4.7 - 1 16 19 - 32 046.67 0.2 1.12
33.5 16.19 19.02 -4.7 - - 16 19 - - 0.19 0.02
33.75 16.14 16.9 -5 - - 16 19 - - 0.14 -2.1
34 16.09 20.81 -5 - 1 16 19 - 32 046.67 0.09 1.81
34.25 16.02 19.04 -5 - - 16 19 - - 0.02 0.04
34.5 15.99 17.12 -5 - - 16 19 - - -0.01 -1.88
34.75 19.58 20.94 -4.6 1 1 16 19 32 046.67 32 046.67 3.58 1.94
35 18.07 19.52 -4.6 - - 16 19 - - 2.07 0.52
35.25 15.92 17.7 -4.6 - - 16 19 - - -0.08 -1.3
35.5 19.95 21.46 -4.6 1 1 16 19 32 046.67 32 046.67 3.95 2.46
35.75 18.11 19.64 -4.2 - - 16 19 - - 2.11 0.64
36 16.2 17.82 -4.2 - - 16 19 - - 0.2 -1.18
36.25 16.85 21.6 -4.2 - 1 16 19 - 32 046.67 0.85 2.6
36.5 16.69 19.77 -4.2 - - 16 19 - - 0.69 0.77
36.75 16.66 17.85 -4.8 - - 16 19 - - 0.66 -1.15
37 16.51 21.63 -4.8 - 1 16 19 - 32 046.67 0.51 2.63
37.25 16.39 19.85 -4.8 - - 16 19 - - 0.39 0.85
37.5 16.35 17.91 -4.8 - - 16 19 - - 0.35 -1.09
37.75 16.42 21.63 -5.1 - 1 16 19 - 32 046.67 0.42 2.63
38 16.25 20.21 -5.1 - - 16 19 - - 0.25 1.21
38.25 19.69 18.45 -5.1 1 - 19 16 32 046.67 - 0.69 2.45
38.5 18.01 18.87 -5.1 - - 19 16 - - -0.99 2.87
38.75 19.32 18.77 -5.2 1 - 19 16 32 046.67 - 0.32 2.77
39 18.63 18.55 -5.2 - - 19 16 - - -0.37 2.55
39.25 20.05 18.49 -5.2 1 - 19 16 32 046.67 - 1.05 2.49
39.5 18.79 18.48 -5.2 - - 19 16 - - -0.21 2.48
39.75 19.99 18.48 -5.6 1 - 19 16 32 046.67 - 0.99 2.48
40 19.27 18.24 -5.6 - - 19 16 - - 0.27 2.24
40.25 17.18 18.12 -5.6 - - 19 16 - - -1.82 2.12
40.5 21.12 18.22 -5.6 1 - 19 16 32 046.67 - 2.12 2.22
40.75 19.29 18.15 -6.1 - - 19 16 - - 0.29 2.15
41 17.27 17.9 -6.1 - - 19 16 - - -1.73 1.9
41.25 21.29 17.91 -6.1 1 - 19 16 32 046.67 - 2.29 1.91
41.5 19.47 17.89 -6.1 - - 19 16 - - 0.47 1.89
41.75 17.32 17.84 -6.1 - - 19 16 - - -1.68 1.84
42 21.36 17.73 -6.1 1 - 19 16 32 046.67 - 2.36 1.73
42.25 19.54 17.63 -6.1 - - 16 16 - - 3.54 1.63
42.5 17.36 17.6 -6.1 - - 16 16 - - 1.36 1.6
42.75 17.83 17.6 -6.1 - - 16 16 - - 1.83 1.6
43 17.83 17.42 -6.1 - - 16 16 - - 1.83 1.42
43.25 17.89 17.35 -6.1 - - 16 16 - - 1.89 1.35
43.5 17.87 17.37 -6.1 - - 16 16 - - 1.87 1.37
43.75 17.88 17.37 -5.9 - - 16 16 - - 1.88 1.37
44 17.6 17.19 -5.9 - - 16 16 - - 1.6 1.19
44.25 17.49 17.12 -5.9 - - 16 16 - - 1.49 1.12
44.5 17.51 17.14 -5.9 - - 16 16 - - 1.51 1.14
44.75 17.51 17.13 -5.8 - - 16 16 - - 1.51 1.13
45 17.28 16.95 -5.8 - - 16 16 - - 1.28 0.95
45.25 17.19 16.89 -5.8 - - 16 16 - - 1.19 0.89
45.5 17.21 16.91 -5.8 - - 16 16 - - 1.21 0.91
45.75 17.22 16.92 -5.4 - - 16 16 - - 1.22 0.92
46 17.01 16.75 -5.4 - - 16 16 - - 1.01 0.75
46.25 16.93 16.69 -5.4 - - 16 16 - - 0.93 0.69
46.5 16.95 16.7 -5.4 - - 16 16 - - 0.95 0.7
46.75 16.95 16.71 -5.2 - - 16 16 - - 0.95 0.71
47 16.76 16.54 -5.2 - - 16 16 - - 0.76 0.54
47.25 16.68 16.48 -5.2 - - 16 16 - - 0.68 0.48
47.5 16.7 16.5 -5.2 - - 16 16 - - 0.7 0.5
47.75 16.7 16.5 -5 - - 16 16 - - 0.7 0.5
48 16.51 16.34 -5 - - 16 16 - - 0.51 0.34
48.25 16.44 16.28 -5 - - 16 16 - - 0.44 0.28
48.5 16.46 16.3 -5 - - 16 16 - - 0.46 0.3
48.75 16.46 16.31 -4.7 - - 16 16 - - 0.46 0.31
49 16.29 16.15 -4.7 - - 16 16 - - 0.29 0.15
49.25 16.22 16.1 -4.7 - - 16 16 - - 0.22 0.1
49.5 16.23 16.11 -4.7 - - 16 16 - - 0.23 0.11
49.75 16.24 16.12 -4.4 - - 16 16 - - 0.24 0.12
50 16.07 15.97 -4.4 - - 16 16 - - 0.07 -0.03
50.25 16.08 19.11 -4.4 - 1 16 16 - 32 046.67 0.08 3.11
50.5 16.06 17.46 -4.4 - - 16 16 - - 0.06 1.46
50.75 16.01 15.5 -4.4 - - 16 16 - - 0.01 -0.5
51 15.94 19.41 -4.4 - 1 16 16 - 32 046.67 -0.06 3.41
51.25 19.35 17.74 -4.4 1 - 16 16 32 046.67 - 3.35 1.74
51.5 17.61 15.77 -4.4 - - 16 16 - - 1.61 -0.23
51.75 15.51 19.46 -4.3 - 1 16 16 - 32 046.67 -0.49 3.46
52 19.7 18.18 -4.3 1 - 16 16 32 046.67 - 3.7 2.18
52.25 17.94 16.38 -4.3 - - 16 16 - - 1.94 0.38
52.5 15.77 16.83 -4.3 - - 16 16 - - -0.23 0.83
52.75 19.75 16.78 -4.1 1 - 16 16 32 046.67 - 3.75 0.78
53 18.43 16.6 -4.1 - - 16 16 - - 2.43 0.6
53.25 16.47 16.48 -4.1 - - 16 16 - - 0.47 0.48
53.5 16.89 16.51 -4.1 - - 16 16 - - 0.89 0.51
53.75 16.8 16.5 -4.1 - - 16 16 - - 0.8 0.5
54 16.59 16.31 -4.1 - - 16 16 - - 0.59 0.31
54.25 16.5 16.24 -4.1 - - 16 16 - - 0.5 0.24
54.5 16.52 16.26 -4.1 - - 16 16 - - 0.52 0.26
54.75 16.52 16.26 -4 - - 16 16 - - 0.52 0.26
55 16.31 16.09 -4 - - 16 16 - - 0.31 0.09
55.25 16.24 16.04 -4 - - 16 16 - - 0.24 0.04
55.5 16.26 16.05 -4 - - 16 16 - - 0.26 0.05
55.75 16.26 16.05 -3.9 - - 16 16 - - 0.26 0.05
56 16.08 15.9 -3.9 - - 16 16 - - 0.08 -0.1
56.25 16.14 19.1 -3.9 - 1 16 19 - 32 046.67 0.14 0.1
56.5 16.1 17.48 -3.9 - - 16 19 - - 0.1 -1.52
56.75 16.12 18.72 -3.8 - 1 16 19 - 32 046.67 0.12 -0.28
57 16.06 21.29 -3.8 - 1 16 19 - 32 046.67 0.06 2.29
57.25 15.95 17.68 -3.8 - - 16 19 - - -0.05 -1.32
57.5 19.51 19.56 -3.8 1 1 16 19 32 046.67 32 046.67 3.51 0.56
57.75 17.76 18.25 -3.6 - - 16 19 - - 1.76 -0.75
58 15.93 19.89 -3.6 - 1 16 19 - 32 046.67 -0.07 0.89
58.25 19.98 19.07 -3.6 1 - 16 19 32 046.67 - 3.98 0.07
58.5 18.08 16.87 -3.6 - - 16 19 - - 2.08 -2.13
58.75 16.05 20.64 -3.4 - 1 16 19 - 32 046.67 0.05 1.64
59 16.68 19.17 -3.4 - - 16 19 - - 0.68 0.17
59.25 16.6 17.38 -3.4 - - 16 19 - - 0.6 -1.62
59.5 16.69 21.08 -3.4 - 1 16 19 - 32 046.67 0.69 2.08
59.75 16.67 19.29 -3.1 - - 16 19 - - 0.67 0.29
60 16.45 17.52 -3.1 - - 16 19 - - 0.45 -1.48
60.25 16.47 21.29 -3.1 - 1 16 19 - 32 046.67 0.47 2.29
60.5 16.45 19.47 -3.1 - - 16 19 - - 0.45 0.47
60.75 16.4 17.55 -2.8 - - 16 19 - - 0.4 -1.45
61 16.35 21.38 -2.8 - 1 16 19 - 32 046.67 0.35 2.38
61.25 16.27 19.6 -2.8 - - 16 19 - - 0.27 0.6
61.5 16.24 17.68 -2.8 - - 16 19 - - 0.24 -1.32
61.75 16.34 21.43 -2.3 - 1 16 19 - 32 046.67 0.34 2.43
62 16.23 20.04 -2.3 - - 16 19 - - 0.23 1.04
62.25 19.7 18.29 -2.3 1 - 19 16 32 046.67 - 0.7 2.29
62.5 18.04 18.72 -2.3 - - 19 16 - - -0.96 2.72
62.75 19.42 18.63 -2.2 1 - 19 16 32 046.67 - 0.42 2.63
63 18.81 18.46 -2.2 - - 19 16 - - -0.19 2.46
63.25 20.24 18.41 -2.2 1 - 19 16 32 046.67 - 1.24 2.41
63.5 18.95 18.39 -2.2 - - 19 16 - - -0.05 2.39
63.75 20.14 18.39 -2.5 1 - 19 16 32 046.67 - 1.14 2.39
64 19.49 18.19 -2.5 - - 19 16 - - 0.49 2.19
64.25 17.42 18.08 -2.5 - - 19 16 - - -1.58 2.08
64.5 21.35 18.17 -2.5 1 - 19 16 32 046.67 - 2.35 2.17
64.75 19.5 18.1 -3.1 - - 19 16 - - 0.5 2.1
65 17.47 17.86 -3.1 - - 19 16 - - -1.53 1.86
65.25 21.5 17.88 -3.1 1 - 19 16 32 046.67 - 2.5 1.88
65.5 19.66 17.86 -3.1 - - 19 16 - - 0.66 1.86
65.75 17.52 17.8 -3.2 - - 19 16 - - -1.48 1.8
66 21.58 17.71 -3.2 1 - 19 16 32 046.67 - 2.58 1.71
66.25 19.75 17.62 -3.2 - - 16 16 - - 3.75 1.62
66.5 17.58 17.59 -3.2 - - 16 16 - - 1.58 1.59
66.75 18.05 17.59 -3.2 - - 16 16 - - 2.05 1.59
67 18.07 17.43 -3.2 - - 16 16 - - 2.07 1.43
67.25 18.13 17.38 -3.2 - - 16 16 - - 2.13 1.38
67.5 18.12 17.39 -3.2 - - 16 16 - - 2.12 1.39
67.75 18.13 17.4 -2.9 - - 16 16 - - 2.13 1.4
68 17.87 17.23 -2.9 - - 16 16 - - 1.87 1.23
68.25 17.76 17.17 -2.9 - - 16 16 - - 1.76 1.17
68.5 17.79 17.19 -2.9 - - 16 16 - - 1.79 1.19
68.75 17.81 17.21 -2.1 - - 16 16 - - 1.81 1.21
69 17.61 17.07 -2.1 - - 16 16 - - 1.61 1.07
69.25 17.53 17.01 -2.1 - - 16 16 - - 1.53 1.01
69.5 17.55 17.02 -2.1 - - 16 16 - - 1.55 1.02
69.75 17.56 17.03 -1.6 - - 16 16 - - 1.56 1.03
70 17.38 16.9 -1.6 - - 16 16 - - 1.38 0.9
70.25 17.31 16.84 -1.6 - - 16 16 - - 1.31 0.84
70.5 17.32 16.86 -1.6 - - 16 16 - - 1.32 0.86
70.75 17.33 16.86 -1.3 - - 16 16 - - 1.33 0.86
71 17.16 16.73 -1.3 - - 16 16 - - 1.16 0.73
71.25 17.1 16.68 -1.3 - - 16 16 - - 1.1 0.68
71.5 17.11 16.69 -1.3 - - 16 16 - - 1.11 0.69
71.75 17.12 16.7 -1 - - 16 16 - - 1.12 0.7
72 16.96 16.57 -1 - - 16 16 - - 0.96 0.57
72.25 16.9 16.52 -1 - - 16 16 - - 0.9 0.52
72.5 16.91 16.53 -1 - - 16 16 - - 0.91 0.53
72.75 16.9 16.52 -1.2 - - 16 16 - - 0.9 0.52
73 16.74 16.39 -1.2 - - 16 16 - - 0.74 0.39
73.25 16.69 16.35 -1.2 - - 16 16 - - 0.69 0.35
73.5 16.7 16.36 -1.2 - - 16 16 - - 0.7 0.36
73.75 16.71 16.37 -0.7 - - 16 16 - - 0.71 0.37
74 16.57 16.25 -0.7 - - 16 16 - - 0.57 0.25
74.25 16.51 16.2 -0.7 - - 16 16 - - 0.51 0.2
74.5 16.52 16.22 -0.7 - - 16 16 - - 0.52 0.22
74.75 16.53 16.22 -0.5 - - 16 16 - - 0.53 0.22
75 16.39 16.1 -0.5 - - 16 16 - - 0.39 0.1
75.25 16.33 16.06 -0.5 - - 16 16 - - 0.33 0.06
75.5 16.35 16.07 -0.5 - - 16 16 - - 0.35 0.07
75.75 16.34 16.06 -0.6 - - 16 16 - - 0.34 0.06
76 16.2 15.94 -0.6 - - 16 16 - - 0.2 -0.06
76.25 16.22 19.1 -0.6 - 1 16 16 - 32 046.67 0.22 3.1
76.5 16.2 17.45 -0.6 - - 16 16 - - 0.2 1.45
76.75 16.14 15.47 -1 - - 16 16 - - 0.14 -0.53
77 16.1 19.42 -1 - 1 16 16 - 32 046.67 0.1 3.42
77.25 16.02 17.68 -1 - - 16 16 - - 0.02 1.68
77.5 15.99 15.74 -1 - - 16 16 - - -0.01 -0.26
77.75 19.56 19.55 -1.3 1 1 16 16 32 046.67 32 046.67 3.56 3.55
78 18.04 18.16 -1.3 - - 16 16 - - 2.04 2.16
78.25 15.9 16.36 -1.3 - - 16 16 - - -0.1 0.36
78.5 19.86 16.93 -1.3 1 - 16 16 32 046.67 - 3.86 0.93
78.75 18.01 16.72 -2.7 - - 16 16 - - 2.01 0.72
79 16.09 16.52 -2.7 - - 16 16 - - 0.09 0.52
79.25 16.66 16.46 -2.7 - - 16 16 - - 0.66 0.46
79.5 16.53 16.48 -2.7 - - 16 16 - - 0.53 0.48
79.75 16.55 16.46 -3.1 - - 16 16 - - 0.55 0.46
80 16.33 16.28 -3.1 - - 16 16 - - 0.33 0.28
80.25 16.39 19.49 -3.1 - 1 16 19 - 32 046.67 0.39 0.49
80.5 16.36 17.88 -3.1 - - 16 19 - - 0.36 -1.12
80.75 16.42 19.14 -2 - 1 16 19 - 32 046.67 0.42 0.14
81 16.32 18.54 -2 - - 16 19 - - 0.32 -0.46
81.25 16.31 19.79 -2 - 1 16 19 - 32 046.67 0.31 0.79
81.5 16.29 18.68 -2 - - 16 19 - - 0.29 -0.32
81.75 16.35 19.8 -0.9 - 1 16 19 - 32 046.67 0.35 0.8
82 16.26 19.21 -0.9 - - 16 19 - - 0.26 0.21
82.25 16.18 17.25 -0.9 - - 16 19 - - 0.18 -1.75
82.5 16.26 21 -0.9 - 1 16 19 - 32 046.67 0.26 2
82.75 16.24 19.2 -0.5 - - 16 19 - - 0.24 0.2
83 16.12 17.46 -0.5 - - 16 19 - - 0.12 -1.54
83.25 16.17 21.26 -0.5 - 1 16 19 - 32 046.67 0.17 2.26
83.5 16.15 19.43 -0.5 - - 16 19 - - 0.15 0.43
83.75 16.15 17.55 0.6 - - 16 19 - - 0.15 -1.45
84 16.18 21.43 0.6 - 1 16 19 - 32 046.67 0.18 2.43
84.25 16.13 19.66 0.6 - - 16 19 - - 0.13 0.66
84.5 16.11 17.73 0.6 - - 16 19 - - 0.11 -1.27
84.75 16.2 21.48 0.7 - 1 16 19 - 32 046.67 0.2 2.48
85 16.15 20.13 0.7 - - 16 19 - - 0.15 1.13
85.25 16.1 18.36 0.7 - - 16 19 - - 0.1 -0.64
85.5 16.19 22.05 0.7 - 1 16 19 - 32 046.67 0.19 3.05
85.75 16.18 20.25 0.5 - - 16 19 - - 0.18 1.25
86 16.12 18.49 0.5 - - 16 19 - - 0.12 -0.51
86.25 19.68 19.1 0.5 1 - 19 16 32 046.67 - 0.68 3.1
86.5 18 18.87 0.5 - - 19 16 - - -1 2.87
86.75 19.33 18.94 0.3 1 - 19 16 32 046.67 - 0.33 2.94
87 18.77 18.7 0.3 - - 19 16 - - -0.23 2.7
87.25 20.21 18.66 0.3 1 - 19 16 32 046.67 - 1.21 2.66
87.5 18.87 18.63 0.3 - - 19 16 - - -0.13 2.63
87.75 20.08 18.64 -0.1 1 - 19 16 32 046.67 - 1.08 2.64
88 19.5 18.47 -0.1 - - 19 16 - - 0.5 2.47
88.25 17.45 18.38 -0.1 - - 19 16 - - -1.55 2.38
88.5 21.4 18.47 -0.1 1 - 19 16 32 046.67 - 2.4 2.47
88.75 19.66 18.43 -0.4 - - 19 16 - - 0.66 2.43
89 17.55 18.19 -0.4 - - 19 16 - - -1.45 2.19
89.25 21.54 18.2 -0.4 1 - 19 16 32 046.67 - 2.54 2.2
89.5 19.72 18.18 -0.4 - - 19 16 - - 0.72 2.18
89.75 17.57 18.14 -0.3 - - 19 16 - - -1.43 2.14
90 21.66 18.07 -0.3 1 - 19 16 32 046.67 - 2.66 2.07
90.25 19.85 17.97 -0.3 - - 16 16 - - 3.85 1.97
90.5 17.65 17.94 -0.3 - - 16 16 - - 1.65 1.94
90.75 18.13 17.94 -0.3 - - 16 16 - - 2.13 1.94
91 18.17 17.8 -0.3 - - 16 16 - - 2.17 1.8
91.25 18.24 17.75 -0.3 - - 16 16 - - 2.24 1.75
91.5 18.23 17.77 -0.3 - - 16 16 - - 2.23 1.77
91.75 18.22 17.76 -0.5 - - 16 16 - - 2.22 1.76
92 17.97 17.6 -0.5 - - 16 16 - - 1.97 1.6
92.25 17.87 17.55 -0.5 - - 16 16 - - 1.87 1.55
92.5 17.89 17.56 -0.5 - - 16 16 - - 1.89 1.56
92.75 17.9 17.56 -0.3 - - 16 16 - - 1.9 1.56
93 17.71 17.42 -0.3 - - 16 16 - - 1.71 1.42
93.25 17.63 17.37 -0.3 - - 16 16 - - 1.63 1.37
93.5 17.65 17.38 -0.3 - - 16 16 - - 1.65 1.38
93.75 17.64 17.38 -0.3 - - 16 16 - - 1.64 1.38
94 17.47 17.24 -0.3 - - 16 16 - - 1.47 1.24
94.25 17.4 17.19 -0.3 - - 16 16 - - 1.4 1.19
94.5 17.41 17.21 -0.3 - - 16 16 - - 1.41 1.21
94.75 17.41 17.21 -0.2 - - 16 16 - - 1.41 1.21
95 17.25 17.07 -0.2 - - 16 16 - - 1.25 1.07
95.25 17.19 17.03 -0.2 - - 16 16 - - 1.19 1.03
95.5 17.2 17.04 -0.2 - - 16 16 - - 1.2 1.04
95.75 17.2 17.03 -0.3 - - 16 16 - - 1.2 1.03
96 17.04 16.9 -0.3 - - 16 16 - - 1.04 0.9
96.25 16.98 16.86 -0.3 - - 16 16 - - 0.98 0.86
96.5 16.99 16.87 -0.3 - - 16 16 - - 0.99 0.87
96.75 16.99 16.86 -0.3 - - 16 16 - - 0.99 0.86
97 16.84 16.74 -0.3 - - 16 16 - - 0.84 0.74
97.25 16.78 16.69 -0.3 - - 16 16 - - 0.78 0.69
97.5 16.79 16.7 -0.3 - - 16 16 - - 0.79 0.7
97.75 16.77 16.68 -1 - - 16 16 - - 0.77 0.68
98 16.61 16.54 -1 - - 16 16 - - 0.61 0.54
98.25 16.56 16.5 -1 - - 16 16 - - 0.56 0.5
98.5 16.57 16.51 -1 - - 16 16 - - 0.57 0.51
98.75 16.57 16.51 -1 - - 16 16 - - 0.57 0.51
99 16.42 16.38 -1 - - 16 16 - - 0.42 0.38
99.25 16.37 16.34 -1 - - 16 16 - - 0.37 0.34
99.5 16.38 16.35 -1 - - 16 16 - - 0.38 0.35
99.75 16.36 16.33 -1.5 - - 16 16 - - 0.36 0.33
100 16.21 16.2 -1.5 - - 16 16 - - 0.21 0.2
100.25 16.16 16.15 -1.5 - - 16 16 - - 0.16 0.15
100.5 16.17 16.16 -1.5 - - 16 16 - - 0.17 0.16
100.75 16.15 16.14 -2.2 - - 16 16 - - 0.15 0.14
101 15.99 16 -2.2 - - 16 16 - - -0.01 0
101.25 19.45 16.04 -2.2 1 - 16 16 32 046.67 - 3.45 0.04
101.5 17.74 16.01 -2.2 - - 16 16 - - 1.74 0.01
101.75 15.56 15.96 -2.4 - - 16 16 - - -0.44 -0.04
102 19.84 19.12 -2.4 1 1 16 16 32 046.67 32 046.67 3.84 3.12
102.25 18.08 17.39 -2.4 - - 16 16 - - 2.08 1.39
102.5 15.86 15.39 -2.4 - - 16 16 - - -0.14 -0.61
102.75 19.91 19.21 -2.6 1 1 16 16 32 046.67 32 046.67 3.91 3.21
103 18.61 17.88 -2.6 - - 16 16 - - 2.61 1.88
103.25 16.62 16.1 -2.6 - - 16 16 - - 0.62 0.1
103.5 17.05 16.59 -2.6 - - 16 16 - - 1.05 0.59
103.75 16.96 16.46 -2.6 - - 16 16 - - 0.96 0.46
104 16.82 16.32 -2.6 - - 16 16 - - 0.82 0.32
104.25 16.86 19.51 -2.6 - 1 16 19 - 32 046.67 0.86 0.51
104.5 16.87 17.91 -2.6 - - 16 19 - - 0.87 -1.09
104.75 16.87 19.13 -2.7 - 1 16 19 - 32 046.67 0.87 0.13
105 16.7 18.49 -2.7 - - 16 19 - - 0.7 -0.51
105.25 16.67 19.74 -2.7 - 1 16 19 - 32 046.67 0.67 0.74
105.5 16.64 18.63 -2.7 - - 16 19 - - 0.64 -0.37
105.75 16.7 19.74 -1.9 - 1 16 19 - 32 046.67 0.7 0.74
106 16.56 19.13 -1.9 - - 16 19 - - 0.56 0.13
106.25 16.47 17.16 -1.9 - - 16 19 - - 0.47 -1.84
106.5 16.56 20.92 -1.9 - 1 16 19 - 32 046.67 0.56 1.92
106.75 16.56 19.13 -1 - - 16 19 - - 0.56 0.13
107 16.41 17.38 -1 - - 16 19 - - 0.41 -1.62
107.25 16.46 21.18 -1 - 1 16 19 - 32 046.67 0.46 2.18
107.5 16.45 19.37 -1 - - 16 19 - - 0.45 0.37
107.75 16.44 17.47 -0.6 - - 16 19 - - 0.44 -1.53
108 16.45 21.33 -0.6 - 1 16 19 - 32 046.67 0.45 2.33
108.25 16.39 19.57 -0.6 - - 16 19 - - 0.39 0.57
108.5 16.37 17.64 -0.6 - - 16 19 - - 0.37 -1.36
108.75 16.47 21.4 - - 1 16 19 - 32 046.67 0.47 2.4
109 16.4 20.04 - - - 16 19 - - 0.4 1.04
109.25 16.33 18.27 - - - 16 19 - - 0.33 -0.73
109.5 16.41 21.96 - - 1 16 19 - 32 046.67 0.41 2.96
109.75 16.37 20.16 0.2 - - 16 19 - - 0.37 1.16
110 16.26 18.4 0.2 - - 16 19 - - 0.26 -0.6
110.25 19.78 19.01 0.2 1 - 19 16 32 046.67 - 0.78 3.01
110.5 18.09 18.77 0.2 - - 19 16 - - -0.91 2.77
110.75 19.45 18.86 0.5 1 - 19 16 32 046.67 - 0.45 2.86
111 18.88 18.62 0.5 - - 19 16 - - -0.12 2.62
111.25 20.4 18.6 0.5 1 - 19 16 32 046.67 - 1.4 2.6
111.5 19.21 18.6 0.5 - - 19 16 - - 0.21 2.6
111.75 16.96 18.54 0.2 - - 19 16 - - -2.04 2.54
112 21.29 18.48 0.2 1 - 19 16 32 046.67 - 2.29 2.48
112.25 19.58 18.39 0.2 - - 19 16 - - 0.58 2.39
112.5 17.41 18.36 0.2 - - 19 16 - - -1.59 2.36
112.75 21.53 18.47 - 1 - 19 16 32 046.67 - 2.53 2.47
113 19.97 18.22 - - - 19 16 - - 0.97 2.22
113.25 17.89 18.1 - - - 19 16 - - -1.11 2.1
113.5 21.84 18.2 - 1 - 19 16 32 046.67 - 2.84 2.2
113.75 20.03 18.16 -0.1 - - 19 16 - - 1.03 2.16
114 18.04 17.96 -0.1 - - 19 16 - - -0.96 1.96
114.25 18.53 17.92 -0.1 - - 16 16 - - 2.53 1.92
114.5 18.39 17.93 -0.1 - - 16 16 - - 2.39 1.93
114.75 18.42 17.93 -0.1 - - 16 16 - - 2.42 1.93
115 18.13 17.76 -0.1 - - 16 16 - - 2.13 1.76
115.25 18.03 17.7 -0.1 - - 16 16 - - 2.03 1.7
115.5 18.05 17.72 -0.1 - - 16 16 - - 2.05 1.72
115.75 18.04 17.71 -0.3 - - 16 16 - - 2.04 1.71
116 17.84 17.56 -0.3 - - 16 16 - - 1.84 1.56
116.25 17.76 17.5 -0.3 - - 16 16 - - 1.76 1.5
116.5 17.78 17.52 -0.3 - - 16 16 - - 1.78 1.52
116.75 17.77 17.52 -0.3 - - 16 16 - - 1.77 1.52
117 17.59 17.37 -0.3 - - 16 16 - - 1.59 1.37
117.25 17.52 17.32 -0.3 - - 16 16 - - 1.52 1.32
117.5 17.54 17.34 -0.3 - - 16 16 - - 1.54 1.34
117.75 17.53 17.33 -0.4 - - 16 16 - - 1.53 1.33
118 17.36 17.19 -0.4 - - 16 16 - - 1.36 1.19
118.25 17.29 17.14 -0.4 - - 16 16 - - 1.29 1.14
118.5 17.31 17.15 -0.4 - - 16 16 - - 1.31 1.15
118.75 17.3 17.15 -0.5 - - 16 16 - - 1.3 1.15
119 17.14 17.01 -0.5 - - 16 16 - - 1.14 1.01
119.25 17.08 16.96 -0.5 - - 16 16 - - 1.08 0.96
119.5 17.09 16.98 -0.5 - - 16 16 - - 1.09 0.98
119.75 17.09 16.97 -0.5 - - 16 16 - - 1.09 0.97
120 16.93 16.84 -0.5 - - 16 16 - - 0.93 0.84
120.25 16.88 16.79 -0.5 - - 16 16 - - 0.88 0.79
120.5 16.89 16.81 -0.5 - - 16 16 - - 0.89 0.81
120.75 16.89 16.81 -0.4 - - 16 16 - - 0.89 0.81
121 16.74 16.68 -0.4 - - 16 16 - - 0.74 0.68
121.25 16.69 16.63 -0.4 - - 16 16 - - 0.69 0.63
121.5 16.7 16.65 -0.4 - - 16 16 - - 0.7 0.65
121.75 16.69 16.64 -0.5 - - 16 16 - - 0.69 0.64
122 16.55 16.51 -0.5 - - 16 16 - - 0.55 0.51
122.25 16.49 16.47 -0.5 - - 16 16 - - 0.49 0.47
122.5 16.51 16.48 -0.5 - - 16 16 - - 0.51 0.48
122.75 16.51 16.48 -0.4 - - 16 16 - - 0.51 0.48
123 16.37 16.36 -0.4 - - 16 16 - - 0.37 0.36
123.25 16.32 16.31 -0.4 - - 16 16 - - 0.32 0.31
123.5 16.33 16.33 -0.4 - - 16 16 - - 0.33 0.33
123.75 16.32 16.32 -0.6 - - 16 16 - - 0.32 0.32
124 16.18 16.19 -0.6 - - 16 16 - - 0.18 0.19
124.25 16.13 16.15 -0.6 - - 16 16 - - 0.13 0.15
124.5 16.14 16.16 -0.6 - - 16 16 - - 0.14 0.16
124.75 16.13 16.15 -0.8 - - 16 16 - - 0.13 0.15
125 15.99 16.03 -0.8 - - 16 16 - - -0.01 0.03
125.25 19.45 16.06 -0.8 1 - 16 16 32 046.67 - 3.45 0.06
125.5 17.75 16.04 -0.8 - - 16 16 - - 1.75 0.04
125.75 15.58 16 -0.4 - - 16 16 - - -0.42 0
126 19.82 15.99 -0.4 1 - 16 16 32 046.67 - 3.82 -0.01
126.25 18.17 19.12 -0.4 - 1 16 16 - 32 046.67 2.17 3.12
126.5 15.95 17.42 -0.4 - - 16 16 - - -0.05 1.42
126.75 19.89 15.53 -0.4 1 - 16 16 32 046.67 - 3.89 -0.47
127 18.71 19.49 -0.4 - 1 16 16 - 32 046.67 2.71 3.49
127.25 16.72 17.72 -0.4 - - 16 16 - - 0.72 1.72
127.5 17.1 15.78 -0.4 - - 16 16 - - 1.1 -0.22
127.75 17.09 19.53 -0.3 - 1 16 16 - 32 046.67 1.09 3.53
128 16.91 18.17 -0.3 - - 16 16 - - 0.91 2.17
128.25 16.81 16.41 -0.3 - - 16 16 - - 0.81 0.41
128.5 16.83 16.9 -0.3 - - 16 16 - - 0.83 0.9
128.75 16.84 16.77 -0.1 - - 16 16 - - 0.84 0.77
129 16.66 16.63 -0.1 - - 16 16 - - 0.66 0.63
129.25 16.6 16.56 -0.1 - - 16 16 - - 0.6 0.56
129.5 16.62 16.59 -0.1 - - 16 16 - - 0.62 0.59
129.75 16.63 16.59 -0.1 - - 16 16 - - 0.63 0.59
130 16.5 16.46 -0.1 - - 16 16 - - 0.5 0.46
130.25 16.45 16.41 -0.1 - - 16 16 - - 0.45 0.41
130.5 16.48 16.44 -0.1 - - 16 16 - - 0.48 0.44
130.75 16.46 16.42 -0.5 - - 16 16 - - 0.46 0.42
131 16.34 16.3 -0.5 - - 16 16 - - 0.34 0.3
131.25 16.31 16.27 -0.5 - - 16 16 - - 0.31 0.27
131.5 16.33 16.29 -0.5 - - 16 16 - - 0.33 0.29
131.75 16.37 16.32 0.2 - - 16 16 - - 0.37 0.32
132 16.29 16.24 0.2 - - 16 16 - - 0.29 0.24
132.25 16.27 16.2 0.2 - - 16 16 - - 0.27 0.2
132.5 16.3 16.22 0.2 - - 16 16 - - 0.3 0.22
132.75 16.38 16.24 1 - - 16 16 - - 0.38 0.24
133 16.38 16.18 1 - - 16 16 - - 0.38 0.18
133.25 16.41 16.16 1 - - 16 16 - - 0.41 0.16
133.5 16.52 16.18 1 - - 16 16 - - 0.52 0.18
133.75 16.57 16.16 0.3 - - 16 16 - - 0.57 0.16
134 16.66 16.1 0.3 - - 16 16 - - 0.66 0.1
134.25 16.72 16.08 0.3 - - 16 16 - - 0.72 0.08
134.5 16.73 16.09 0.3 - - 16 16 - - 0.73 0.09
134.75 16.7 16.07 - - - 16 16 - - 0.7 0.07
135 16.75 16 - - - 16 16 - - 0.75 0
135.25 16.76 15.98 - - - 16 16 - - 0.76 -0.02
135.5 16.8 19.18 - - 1 16 16 - 32 046.67 0.8 3.18
135.75 16.7 17.46 -1.3 - - 16 16 - - 0.7 1.46
136 16.66 15.75 -1.3 - - 16 16 - - 0.66 -0.25
136.25 16.7 19.58 -1.3 - 1 16 16 - 32 046.67 0.7 3.58
136.5 16.57 17.72 -1.3 - - 16 16 - - 0.57 1.72
136.75 16.53 15.78 -2.1 - - 16 16 - - 0.53 -0.22
137 16.32 19.6 -2.1 - 1 16 16 - 32 046.67 0.32 3.6
137.25 16.18 17.83 -2.1 - - 16 16 - - 0.18 1.83
137.5 16.16 15.9 -2.1 - - 16 16 - - 0.16 -0.1
137.75 16.17 19.57 -4 - 1 16 16 - 32 046.67 0.17 3.57
138 15.97 18.13 -4 - - 16 16 - - -0.03 2.13
138.25 19.38 16.45 -4 1 - 16 16 32 046.67 - 3.38 0.45
138.5 17.67 16.92 -4 - - 16 16 - - 1.67 0.92
138.75 15.5 16.74 -4 - - 16 16 - - -0.5 0.74
139 19.68 16.66 -4 1 - 16 16 32 046.67 - 3.68 0.66
139.25 17.93 16.54 -4 - - 16 16 - - 1.93 0.54
139.5 15.78 16.52 -4 - - 16 16 - - -0.22 0.52
139.75 19.7 16.55 -5.4 1 - 16 16 32 046.67 - 3.7 0.55
140 18.34 16.33 -5.4 - - 16 16 - - 2.34 0.33
140.25 16.38 16.23 -5.4 - - 16 16 - - 0.38 0.23
140.5 16.82 16.25 -5.4 - - 16 16 - - 0.82 0.25
140.75 16.74 16.26 -4.9 - - 16 16 - - 0.74 0.26
141 16.54 16.09 -4.9 - - 16 16 - - 0.54 0.09
141.25 16.44 16.02 -4.9 - - 16 16 - - 0.44 0.02
141.5 16.46 16.04 -4.9 - - 16 16 - - 0.46 0.04
141.75 16.49 16.07 -3.8 - - 16 16 - - 0.49 0.07
142 16.3 15.92 -3.8 - - 16 16 - - 0.3 -0.08
142.25 16.29 19.05 -3.8 - 1 16 16 - 32 046.67 0.29 3.05
142.5 16.28 17.41 -3.8 - - 16 16 - - 0.28 1.41
142.75 16.25 15.46 -3.2 - - 16 16 - - 0.25 -0.54
143 16.18 19.39 -3.2 - 1 16 16 - 32 046.67 0.18 3.39
143.25 16.08 17.63 -3.2 - - 16 16 - - 0.08 1.63
143.5 16.05 15.7 -3.2 - - 16 16 - - 0.05 -0.3
143.75 16.13 19.44 -3 - 1 16 16 - 32 046.67 0.13 3.44
144 15.97 18.06 -3 - - 16 16 - - -0.03 2.06
144.25 19.37 16.37 -3 1 - 16 16 32 046.67 - 3.37 0.37
144.5 17.68 16.82 -3 - - 16 16 - - 1.68 0.82
144.75 15.51 16.65 -2.6 - - 16 16 - - -0.49 0.65
145 19.71 16.59 -2.6 1 - 16 16 32 046.67 - 3.71 0.59
145.25 17.98 16.48 -2.6 - - 16 16 - - 1.98 0.48
145.5 15.8 16.45 -2.6 - - 16 16 - - -0.2 0.45
145.75 19.79 16.54 -2.1 1 - 16 16 32 046.67 - 3.79 0.54
146 18.5 16.37 -2.1 - - 16 16 - - 2.5 0.37
146.25 16.53 16.27 -2.1 - - 16 16 - - 0.53 0.27
146.5 16.96 16.29 -2.1 - - 16 16 - - 0.96 0.29
146.75 16.86 16.28 -2.2 - - 16 16 - - 0.86 0.28
147 16.66 16.12 -2.2 - - 16 16 - - 0.66 0.12
147.25 16.58 16.06 -2.2 - - 16 16 - - 0.58 0.06
147.5 16.6 16.08 -2.2 - - 16 16 - - 0.6 0.08
147.75 16.59 16.07 -2.4 - - 16 16 - - 0.59 0.07
148 16.39 15.92 -2.4 - - 16 16 - - 0.39 -0.08
148.25 16.39 19.06 -2.4 - 1 16 16 - 32 046.67 0.39 3.06
148.5 16.37 17.41 -2.4 - - 16 16 - - 0.37 1.41
148.75 16.31 15.43 -2.8 - - 16 16 - - 0.31 -0.57
149 16.23 19.35 -2.8 - 1 16 16 - 32 046.67 0.23 3.35
149.25 16.14 17.61 -2.8 - - 16 16 - - 0.14 1.61
149.5 16.1 15.67 -2.8 - - 16 16 - - 0.1 -0.33
149.75 16.17 19.39 -3.1 - 1 16 16 - 32 046.67 0.17 3.39
150 16 18.01 -3.1 - - 16 16 - - 0 2.01
150.25 19.4 16.32 -3.1 1 - 16 16 32 046.67 - 3.4 0.32
150.5 17.71 16.77 -3.1 - - 16 16 - - 1.71 0.77
150.75 15.52 16.59 -3.2 - - 16 16 - - -0.48 0.59
151 19.71 16.52 -3.2 1 - 16 16 32 046.67 - 3.71 0.52
151.25 17.98 16.41 -3.2 - - 16 16 - - 1.98 0.41
151.5 15.81 16.38 -3.2 - - 16 16 - - -0.19 0.38
151.75 19.78 16.46 -3.2 1 - 16 16 32 046.67 - 3.78 0.46
152 18.64 16.3 -3.2 - - 16 16 - - 2.64 0.3
152.25 16.73 16.22 -3.2 - - 16 16 - - 0.73 0.22
152.5 17.15 16.25 -3.2 - - 16 16 - - 1.15 0.25
152.75 17.03 16.24 -3.3 - - 16 16 - - 1.03 0.24
153 16.88 16.1 -3.3 - - 16 16 - - 0.88 0.1
153.25 16.79 16.05 -3.3 - - 16 16 - - 0.79 0.05
153.5 16.8 16.07 -3.3 - - 16 16 - - 0.8 0.07
153.75 16.79 16.07 -3.3 - - 16 16 - - 0.79 0.07
154 16.6 15.93 -3.3 - - 16 16 - - 0.6 -0.07
154.25 16.6 19.08 -3.3 - 1 16 16 - 32 046.67 0.6 3.08
154.5 16.58 17.43 -3.3 - - 16 16 - - 0.58 1.43
154.75 16.53 15.48 -3.1 - - 16 16 - - 0.53 -0.52
155 16.48 19.43 -3.1 - 1 16 16 - 32 046.67 0.48 3.43
155.25 16.41 17.7 -3.1 - - 16 16 - - 0.41 1.7
155.5 16.37 15.75 -3.1 - - 16 16 - - 0.37 -0.25
155.75 16.45 19.49 -2.9 - 1 16 16 - 32 046.67 0.45 3.49
156 16.32 18.14 -2.9 - - 16 16 - - 0.32 2.14
156.25 16.23 16.38 -2.9 - - 16 16 - - 0.23 0.38
156.5 16.24 16.88 -2.9 - - 16 16 - - 0.24 0.88
156.75 16.24 16.74 -2.8 - - 16 16 - - 0.24 0.74
157 16.11 16.6 -2.8 - - 16 16 - - 0.11 0.6
157.25 16.06 16.53 -2.8 - - 16 16 - - 0.06 0.53
157.5 16.07 16.55 -2.8 - - 16 16 - - 0.07 0.55
157.75 16.08 16.56 -2.3 - - 16 16 - - 0.08 0.56
158 15.96 16.41 -2.3 - - 16 16 - - -0.04 0.41
158.25 19.41 16.42 -2.3 1 - 16 16 32 046.67 - 3.41 0.42
158.5 17.7 16.4 -2.3 - - 16 16 - - 1.7 0.4
158.75 15.53 16.35 -2.1 - - 16 16 - - -0.47 0.35
159 19.77 16.31 -2.1 1 - 16 16 32 046.67 - 3.77 0.31
159.25 18.04 16.23 -2.1 - - 16 16 - - 2.04 0.23
159.5 15.89 16.19 -2.1 - - 16 16 - - -0.11 0.19
159.75 19.87 16.27 -2.1 1 - 16 16 32 046.67 - 3.87 0.27
160 18.6 16.13 -2.1 - - 16 16 - - 2.6 0.13
160.25 16.66 16.05 -2.1 - - 16 16 - - 0.66 0.05
160.5 17.09 16.06 -2.1 - - 16 16 - - 1.09 0.06
160.75 16.96 16.04 -2.3 - - 16 16 - - 0.96 0.04
161 16.73 15.88 -2.3 - - 16 16 - - 0.73 -0.12
161.25 16.71 19.02 -2.3 - 1 16 16 - 32 046.67 0.71 3.02
161.5 16.7 17.37 -2.3 - - 16 16 - - 0.7 1.37
161.75 16.65 15.41 -2.3 - - 16 16 - - 0.65 -0.59
162 16.54 19.33 -2.3 - 1 16 16 - 32 046.67 0.54 3.33
162.25 16.44 17.58 -2.3 - - 16 16 - - 0.44 1.58
162.5 16.41 15.64 -2.3 - - 16 16 - - 0.41 -0.36
162.75 16.49 19.38 -2.3 - 1 16 16 - 32 046.67 0.49 3.38
163 16.31 18 -2.3 - - 16 16 - - 0.31 2
163.25 16.21 16.24 -2.3 - - 16 16 - - 0.21 0.24
163.5 16.23 16.73 -2.3 - - 16 16 - - 0.23 0.73
163.75 16.22 16.59 -2.4 - - 16 16 - - 0.22 0.59
164 16.05 16.42 -2.4 - - 16 16 - - 0.05 0.42
164.25 15.98 16.34 -2.4 - - 16 16 - - -0.02 0.34
164.5 19.5 16.44 -2.4 1 - 16 16 32 046.67 - 3.5 0.44
164.75 17.78 16.39 -2.5 - - 16 16 - - 1.78 0.39
165 15.84 16.19 -2.5 - - 16 16 - - -0.16 0.19
165.25 19.9 16.21 -2.5 1 - 16 16 32 046.67 - 3.9 0.21
165.5 18.07 16.19 -2.5 - - 16 16 - - 2.07 0.19
165.75 15.91 16.14 -2.6 - - 16 16 - - -0.09 0.14
166 20.04 16.08 -2.6 1 - 16 16 32 046.67 - 4.04 0.08
166.25 18.28 15.99 -2.6 - - 16 16 - - 2.28 -0.01
166.5 16.19 19.15 -2.6 - 1 16 16 - 32 046.67 0.19 3.15
166.75 16.63 17.5 -2.5 - - 16 16 - - 0.63 1.5
167 16.66 15.75 -2.5 - - 16 16 - - 0.66 -0.25
167.25 16.83 19.56 -2.5 - 1 16 16 - 32 046.67 0.83 3.56
167.5 16.78 17.73 -2.5 - - 16 16 - - 0.78 1.73
167.75 16.74 15.81 -2.6 - - 16 16 - - 0.74 -0.19
168 16.59 19.65 -2.6 - 1 16 16 - 32 046.67 0.59 3.65
168.25 16.48 17.88 -2.6 - - 16 16 - - 0.48 1.88
168.5 16.45 15.95 -2.6 - - 16 16 - - 0.45 -0.05
168.75 16.52 19.68 -2.6 - 1 16 16 - 32 046.67 0.52 3.68
169 16.34 18.29 -2.6 - - 16 16 - - 0.34 2.29
169.25 16.23 16.51 -2.6 - - 16 16 - - 0.23 0.51
169.5 16.25 17.01 -2.6 - - 16 16 - - 0.25 1.01
169.75 16.24 16.86 -3 - - 16 16 - - 0.24 0.86
170 16.05 16.67 -3 - - 16 16 - - 0.05 0.67
170.25 15.99 16.58 -3 - - 16 16 - - -0.01 0.58
170.5 19.5 16.68 -3 1 - 16 16 32 046.67 - 3.5 0.68
170.75 17.77 16.62 -3.6 - - 16 16 - - 1.77 0.62
171 15.81 16.4 -3.6 - - 16 16 - - -0.19 0.4
171.25 19.87 16.42 -3.6 1 - 16 16 32 046.67 - 3.87 0.42
171.5 18.04 16.4 -3.6 - - 16 16 - - 2.04 0.4
171.75 15.88 16.35 -3.6 - - 16 16 - - -0.12 0.35
172 20 16.27 -3.6 1 - 16 16 32 046.67 - 4 0.27
172.25 18.24 16.18 -3.6 - - 16 16 - - 2.24 0.18
172.5 16.08 16.15 -3.6 - - 16 16 - - 0.08 0.15
172.75 16.55 16.16 -3.5 - - 16 16 - - 0.55 0.16
173 16.61 16.01 -3.5 - - 16 16 - - 0.61 0.01
173.25 16.68 15.96 -3.5 - - 16 16 - - 0.68 -0.04
173.5 16.74 19.17 -3.5 - 1 16 16 - 32 046.67 0.74 3.17
173.75 16.71 17.5 -3.5 - - 16 16 - - 0.71 1.5
174 16.44 15.72 -3.5 - - 16 16 - - 0.44 -0.28
174.25 16.44 19.53 -3.5 - 1 16 16 - 32 046.67 0.44 3.53
174.5 16.42 17.7 -3.5 - - 16 16 - - 0.42 1.7
174.75 16.37 15.78 -3.6 - - 16 16 - - 0.37 -0.22
175 16.27 19.62 -3.6 - 1 16 16 - 32 046.67 0.27 3.62
175.25 16.17 17.85 -3.6 - - 16 16 - - 0.17 1.85
175.5 16.14 15.92 -3.6 - - 16 16 - - 0.14 -0.08
175.75 16.23 19.66 -3.3 - 1 16 16 - 32 046.67 0.23 3.66
176 16.06 18.27 -3.3 - - 16 16 - - 0.06 2.27
176.25 16.11 19.76 -3.3 - 1 16 19 - 32 046.67 0.11 0.76
176.5 16.06 18.63 -3.3 - - 16 19 - - 0.06 -0.37
176.75 16.12 19.73 -3 - 1 16 19 - 32 046.67 0.12 0.73
177 16.05 19.1 -3 - - 16 19 - - 0.05 0.1
177.25 16 17.14 -3 - - 16 19 - - 0 -1.86
177.5 19.61 20.97 -3 1 1 16 19 32 046.67 32 046.67 3.61 1.97
177.75 17.88 19.14 -2.5 - - 16 19 - - 1.88 0.14
178 15.97 17.35 -2.5 - - 16 19 - - -0.03 -1.65
178.25 20.14 21.22 -2.5 1 1 16 19 32 046.67 32 046.67 4.14 2.22
178.5 18.23 19.36 -2.5 - - 16 19 - - 2.23 0.36
178.75 16.05 17.43 -1.7 - - 16 19 - - 0.05 -1.57
179 16.84 21.3 -1.7 - 1 16 19 - 32 046.67 0.84 2.3
179.25 16.79 19.53 -1.7 - - 16 19 - - 0.79 0.53
179.5 16.75 17.6 -1.7 - - 16 19 - - 0.75 -1.4
179.75 16.86 21.37 -0.7 - 1 16 19 - 32 046.67 0.86 2.37
180 16.71 20.02 -0.7 - - 16 19 - - 0.71 1.02
180.25 16.62 18.25 -0.7 - - 16 19 - - 0.62 -0.75
180.5 16.7 21.94 -0.7 - 1 16 19 - 32 046.67 0.7 2.94
180.75 16.67 20.15 -0.3 - - 16 19 - - 0.67 1.15
181 16.53 18.39 -0.3 - - 16 19 - - 0.53 -0.61
181.25 16.56 22.17 -0.3 - 1 16 19 - 32 046.67 0.56 3.17
181.5 16.53 20.33 -0.3 - - 16 19 - - 0.53 1.33
181.75 16.47 18.41 -0.3 - - 16 19 - - 0.47 -0.59
182 16.45 22.24 -0.3 - 1 16 19 - 32 046.67 0.45 3.24
182.25 19.92 20.48 -0.3 1 - 19 16 32 046.67 - 0.92 4.48
182.5 18.19 18.48 -0.3 - - 19 16 - - -0.81 2.48
182.75 19.5 19.05 -0.3 1 - 19 16 32 046.67 - 0.5 3.05
183 18.87 19 -0.3 - - 19 16 - - -0.13 3
183.25 20.32 19.12 -0.3 1 - 19 16 32 046.67 - 1.32 3.12
183.5 19.04 19.06 -0.3 - - 19 16 - - 0.04 3.06
183.75 16.76 19.01 -0.2 - - 19 16 - - -2.24 3.01
184 20.98 18.87 -0.2 1 - 19 16 32 046.67 - 1.98 2.87
184.25 19.24 18.75 -0.2 - - 19 16 - - 0.24 2.75
184.5 17.08 18.73 -0.2 - - 19 16 - - -1.92 2.73
184.75 21.05 18.8 - 1 - 19 16 32 046.67 - 2.05 2.8
185 19.72 18.6 - - - 19 16 - - 0.72 2.6
185.25 17.74 18.5 - - - 19 16 - - -1.26 2.5
185.5 21.68 18.6 - 1 - 19 16 32 046.67 - 2.68 2.6
185.75 19.89 18.57 0.6 - - 19 16 - - 0.89 2.57
186 17.92 18.38 0.6 - - 19 16 - - -1.08 2.38
186.25 18.42 18.33 0.6 - - 16 16 - - 2.42 2.33
186.5 18.27 18.34 0.6 - - 16 16 - - 2.27 2.34
186.75 18.3 18.34 0.6 - - 16 16 - - 2.3 2.34
187 18.03 18.17 0.6 - - 16 16 - - 2.03 2.17
187.25 17.93 18.11 0.6 - - 16 16 - - 1.93 2.11
187.5 17.95 18.13 0.6 - - 16 16 - - 1.95 2.13
187.75 17.94 18.12 0.5 - - 16 16 - - 1.94 2.12
188 17.75 17.96 0.5 - - 16 16 - - 1.75 1.96
188.25 17.68 17.91 0.5 - - 16 16 - - 1.68 1.91
188.5 17.69 17.92 0.5 - - 16 16 - - 1.69 1.92
188.75 17.68 17.91 0.3 - - 16 16 - - 1.68 1.91
189 17.51 17.76 0.3 - - 16 16 - - 1.51 1.76
189.25 17.44 17.71 0.3 - - 16 16 - - 1.44 1.71
189.5 17.45 17.73 0.3 - - 16 16 - - 1.45 1.73
189.75 17.45 17.72 0.3 - - 16 16 - - 1.45 1.72
190 17.29 17.58 0.3 - - 16 16 - - 1.29 1.58
190.25 17.22 17.53 0.3 - - 16 16 - - 1.22 1.53
190.5 17.24 17.54 0.3 - - 16 16 - - 1.24 1.54
190.75 17.24 17.54 0.5 - - 16 16 - - 1.24 1.54
191 17.09 17.41 0.5 - - 16 16 - - 1.09 1.41
191.25 17.03 17.36 0.5 - - 16 16 - - 1.03 1.36
191.5 17.04 17.37 0.5 - - 16 16 - - 1.04 1.37
191.75 17.04 17.37 0.6 - - 16 16 - - 1.04 1.37
192 16.9 17.24 0.6 - - 16 16 - - 0.9 1.24
192.25 16.84 17.19 0.6 - - 16 16 - - 0.84 1.19
192.5 16.85 17.21 0.6 - - 16 16 - - 0.85 1.21
192.75 16.85 17.2 0.5 - - 16 16 - - 0.85 1.2
193 16.7 17.07 0.5 - - 16 16 - - 0.7 1.07
193.25 16.65 17.02 0.5 - - 16 16 - - 0.65 1.02
193.5 16.66 17.03 0.5 - - 16 16 - - 0.66 1.03
193.75 16.66 17.03 0.5 - - 16 16 - - 0.66 1.03
194 16.52 16.9 0.5 - - 16 16 - - 0.52 0.9
194.25 16.47 16.86 0.5 - - 16 16 - - 0.47 0.86
194.5 16.48 16.87 0.5 - - 16 16 - - 0.48 0.87
194.75 16.48 16.87 0.5 - - 16 16 - - 0.48 0.87
195 16.34 16.74 0.5 - - 16 16 - - 0.34 0.74
195.25 16.29 16.69 0.5 - - 16 16 - - 0.29 0.69
195.5 16.3 16.71 0.5 - - 16 16 - - 0.3 0.71
195.75 16.3 16.7 0.5 - - 16 16 - - 0.3 0.7
196 16.17 16.58 0.5 - - 16 16 - - 0.17 0.58
196.25 16.12 16.54 0.5 - - 16 16 - - 0.12 0.54
196.5 16.13 16.55 0.5 - - 16 16 - - 0.13 0.55
196.75 16.13 16.54 0.4 - - 16 16 - - 0.13 0.54
197 16 16.42 0.4 - - 16 16 - - 0 0.42
197.25 19.46 16.45 0.4 1 - 16 16 32 046.67 - 3.46 0.45
197.5 17.75 16.43 0.4 - - 16 16 - - 1.75 0.43
197.75 15.57 16.38 0.5 - - 16 16 - - -0.43 0.38
198 19.82 16.36 0.5 1 - 16 16 32 046.67 - 3.82 0.36
198.25 18.09 16.29 0.5 - - 16 16 - - 2.09 0.29
198.5 15.91 16.26 0.5 - - 16 16 - - -0.09 0.26
198.75 19.89 16.34 0.5 1 - 16 16 32 046.67 - 3.89 0.34
199 18.62 16.21 0.5 - - 16 16 - - 2.62 0.21
199.25 16.66 16.14 0.5 - - 16 16 - - 0.66 0.14
199.5 17.08 16.15 0.5 - - 16 16 - - 1.08 0.15
199.75 16.99 16.15 0.5 - - 16 16 - - 0.99 0.15
200 16.85 16.04 0.5 - - 16 16 - - 0.85 0.04
200.25 16.93 19.28 0.5 - 1 16 19 - 32 046.67 0.93 0.28
200.5 16.9 17.67 0.5 - - 16 19 - - 0.9 -1.33
200.75 16.93 18.9 0.7 - 1 16 19 - 32 046.67 0.93 -0.1
201 16.9 21.53 0.7 - 1 16 19 - 32 046.67 0.9 2.53
201.25 16.81 17.94 0.7 - - 16 19 - - 0.81 -1.06
201.5 16.86 19.72 0.7 - 1 16 19 - 32 046.67 0.86 0.72
201.75 16.8 18.46 0.8 - - 16 19 - - 0.8 -0.54
202 16.73 20.14 0.8 - 1 16 19 - 32 046.67 0.73 1.14
202.25 16.67 19.25 0.8 - - 16 19 - - 0.67 0.25
202.5 16.62 17.07 0.8 - - 16 19 - - 0.62 -1.93
202.75 16.72 20.9 1.6 - 1 16 19 - 32 046.67 0.72 1.9
203 16.61 19.47 1.6 - - 16 19 - - 0.61 0.47
203.25 16.53 17.68 1.6 - - 16 19 - - 0.53 -1.32
203.5 16.62 21.38 1.6 - 1 16 19 - 32 046.67 0.62 2.38
203.75 16.59 19.6 1.7 - - 16 19 - - 0.59 0.6
204 16.47 17.84 1.7 - - 16 19 - - 0.47 -1.16
204.25 16.51 21.64 1.7 - 1 16 19 - 32 046.67 0.51 2.64
204.5 16.49 19.82 1.7 - - 16 19 - - 0.49 0.82
204.75 16.45 17.9 2.2 - - 16 19 - - 0.45 -1.1
205 16.46 21.77 2.2 - 1 16 19 - 32 046.67 0.46 2.77
205.25 16.4 20.01 2.2 - - 16 19 - - 0.4 1.01
205.5 16.37 18.07 2.2 - - 16 19 - - 0.37 -0.93
205.75 16.45 21.82 2.3 - 1 16 19 - 32 046.67 0.45 2.82
206 16.35 20.44 2.3 - - 16 19 - - 0.35 1.44
206.25 19.83 18.69 2.3 1 - 19 16 32 046.67 - 0.83 2.69
206.5 18.14 19.1 2.3 - - 19 16 - - -0.86 3.1
206.75 19.47 19.01 2.4 1 - 19 16 32 046.67 - 0.47 3.01
207 18.85 18.85 2.4 - - 19 16 - - -0.15 2.85
207.25 20.3 18.81 2.4 1 - 19 16 32 046.67 - 1.3 2.81
207.5 19.02 18.79 2.4 - - 19 16 - - 0.02 2.79
207.75 16.73 18.73 2.5 - - 19 16 - - -2.27 2.73
208 20.98 18.64 2.5 1 - 19 16 32 046.67 - 1.98 2.64
208.25 19.24 18.54 2.5 - - 19 16 - - 0.24 2.54
208.5 17.05 18.51 2.5 - - 19 16 - - -1.95 2.51
208.75 21.02 18.57 2.1 1 - 19 16 32 046.67 - 2.02 2.57
209 19.71 18.39 2.1 - - 19 16 - - 0.71 2.39
209.25 17.74 18.3 2.1 - - 19 16 - - -1.26 2.3
209.5 21.68 18.39 2.1 1 - 19 16 32 046.67 - 2.68 2.39
209.75 19.86 18.34 1.5 - - 19 16 - - 0.86 2.34
210 17.88 18.14 1.5 - - 19 16 - - -1.12 2.14
210.25 18.38 18.1 1.5 - - 16 16 - - 2.38 2.1
210.5 18.24 18.11 1.5 - - 16 16 - - 2.24 2.11
210.75 18.27 18.11 1.5 - - 16 16 - - 2.27 2.11
211 18.01 17.95 1.5 - - 16 16 - - 2.01 1.95
211.25 17.91 17.9 1.5 - - 16 16 - - 1.91 1.9
211.5 17.93 17.91 1.5 - - 16 16 - - 1.93 1.91
211.75 17.92 17.91 1.4 - - 16 16 - - 1.92 1.91
212 17.74 17.76 1.4 - - 16 16 - - 1.74 1.76
212.25 17.67 17.71 1.4 - - 16 16 - - 1.67 1.71
212.5 17.68 17.72 1.4 - - 16 16 - - 1.68 1.72
212.75 17.68 17.72 1.4 - - 16 16 - - 1.68 1.72
213 17.51 17.58 1.4 - - 16 16 - - 1.51 1.58
213.25 17.45 17.53 1.4 - - 16 16 - - 1.45 1.53
213.5 17.46 17.55 1.4 - - 16 16 - - 1.46 1.55
213.75 17.45 17.54 1.2 - - 16 16 - - 1.45 1.54
214 17.29 17.4 1.2 - - 16 16 - - 1.29 1.4
214.25 17.23 17.36 1.2 - - 16 16 - - 1.23 1.36
214.5 17.25 17.37 1.2 - - 16 16 - - 1.25 1.37
214.75 17.24 17.36 1.2 - - 16 16 - - 1.24 1.36
215 17.09 17.24 1.2 - - 16 16 - - 1.09 1.24
215.25 17.04 17.19 1.2 - - 16 16 - - 1.04 1.19
215.5 17.05 17.2 1.2 - - 16 16 - - 1.05 1.2
215.75 17.04 17.19 1 - - 16 16 - - 1.04 1.19
216 16.89 17.06 1 - - 16 16 - - 0.89 1.06
216.25 16.84 17.02 1 - - 16 16 - - 0.84 1.02
216.5 16.85 17.03 1 - - 16 16 - - 0.85 1.03
216.75 16.85 17.03 1 - - 16 16 - - 0.85 1.03
217 16.71 16.9 1 - - 16 16 - - 0.71 0.9
217.25 16.66 16.86 1 - - 16 16 - - 0.66 0.86
217.5 16.67 16.87 1 - - 16 16 - - 0.67 0.87
217.75 16.66 16.86 0.9 - - 16 16 - - 0.66 0.86
218 16.53 16.74 0.9 - - 16 16 - - 0.53 0.74
218.25 16.48 16.7 0.9 - - 16 16 - - 0.48 0.7
218.5 16.49 16.71 0.9 - - 16 16 - - 0.49 0.71
218.75 16.48 16.7 0.7 - - 16 16 - - 0.48 0.7
219 16.34 16.57 0.7 - - 16 16 - - 0.34 0.57
219.25 16.29 16.53 0.7 - - 16 16 - - 0.29 0.53
219.5 16.3 16.54 0.7 - - 16 16 - - 0.3 0.54
219.75 16.3 16.54 0.7 - - 16 16 - - 0.3 0.54
220 16.17 16.42 0.7 - - 16 16 - - 0.17 0.42
220.25 16.12 16.38 0.7 - - 16 16 - - 0.12 0.38
220.5 16.13 16.39 0.7 - - 16 16 - - 0.13 0.39
220.75 16.14 16.39 1 - - 16 16 - - 0.14 0.39
221 16.02 16.28 1 - - 16 16 - - 0.02 0.28
221.25 15.97 16.24 1 - - 16 16 - - -0.03 0.24
221.5 19.5 16.32 1 1 - 16 16 32 046.67 - 3.5 0.32
221.75 17.78 16.29 1.2 - - 16 16 - - 1.78 0.29
222 15.88 16.16 1.2 - - 16 16 - - -0.12 0.16
222.25 19.96 16.2 1.2 1 - 16 16 32 046.67 - 3.96 0.2
222.5 18.12 16.18 1.2 - - 16 16 - - 2.12 0.18
222.75 15.97 16.14 1.5 - - 16 16 - - -0.03 0.14
223 20.15 16.13 1.5 1 - 16 16 32 046.67 - 4.15 0.13
223.25 18.41 16.06 1.5 - - 16 16 - - 2.41 0.06
223.5 16.23 16.02 1.5 - - 16 16 - - 0.23 0.02
223.75 16.71 16.03 1.8 - - 16 16 - - 0.71 0.03
224 16.83 15.95 1.8 - - 16 16 - - 0.83 -0.05
224.25 17.05 19.19 1.8 - 1 16 19 - 32 046.67 1.05 0.19
224.5 16.98 17.57 1.8 - - 16 19 - - 0.98 -1.43
224.75 17.02 18.81 2 - 1 16 19 - 32 046.67 1.02 -0.19
225 16.96 21.44 2 - 1 16 19 - 32 046.67 0.96 2.44
225.25 16.86 17.85 2 - - 16 19 - - 0.86 -1.15
225.5 16.93 19.64 2 - 1 16 19 - 32 046.67 0.93 0.64
225.75 16.9 18.38 2.2 - - 16 19 - - 0.9 -0.62
226 16.84 20.08 2.2 - 1 16 19 - 32 046.67 0.84 1.08
226.25 16.77 19.19 2.2 - - 16 19 - - 0.77 0.19
226.5 16.72 17.01 2.2 - - 16 19 - - 0.72 -1.99
226.75 16.82 20.84 2.5 - 1 16 19 - 32 046.67 0.82 1.84
227 16.71 19.42 2.5 - - 16 19 - - 0.71 0.42
227.25 16.63 17.64 2.5 - - 16 19 - - 0.63 -1.36
227.5 16.7 21.32 2.5 - 1 16 19 - 32 046.67 0.7 2.32
227.75 16.69 19.54 3 - - 16 19 - - 0.69 0.54
228 16.58 17.81 3 - - 16 19 - - 0.58 -1.19
228.25 16.63 21.61 3 - 1 16 19 - 32 046.67 0.63 2.61
228.5 16.59 19.77 3 - - 16 19 - - 0.59 0.77
228.75 16.54 17.84 2.8 - - 16 19 - - 0.54 -1.16
229 16.55 21.72 2.8 - 1 16 19 - 32 046.67 0.55 2.72
229.25 16.51 19.96 2.8 - - 16 19 - - 0.51 0.96
229.5 16.49 18.03 2.8 - - 16 19 - - 0.49 -0.97
229.75 16.57 21.78 2.9 - 1 16 19 - 32 046.67 0.57 2.78
230 16.5 20.42 2.9 - - 16 19 - - 0.5 1.42
230.25 19.98 18.67 2.9 1 - 19 16 32 046.67 - 0.98 2.67
230.5 18.28 19.08 2.9 - - 19 16 - - -0.72 3.08
230.75 19.59 18.97 2.8 1 - 19 16 32 046.67 - 0.59 2.97
231 18.98 18.81 2.8 - - 19 16 - - -0.02 2.81
231.25 20.43 18.77 2.8 1 - 19 16 32 046.67 - 1.43 2.77
231.5 19.14 18.75 2.8 - - 19 16 - - 0.14 2.75
231.75 16.84 18.68 2.4 - - 19 16 - - -2.16 2.68
232 21.09 18.59 2.4 1 - 19 16 32 046.67 - 2.09 2.59
232.25 19.37 18.5 2.4 - - 19 16 - - 0.37 2.5
232.5 17.19 18.47 2.4 - - 19 16 - - -1.81 2.47
232.75 21.15 18.52 2.1 1 - 19 16 32 046.67 - 2.15 2.52
233 19.83 18.34 2.1 - - 19 16 - - 0.83 2.34
233.25 17.86 18.25 2.1 - - 19 16 - - -1.14 2.25
233.5 21.79 18.35 2.1 1 - 19 16 32 046.67 - 2.79 2.35
233.75 19.99 18.31 2.2 - - 19 16 - - 0.99 2.31
234 18.02 18.13 2.2 - - 19 16 - - -0.98 2.13
234.25 18.52 18.09 2.2 - - 16 16 - - 2.52 2.09
234.5 18.38 18.1 2.2 - - 16 16 - - 2.38 2.1
234.75 18.41 18.09 2.2 - - 16 16 - - 2.41 2.09
235 18.15 17.94 2.2 - - 16 16 - - 2.15 1.94
235.25 18.05 17.89 2.2 - - 16 16 - - 2.05 1.89
235.5 18.07 17.9 2.2 - - 16 16 - - 2.07 1.9
235.75 18.05 17.88 1.5 - - 16 16 - - 2.05 1.88
236 17.85 17.73 1.5 - - 16 16 - - 1.85 1.73
236.25 17.79 17.68 1.5 - - 16 16 - - 1.79 1.68
236.5 17.8 17.7 1.5 - - 16 16 - - 1.8 1.7
236.75 17.79 17.69 1.3 - - 16 16 - - 1.79 1.69
237 17.62 17.55 1.3 - - 16 16 - - 1.62 1.55
237.25 17.56 17.5 1.3 - - 16 16 - - 1.56 1.5
237.5 17.57 17.51 1.3 - - 16 16 - - 1.57 1.51
237.75 17.57 17.51 1.5 - - 16 16 - - 1.57 1.51
238 17.42 17.39 1.5 - - 16 16 - - 1.42 1.39
238.25 17.36 17.34 1.5 - - 16 16 - - 1.36 1.34
238.5 17.37 17.35 1.5 - - 16 16 - - 1.37 1.35
238.75 17.37 17.35 1.6 - - 16 16 - - 1.37 1.35
239 17.22 17.22 1.6 - - 16 16 - - 1.22 1.22
239.25 17.17 17.18 1.6 - - 16 16 - - 1.17 1.18
239.5 17.18 17.19 1.6 - - 16 16 - - 1.18 1.19
239.75 17.18 17.19 1.6 - - 16 16 - - 1.18 1.19
240 17.04 17.06 1.6 - - 16 16 - - 1.04 1.06
240.25 16.98 17.02 1.6 - - 16 16 - - 0.98 1.02
240.5 16.99 17.03 1.6 - - 16 16 - - 0.99 1.03
240.75 16.99 17.03 1.5 - - 16 16 - - 0.99 1.03
241 16.85 16.9 1.5 - - 16 16 - - 0.85 0.9
241.25 16.8 16.86 1.5 - - 16 16 - - 0.8 0.86
241.5 16.81 16.87 1.5 - - 16 16 - - 0.81 0.87
241.75 16.8 16.86 1.3 - - 16 16 - - 0.8 0.86
242 16.66 16.74 1.3 - - 16 16 - - 0.66 0.74
242.25 16.61 16.7 1.3 - - 16 16 - - 0.61 0.7
242.5 16.62 16.71 1.3 - - 16 16 - - 0.62 0.71
242.75 16.62 16.7 1.2 - - 16 16 - - 0.62 0.7
243 16.49 16.58 1.2 - - 16 16 - - 0.49 0.58
243.25 16.44 16.54 1.2 - - 16 16 - - 0.44 0.54
243.5 16.45 16.55 1.2 - - 16 16 - - 0.45 0.55
243.75 16.44 16.55 1.1 - - 16 16 - - 0.44 0.55
244 16.31 16.43 1.1 - - 16 16 - - 0.31 0.43
244.25 16.26 16.39 1.1 - - 16 16 - - 0.26 0.39
244.5 16.27 16.4 1.1 - - 16 16 - - 0.27 0.4
244.75 16.27 16.4 1.1 - - 16 16 - - 0.27 0.4
245 16.14 16.28 1.1 - - 16 16 - - 0.14 0.28
245.25 16.1 16.24 1.1 - - 16 16 - - 0.1 0.24
245.5 16.11 16.25 1.1 - - 16 16 - - 0.11 0.25
245.75 16.1 16.24 1 - - 16 16 - - 0.1 0.24
246 15.98 16.13 1 - - 16 16 - - -0.02 0.13
246.25 19.44 16.16 1 1 - 16 16 32 046.67 - 3.44 0.16
246.5 17.74 16.14 1 - - 16 16 - - 1.74 0.14
246.75 15.54 16.08 0.8 - - 16 16 - - -0.46 0.08
247 19.79 16.07 0.8 1 - 16 16 32 046.67 - 3.79 0.07
247.25 18.07 16 0.8 - - 16 16 - - 2.07 0
247.5 15.88 15.96 0.8 - - 16 16 - - -0.12 -0.04
247.75 19.94 19.24 0.6 1 1 16 16 32 046.67 32 046.67 3.94 3.24
248 18.72 17.76 0.6 - - 16 16 - - 2.72 1.76
248.25 16.84 19.1 0.6 - 1 16 19 - 32 046.67 0.84 0.1
248.5 17.25 18.01 0.6 - - 16 19 - - 1.25 -0.99
248.75 17.18 19.1 0.8 - 1 16 19 - 32 046.67 1.18 0.1
249 17.05 18.56 0.8 - - 16 19 - - 1.05 -0.44
249.25 17.02 19.82 0.8 - 1 16 19 - 32 046.67 1.02 0.82
249.5 17 18.7 0.8 - - 16 19 - - 1 -0.3
249.75 17.03 19.79 0.8 - 1 16 19 - 32 046.67 1.03 0.79
250 16.88 19.19 0.8 - - 16 19 - - 0.88 0.19
250.25 16.8 17.23 0.8 - - 16 19 - - 0.8 -1.77
250.5 16.88 20.98 0.8 - 1 16 19 - 32 046.67 0.88 1.98
250.75 16.85 19.17 0.8 - - 16 19 - - 0.85 0.17
251 16.7 17.43 0.8 - - 16 19 - - 0.7 -1.57
251.25 16.74 21.23 0.8 - 1 16 19 - 32 046.67 0.74 2.23
251.5 16.72 19.4 0.8 - - 16 19 - - 0.72 0.4
251.75 16.67 17.48 0.6 - - 16 19 - - 0.67 -1.52
252 16.65 21.34 0.6 - 1 16 19 - 32 046.67 0.65 2.34
252.25 16.58 19.58 0.6 - - 16 19 - - 0.58 0.58
252.5 16.55 17.64 0.6 - - 16 19 - - 0.55 -1.36
252.75 16.64 21.39 0.8 - 1 16 19 - 32 046.67 0.64 2.39
253 16.56 20.03 0.8 - - 16 19 - - 0.56 1.03
253.25 16.52 18.27 0.8 - - 16 19 - - 0.52 -0.73
253.5 16.63 21.97 0.8 - 1 16 19 - 32 046.67 0.63 2.97
253.75 16.66 20.19 0.9 - - 16 19 - - 0.66 1.19
254 16.61 18.44 0.9 - - 16 19 - - 0.61 -0.56
254.25 20.18 19.06 0.9 1 - 19 16 32 046.67 - 1.18 3.06
254.5 18.56 18.83 0.9 - - 19 16 - - -0.44 2.83
254.75 19.91 18.91 0.5 1 - 19 16 32 046.67 - 0.91 2.91
255 19.42 18.69 0.5 - - 19 16 - - 0.42 2.69
255.25 17.43 18.59 0.5 - - 19 16 - - -1.57 2.59
255.5 21.38 18.68 0.5 1 - 19 16 32 046.67 - 2.38 2.68
255.75 19.54 18.62 0.2 - - 19 16 - - 0.54 2.62
256 17.76 18.45 0.2 - - 19 16 - - -1.24 2.45
256.25 21.85 18.48 0.2 1 - 19 16 32 046.67 - 2.85 2.48
256.5 19.93 18.44 0.2 - - 19 16 - - 0.93 2.44
256.75 17.73 18.35 -0.5 - - 19 16 - - -1.27 2.35
257 21.7 18.23 -0.5 1 - 19 16 32 046.67 - 2.7 2.23
257.25 19.9 18.13 -0.5 - - 19 16 - - 0.9 2.13
257.5 17.74 18.1 -0.5 - - 19 16 - - -1.26 2.1
257.75 21.69 18.16 -1.1 1 - 19 16 32 046.67 - 2.69 2.16
258 20.34 17.98 -1.1 - - 19 16 - - 1.34 1.98
258.25 18.32 17.88 -1.1 - - 16 16 - - 2.32 1.88
258.5 18.72 17.9 -1.1 - - 16 16 - - 2.72 1.9
258.75 18.64 17.9 -1.1 - - 16 16 - - 2.64 1.9
259 18.41 17.73 -1.1 - - 16 16 - - 2.41 1.73
259.25 18.31 17.67 -1.1 - - 16 16 - - 2.31 1.67
259.5 18.33 17.69 -1.1 - - 16 16 - - 2.33 1.69
259.75 18.32 17.68 -1.3 - - 16 16 - - 2.32 1.68
260 18.09 17.52 -1.3 - - 16 16 - - 2.09 1.52
260.25 18.01 17.47 -1.3 - - 16 16 - - 2.01 1.47
260.5 18.03 17.48 -1.3 - - 16 16 - - 2.03 1.48
260.75 18.02 17.48 -1.2 - - 16 16 - - 2.02 1.48
261 17.83 17.33 -1.2 - - 16 16 - - 1.83 1.33
261.25 17.76 17.28 -1.2 - - 16 16 - - 1.76 1.28
261.5 17.77 17.29 -1.2 - - 16 16 - - 1.77 1.29
261.75 17.77 17.29 -1.3 - - 16 16 - - 1.77 1.29
262 17.58 17.14 -1.3 - - 16 16 - - 1.58 1.14
262.25 17.51 17.09 -1.3 - - 16 16 - - 1.51 1.09
262.5 17.53 17.1 -1.3 - - 16 16 - - 1.53 1.1
262.75 17.52 17.09 -1.6 - - 16 16 - - 1.52 1.09
263 17.34 16.95 -1.6 - - 16 16 - - 1.34 0.95
263.25 17.27 16.9 -1.6 - - 16 16 - - 1.27 0.9
263.5 17.29 16.91 -1.6 - - 16 16 - - 1.29 0.91
263.75 17.28 16.9 -1.9 - - 16 16 - - 1.28 0.9
264 17.1 16.76 -1.9 - - 16 16 - - 1.1 0.76
264.25 17.04 16.71 -1.9 - - 16 16 - - 1.04 0.71
264.5 17.06 16.72 -1.9 - - 16 16 - - 1.06 0.72
264.75 17.04 16.71 -2.2 - - 16 16 - - 1.04 0.71
265 16.88 16.57 -2.2 - - 16 16 - - 0.88 0.57
265.25 16.82 16.52 -2.2 - - 16 16 - - 0.82 0.52
265.5 16.83 16.53 -2.2 - - 16 16 - - 0.83 0.53
265.75 16.83 16.53 -2.2 - - 16 16 - - 0.83 0.53
266 16.67 16.39 -2.2 - - 16 16 - - 0.67 0.39
266.25 16.61 16.34 -2.2 - - 16 16 - - 0.61 0.34
266.5 16.62 16.36 -2.2 - - 16 16 - - 0.62 0.36
266.75 16.62 16.35 -2.2 - - 16 16 - - 0.62 0.35
267 16.46 16.22 -2.2 - - 16 16 - - 0.46 0.22
267.25 16.4 16.17 -2.2 - - 16 16 - - 0.4 0.17
267.5 16.42 16.18 -2.2 - - 16 16 - - 0.42 0.18
267.75 16.41 16.18 -2.3 - - 16 16 - - 0.41 0.18
268 16.26 16.04 -2.3 - - 16 16 - - 0.26 0.04
268.25 16.2 16 -2.3 - - 16 16 - - 0.2 0
268.5 16.29 19.21 -2.3 - 1 16 16 - 32 046.67 0.29 3.21
268.75 16.25 17.54 -2.4 - - 16 16 - - 0.25 1.54
269 16.08 15.79 -2.4 - - 16 16 - - 0.08 -0.21
269.25 16.11 19.61 -2.4 - 1 16 16 - 32 046.67 0.11 3.61
269.5 16.08 17.77 -2.4 - - 16 16 - - 0.08 1.77
269.75 16.04 15.86 -2.4 - - 16 16 - - 0.04 -0.14
270 15.99 19.72 -2.4 - 1 16 16 - 32 046.67 -0.01 3.72
270.25 19.41 18.03 -2.4 1 - 16 16 32 046.67 - 3.41 2.03
270.5 17.66 16.06 -2.4 - - 16 16 - - 1.66 0.06
270.75 15.48 16.56 -2.4 - - 16 16 - - -0.52 0.56
271 19.72 16.65 -2.4 1 - 16 16 32 046.67 - 3.72 0.65
271.25 18 16.71 -2.4 - - 16 16 - - 2 0.71
271.5 15.82 16.64 -2.4 - - 16 16 - - -0.18 0.64
271.75 19.79 16.72 -2.7 1 - 16 16 32 046.67 - 3.79 0.72
272 18.55 16.52 -2.7 - - 16 16 - - 2.55 0.52
272.25 16.71 19.68 -2.7 - 1 16 19 - 32 046.67 0.71 0.68
272.5 17.1 18.08 -2.7 - - 16 19 - - 1.1 -0.92
272.75 17.02 19.3 -2.8 - 1 16 19 - 32 046.67 1.02 0.3
273 16.87 18.67 -2.8 - - 16 19 - - 0.87 -0.33
273.25 16.85 19.92 -2.8 - 1 16 19 - 32 046.67 0.85 0.92
273.5 16.83 18.81 -2.8 - - 16 19 - - 0.83 -0.19
273.75 16.86 19.9 -2.6 - 1 16 19 - 32 046.67 0.86 0.9
274 16.7 19.29 -2.6 - - 16 19 - - 0.7 0.29
274.25 16.61 17.32 -2.6 - - 16 19 - - 0.61 -1.68
274.5 16.69 21.07 -2.6 - 1 16 19 - 32 046.67 0.69 2.07
274.75 16.67 19.26 -2.3 - - 16 19 - - 0.67 0.26
275 16.5 17.5 -2.3 - - 16 19 - - 0.5 -1.5
275.25 16.54 21.29 -2.3 - 1 16 19 - 32 046.67 0.54 2.29
275.5 16.51 19.46 -2.3 - - 16 19 - - 0.51 0.46
275.75 16.47 17.55 -2.1 - - 16 19 - - 0.47 -1.45
276 16.44 21.39 -2.1 - 1 16 19 - 32 046.67 0.44 2.39
276.25 16.37 19.62 -2.1 - - 16 19 - - 0.37 0.62
276.5 16.34 17.69 -2.1 - - 16 19 - - 0.34 -1.31
276.75 16.42 21.43 -2 - 1 16 19 - 32 046.67 0.42 2.43
277 16.3 20.05 -2 - - 16 19 - - 0.3 1.05
277.25 16.23 18.28 -2 - - 16 19 - - 0.23 -0.72
277.5 16.31 21.97 -2 - 1 16 19 - 32 046.67 0.31 2.97
277.75 16.28 20.17 -1.9 - - 16 19 - - 0.28 1.17
278 16.14 18.39 -1.9 - - 16 19 - - 0.14 -0.61
278.25 19.64 18.99 -1.9 1 - 19 16 32 046.67 - 0.64 2.99
278.5 17.96 18.75 -1.9 - - 19 16 - - -1.04 2.75
278.75 19.27 18.83 -2 1 - 19 16 32 046.67 - 0.27 2.83
279 18.63 18.56 -2 - - 19 16 - - -0.37 2.56
279.25 20.08 18.52 -2 1 - 19 16 32 046.67 - 1.08 2.52
279.5 18.81 18.5 -2 - - 19 16 - - -0.19 2.5
279.75 20.03 18.52 -2 1 - 19 16 32 046.67 - 1.03 2.52
280 19.38 18.33 -2 - - 19 16 - - 0.38 2.33
280.25 17.31 18.23 -2 - - 19 16 - - -1.69 2.23
280.5 21.24 18.32 -2 1 - 19 16 32 046.67 - 2.24 2.32
280.75 19.39 18.25 -2.3 - - 19 16 - - 0.39 2.25
281 17.4 18.03 -2.3 - - 19 16 - - -1.6 2.03
281.25 21.44 18.05 -2.3 1 - 19 16 32 046.67 - 2.44 2.05
281.5 19.61 18.03 -2.3 - - 19 16 - - 0.61 2.03
281.75 17.45 17.97 -2.6 - - 19 16 - - -1.55 1.97
282 21.52 17.88 -2.6 1 - 19 16 32 046.67 - 2.52 1.88
282.25 19.71 17.79 -2.6 - - 16 16 - - 3.71 1.79
282.5 17.52 17.76 -2.6 - - 16 16 - - 1.52 1.76
282.75 17.99 17.76 -2.6 - - 16 16 - - 1.99 1.76
283 18.02 17.6 -2.6 - - 16 16 - - 2.02 1.6
283.25 18.09 17.55 -2.6 - - 16 16 - - 2.09 1.55
283.5 18.07 17.56 -2.6 - - 16 16 - - 2.07 1.56
283.75 18.07 17.55 -2.9 - - 16 16 - - 2.07 1.55
284 17.8 17.38 -2.9 - - 16 16 - - 1.8 1.38
284.25 17.7 17.32 -2.9 - - 16 16 - - 1.7 1.32
284.5 17.72 17.33 -2.9 - - 16 16 - - 1.72 1.33
284.75 17.71 17.33 -3 - - 16 16 - - 1.71 1.33
285 17.5 17.16 -3 - - 16 16 - - 1.5 1.16
285.25 17.42 17.11 -3 - - 16 16 - - 1.42 1.11
285.5 17.43 17.12 -3 - - 16 16 - - 1.43 1.12
285.75 17.43 17.12 -3.1 - - 16 16 - - 1.43 1.12
286 17.23 16.96 -3.1 - - 16 16 - - 1.23 0.96
286.25 17.16 16.9 -3.1 - - 16 16 - - 1.16 0.9
286.5 17.18 16.92 -3.1 - - 16 16 - - 1.18 0.92
286.75 17.17 16.92 -3.1 - - 16 16 - - 1.17 0.92
287 16.99 16.77 -3.1 - - 16 16 - - 0.99 0.77
287.25 16.92 16.71 -3.1 - - 16 16 - - 0.92 0.71
287.5 16.94 16.73 -3.1 - - 16 16 - - 0.94 0.73
287.75 16.93 16.72 -3.3 - - 16 16 - - 0.93 0.72
288 16.75 16.57 -3.3 - - 16 16 - - 0.75 0.57
288.25 16.68 16.51 -3.3 - - 16 16 - - 0.68 0.51
288.5 16.7 16.53 -3.3 - - 16 16 - - 0.7 0.53
288.75 16.69 16.52 -3.3 - - 16 16 - - 0.69 0.52
289 16.52 16.38 -3.3 - - 16 16 - - 0.52 0.38
289.25 16.46 16.33 -3.3 - - 16 16 - - 0.46 0.33
289.5 16.47 16.34 -3.3 - - 16 16 - - 0.47 0.34
289.75 16.47 16.34 -3.2 - - 16 16 - - 0.47 0.34
290 16.31 16.2 -3.2 - - 16 16 - - 0.31 0.2
290.25 16.25 16.15 -3.2 - - 16 16 - - 0.25 0.15
290.5 16.26 16.16 -3.2 - - 16 16 - - 0.26 0.16
290.75 16.27 16.17 -3 - - 16 16 - - 0.27 0.17
291 16.11 16.03 -3 - - 16 16 - - 0.11 0.03
291.25 16.05 15.98 -3 - - 16 16 - - 0.05 -0.02
291.5 16.14 19.19 -3 - 1 16 16 - 32 046.67 0.14 3.19
291.75 16.11 17.53 -2.9 - - 16 16 - - 0.11 1.53
292 15.93 15.77 -2.9 - - 16 16 - - -0.07 -0.23
292.25 19.47 19.67 -2.9 1 1 16 16 32 046.67 32 046.67 3.47 3.67
292.5 17.73 17.8 -2.9 - - 16 16 - - 1.73 1.8
292.75 15.5 15.84 -2.9 - - 16 16 - - -0.5 -0.16
293 19.81 19.8 -2.9 1 1 16 16 32 046.67 32 046.67 3.81 3.8
293.25 18.05 18 -2.9 - - 16 16 - - 2.05 2
293.5 15.83 16.02 -2.9 - - 16 16 - - -0.17 0.02
293.75 19.81 16.65 -2.9 1 - 16 16 32 046.67 - 3.81 0.65
294 18.53 16.63 -2.9 - - 16 16 - - 2.53 0.63
294.25 16.57 16.69 -2.9 - - 16 16 - - 0.57 0.69
294.5 17 16.66 -2.9 - - 16 16 - - 1 0.66
294.75 16.9 16.67 -3.1 - - 16 16 - - 0.9 0.67
295 16.7 16.45 -3.1 - - 16 16 - - 0.7 0.45
295.25 16.61 16.37 -3.1 - - 16 16 - - 0.61 0.37
295.5 16.63 16.39 -3.1 - - 16 16 - - 0.63 0.39
295.75 16.62 16.38 -3.2 - - 16 16 - - 0.62 0.38
296 16.52 16.23 -3.2 - - 16 16 - - 0.52 0.23
296.25 16.49 16.19 -3.2 - - 16 16 - - 0.49 0.19
296.5 16.51 16.21 -3.2 - - 16 16 - - 0.51 0.21
296.75 16.5 16.21 -3.2 - - 16 16 - - 0.5 0.21
297 16.36 16.08 -3.2 - - 16 16 - - 0.36 0.08
297.25 16.3 16.04 -3.2 - - 16 16 - - 0.3 0.04
297.5 16.32 16.06 -3.2 - - 16 16 - - 0.32 0.06
297.75 16.34 16.07 -2.9 - - 16 16 - - 0.34 0.07
298 16.22 15.96 -2.9 - - 16 16 - - 0.22 -0.04
298.25 16.25 19.12 -2.9 - 1 16 16 - 32 046.67 0.25 3.12
298.5 16.23 17.47 -2.9 - - 16 16 - - 0.23 1.47
298.75 16.2 15.52 -2.7 - - 16 16 - - 0.2 -0.48
299 16.22 19.5 -2.7 - 1 16 16 - 32 046.67 0.22 3.5
299.25 16.18 17.77 -2.7 - - 16 16 - - 0.18 1.77
299.5 16.2 15.84 -2.7 - - 16 16 - - 0.2 -0.16
299.75 16.34 19.59 -2.4 - 1 16 16 - 32 046.67 0.34 3.59
300 16.38 18.27 -2.4 - - 16 16 - - 0.38 2.27
300.25 16.43 16.53 -2.4 - - 16 16 - - 0.43 0.53
300.5 16.56 17.02 -2.4 - - 16 16 - - 0.56 1.02
300.75 16.69 16.91 -1.8 - - 16 16 - - 0.69 0.91
301 16.85 16.81 -1.8 - - 16 16 - - 0.85 0.81
301.25 16.94 16.75 -1.8 - - 16 16 - - 0.94 0.75
301.5 16.99 16.78 -1.8 - - 16 16 - - 0.99 0.78
301.75 17.04 16.8 -1.2 - - 16 16 - - 1.04 0.8
302 17.25 16.7 -1.2 - - 16 16 - - 1.25 0.7
302.25 17.31 16.67 -1.2 - - 16 16 - - 1.31 0.67
302.5 17.28 16.68 -1.2 - - 16 16 - - 1.28 0.68
302.75 17.23 16.66 -1.6 - - 16 16 - - 1.23 0.66
303 17.35 16.57 -1.6 - - 16 16 - - 1.35 0.57
303.25 17.37 16.54 -1.6 - - 16 16 - - 1.37 0.54
303.5 17.29 16.54 -1.6 - - 16 16 - - 1.29 0.54
303.75 17.24 16.54 -1.2 - - 16 16 - - 1.24 0.54
304 17.29 16.46 -1.2 - - 16 16 - - 1.29 0.46
304.25 17.25 16.42 -1.2 - - 16 16 - - 1.25 0.42
304.5 17.11 16.39 -1.2 - - 16 16 - - 1.11 0.39
304.75 16.98 16.33 -2.5 - - 16 16 - - 0.98 0.33
305 16.66 16.13 -2.5 - - 16 16 - - 0.66 0.13
305.25 16.57 16.08 -2.5 - - 16 16 - - 0.57 0.08
305.5 16.59 16.09 -2.5 - - 16 16 - - 0.59 0.09
305.75 16.53 16.04 -4.1 - - 16 16 - - 0.53 0.04
306 16.31 15.86 -4.1 - - 16 16 - - 0.31 -0.14
306.25 16.31 19 -4.1 - 1 16 16 - 32 046.67 0.31 3
306.5 16.29 17.35 -4.1 - - 16 16 - - 0.29 1.35
306.75 16.24 15.39 -4.1 - - 16 16 - - 0.24 -0.61
307 16.16 19.31 -4.1 - 1 16 16 - 32 046.67 0.16 3.31
307.25 16.06 17.55 -4.1 - - 16 16 - - 0.06 1.55
307.5 16.03 15.62 -4.1 - - 16 16 - - 0.03 -0.38
307.75 16.1 19.35 -4.3 - 1 16 16 - 32 046.67 0.1 3.35
308 15.92 17.96 -4.3 - - 16 16 - - -0.08 1.96
308.25 19.32 16.26 -4.3 1 - 16 16 32 046.67 - 3.32 0.26
308.5 17.63 16.72 -4.3 - - 16 16 - - 1.63 0.72
308.75 15.45 16.54 -4.2 - - 16 16 - - -0.55 0.54
309 19.63 16.47 -4.2 1 - 16 16 32 046.67 - 3.63 0.47
309.25 17.88 16.35 -4.2 - - 16 16 - - 1.88 0.35
309.5 15.73 16.33 -4.2 - - 16 16 - - -0.27 0.33
309.75 19.69 16.4 -4.5 1 - 16 16 32 046.67 - 3.69 0.4
310 18.35 16.2 -4.5 - - 16 16 - - 2.35 0.2
310.25 16.38 16.1 -4.5 - - 16 16 - - 0.38 0.1
310.5 16.82 16.12 -4.5 - - 16 16 - - 0.82 0.12
310.75 16.72 16.1 -4.8 - - 16 16 - - 0.72 0.1
311 16.5 15.92 -4.8 - - 16 16 - - 0.5 -0.08
311.25 16.48 19.05 -4.8 - 1 16 16 - 32 046.67 0.48 3.05
311.5 16.46 17.39 -4.8 - - 16 16 - - 0.46 1.39
311.75 16.41 15.43 -4.9 - - 16 16 - - 0.41 -0.57
312 16.29 19.34 -4.9 - 1 16 16 - 32 046.67 0.29 3.34
312.25 16.18 17.56 -4.9 - - 16 16 - - 0.18 1.56
312.5 16.16 15.63 -4.9 - - 16 16 - - 0.16 -0.37
312.75 16.23 19.38 -5 - 1 16 16 - 32 046.67 0.23 3.38
313 16.03 17.95 -5 - - 16 16 - - 0.03 1.95
313.25 15.93 16.18 -5 - - 16 16 - - -0.07 0.18
313.5 19.44 16.77 -5 1 - 16 16 32 046.67 - 3.44 0.77
313.75 17.71 16.59 -5.2 - - 16 16 - - 1.71 0.59
314 15.75 16.37 -5.2 - - 16 16 - - -0.25 0.37
314.25 19.8 16.37 -5.2 1 - 16 16 32 046.67 - 3.8 0.37
314.5 17.95 16.36 -5.2 - - 16 16 - - 1.95 0.36
314.75 15.81 16.3 -5.3 - - 16 16 - - -0.19 0.3
315 19.91 16.2 -5.3 1 - 16 16 32 046.67 - 3.91 0.2
315.25 18.13 16.09 -5.3 - - 16 16 - - 2.13 0.09
315.5 15.98 16.07 -5.3 - - 16 16 - - -0.02 0.07
315.75 19.94 16.13 -5.6 1 - 16 16 32 046.67 - 3.94 0.13
316 18.57 15.94 -5.6 - - 16 16 - - 2.57 -0.06
316.25 16.67 19.04 -5.6 - 1 16 16 - 32 046.67 0.67 3.04
316.5 17.08 17.38 -5.6 - - 16 16 - - 1.08 1.38
316.75 16.94 15.42 -5.8 - - 16 16 - - 0.94 -0.58
317 16.8 19.31 -5.8 - 1 16 16 - 32 046.67 0.8 3.31
317.25 16.67 17.54 -5.8 - - 16 16 - - 0.67 1.54
317.5 16.65 15.61 -5.8 - - 16 16 - - 0.65 -0.39
317.75 16.7 19.34 -6.3 - 1 16 16 - 32 046.67 0.7 3.34
318 16.46 17.9 -6.3 - - 16 16 - - 0.46 1.9
318.25 16.34 16.13 -6.3 - - 16 16 - - 0.34 0.13
318.5 16.36 16.63 -6.3 - - 16 16 - - 0.36 0.63
318.75 16.34 16.48 -6.7 - - 16 16 - - 0.34 0.48
319 16.12 16.28 -6.7 - - 16 16 - - 0.12 0.28
319.25 16.04 16.18 -6.7 - - 16 16 - - 0.04 0.18
319.5 16.06 16.21 -6.7 - - 16 16 - - 0.06 0.21
319.75 16.05 16.2 -6.9 - - 16 16 - - 0.05 0.2
320 16.01 16.01 -6.9 - - 16 16 - - 0.01 0.01
320.25 15.99 15.96 -6.9 - - 16 16 - - -0.01 -0.04
320.5 19.55 19.25 -6.9 1 1 16 16 32 046.67 32 046.67 3.55 3.25
320.75 17.83 17.56 -6.3 - - 16 16 - - 1.83 1.56
321 15.95 15.79 -6.3 - - 16 16 - - -0.05 -0.21
321.25 20.12 19.69 -6.3 1 1 16 16 32 046.67 32 046.67 4.12 3.69
321.5 18.29 17.84 -6.3 - - 16 16 - - 2.29 1.84
321.75 16.14 15.9 -6.2 - - 16 16 - - 0.14 -0.1
322 16.98 19.78 -6.2 - 1 16 16 - 32 046.67 0.98 3.78
322.25 16.98 18.03 -6.2 - - 16 16 - - 0.98 2.03
322.5 16.98 16.11 -6.2 - - 16 16 - - 0.98 0.11
322.75 17.05 16.67 -5.8 - - 16 16 - - 1.05 0.67
323 17.05 16.68 -5.8 - - 16 16 - - 1.05 0.68
323.25 17.11 16.78 -5.8 - - 16 16 - - 1.11 0.78
323.5 17.2 16.75 -5.8 - - 16 16 - - 1.2 0.75
323.75 17.31 16.78 -4.9 - - 16 16 - - 1.31 0.78
324 17.45 16.61 -4.9 - - 16 16 - - 1.45 0.61
324.25 17.53 16.53 -4.9 - - 16 16 - - 1.53 0.53
324.5 17.58 16.55 -4.9 - - 16 16 - - 1.58 0.55
324.75 17.66 16.59 -3.4 - - 16 16 - - 1.66 0.59
325 17.88 16.49 -3.4 - - 16 16 - - 1.88 0.49
325.25 17.94 16.45 -3.4 - - 16 16 - - 1.94 0.45
325.5 17.92 16.47 -3.4 - - 16 16 - - 1.92 0.47
325.75 17.94 16.5 -2.7 - - 16 16 - - 1.94 0.5
326 18.14 16.43 -2.7 - - 16 16 - - 2.14 0.43
326.25 18.2 16.4 -2.7 - - 16 16 - - 2.2 0.4
326.5 18.17 16.41 -2.7 - - 16 16 - - 2.17 0.41
326.75 18.15 16.44 -1.8 - - 16 16 - - 2.15 0.44
327 18.28 16.37 -1.8 - - 16 16 - - 2.28 0.37
327.25 18.27 16.34 -1.8 - - 16 16 - - 2.27 0.34
327.5 18.19 16.34 -1.8 - - 16 16 - - 2.19 0.34
327.75 18.14 16.34 -1.5 - - 16 16 - - 2.14 0.34
328 18.16 16.26 -1.5 - - 16 16 - - 2.16 0.26
328.25 18.11 16.22 -1.5 - - 16 16 - - 2.11 0.22
328.5 17.96 16.2 -1.5 - - 16 16 - - 1.96 0.2
328.75 17.86 16.16 -1.8 - - 16 16 - - 1.86 0.16
329 17.53 15.98 -1.8 - - 16 16 - - 1.53 -0.02
329.25 17.49 19.12 -1.8 - 1 16 16 - 32 046.67 1.49 3.12
329.5 17.48 17.47 -1.8 - - 16 16 - - 1.48 1.47
329.75 17.36 15.44 -3.9 - - 16 16 - - 1.36 -0.56
330 17.21 19.33 -3.9 - 1 16 16 - 32 046.67 1.21 3.33
330.25 17.11 17.59 -3.9 - - 16 16 - - 1.11 1.59
330.5 17.08 15.65 -3.9 - - 16 16 - - 1.08 -0.35
330.75 17.16 19.38 -3.9 - 1 16 16 - 32 046.67 1.16 3.38
331 16.95 17.99 -3.9 - - 16 16 - - 0.95 1.99
331.25 16.84 16.22 -3.9 - - 16 16 - - 0.84 0.22
331.5 16.86 16.72 -3.9 - - 16 16 - - 0.86 0.72
331.75 16.84 16.56 -4.4 - - 16 16 - - 0.84 0.56
332 16.63 16.38 -4.4 - - 16 16 - - 0.63 0.38
332.25 16.56 16.29 -4.4 - - 16 16 - - 0.56 0.29
332.5 16.58 16.32 -4.4 - - 16 16 - - 0.58 0.32
332.75 16.55 16.29 -5 - - 16 16 - - 0.55 0.29
333 16.35 16.09 -5 - - 16 16 - - 0.35 0.09
333.25 16.28 16.02 -5 - - 16 16 - - 0.28 0.02
333.5 16.3 16.04 -5 - - 16 16 - - 0.3 0.04
333.75 16.28 16.02 -5.4 - - 16 16 - - 0.28 0.02
334 16.08 15.83 -5.4 - - 16 16 - - 0.08 -0.17
334.25 16.09 18.96 -5.4 - 1 16 16 - 32 046.67 0.09 2.96
334.5 16.07 17.32 -5.4 - - 16 16 - - 0.07 1.32
334.75 16.01 15.34 -5.8 - - 16 16 - - 0.01 -0.66
335 15.92 19.23 -5.8 - 1 16 16 - 32 046.67 -0.08 3.23
335.25 19.32 17.55 -5.8 1 - 16 16 32 046.67 - 3.32 1.55
335.5 17.57 15.58 -5.8 - - 16 16 - - 1.57 -0.42
335.75 15.47 19.26 -5.9 - 1 16 16 - 32 046.67 -0.53 3.26
336 19.64 17.95 -5.9 1 - 16 16 32 046.67 - 3.64 1.95
336.25 17.87 16.15 -5.9 - - 16 16 - - 1.87 0.15
336.5 15.71 16.6 -5.9 - - 16 16 - - -0.29 0.6
336.75 19.66 16.53 -6.2 1 - 16 16 32 046.67 - 3.66 0.53
337 18.32 16.33 -6.2 - - 16 16 - - 2.32 0.33
337.25 16.35 16.21 -6.2 - - 16 16 - - 0.35 0.21
337.5 16.78 16.23 -6.2 - - 16 16 - - 0.78 0.23
337.75 16.68 16.22 -6.4 - - 16 16 - - 0.68 0.22
338 16.45 16 -6.4 - - 16 16 - - 0.45 0
338.25 16.35 15.93 -6.4 - - 16 16 - - 0.35 -0.07
338.5 16.45 19.14 -6.4 - 1 16 16 - 32 046.67 0.45 3.14
338.75 16.4 17.46 -6.7 - - 16 16 - - 0.4 1.46
339 16.14 15.65 -6.7 - - 16 16 - - 0.14 -0.35
339.25 16.14 19.44 -6.7 - 1 16 16 - 32 046.67 0.14 3.44
339.5 16.12 17.6 -6.7 - - 16 16 - - 0.12 1.6
339.75 16.07 15.68 -6.9 - - 16 16 - - 0.07 -0.32
340 15.95 19.48 -6.9 - 1 16 16 - 32 046.67 -0.05 3.48
340.25 19.34 17.77 -6.9 1 - 16 16 32 046.67 - 3.34 1.77
340.5 17.58 15.82 -6.9 - - 16 16 - - 1.58 -0.18
340.75 15.5 19.51 -6.7 - 1 16 16 - 32 046.67 -0.5 3.51
341 19.66 18.17 -6.7 1 - 16 16 32 046.67 - 3.66 2.17
341.25 17.87 16.37 -6.7 - - 16 16 - - 1.87 0.37
341.5 15.7 16.82 -6.7 - - 16 16 - - -0.3 0.82
341.75 19.69 16.77 -6.6 1 - 16 16 32 046.67 - 3.69 0.77
342 18.33 16.55 -6.6 - - 16 16 - - 2.33 0.55
342.25 16.35 16.42 -6.6 - - 16 16 - - 0.35 0.42
342.5 16.79 16.45 -6.6 - - 16 16 - - 0.79 0.45
342.75 16.69 16.44 -6.8 - - 16 16 - - 0.69 0.44
343 16.45 16.21 -6.8 - - 16 16 - - 0.45 0.21
343.25 16.35 16.13 -6.8 - - 16 16 - - 0.35 0.13
343.5 16.37 16.15 -6.8 - - 16 16 - - 0.37 0.15
343.75 16.38 16.16 -6.5 - - 16 16 - - 0.38 0.16
344 16.48 16.02 -6.5 - - 16 16 - - 0.48 0.02
344.25 16.58 19.22 -6.5 - 1 16 19 - 32 046.67 0.58 0.22
344.5 16.43 17.59 -6.5 - - 16 19 - - 0.43 -1.41
344.75 16.52 18.85 -6.1 - 1 16 19 - 32 046.67 0.52 -0.15
345 16.64 21.43 -6.1 - 1 16 19 - 32 046.67 0.64 2.43
345.25 16.62 17.83 -6.1 - - 16 19 - - 0.62 -1.17
345.5 16.73 19.63 -6.1 - 1 16 19 - 32 046.67 0.73 0.63
345.75 16.85 18.46 -3.4 - - 16 19 - - 0.85 -0.54
346 17.03 20.16 -3.4 - 1 16 19 - 32 046.67 1.03 1.16
346.25 17.07 19.25 -3.4 - - 16 19 - - 1.07 0.25
346.5 17.08 17.09 -3.4 - - 16 19 - - 1.08 -1.91
346.75 17.34 21.02 0.4 - 1 16 19 - 32 046.67 1.34 2.02
347 17.56 19.64 0.4 - - 16 19 - - 1.56 0.64
347.25 17.59 17.85 0.4 - - 16 19 - - 1.59 -1.15
347.5 17.71 21.55 0.4 - 1 16 19 - 32 046.67 1.71 2.55
347.75 17.76 19.79 1.9 - - 16 19 - - 1.76 0.79
348 17.98 18.07 1.9 - - 16 19 - - 1.98 -0.93
348.25 18.17 21.86 1.9 - 1 16 19 - 32 046.67 2.17 2.86
348.5 18.14 20.03 1.9 - - 16 19 - - 2.14 1.03
348.75 18.17 18.17 3.7 - - 16 19 - - 2.17 -0.83
349 18.55 22.1 3.7 - 1 16 19 - 32 046.67 2.55 3.1
349.25 18.61 20.34 3.7 - - 16 19 - - 2.61 1.34
349.5 18.54 18.41 3.7 - - 16 19 - - 2.54 -0.59
349.75 18.68 22.23 5.9 - 1 16 19 - 32 046.67 2.68 3.23
350 18.96 20.95 5.9 - - 16 19 - - 2.96 1.95
350.25 22.55 19.22 5.9 1 - 19 16 32 046.67 - 3.55 3.22
350.5 20.82 19.64 5.9 - - 19 16 - - 1.82 3.64
350.75 18.63 19.52 7.5 - - 19 16 - - -0.37 3.52
351 23.2 19.56 7.5 1 - 19 16 32 046.67 - 4.2 3.56
351.25 21.54 19.46 7.5 - - 19 16 - - 2.54 3.46
351.5 19.26 19.42 7.5 - - 19 16 - - 0.26 3.42
351.75 19.67 19.43 8 - - 19 16 - - 0.67 3.43
352 20 19.35 8 - - 19 16 - - 1 3.35
352.25 20.12 19.31 8 - - 19 16 - - 1.12 3.31
352.5 19.94 19.29 8 - - 19 16 - - 0.94 3.29
352.75 19.76 19.18 5.7 - - 19 16 - - 0.76 3.18
353 19.39 18.96 5.7 - - 19 16 - - 0.39 2.96
353.25 19.29 18.91 5.7 - - 19 16 - - 0.29 2.91
353.5 19.31 18.93 5.7 - - 19 16 - - 0.31 2.93
353.75 19.14 18.76 0.2 - - 19 16 - - 0.14 2.76
354 18.85 18.52 0.2 - - 19 16 - - -0.15 2.52
354.25 18.75 18.49 0.2 - - 16 16 - - 2.75 2.49
354.5 18.74 18.5 0.2 - - 16 16 - - 2.74 2.5
354.75 18.74 18.49 0.2 - - 16 16 - - 2.74 2.49
355 18.54 18.33 0.2 - - 16 16 - - 2.54 2.33
355.25 18.46 18.27 0.2 - - 16 16 - - 2.46 2.27
355.5 18.47 18.28 0.2 - - 16 16 - - 2.47 2.28
355.75 18.44 18.25 -0.7 - - 16 16 - - 2.44 2.25
356 18.24 18.08 -0.7 - - 16 16 - - 2.24 2.08
356.25 18.17 18.03 -0.7 - - 16 16 - - 2.17 2.03
356.5 18.18 18.04 -0.7 - - 16 16 - - 2.18 2.04
356.75 18.15 18.01 -1.5 - - 16 16 - - 2.15 2.01
357 17.95 17.84 -1.5 - - 16 16 - - 1.95 1.84
357.25 17.89 17.79 -1.5 - - 16 16 - - 1.89 1.79
357.5 17.9 17.8 -1.5 - - 16 16 - - 1.9 1.8
357.75 17.88 17.78 -2.2 - - 16 16 - - 1.88 1.78
358 17.68 17.61 -2.2 - - 16 16 - - 1.68 1.61
358.25 17.61 17.56 -2.2 - - 16 16 - - 1.61 1.56
358.5 17.63 17.57 -2.2 - - 16 16 - - 1.63 1.57
358.75 17.6 17.54 -3 - - 16 16 - - 1.6 1.54
359 17.4 17.37 -3 - - 16 16 - - 1.4 1.37
359.25 17.34 17.32 -3 - - 16 16 - - 1.34 1.32
359.5 17.35 17.33 -3 - - 16 16 - - 1.35 1.33
359.75 17.34 17.31 -3.4 - - 16 16 - - 1.34 1.31
360 17.15 17.15 -3.4 - - 16 16 - - 1.15 1.15
360.25 17.09 17.09 -3.4 - - 16 16 - - 1.09 1.09
360.5 17.1 17.11 -3.4 - - 16 16 - - 1.1 1.11
360.75 17.08 17.09 -3.8 - - 16 16 - - 1.08 1.09
361 16.9 16.93 -3.8 - - 16 16 - - 0.9 0.93
361.25 16.83 16.87 -3.8 - - 16 16 - - 0.83 0.87
361.5 16.85 16.89 -3.8 - - 16 16 - - 0.85 0.89
361.75 16.83 16.86 -4.4 - - 16 16 - - 0.83 0.86
362 16.64 16.7 -4.4 - - 16 16 - - 0.64 0.7
362.25 16.58 16.64 -4.4 - - 16 16 - - 0.58 0.64
362.5 16.59 16.66 -4.4 - - 16 16 - - 0.59 0.66
362.75 16.58 16.64 -4.7 - - 16 16 - - 0.58 0.64
363 16.4 16.48 -4.7 - - 16 16 - - 0.4 0.48
363.25 16.33 16.42 -4.7 - - 16 16 - - 0.33 0.42
363.5 16.35 16.44 -4.7 - - 16 16 - - 0.35 0.44
363.75 16.35 16.44 -4.6 - - 16 16 - - 0.35 0.44
364 16.17 16.28 -4.6 - - 16 16 - - 0.17 0.28
364.25 16.11 16.22 -4.6 - - 16 16 - - 0.11 0.22
364.5 16.12 16.24 -4.6 - - 16 16 - - 0.12 0.24
364.75 16.12 16.24 -4.5 - - 16 16 - - 0.12 0.24
365 15.96 16.09 -4.5 - - 16 16 - - -0.04 0.09
365.25 19.39 16.11 -4.5 1 - 16 16 32 046.67 - 3.39 0.11
365.5 17.68 16.08 -4.5 - - 16 16 - - 1.68 0.08
365.75 15.5 16.02 -4.9 - - 16 16 - - -0.5 0.02
366 19.68 15.96 -4.9 1 - 16 16 32 046.67 - 3.68 -0.04
366.25 18.01 19.07 -4.9 - 1 16 16 - 32 046.67 2.01 3.07
366.5 15.81 17.36 -4.9 - - 16 16 - - -0.19 1.36
366.75 19.73 15.47 -5.2 1 - 16 16 32 046.67 - 3.73 -0.53
367 18.49 19.39 -5.2 - 1 16 16 - 32 046.67 2.49 3.39
367.25 16.51 17.59 -5.2 - - 16 16 - - 0.51 1.59
367.5 16.89 15.66 -5.2 - - 16 16 - - 0.89 -0.34
367.75 16.88 19.41 -5.1 - 1 16 16 - 32 046.67 0.88 3.41
368 17.07 18.07 -5.1 - - 16 16 - - 1.07 2.07
368.25 17.15 19.58 -5.1 - 1 16 19 - 32 046.67 1.15 0.58
368.5 16.96 18.43 -5.1 - - 16 19 - - 0.96 -0.57
368.75 17.06 19.55 -4.5 - 1 16 19 - 32 046.67 1.06 0.55
369 17.13 18.94 -4.5 - - 16 19 - - 1.13 -0.06
369.25 17.24 20.18 -4.5 - 1 16 19 - 32 046.67 1.24 1.18
369.5 17.29 19.08 -4.5 - - 16 19 - - 1.29 0.08
369.75 17.43 17.11 -0.9 - - 16 19 - - 1.43 -1.89
370 17.68 21.12 -0.9 - 1 16 19 - 32 046.67 1.68 2.12
370.25 17.71 19.33 -0.9 - - 16 19 - - 1.71 0.33
370.5 17.71 17.41 -0.9 - - 16 19 - - 1.71 -1.59
370.75 17.95 21.27 2.7 - 1 16 19 - 32 046.67 1.95 2.27
371 18.2 19.98 2.7 - - 16 19 - - 2.2 0.98
371.25 18.24 18.2 2.7 - - 16 19 - - 2.24 -0.8
371.5 18.34 21.9 2.7 - 1 16 19 - 32 046.67 2.34 2.9
371.75 18.41 20.16 5.1 - - 16 19 - - 2.41 1.16
372 18.68 18.47 5.1 - - 16 19 - - 2.68 -0.53
372.25 18.87 22.28 5.1 - 1 16 19 - 32 046.67 2.87 3.28
372.5 18.84 20.44 5.1 - - 16 19 - - 2.84 1.44
372.75 18.88 18.59 7.2 - - 16 19 - - 2.88 -0.41
373 19.28 22.54 7.2 - 1 16 19 - 32 046.67 3.28 3.54
373.25 19.34 20.79 7.2 - - 16 19 - - 3.34 1.79
373.5 19.26 18.86 7.2 - - 16 19 - - 3.26 -0.14
373.75 19.36 22.63 7.8 - 1 16 19 - 32 046.67 3.36 3.63
374 19.63 21.35 7.8 - - 16 19 - - 3.63 2.35
374.25 19.73 19.55 7.8 - - 19 16 - - 0.73 3.55
374.5 19.71 20.01 7.8 - - 19 16 - - 0.71 4.01
374.75 19.69 19.91 8.5 - - 19 16 - - 0.69 3.91
375 19.89 19.84 8.5 - - 19 16 - - 0.89 3.84
375.25 19.91 19.78 8.5 - - 19 16 - - 0.91 3.78
375.5 19.81 19.79 8.5 - - 19 16 - - 0.81 3.79
375.75 19.72 19.77 8.2 - - 19 16 - - 0.72 3.77
376 19.8 19.67 8.2 - - 19 16 - - 0.8 3.67
376.25 19.77 19.62 8.2 - - 19 16 - - 0.77 3.62
376.5 19.61 19.6 8.2 - - 19 16 - - 0.61 3.6
376.75 19.37 19.51 7.5 - - 19 16 - - 0.37 3.51
377 19.17 19.35 7.5 - - 19 16 - - 0.17 3.35
377.25 19.13 19.3 7.5 - - 19 16 - - 0.13 3.3
377.5 19.13 19.31 7.5 - - 19 16 - - 0.13 3.31
377.75 19.02 19.2 4 - - 19 16 - - 0.02 3.2
378 18.76 18.96 2.6 - - 19 16 - - -0.24 2.96
378.25 18.65 18.91 2.6 - - 16 16 - - 2.65 2.91
378.5 18.64 18.92 2.6 - - 16 16 - - 2.64 2.92
378.75 18.64 18.92 2.6 - - 16 16 - - 2.64 2.92
379 18.47 18.76 2.6 - - 16 16 - - 2.47 2.76
379.25 18.4 18.71 2.6 - - 16 16 - - 2.4 2.71
379.5 18.42 18.72 2.6 - - 16 16 - - 2.42 2.72
379.75 18.38 18.68 1.3 - - 16 16 - - 2.38 2.68
380 18.19 18.51 1.3 - - 16 16 - - 2.19 2.51
380.25 18.13 18.47 1.3 - - 16 16 - - 2.13 2.47
380.5 18.14 18.48 1.3 - - 16 16 - - 2.14 2.48
380.75 18.12 18.46 0.7 - - 16 16 - - 2.12 2.46
381 17.95 18.3 0.7 - - 16 16 - - 1.95 2.3
381.25 17.89 18.25 0.7 - - 16 16 - - 1.89 2.25
381.5 17.9 18.26 0.7 - - 16 16 - - 1.9 2.26
381.75 17.88 18.24 - - - 16 16 - - 1.88 2.24
382 17.7 18.08 - - - 16 16 - - 1.7 2.08
382.25 17.65 18.03 - - - 16 16 - - 1.65 2.03
382.5 17.66 18.04 - - - 16 16 - - 1.66 2.04
382.75 17.63 18.02 -0.7 - - 16 16 - - 1.63 2.02
383 17.46 17.86 -0.7 - - 16 16 - - 1.46 1.86
383.25 17.4 17.81 -0.7 - - 16 16 - - 1.4 1.81
383.5 17.42 17.82 -0.7 - - 16 16 - - 1.42 1.82
383.75 17.39 17.8 -1.4 - - 16 16 - - 1.39 1.8
384 17.22 17.64 -1.4 - - 16 16 - - 1.22 1.64
384.25 17.16 17.59 -1.4 - - 16 16 - - 1.16 1.59
384.5 17.17 17.6 -1.4 - - 16 16 - - 1.17 1.6
384.75 17.15 17.57 -2.2 - - 16 16 - - 1.15 1.57
385 16.97 17.41 -2.2 - - 16 16 - - 0.97 1.41
385.25 16.91 17.36 -2.2 - - 16 16 - - 0.91 1.36
385.5 16.93 17.37 -2.2 - - 16 16 - - 0.93 1.37
385.75 16.95 17.4 -1.4 - - 16 16 - - 0.95 1.4
386 16.8 17.26 -1.4 - - 16 16 - - 0.8 1.26
386.25 16.74 17.2 -1.4 - - 16 16 - - 0.74 1.2
386.5 16.75 17.22 -1.4 - - 16 16 - - 0.75 1.22
386.75 16.81 17.27 0.6 - - 16 16 - - 0.81 1.27
387 16.7 17.16 0.6 - - 16 16 - - 0.7 1.16
387.25 16.64 17.1 0.6 - - 16 16 - - 0.64 1.1
387.5 16.65 17.12 0.6 - - 16 16 - - 0.65 1.12
387.75 16.71 17.18 2.8 - - 16 16 - - 0.71 1.18
388 16.62 17.09 2.8 - - 16 16 - - 0.62 1.09
388.25 16.57 17.04 2.8 - - 16 16 - - 0.57 1.04
388.5 16.58 17.05 2.8 - - 16 16 - - 0.58 1.05
388.75 16.59 17.06 3.3 - - 16 16 - - 0.59 1.06
389 16.48 16.96 3.3 - - 16 16 - - 0.48 0.96
389.25 16.44 16.91 3.3 - - 16 16 - - 0.44 0.91
389.5 16.45 16.92 3.3 - - 16 16 - - 0.45 0.92
389.75 16.45 16.93 3.6 - - 16 16 - - 0.45 0.93
390 16.34 16.82 3.6 - - 16 16 - - 0.34 0.82
390.25 16.3 16.78 3.6 - - 16 16 - - 0.3 0.78
390.5 16.31 16.79 3.6 - - 16 16 - - 0.31 0.79
390.75 16.31 16.8 3.8 - - 16 16 - - 0.31 0.8
391 16.2 16.69 3.8 - - 16 16 - - 0.2 0.69
391.25 16.16 16.65 3.8 - - 16 16 - - 0.16 0.65
391.5 16.17 16.66 3.8 - - 16 16 - - 0.17 0.66
391.75 16.2 16.69 4.7 - - 16 16 - - 0.2 0.69
392 16.25 16.63 4.7 - - 16 16 - - 0.25 0.63
392.25 16.35 19.87 4.7 - 1 16 19 - 32 046.67 0.35 0.87
392.5 16.27 18.24 4.7 - - 16 19 - - 0.27 -0.76
392.75 16.39 19.51 5.1 - 1 16 19 - 32 046.67 0.39 0.51
393 16.46 18.98 5.1 - - 16 19 - - 0.46 -0.02
393.25 16.56 20.27 5.1 - 1 16 19 - 32 046.67 0.56 1.27
393.5 16.59 19.16 5.1 - - 16 19 - - 0.59 0.16
393.75 16.73 17.16 8.5 - - 16 19 - - 0.73 -1.84
394 17.03 21.27 8.5 - 1 16 19 - 32 046.67 1.03 2.27
394.25 17.09 19.53 8.5 - - 16 19 - - 1.09 0.53
394.5 17.12 17.59 8.5 - - 16 19 - - 1.12 -1.41
394.75 17.31 21.38 9.8 - 1 16 19 - 32 046.67 1.31 2.38
395 17.57 20.13 9.8 - - 16 19 - - 1.57 1.13
395.25 17.64 18.39 9.8 - - 16 19 - - 1.64 -0.61
395.5 17.74 22.07 9.8 - 1 16 19 - 32 046.67 1.74 3.07
395.75 17.76 20.29 10.4 - - 16 19 - - 1.76 1.29
396 18.03 18.63 10.4 - - 16 19 - - 2.03 -0.37
396.25 18.24 22.46 10.4 - 1 16 19 - 32 046.67 2.24 3.46
396.5 18.2 20.62 10.4 - - 16 19 - - 2.2 1.62
396.75 18.2 18.72 11.1 - - 16 19 - - 2.2 -0.28
397 18.61 22.69 11.1 - 1 16 19 - 32 046.67 2.61 3.69
397.25 18.69 20.97 11.1 - - 16 19 - - 2.69 1.97
397.5 18.59 19.03 11.1 - - 16 19 - - 2.59 0.03
397.75 18.54 19.57 11 - - 16 19 - - 2.54 0.57
398 18.73 19.68 11 - - 16 19 - - 2.73 0.68
398.25 22.27 19.83 11 1 - 19 16 32 046.67 - 3.27 3.83
398.5 20.43 19.71 11 - - 19 16 - - 1.43 3.71
398.75 18.02 19.58 7.9 - - 19 16 - - -0.98 3.58
399 22.37 19.5 7.9 1 - 19 16 32 046.67 - 3.37 3.5
399.25 20.68 19.43 7.9 - - 19 16 - - 1.68 3.43
399.5 18.38 19.37 7.9 - - 19 16 - - -0.62 3.37
399.75 22.27 19.39 6.6 1 - 19 16 32 046.67 - 3.27 3.39
400 21.03 19.25 6.6 - - 19 16 - - 2.03 3.25
400.25 19.12 19.18 6.6 - - 19 16 - - 0.12 3.18
400.5 19.55 19.18 6.6 - - 19 16 - - 0.55 3.18
400.75 19.5 19.16 5.7 - - 19 16 - - 0.5 3.16
401 20.23 19.27 5.7 - - 19 16 - - 1.23 3.27
401.25 19.42 19.01 5.7 - - 19 16 - - 0.42 3.01
401.5 19 18.9 5.7 - - 19 16 - - 0 2.9
401.75 19.08 18.92 5.2 - - 19 16 - - 0.08 2.92
402 18.99 18.81 5.2 - - 19 16 - - -0.01 2.81
402.25 18.94 18.77 5.2 - - 16 16 - - 2.94 2.77
402.5 18.91 18.78 5.2 - - 16 16 - - 2.91 2.78
402.75 18.92 18.78 5.2 - - 16 16 - - 2.92 2.78
403 18.74 18.65 5.2 - - 16 16 - - 2.74 2.65
403.25 18.68 18.6 5.2 - - 16 16 - - 2.68 2.6
403.5 18.69 18.62 5.2 - - 16 16 - - 2.69 2.62
403.75 18.7 18.62 5.5 - - 16 16 - - 2.7 2.62
404 18.55 18.51 5.5 - - 16 16 - - 2.55 2.51
404.25 18.49 18.46 5.5 - - 16 16 - - 2.49 2.46
404.5 18.5 18.48 5.5 - - 16 16 - - 2.5 2.48
404.75 18.49 18.46 5.2 - - 16 16 - - 2.49 2.46
405 18.35 18.35 5.2 - - 16 16 - - 2.35 2.35
405.25 18.29 18.31 5.2 - - 16 16 - - 2.29 2.31
405.5 18.31 18.32 5.2 - - 16 16 - - 2.31 2.32
405.75 18.29 18.3 4.6 - - 16 16 - - 2.29 2.3
406 18.14 18.17 4.6 - - 16 16 - - 2.14 2.17
406.25 18.09 18.14 4.6 - - 16 16 - - 2.09 2.14
406.5 18.1 18.15 4.6 - - 16 16 - - 2.1 2.15
406.75 18.09 18.13 4.2 - - 16 16 - - 2.09 2.13
407 17.95 18.01 4.2 - - 16 16 - - 1.95 2.01
407.25 17.9 17.97 4.2 - - 16 16 - - 1.9 1.97
407.5 17.91 17.98 4.2 - - 16 16 - - 1.91 1.98
407.75 17.91 17.98 4.2 - - 16 16 - - 1.91 1.98
408 17.78 17.87 4.2 - - 16 16 - - 1.78 1.87
408.25 17.73 17.83 4.2 - - 16 16 - - 1.73 1.83
408.5 17.74 17.84 4.2 - - 16 16 - - 1.74 1.84
408.75 17.73 17.83 3.9 - - 16 16 - - 1.73 1.83
409 17.59 17.71 3.9 - - 16 16 - - 1.59 1.71
409.25 17.55 17.67 3.9 - - 16 16 - - 1.55 1.67
409.5 17.56 17.68 3.9 - - 16 16 - - 1.56 1.68
409.75 17.53 17.66 3.2 - - 16 16 - - 1.53 1.66
410 17.4 17.54 3.2 - - 16 16 - - 1.4 1.54
410.25 17.35 17.5 3.2 - - 16 16 - - 1.35 1.5
410.5 17.36 17.51 3.2 - - 16 16 - - 1.36 1.51
410.75 17.35 17.5 3 - - 16 16 - - 1.35 1.5
411 17.22 17.38 3 - - 16 16 - - 1.22 1.38
411.25 17.18 17.34 3 - - 16 16 - - 1.18 1.34
411.5 17.19 17.35 3 - - 16 16 - - 1.19 1.35
411.75 17.18 17.34 2.7 - - 16 16 - - 1.18 1.34
412 17.05 17.23 2.7 - - 16 16 - - 1.05 1.23
412.25 17 17.19 2.7 - - 16 16 - - 1 1.19
412.5 17.01 17.2 2.7 - - 16 16 - - 1.01 1.2
412.75 17 17.19 2.5 - - 16 16 - - 1 1.19
413 16.88 17.07 2.5 - - 16 16 - - 0.88 1.07
413.25 16.83 17.03 2.5 - - 16 16 - - 0.83 1.03
413.5 16.84 17.04 2.5 - - 16 16 - - 0.84 1.04
413.75 16.84 17.04 2.6 - - 16 16 - - 0.84 1.04
414 16.72 16.93 2.6 - - 16 16 - - 0.72 0.93
414.25 16.68 16.89 2.6 - - 16 16 - - 0.68 0.89
414.5 16.68 16.9 2.6 - - 16 16 - - 0.68 0.9
414.75 16.68 16.89 2.4 - - 16 16 - - 0.68 0.89
415 16.55 16.78 2.4 - - 16 16 - - 0.55 0.78
415.25 16.51 16.74 2.4 - - 16 16 - - 0.51 0.74
415.5 16.52 16.75 2.4 - - 16 16 - - 0.52 0.75
415.75 16.52 16.75 2.5 - - 16 16 - - 0.52 0.75
416 16.46 16.66 2.5 - - 16 16 - - 0.46 0.66
416.25 16.56 19.9 2.5 - 1 16 19 - 32 046.67 0.56 0.9
416.5 16.54 18.29 2.5 - - 16 19 - - 0.54 -0.71
416.75 16.55 19.52 2.7 - 1 16 19 - 32 046.67 0.55 0.52
417 16.49 18.96 2.7 - - 16 19 - - 0.49 -0.04
417.25 16.5 20.24 2.7 - 1 16 19 - 32 046.67 0.5 1.24
417.5 16.47 19.12 2.7 - - 16 19 - - 0.47 0.12
417.75 16.46 17.03 3.4 - - 16 19 - - 0.46 -1.97
418 16.5 21.05 3.4 - 1 16 19 - 32 046.67 0.5 2.05
418.25 16.44 19.3 3.4 - - 16 19 - - 0.44 0.3
418.5 16.41 17.36 3.4 - - 16 19 - - 0.41 -1.64
418.75 16.54 21.16 4.8 - 1 16 19 - 32 046.67 0.54 2.16
419 16.5 19.85 4.8 - - 16 19 - - 0.5 0.85
419.25 16.43 18.09 4.8 - - 16 19 - - 0.43 -0.91
419.5 16.52 21.78 4.8 - 1 16 19 - 32 046.67 0.52 2.78
419.75 16.53 20.02 6 - - 16 19 - - 0.53 1.02
420 16.49 18.33 6 - - 16 19 - - 0.49 -0.67
420.25 16.59 22.15 6 - 1 16 19 - 32 046.67 0.59 3.15
420.5 16.62 20.33 6 - - 16 19 - - 0.62 1.33
420.75 16.63 18.43 6.4 - - 16 19 - - 0.63 -0.57
421 16.74 22.35 6.4 - 1 16 19 - 32 046.67 0.74 3.35
421.25 16.74 20.61 6.4 - - 16 19 - - 0.74 1.61
421.5 16.7 18.67 6.4 - - 16 19 - - 0.7 -0.33
421.75 16.8 22.44 7.3 - 1 16 19 - 32 046.67 0.8 3.44
422 16.84 21.14 7.3 - - 16 19 - - 0.84 2.14
422.25 20.35 19.4 7.3 1 - 19 16 32 046.67 - 1.35 3.4
422.5 18.65 19.81 7.3 - - 19 16 - - -0.35 3.81
422.75 19.98 19.71 7.3 1 - 19 16 32 046.67 - 0.98 3.71
423 19.53 19.61 7.3 - - 19 16 - - 0.53 3.61
423.25 17.56 19.52 7.3 - - 19 16 - - -1.44 3.52
423.5 21.55 19.62 7.3 1 - 19 16 32 046.67 - 2.55 3.62
423.75 19.8 19.6 7.8 - - 19 16 - - 0.8 3.6
424 18.06 19.46 7.8 - - 19 16 - - -0.94 3.46
424.25 22.16 19.49 7.8 1 - 19 16 32 046.67 - 3.16 3.49
424.5 20.25 19.45 7.8 - - 19 16 - - 1.25 3.45
424.75 18.11 19.38 6.7 - - 19 16 - - -0.89 3.38
425 23.2 19.59 6.7 1 - 19 16 32 046.67 - 4.2 3.59
425.25 20.67 19.29 6.7 - - 19 16 - - 1.67 3.29
425.5 18.03 19.12 6.7 - - 19 16 - - -0.97 3.12
425.75 22.05 19.18 4.8 1 - 19 16 32 046.67 - 3.05 3.18
426 20.8 19.01 3.9 - - 19 16 - - 1.8 3.01
426.25 18.84 18.94 3.9 - - 16 16 - - 2.84 2.94
426.5 19.23 18.95 3.9 - - 16 16 - - 3.23 2.95
426.75 19.15 18.95 3.9 - - 16 16 - - 3.15 2.95
427 18.93 18.8 3.9 - - 16 16 - - 2.93 2.8
427.25 18.84 18.74 3.9 - - 16 16 - - 2.84 2.74
427.5 18.86 18.76 3.9 - - 16 16 - - 2.86 2.76
427.75 18.85 18.75 3.7 - - 16 16 - - 2.85 2.75
428 18.65 18.61 3.7 - - 16 16 - - 2.65 2.61
428.25 18.58 18.56 3.7 - - 16 16 - - 2.58 2.56
428.5 18.59 18.57 3.7 - - 16 16 - - 2.59 2.57
428.75 18.6 18.58 3.9 - - 16 16 - - 2.6 2.58
429 18.43 18.45 3.9 - - 16 16 - - 2.43 2.45
429.25 18.37 18.4 3.9 - - 16 16 - - 2.37 2.4
429.5 18.38 18.42 3.9 - - 16 16 - - 2.38 2.42
429.75 18.39 18.42 4.2 - - 16 16 - - 2.39 2.42
430 18.24 18.31 4.2 - - 16 16 - - 2.24 2.31
430.25 18.18 18.26 4.2 - - 16 16 - - 2.18 2.26
430.5 18.19 18.27 4.2 - - 16 16 - - 2.19 2.27
430.75 18.21 18.29 4.8 - - 16 16 - - 2.21 2.29
431 18.08 18.18 4.8 - - 16 16 - - 2.08 2.18
431.25 18.02 18.14 4.8 - - 16 16 - - 2.02 2.14
431.5 18.03 18.15 4.8 - - 16 16 - - 2.03 2.15
431.75 18.03 18.14 4.6 - - 16 16 - - 2.03 2.14
432 17.89 18.03 4.6 - - 16 16 - - 1.89 2.03
432.25 17.84 17.99 4.6 - - 16 16 - - 1.84 1.99
432.5 17.85 18 4.6 - - 16 16 - - 1.85 2
432.75 17.84 17.99 4.4 - - 16 16 - - 1.84 1.99
433 17.71 17.88 4.4 - - 16 16 - - 1.71 1.88
433.25 17.67 17.84 4.4 - - 16 16 - - 1.67 1.84
433.5 17.68 17.85 4.4 - - 16 16 - - 1.68 1.85
433.75 17.68 17.85 4.5 - - 16 16 - - 1.68 1.85
434 17.56 17.75 4.5 - - 16 16 - - 1.56 1.75
434.25 17.51 17.71 4.5 - - 16 16 - - 1.51 1.71
434.5 17.52 17.72 4.5 - - 16 16 - - 1.52 1.72
434.75 17.5 17.7 3.8 - - 16 16 - - 1.5 1.7
435 17.36 17.58 3.8 - - 16 16 - - 1.36 1.58
435.25 17.32 17.55 3.8 - - 16 16 - - 1.32 1.55
435.5 17.33 17.56 3.8 - - 16 16 - - 1.33 1.56
435.75 17.34 17.57 4.1 - - 16 16 - - 1.34 1.57
436 17.22 17.47 4.1 - - 16 16 - - 1.22 1.47
436.25 17.18 17.43 4.1 - - 16 16 - - 1.18 1.43
436.5 17.19 17.44 4.1 - - 16 16 - - 1.19 1.44
436.75 17.19 17.44 4.2 - - 16 16 - - 1.19 1.44
437 17.07 17.34 4.2 - - 16 16 - - 1.07 1.34
437.25 17.03 17.3 4.2 - - 16 16 - - 1.03 1.3
437.5 17.04 17.31 4.2 - - 16 16 - - 1.04 1.31
437.75 17.06 17.33 4.9 - - 16 16 - - 1.06 1.33
438 16.96 17.24 4.9 - - 16 16 - - 0.96 1.24
438.25 16.92 17.2 4.9 - - 16 16 - - 0.92 1.2
438.5 16.93 17.21 4.9 - - 16 16 - - 0.93 1.21
438.75 16.94 17.23 5.4 - - 16 16 - - 0.94 1.23
439 16.85 17.14 5.4 - - 16 16 - - 0.85 1.14
439.25 16.81 17.11 5.4 - - 16 16 - - 0.81 1.11
439.5 16.81 17.11 5.4 - - 16 16 - - 0.81 1.11
439.75 16.91 17.21 8.6 - - 16 16 - - 0.91 1.21
440 16.88 17.18 8.6 - - 16 16 - - 0.88 1.18
440.25 16.92 20.41 8.6 - 1 16 19 - 32 046.67 0.92 1.41
440.5 16.9 18.79 8.6 - - 16 19 - - 0.9 -0.21
440.75 16.94 20.02 8.6 - 1 16 19 - 32 046.67 0.94 1.02
441 16.89 19.49 8.6 - - 16 19 - - 0.89 0.49
441.25 16.85 17.58 8.6 - - 16 19 - - 0.85 -1.42
441.5 16.94 21.32 8.6 - 1 16 19 - 32 046.67 0.94 2.32
441.75 16.93 19.54 9.2 - - 16 19 - - 0.93 0.54
442 16.86 17.88 9.2 - - 16 19 - - 0.86 -1.12
442.25 16.93 21.72 9.2 - 1 16 19 - 32 046.67 0.93 2.72
442.5 16.9 19.88 9.2 - - 16 19 - - 0.9 0.88
442.75 16.86 17.96 9.1 - - 16 19 - - 0.86 -1.04
443 16.91 21.9 9.1 - 1 16 19 - 32 046.67 0.91 2.9
443.25 16.86 20.15 9.1 - - 16 19 - - 0.86 1.15
443.5 16.82 18.2 9.1 - - 16 19 - - 0.82 -0.8
443.75 16.88 21.93 8.6 - 1 16 19 - 32 046.67 0.88 2.93
444 16.81 20.61 8.6 - - 16 19 - - 0.81 1.61
444.25 16.76 18.85 8.6 - - 16 19 - - 0.76 -0.15
444.5 16.83 22.54 8.6 - 1 16 19 - 32 046.67 0.83 3.54
444.75 16.78 20.72 8.2 - - 16 19 - - 0.78 1.72
445 16.68 18.98 8.2 - - 16 19 - - 0.68 -0.02
445.25 16.75 22.79 8.2 - 1 16 19 - 32 046.67 0.75 3.79
445.5 16.71 20.96 8.2 - - 16 19 - - 0.71 1.96
445.75 16.66 19.02 7.9 - - 16 19 - - 0.66 0.02
446 16.61 19.7 7.9 - - 16 19 - - 0.61 0.7
446.25 20.16 19.64 7.9 1 - 19 16 32 046.67 - 1.16 3.64
446.5 18.48 19.6 7.9 - - 19 16 - - -0.52 3.6
446.75 19.81 19.63 7.9 1 - 19 16 32 046.67 - 0.81 3.63
447 19.24 19.47 7.9 - - 19 16 - - 0.24 3.47
447.25 17.25 19.39 7.9 - - 19 16 - - -1.75 3.39
447.5 21.24 19.5 7.9 1 - 19 16 32 046.67 - 2.24 3.5
447.75 19.47 19.45 7.2 - - 19 16 - - 0.47 3.45
448 17.7 19.3 7.2 - - 19 16 - - -1.3 3.3
448.25 21.83 19.35 7.2 1 - 19 16 32 046.67 - 2.83 3.35
448.5 19.97 19.32 7.2 - - 19 16 - - 0.97 3.32
448.75 17.8 19.24 5.9 - - 19 16 - - -1.2 3.24
449 22.53 19.34 5.9 1 - 19 16 32 046.67 - 3.53 3.34
449.25 20.28 19.12 5.9 - - 19 16 - - 1.28 3.12
449.5 17.8 19 5.9 - - 19 16 - - -1.2 3
449.75 21.85 19.1 6 1 - 19 16 32 046.67 - 2.85 3.1
450 20.63 18.97 5.5 - - 19 16 - - 1.63 2.97
450.25 18.65 18.89 5.5 - - 16 16 - - 2.65 2.89
450.5 19.04 18.91 5.5 - - 16 16 - - 3.04 2.91
450.75 18.95 18.91 5.5 - - 16 16 - - 2.95 2.91
451 18.77 18.77 5.5 - - 16 16 - - 2.77 2.77
451.25 18.69 18.72 5.5 - - 16 16 - - 2.69 2.72
451.5 18.7 18.74 5.5 - - 16 16 - - 2.7 2.74
451.75 18.7 18.73 5.4 - - 16 16 - - 2.7 2.73
452 18.52 18.61 5.4 - - 16 16 - - 2.52 2.61
452.25 18.45 18.56 5.4 - - 16 16 - - 2.45 2.56
452.5 18.46 18.58 5.4 - - 16 16 - - 2.46 2.58
452.75 18.45 18.57 5.2 - - 16 16 - - 2.45 2.57
453 18.3 18.45 5.2 - - 16 16 - - 2.3 2.45
453.25 18.24 18.41 5.2 - - 16 16 - - 2.24 2.41
453.5 18.25 18.42 5.2 - - 16 16 - - 2.25 2.42
453.75 18.24 18.4 4.9 - - 16 16 - - 2.24 2.4
454 18.09 18.29 4.9 - - 16 16 - - 2.09 2.29
454.25 18.04 18.25 4.9 - - 16 16 - - 2.04 2.25
454.5 18.05 18.26 4.9 - - 16 16 - - 2.05 2.26
454.75 18.05 18.25 4.8 - - 16 16 - - 2.05 2.25
455 17.91 18.14 4.8 - - 16 16 - - 1.91 2.14
455.25 17.86 18.1 4.8 - - 16 16 - - 1.86 2.1
455.5 17.87 18.11 4.8 - - 16 16 - - 1.87 2.11
455.75 17.86 18.1 4.5 - - 16 16 - - 1.86 2.1
456 17.73 17.98 4.5 - - 16 16 - - 1.73 1.98
456.25 17.68 17.95 4.5 - - 16 16 - - 1.68 1.95
456.5 17.69 17.96 4.5 - - 16 16 - - 1.69 1.96
456.75 17.69 17.95 4.5 - - 16 16 - - 1.69 1.95
457 17.56 17.85 4.5 - - 16 16 - - 1.56 1.85
457.25 17.52 17.81 4.5 - - 16 16 - - 1.52 1.81
457.5 17.53 17.82 4.5 - - 16 16 - - 1.53 1.82
457.75 17.52 17.81 4.5 - - 16 16 - - 1.52 1.81
458 17.41 17.71 4.5 - - 16 16 - - 1.41 1.71
458.25 17.36 17.67 4.5 - - 16 16 - - 1.36 1.67
458.5 17.37 17.68 4.5 - - 16 16 - - 1.37 1.68
458.75 17.37 17.68 4.7 - - 16 16 - - 1.37 1.68
459 17.26 17.58 4.7 - - 16 16 - - 1.26 1.58
459.25 17.22 17.54 4.7 - - 16 16 - - 1.22 1.54
459.5 17.23 17.55 4.7 - - 16 16 - - 1.23 1.55
459.75 17.22 17.54 4.5 - - 16 16 - - 1.22 1.54
460 17.1 17.44 4.5 - - 16 16 - - 1.1 1.44
460.25 17.06 17.4 4.5 - - 16 16 - - 1.06 1.4
460.5 17.07 17.41 4.5 - - 16 16 - - 1.07 1.41
460.75 17.06 17.4 4.3 - - 16 16 - - 1.06 1.4
461 16.95 17.3 4.3 - - 16 16 - - 0.95 1.3
461.25 16.91 17.26 4.3 - - 16 16 - - 0.91 1.26
461.5 16.92 17.27 4.3 - - 16 16 - - 0.92 1.27
461.75 16.91 17.27 4.3 - - 16 16 - - 0.91 1.27
462 16.81 17.17 4.3 - - 16 16 - - 0.81 1.17
462.25 16.76 17.13 4.3 - - 16 16 - - 0.76 1.13
462.5 16.77 17.14 4.3 - - 16 16 - - 0.77 1.14
462.75 16.77 17.14 4.4 - - 16 16 - - 0.77 1.14
463 16.67 17.04 4.4 - - 16 16 - - 0.67 1.04
463.25 16.63 17.01 4.4 - - 16 16 - - 0.63 1.01
463.5 16.64 17.02 4.4 - - 16 16 - - 0.64 1.02
463.75 16.64 17.02 4.5 - - 16 16 - - 0.64 1.02
464 16.54 16.92 4.5 - - 16 16 - - 0.54 0.92
464.25 16.5 16.89 4.5 - - 16 16 - - 0.5 0.89
464.5 16.51 16.9 4.5 - - 16 16 - - 0.51 0.9
464.75 16.5 16.89 4.3 - - 16 16 - - 0.5 0.89
465 16.41 16.8 4.3 - - 16 16 - - 0.41 0.8
465.25 16.38 16.77 4.3 - - 16 16 - - 0.38 0.77
465.5 16.39 16.79 4.3 - - 16 16 - - 0.39 0.79
465.75 16.41 16.81 4.9 - - 16 16 - - 0.41 0.81
466 16.33 16.73 4.9 - - 16 16 - - 0.33 0.73
466.25 16.31 16.71 4.9 - - 16 16 - - 0.31 0.71
466.5 16.33 16.72 4.9 - - 16 16 - - 0.33 0.72
466.75 16.35 16.74 5.2 - - 16 16 - - 0.35 0.74
467 16.34 16.69 5.2 - - 16 16 - - 0.34 0.69
467.25 16.37 16.69 5.2 - - 16 16 - - 0.37 0.69
467.5 16.41 16.71 5.2 - - 16 16 - - 0.41 0.71
467.75 16.38 16.71 5 - - 16 16 - - 0.38 0.71
468 16.33 16.65 5 - - 16 16 - - 0.33 0.65
468.25 16.31 16.63 5 - - 16 16 - - 0.31 0.63
468.5 16.3 16.63 5 - - 16 16 - - 0.3 0.63
468.75 16.29 16.63 5 - - 16 16 - - 0.29 0.63
469 16.24 16.57 5 - - 16 16 - - 0.24 0.57
469.25 16.22 16.55 5 - - 16 16 - - 0.22 0.55
469.5 16.22 16.55 5 - - 16 16 - - 0.22 0.55
469.75 16.22 16.56 5.2 - - 16 16 - - 0.22 0.56
470 16.17 16.5 5.2 - - 16 16 - - 0.17 0.5
470.25 16.15 16.48 5.2 - - 16 16 - - 0.15 0.48
470.5 16.16 16.48 5.2 - - 16 16 - - 0.16 0.48
470.75 16.14 16.47 5 - - 16 16 - - 0.14 0.47
471 16.07 16.4 5 - - 16 16 - - 0.07 0.4
471.25 16.03 16.37 5 - - 16 16 - - 0.03 0.37
471.5 16.02 16.36 5 - - 16 16 - - 0.02 0.36
471.75 16.01 16.35 5 - - 16 16 - - 0.01 0.35
472 15.93 16.27 5 - - 16 16 - - -0.07 0.27
472.25 19.41 16.31 5 1 - 16 16 32 046.67 - 3.41 0.31
472.5 17.68 16.27 5 - - 16 16 - - 1.68 0.27
472.75 15.47 16.21 4.6 - - 16 16 - - -0.53 0.21
473 19.74 16.21 4.6 1 - 16 16 32 046.67 - 3.74 0.21
473.25 18.03 16.16 4.6 - - 16 16 - - 2.03 0.16
473.5 15.85 16.11 4.6 - - 16 16 - - -0.15 0.11
473.75 19.81 16.17 3.9 1 - 16 16 32 046.67 - 3.81 0.17
474 18.54 16.06 3.6 - - 16 16 - - 2.54 0.06
474.25 16.58 15.99 3.6 - - 16 16 - - 0.58 -0.01
474.5 17.08 19.21 3.6 - 1 16 16 - 32 046.67 1.08 3.21
474.75 16.96 17.55 3.6 - - 16 16 - - 0.96 1.55
475 16.78 15.82 3.6 - - 16 16 - - 0.78 -0.18
475.25 16.8 19.66 3.6 - 1 16 16 - 32 046.67 0.8 3.66
475.5 16.78 17.82 3.6 - - 16 16 - - 0.78 1.82
475.75 16.73 15.9 3.7 - - 16 16 - - 0.73 -0.1
476 16.67 19.81 3.7 - 1 16 16 - 32 046.67 0.67 3.81
476.25 16.59 18.06 3.7 - - 16 16 - - 0.59 2.06
476.5 16.55 16.12 3.7 - - 16 16 - - 0.55 0.12
476.75 16.56 16.66 3.8 - - 16 16 - - 0.56 0.66
477 16.44 16.69 3.8 - - 16 16 - - 0.44 0.69
477.25 16.4 16.79 3.8 - - 16 16 - - 0.4 0.79
477.5 16.41 16.76 3.8 - - 16 16 - - 0.41 0.76
477.75 16.4 16.76 3.6 - - 16 16 - - 0.4 0.76
478 16.27 16.59 3.6 - - 16 16 - - 0.27 0.59
478.25 16.22 16.53 3.6 - - 16 16 - - 0.22 0.53
478.5 16.23 16.55 3.6 - - 16 16 - - 0.23 0.55
478.75 16.23 16.54 3.6 - - 16 16 - - 0.23 0.54
479 16.11 16.42 3.6 - - 16 16 - - 0.11 0.42
479.25 16.06 16.37 3.6 - - 16 16 - - 0.06 0.37
479.5 16.07 16.38 3.6 - - 16 16 - - 0.07 0.38
479.75 16.07 16.38 3.6 - - 16 16 - - 0.07 0.38
480 15.96 16.27 3.6 - - 16 16 - - -0.04 0.27
480.25 19.43 16.3 3.6 1 - 16 16 32 046.67 - 3.43 0.3
480.5 17.72 16.28 3.6 - - 16 16 - - 1.72 0.28
480.75 15.54 16.23 3.8 - - 16 16 - - -0.46 0.23
481 19.8 16.23 3.8 1 - 16 16 32 046.67 - 3.8 0.23
481.25 18.09 16.16 3.8 - - 16 16 - - 2.09 0.16
481.5 15.9 16.13 3.8 - - 16 16 - - -0.1 0.13
481.75 19.89 16.21 3.8 1 - 16 16 32 046.67 - 3.89 0.21
482 18.63 16.1 3.8 - - 16 16 - - 2.63 0.1
482.25 16.68 16.03 3.8 - - 16 16 - - 0.68 0.03
482.5 17.1 16.05 3.8 - - 16 16 - - 1.1 0.05
482.75 17.01 16.05 3.9 - - 16 16 - - 1.01 0.05
483 16.86 15.95 3.9 - - 16 16 - - 0.86 -0.05
483.25 16.86 19.11 3.9 - 1 16 16 - 32 046.67 0.86 3.11
483.5 16.84 17.46 3.9 - - 16 16 - - 0.84 1.46
483.75 16.79 15.48 3.8 - - 16 16 - - 0.79 -0.52
484 16.73 19.47 3.8 - 1 16 16 - 32 046.67 0.73 3.47
484.25 16.65 17.73 3.8 - - 16 16 - - 0.65 1.73
484.5 16.61 15.78 3.8 - - 16 16 - - 0.61 -0.22
484.75 16.69 19.53 3.8 - 1 16 16 - 32 046.67 0.69 3.53
485 16.55 18.19 3.8 - - 16 16 - - 0.55 2.19
485.25 16.47 16.44 3.8 - - 16 16 - - 0.47 0.44
485.5 16.48 16.92 3.8 - - 16 16 - - 0.48 0.92
485.75 16.49 16.79 3.9 - - 16 16 - - 0.49 0.79
486 16.36 16.67 3.9 - - 16 16 - - 0.36 0.67
486.25 16.31 16.6 3.9 - - 16 16 - - 0.31 0.6
486.5 16.32 16.62 3.9 - - 16 16 - - 0.32 0.62
486.75 16.31 16.61 3.8 - - 16 16 - - 0.31 0.61
487 16.19 16.47 3.8 - - 16 16 - - 0.19 0.47
487.25 16.14 16.42 3.8 - - 16 16 - - 0.14 0.42
487.5 16.15 16.43 3.8 - - 16 16 - - 0.15 0.43
487.75 16.15 16.43 3.7 - - 16 16 - - 0.15 0.43
488 16.08 16.32 3.7 - - 16 16 - - 0.08 0.32
488.25 16.1 16.3 3.7 - - 16 16 - - 0.1 0.3
488.5 16.11 16.32 3.7 - - 16 16 - - 0.11 0.32
488.75 16.1 16.32 3.8 - - 16 16 - - 0.1 0.32
489 16.02 16.23 3.8 - - 16 16 - - 0.02 0.23
489.25 15.99 16.2 3.8 - - 16 16 - - -0.01 0.2
489.5 19.52 16.3 3.8 1 - 16 16 32 046.67 - 3.52 0.3
489.75 17.83 16.28 4.1 - - 16 16 - - 1.83 0.28
490 16 16.19 4.1 - - 16 16 - - 0 0.19
490.25 16.63 16.19 4.1 - - 16 16 - - 0.63 0.19
490.5 16.56 16.21 4.1 - - 16 16 - - 0.56 0.21
490.75 16.65 16.24 4.6 - - 16 16 - - 0.65 0.24
491 16.6 16.19 4.6 - - 16 16 - - 0.6 0.19
491.25 16.62 16.18 4.6 - - 16 16 - - 0.62 0.18
491.5 16.73 16.2 4.6 - - 16 16 - - 0.73 0.2
491.75 16.85 16.23 5.6 - - 16 16 - - 0.85 0.23
492 17.05 16.21 5.6 - - 16 16 - - 1.05 0.21
492.25 17.22 16.2 5.6 - - 16 16 - - 1.22 0.2
492.5 17.37 16.2 5.6 - - 16 16 - - 1.37 0.2
492.75 17.53 16.22 6.4 - - 16 16 - - 1.53 0.22
493 17.89 16.22 6.4 - - 16 16 - - 1.89 0.22
493.25 18.07 16.22 6.4 - - 16 16 - - 2.07 0.22
493.5 18.1 16.23 6.4 - - 16 16 - - 2.1 0.23
493.75 18.12 16.27 7.5 - - 16 16 - - 2.12 0.27
494 18.47 16.3 7.5 - - 16 16 - - 2.47 0.3
494.25 18.53 16.3 7.5 - - 16 16 - - 2.53 0.3
494.5 18.4 16.31 7.5 - - 16 16 - - 2.4 0.31
494.75 18.36 16.35 9.2 - - 16 16 - - 2.36 0.35
495 18.57 16.39 9.2 - - 16 16 - - 2.57 0.39
495.25 18.54 16.37 9.2 - - 16 16 - - 2.54 0.37
495.5 18.38 16.35 9.2 - - 16 16 - - 2.38 0.35
495.75 18.23 16.31 8.5 - - 16 16 - - 2.23 0.31
496 18.21 16.28 8.5 - - 16 16 - - 2.21 0.28
496.25 18.15 16.25 8.5 - - 16 16 - - 2.15 0.25
496.5 18.03 16.22 8.5 - - 16 16 - - 2.03 0.22
496.75 17.91 16.17 8 - - 16 16 - - 1.91 0.17
497 17.76 16.09 8 - - 16 16 - - 1.76 0.09
497.25 17.71 16.07 8 - - 16 16 - - 1.71 0.07
497.5 17.71 16.07 8 - - 16 16 - - 1.71 0.07
497.75 17.68 16.04 6.9 - - 16 16 - - 1.68 0.04
498 17.51 15.93 6.3 - - 16 16 - - 1.51 -0.07
498.25 17.52 19.11 6.3 - 1 16 16 - 32 046.67 1.52 3.11
498.5 17.5 17.45 6.3 - - 16 16 - - 1.5 1.45
498.75 17.45 15.48 6.3 - - 16 16 - - 1.45 -0.52
499 17.42 19.48 6.3 - 1 16 16 - 32 046.67 1.42 3.48
499.25 17.35 17.75 6.3 - - 16 16 - - 1.35 1.75
499.5 17.31 15.8 6.3 - - 16 16 - - 1.31 -0.2
499.75 17.4 19.56 6.5 - 1 16 16 - 32 046.67 1.4 3.56
500 17.28 18.24 6.5 - - 16 16 - - 1.28 2.24
500.25 17.2 16.49 6.5 - - 16 16 - - 1.2 0.49
500.5 17.21 16.98 6.5 - - 16 16 - - 1.21 0.98
500.75 17.21 16.84 6.5 - - 16 16 - - 1.21 0.84
501 17.09 16.74 6.5 - - 16 16 - - 1.09 0.74
501.25 17.05 16.68 6.5 - - 16 16 - - 1.05 0.68
501.5 17.06 16.69 6.5 - - 16 16 - - 1.06 0.69
501.75 17.03 16.67 5.7 - - 16 16 - - 1.03 0.67
502 16.9 16.53 5.7 - - 16 16 - - 0.9 0.53
502.25 16.87 16.49 5.7 - - 16 16 - - 0.87 0.49
502.5 16.87 16.5 5.7 - - 16 16 - - 0.87 0.5
502.75 16.84 16.47 4.6 - - 16 16 - - 0.84 0.47
503 16.71 16.34 4.6 - - 16 16 - - 0.71 0.34
503.25 16.67 16.31 4.6 - - 16 16 - - 0.67 0.31
503.5 16.68 16.31 4.6 - - 16 16 - - 0.68 0.31
503.75 16.66 16.29 4 - - 16 16 - - 0.66 0.29
504 16.53 16.18 4 - - 16 16 - - 0.53 0.18
504.25 16.49 16.14 4 - - 16 16 - - 0.49 0.14
504.5 16.5 16.15 4 - - 16 16 - - 0.5 0.15
504.75 16.55 16.2 5.7 - - 16 16 - - 0.55 0.2
505 16.47 16.12 5.7 - - 16 16 - - 0.47 0.12
505.25 16.42 16.08 5.7 - - 16 16 - - 0.42 0.08
505.5 16.43 16.09 5.7 - - 16 16 - - 0.43 0.09
505.75 16.41 16.07 5.2 - - 16 16 - - 0.41 0.07
506 16.3 15.98 5.2 - - 16 16 - - 0.3 -0.02
506.25 16.34 19.15 5.2 - 1 16 16 - 32 046.67 0.34 3.15
506.5 16.32 17.5 5.2 - - 16 16 - - 0.32 1.5
506.75 16.3 15.56 6.4 - - 16 16 - - 0.3 -0.44
507 16.33 19.57 6.4 - 1 16 16 - 32 046.67 0.33 3.57
507.25 16.26 17.83 6.4 - - 16 16 - - 0.26 1.83
507.5 16.22 15.88 6.4 - - 16 16 - - 0.22 -0.12
507.75 16.28 19.61 5.8 - 1 16 16 - 32 046.67 0.28 3.61
508 16.18 18.28 5.8 - - 16 16 - - 0.18 2.28
508.25 16.11 16.53 5.8 - - 16 16 - - 0.11 0.53
508.5 16.12 17.02 5.8 - - 16 16 - - 0.12 1.02
508.75 16.13 16.89 5.9 - - 16 16 - - 0.13 0.89
509 16.03 16.77 5.9 - - 16 16 - - 0.03 0.77
509.25 15.99 16.71 5.9 - - 16 16 - - -0.01 0.71
509.5 19.51 16.8 5.9 1 - 16 16 32 046.67 - 3.51 0.8
509.75 17.78 16.75 5.5 - - 16 16 - - 1.78 0.75
510 15.9 16.59 5.5 - - 16 16 - - -0.1 0.59
510.25 20 16.63 5.5 1 - 16 16 32 046.67 - 4 0.63
510.5 18.15 16.61 5.5 - - 16 16 - - 2.15 0.61
510.75 15.98 16.54 5.1 - - 16 16 - - -0.02 0.54
511 20.18 16.52 5.1 1 - 16 16 32 046.67 - 4.18 0.52
511.25 18.44 16.45 5.1 - - 16 16 - - 2.44 0.45
511.5 16.26 16.42 5.1 - - 16 16 - - 0.26 0.42
511.75 16.72 16.41 4.8 - - 16 16 - - 0.72 0.41
512 16.89 16.33 4.8 - - 16 16 - - 0.89 0.33
512.25 17.1 19.58 4.8 - 1 16 19 - 32 046.67 1.1 0.58
512.5 17.04 17.96 4.8 - - 16 19 - - 1.04 -1.04
512.75 17.04 19.17 4.3 - 1 16 19 - 32 046.67 1.04 0.17
513 16.89 18.6 4.3 - - 16 19 - - 0.89 -0.4
513.25 16.89 19.89 4.3 - 1 16 19 - 32 046.67 0.89 0.89
513.5 16.88 18.76 4.3 - - 16 19 - - 0.88 -0.24
513.75 17 19.95 7.2 - 1 16 19 - 32 046.67 1 0.95
514 16.96 19.43 7.2 - - 16 19 - - 0.96 0.43
514.25 16.88 17.47 7.2 - - 16 19 - - 0.88 -1.53
514.5 16.97 21.23 7.2 - 1 16 19 - 32 046.67 0.97 2.23
514.75 16.98 19.46 8.3 - - 16 19 - - 0.98 0.46
515 16.91 17.78 8.3 - - 16 19 - - 0.91 -1.22
515.25 16.97 21.59 8.3 - 1 16 19 - 32 046.67 0.97 2.59
515.5 16.93 19.76 8.3 - - 16 19 - - 0.93 0.76
515.75 16.89 17.84 9.2 - - 16 19 - - 0.89 -1.16
516 16.94 21.77 9.2 - 1 16 19 - 32 046.67 0.94 2.77
516.25 16.88 20.01 9.2 - - 16 19 - - 0.88 1.01
516.5 16.83 18.06 9.2 - - 16 19 - - 0.83 -0.94
516.75 16.94 21.83 10.1 - 1 16 19 - 32 046.67 0.94 2.83
517 16.9 20.51 10.1 - - 16 19 - - 0.9 1.51
517.25 16.84 18.76 10.1 - - 16 19 - - 0.84 -0.24
517.5 16.92 22.45 10.1 - 1 16 19 - 32 046.67 0.92 3.45
517.75 16.97 20.73 12.6 - - 16 19 - - 0.97 1.73
518 16.94 19.05 12.6 - - 16 19 - - 0.94 0.05
518.25 20.49 19.68 12.6 1 - 19 16 32 046.67 - 1.49 3.68
518.5 18.8 19.44 12.6 - - 19 16 - - -0.2 3.44
518.75 20.13 19.54 13.1 1 - 19 16 32 046.67 - 1.13 3.54
519 19.59 19.37 13.1 - - 19 16 - - 0.59 3.37
519.25 17.55 19.28 13.1 - - 19 16 - - -1.45 3.28
519.5 21.49 19.36 13.1 1 - 19 16 32 046.67 - 2.49 3.36
519.75 19.68 19.32 13.3 - - 19 16 - - 0.68 3.32
520 17.85 19.19 13.3 - - 19 16 - - -1.15 3.19
520.25 21.95 19.24 13.3 1 - 19 16 32 046.67 - 2.95 3.24
520.5 20.09 19.2 13.3 - - 19 16 - - 1.09 3.2
520.75 17.92 19.14 13 - - 19 16 - - -1.08 3.14
521 22.14 19.14 13 1 - 19 16 32 046.67 - 3.14 3.14
521.25 20.41 19.07 13 - - 19 16 - - 1.41 3.07
521.5 18.22 19.03 13 - - 19 16 - - -0.78 3.03
521.75 22.16 19.07 11.7 1 - 19 16 32 046.67 - 3.16 3.07
522 20.92 18.97 12 - - 19 16 - - 1.92 2.97
522.25 18.94 18.91 12 - - 16 16 - - 2.94 2.91
522.5 19.33 18.92 12 - - 16 16 - - 3.33 2.92
522.75 19.25 18.92 12 - - 16 16 - - 3.25 2.92
523 19.11 18.83 12 - - 16 16 - - 3.11 2.83
523.25 19.05 18.8 12 - - 16 16 - - 3.05 2.8
523.5 19.07 18.81 12 - - 16 16 - - 3.07 2.81
523.75 19.05 18.79 11.6 - - 16 16 - - 3.05 2.79
524 18.91 18.71 11.6 - - 16 16 - - 2.91 2.71
524.25 18.86 18.68 11.6 - - 16 16 - - 2.86 2.68
524.5 18.87 18.69 11.6 - - 16 16 - - 2.87 2.69
524.75 18.86 18.67 11.2 - - 16 16 - - 2.86 2.67
525 18.74 18.59 11.2 - - 16 16 - - 2.74 2.59
525.25 18.7 18.56 11.2 - - 16 16 - - 2.7 2.56
525.5 18.71 18.57 11.2 - - 16 16 - - 2.71 2.57
525.75 18.75 18.61 12.7 - - 16 16 - - 2.75 2.61
526 18.68 18.57 12.7 - - 16 16 - - 2.68 2.57
526.25 18.63 18.53 12.7 - - 16 16 - - 2.63 2.53
526.5 18.64 18.54 12.7 - - 16 16 - - 2.64 2.54
526.75 18.63 18.52 12.2 - - 16 16 - - 2.63 2.52
527 18.54 18.45 12.2 - - 16 16 - - 2.54 2.45
527.25 18.51 18.43 12.2 - - 16 16 - - 2.51 2.43
527.5 18.51 18.44 12.2 - - 16 16 - - 2.51 2.44
527.75 18.47 18.4 10.8 - - 16 16 - - 2.47 2.4
528 18.36 18.31 10.8 - - 16 16 - - 2.36 2.31
528.25 18.33 18.29 10.8 - - 16 16 - - 2.33 2.29
528.5 18.34 18.3 10.8 - - 16 16 - - 2.34 2.3
528.75 18.35 18.31 11.2 - - 16 16 - - 2.35 2.31
529 18.27 18.24 11.2 - - 16 16 - - 2.27 2.24
529.25 18.24 18.22 11.2 - - 16 16 - - 2.24 2.22
529.5 18.24 18.22 11.2 - - 16 16 - - 2.24 2.22
529.75 18.24 18.22 11 - - 16 16 - - 2.24 2.22
530 18.15 18.15 11 - - 16 16 - - 2.15 2.15
530.25 18.12 18.12 11 - - 16 16 - - 2.12 2.12
530.5 18.13 18.13 11 - - 16 16 - - 2.13 2.13
530.75 18.13 18.13 10.9 - - 16 16 - - 2.13 2.13
531 18.05 18.06 10.9 - - 16 16 - - 2.05 2.06
531.25 18.02 18.04 10.9 - - 16 16 - - 2.02 2.04
531.5 18.02 18.04 10.9 - - 16 16 - - 2.02 2.04
531.75 18 18.02 10.1 - - 16 16 - - 2 2.02
532 17.91 17.94 10.1 - - 16 16 - - 1.91 1.94
532.25 17.88 17.92 10.1 - - 16 16 - - 1.88 1.92
532.5 17.89 17.92 10.1 - - 16 16 - - 1.89 1.92
532.75 17.86 17.9 9.4 - - 16 16 - - 1.86 1.9
533 17.77 17.82 9.4 - - 16 16 - - 1.77 1.82
533.25 17.74 17.8 9.4 - - 16 16 - - 1.74 1.8
533.5 17.75 17.8 9.4 - - 16 16 - - 1.75 1.8
533.75 17.75 17.8 9.4 - - 16 16 - - 1.75 1.8
534 17.66 17.73 9.4 - - 16 16 - - 1.66 1.73
534.25 17.63 17.7 9.4 - - 16 16 - - 1.63 1.7
534.5 17.64 17.71 9.4 - - 16 16 - - 1.64 1.71
534.75 17.62 17.69 8.7 - - 16 16 - - 1.62 1.69
535 17.52 17.6 8.7 - - 16 16 - - 1.52 1.6
535.25 17.5 17.58 8.7 - - 16 16 - - 1.5 1.58
535.5 17.5 17.59 8.7 - - 16 16 - - 1.5 1.59
535.75 17.52 17.6 9.3 - - 16 16 - - 1.52 1.6
536 17.48 17.55 9.3 - - 16 16 - - 1.48 1.55
536.25 17.53 20.79 9.3 - 1 16 19 - 32 046.67 1.53 1.79
536.5 17.49 19.17 9.3 - - 16 19 - - 1.49 0.17
536.75 17.47 17.22 9.9 - - 16 19 - - 1.47 -1.78
537 17.53 21.28 9.9 - 1 16 19 - 32 046.67 1.53 2.28
537.25 17.49 19.57 9.9 - - 16 19 - - 1.49 0.57
537.5 17.46 17.63 9.9 - - 16 19 - - 1.46 -1.37
537.75 17.54 21.36 9.6 - 1 16 19 - 32 046.67 1.54 2.36
538 17.49 20.09 9.6 - - 16 19 - - 1.49 1.09
538.25 17.45 18.37 9.6 - - 16 19 - - 1.45 -0.63
538.5 17.54 22.06 9.6 - 1 16 19 - 32 046.67 1.54 3.06
538.75 17.55 20.3 10.5 - - 16 19 - - 1.55 1.3
539 17.53 18.64 10.5 - - 16 19 - - 1.53 -0.36
539.25 17.68 22.48 10.5 - 1 16 19 - 32 046.67 1.68 3.48
539.5 17.71 20.66 10.5 - - 16 19 - - 1.71 1.66
539.75 17.8 18.79 12.1 - - 16 19 - - 1.8 -0.21
540 18.08 22.78 12.1 - 1 16 19 - 32 046.67 2.08 3.78
540.25 18.22 21.05 12.1 - - 16 19 - - 2.22 2.05
540.5 18.28 19.12 12.1 - - 16 19 - - 2.28 0.12
540.75 18.33 19.69 12.8 - - 16 19 - - 2.33 0.69
541 18.45 19.81 12.8 - - 16 19 - - 2.45 0.81
541.25 18.4 19.94 12.8 - - 16 19 - - 2.4 0.94
541.5 18.23 19.89 12.8 - - 16 19 - - 2.23 0.89
541.75 18.18 19.91 13.1 - - 16 19 - - 2.18 0.91
542 18.27 19.83 13.1 - - 16 19 - - 2.27 0.83
542.25 21.85 19.82 13.1 1 - 19 16 32 046.67 - 2.85 3.82
542.5 20.14 19.75 13.1 - - 19 16 - - 1.14 3.75
542.75 17.92 19.69 12.5 - - 19 16 - - -1.08 3.69
543 22.31 19.72 12.5 1 - 19 16 32 046.67 - 3.31 3.72
543.25 20.65 19.67 12.5 - - 19 16 - - 1.65 3.67
543.5 18.45 19.62 12.5 - - 19 16 - - -0.55 3.62
543.75 22.45 19.69 12.3 1 - 19 16 32 046.67 - 3.45 3.69
544 21.32 19.62 12.3 - - 19 16 - - 2.32 3.62
544.25 19.38 19.56 12.3 - - 19 16 - - 0.38 3.56
544.5 19.76 19.55 12.3 - - 19 16 - - 0.76 3.55
544.75 19.63 19.52 11.7 - - 19 16 - - 0.63 3.52
545 19.63 19.45 11.7 - - 19 16 - - 0.63 3.45
545.25 19.43 19.37 11.7 - - 19 16 - - 0.43 3.37
545.5 19.36 19.36 11.7 - - 19 16 - - 0.36 3.36
545.75 19.35 19.33 10.8 - - 19 16 - - 0.35 3.33
546 19.2 19.21 9.9 - - 19 16 - - 0.2 3.21
546.25 19.11 19.17 9.9 - - 16 16 - - 3.11 3.17
546.5 19.09 19.18 9.9 - - 16 16 - - 3.09 3.18
546.75 19.1 19.17 9.9 - - 16 16 - - 3.1 3.17
547 18.97 19.08 9.9 - - 16 16 - - 2.97 3.08
547.25 18.93 19.05 9.9 - - 16 16 - - 2.93 3.05
547.5 18.94 19.06 9.9 - - 16 16 - - 2.94 3.06
547.75 18.94 19.06 10.1 - - 16 16 - - 2.94 3.06
548 18.84 18.98 10.1 - - 16 16 - - 2.84 2.98
548.25 18.79 18.94 10.1 - - 16 16 - - 2.79 2.94
548.5 18.8 18.95 10.1 - - 16 16 - - 2.8 2.95
548.75 18.77 18.92 9.1 - - 16 16 - - 2.77 2.92
549 18.65 18.82 9.1 - - 16 16 - - 2.65 2.82
549.25 18.62 18.79 9.1 - - 16 16 - - 2.62 2.79
549.5 18.62 18.8 9.1 - - 16 16 - - 2.62 2.8
549.75 18.67 18.85 10.7 - - 16 16 - - 2.67 2.85
550 18.6 18.79 10.7 - - 16 16 - - 2.6 2.79
550.25 18.56 18.75 10.7 - - 16 16 - - 2.56 2.75
550.5 18.57 18.76 10.7 - - 16 16 - - 2.57 2.76
550.75 18.56 18.75 10.5 - - 16 16 - - 2.56 2.75
551 18.47 18.68 10.5 - - 16 16 - - 2.47 2.68
551.25 18.44 18.65 10.5 - - 16 16 - - 2.44 2.65
551.5 18.45 18.66 10.5 - - 16 16 - - 2.45 2.66
551.75 18.39 18.61 8.8 - - 16 16 - - 2.39 2.61
552 18.28 18.5 8.8 - - 16 16 - - 2.28 2.5
552.25 18.25 18.48 8.8 - - 16 16 - - 2.25 2.48
552.5 18.26 18.49 8.8 - - 16 16 - - 2.26 2.49
552.75 18.27 18.5 9.1 - - 16 16 - - 2.27 2.5
553 18.18 18.42 9.1 - - 16 16 - - 2.18 2.42
553.25 18.14 18.39 9.1 - - 16 16 - - 2.14 2.39
553.5 18.15 18.4 9.1 - - 16 16 - - 2.15 2.4
553.75 18.11 18.36 7.9 - - 16 16 - - 2.11 2.36
554 18 18.26 7.9 - - 16 16 - - 2 2.26
554.25 17.97 18.24 7.9 - - 16 16 - - 1.97 2.24
554.5 17.98 18.24 7.9 - - 16 16 - - 1.98 2.24
554.75 17.96 18.22 7.2 - - 16 16 - - 1.96 2.22
555 17.85 18.12 7.2 - - 16 16 - - 1.85 2.12
555.25 17.82 18.1 7.2 - - 16 16 - - 1.82 2.1
555.5 17.83 18.1 7.2 - - 16 16 - - 1.83 2.1
555.75 17.79 18.07 6.2 - - 16 16 - - 1.79 2.07
556 17.68 17.97 6.2 - - 16 16 - - 1.68 1.97
556.25 17.65 17.94 6.2 - - 16 16 - - 1.65 1.94
556.5 17.65 17.95 6.2 - - 16 16 - - 1.65 1.95
556.75 17.64 17.94 5.9 - - 16 16 - - 1.64 1.94
557 17.54 17.84 5.9 - - 16 16 - - 1.54 1.84
557.25 17.5 17.81 5.9 - - 16 16 - - 1.5 1.81
557.5 17.51 17.82 5.9 - - 16 16 - - 1.51 1.82
557.75 17.5 17.81 5.7 - - 16 16 - - 1.5 1.81
558 17.4 17.71 5.7 - - 16 16 - - 1.4 1.71
558.25 17.36 17.68 5.7 - - 16 16 - - 1.36 1.68
558.5 17.37 17.69 5.7 - - 16 16 - - 1.37 1.69
558.75 17.37 17.69 5.8 - - 16 16 - - 1.37 1.69
559 17.27 17.6 5.8 - - 16 16 - - 1.27 1.6
559.25 17.24 17.56 5.8 - - 16 16 - - 1.24 1.56
559.5 17.25 17.57 5.8 - - 16 16 - - 1.25 1.57
559.75 17.26 17.59 6.4 - - 16 16 - - 1.26 1.59
560 17.99 17.68 6.4 - - 16 16 - - 1.99 1.68
560.25 17.99 20.9 6.4 - 1 16 19 - 32 046.67 1.99 1.9
560.5 17.67 19.22 6.4 - - 16 19 - - 1.67 0.22
560.75 17.71 17.25 6.2 - - 16 19 - - 1.71 -1.75
561 18.08 21.34 6.2 - 1 16 19 - 32 046.67 2.08 2.34
561.25 18.22 19.64 6.2 - - 16 19 - - 2.22 0.64
561.5 18.24 17.7 6.2 - - 16 19 - - 2.24 -1.3
561.75 18.42 21.46 6.5 - 1 16 19 - 32 046.67 2.42 2.46
562 18.69 20.22 6.5 - - 16 19 - - 2.69 1.22
562.25 18.8 18.5 6.5 - - 16 19 - - 2.8 -0.5
562.5 18.94 22.18 6.5 - 1 16 19 - 32 046.67 2.94 3.18
562.75 19.03 20.44 8.4 - - 16 19 - - 3.03 1.44
563 19.39 18.82 8.4 - - 16 19 - - 3.39 -0.18
563.25 19.63 22.65 8.4 - 1 16 19 - 32 046.67 3.63 3.65
563.5 19.6 20.8 8.4 - - 16 19 - - 3.6 1.8
563.75 19.61 18.96 11.5 - - 16 19 - - 3.61 -0.04
564 20.03 22.98 11.5 - 1 16 19 - 32 046.67 4.03 3.98
564.25 20.03 21.24 11.5 - - 16 19 - - 4.03 2.24
564.5 19.85 19.3 11.5 - - 16 19 - - 3.85 0.3
564.75 19.8 19.86 12 - - 16 19 - - 3.8 0.86
565 20.03 19.99 12 - - 16 19 - - 4.03 0.99
565.25 20.08 20.13 12 - - 16 19 - - 4.08 1.13
565.5 20.01 20.1 12 - - 16 19 - - 4.01 1.1
565.75 19.98 20.12 12.3 - - 16 19 - - 3.98 1.12
566 20.08 20.04 12.3 - - 16 19 - - 4.08 1.04
566.25 20.08 19.95 12.3 - - 19 16 - - 1.08 3.95
566.5 20.01 19.91 12.3 - - 19 16 - - 1.01 3.91
566.75 19.96 19.91 12.2 - - 19 16 - - 0.96 3.91
567 20 19.85 12.2 - - 19 16 - - 1 3.85
567.25 20 19.83 12.2 - - 19 16 - - 1 3.83
567.5 19.96 19.82 12.2 - - 19 16 - - 0.96 3.82
567.75 19.93 19.82 12.4 - - 19 16 - - 0.93 3.82
568 19.91 19.76 12.4 - - 19 16 - - 0.91 3.76
568.25 19.87 19.72 12.4 - - 19 16 - - 0.87 3.72
568.5 19.81 19.7 12.4 - - 19 16 - - 0.81 3.7
568.75 19.71 19.65 12 - - 19 16 - - 0.71 3.65
569 19.6 19.56 12 - - 19 16 - - 0.6 3.56
569.25 19.57 19.53 12 - - 19 16 - - 0.57 3.53
569.5 19.57 19.53 12 - - 19 16 - - 0.57 3.53
569.75 19.54 19.5 11.1 - - 19 16 - - 0.54 3.5
570 19.37 19.34 9.1 - - 19 16 - - 0.37 3.34
570.25 19.26 19.28 9.1 - - 16 16 - - 3.26 3.28
570.5 19.24 19.3 9.1 - - 16 16 - - 3.24 3.3
570.75 19.25 19.29 9.1 - - 16 16 - - 3.25 3.29
571 19.13 19.19 9.1 - - 16 16 - - 3.13 3.19
571.25 19.09 19.16 9.1 - - 16 16 - - 3.09 3.16
571.5 19.1 19.17 9.1 - - 16 16 - - 3.1 3.17
571.75 19.08 19.15 8.5 - - 16 16 - - 3.08 3.15
572 18.96 19.04 8.5 - - 16 16 - - 2.96 3.04
572.25 18.92 19.01 8.5 - - 16 16 - - 2.92 3.01
572.5 18.92 19.02 8.5 - - 16 16 - - 2.92 3.02
572.75 18.89 18.98 7.3 - - 16 16 - - 2.89 2.98
573 18.75 18.87 7.3 - - 16 16 - - 2.75 2.87
573.25 18.72 18.84 7.3 - - 16 16 - - 2.72 2.84
573.5 18.72 18.85 7.3 - - 16 16 - - 2.72 2.85
573.75 18.69 18.81 6.3 - - 16 16 - - 2.69 2.81
574 18.56 18.7 6.3 - - 16 16 - - 2.56 2.7
574.25 18.52 18.67 6.3 - - 16 16 - - 2.52 2.67
574.5 18.53 18.67 6.3 - - 16 16 - - 2.53 2.67
574.75 18.5 18.64 5.3 - - 16 16 - - 2.5 2.64
575 18.36 18.52 5.3 - - 16 16 - - 2.36 2.52
575.25 18.32 18.49 5.3 - - 16 16 - - 2.32 2.49
575.5 18.33 18.5 5.3 - - 16 16 - - 2.33 2.5
575.75 18.3 18.47 4.5 - - 16 16 - - 2.3 2.47
576 18.17 18.35 4.5 - - 16 16 - - 2.17 2.35
576.25 18.13 18.31 4.5 - - 16 16 - - 2.13 2.31
576.5 18.13 18.32 4.5 - - 16 16 - - 2.13 2.32
576.75 18.12 18.31 4.1 - - 16 16 - - 2.12 2.31
577 17.99 18.19 4.1 - - 16 16 - - 1.99 2.19
577.25 17.95 18.15 4.1 - - 16 16 - - 1.95 2.15
577.5 17.96 18.16 4.1 - - 16 16 - - 1.96 2.16
577.75 17.93 18.13 3.2 - - 16 16 - - 1.93 2.13
578 17.79 18.01 3.2 - - 16 16 - - 1.79 2.01
578.25 17.74 17.97 3.2 - - 16 16 - - 1.74 1.97
578.5 17.75 17.98 3.2 - - 16 16 - - 1.75 1.98
578.75 17.74 17.96 2.7 - - 16 16 - - 1.74 1.96
579 17.6 17.84 2.7 - - 16 16 - - 1.6 1.84
579.25 17.56 17.8 2.7 - - 16 16 - - 1.56 1.8
579.5 17.57 17.81 2.7 - - 16 16 - - 1.57 1.81
579.75 17.55 17.79 2.2 - - 16 16 - - 1.55 1.79
580 17.41 17.67 2.2 - - 16 16 - - 1.41 1.67
580.25 17.37 17.63 2.2 - - 16 16 - - 1.37 1.63
580.5 17.38 17.64 2.2 - - 16 16 - - 1.38 1.64
580.75 17.36 17.63 1.9 - - 16 16 - - 1.36 1.63
581 17.23 17.5 1.9 - - 16 16 - - 1.23 1.5
581.25 17.18 17.46 1.9 - - 16 16 - - 1.18 1.46
581.5 17.19 17.47 1.9 - - 16 16 - - 1.19 1.47
581.75 17.23 17.5 3.1 - - 16 16 - - 1.23 1.5
582 17.13 17.41 3.1 - - 16 16 - - 1.13 1.41
582.25 17.07 17.36 3.1 - - 16 16 - - 1.07 1.36
582.5 17.08 17.37 3.1 - - 16 16 - - 1.08 1.37
582.75 17.11 17.4 4 - - 16 16 - - 1.11 1.4
583 17.01 17.3 4 - - 16 16 - - 1.01 1.3
583.25 16.96 17.26 4 - - 16 16 - - 0.96 1.26
583.5 16.97 17.27 4 - - 16 16 - - 0.97 1.27
583.75 16.95 17.25 3.4 - - 16 16 - - 0.95 1.25
584 16.97 17.17 3.4 - - 16 16 - - 0.97 1.17
584.25 17.05 20.42 3.4 - 1 16 19 - 32 046.67 1.05 1.42
584.5 17.03 18.81 3.4 - - 16 19 - - 1.03 -0.19
584.75 17.1 20.06 3.8 - 1 16 19 - 32 046.67 1.1 1.06
585 17.1 19.51 3.8 - - 16 19 - - 1.1 0.51
585.25 17.09 17.6 3.8 - - 16 19 - - 1.09 -1.4
585.5 17.21 21.35 3.8 - 1 16 19 - 32 046.67 1.21 2.35
585.75 17.23 19.57 4.3 - - 16 19 - - 1.23 0.57
586 17.24 17.91 4.3 - - 16 19 - - 1.24 -1.09
586.25 17.36 21.75 4.3 - 1 16 19 - 32 046.67 1.36 2.75
586.5 17.36 19.92 4.3 - - 16 19 - - 1.36 0.92
586.75 17.3 18.01 4.5 - - 16 19 - - 1.3 -0.99
587 17.43 21.95 4.5 - 1 16 19 - 32 046.67 1.43 2.95
587.25 17.42 20.21 4.5 - - 16 19 - - 1.42 1.21
587.5 17.37 18.27 4.5 - - 16 19 - - 1.37 -0.73
587.75 17.45 22.01 4.3 - 1 16 19 - 32 046.67 1.45 3.01
588 17.51 20.71 4.3 - - 16 19 - - 1.51 1.71
588.25 17.56 18.97 4.3 - - 16 19 - - 1.56 -0.03
588.5 17.69 22.65 4.3 - 1 16 19 - 32 046.67 1.69 3.65
588.75 17.72 20.86 4.6 - - 16 19 - - 1.72 1.86
589 17.9 19.16 4.6 - - 16 19 - - 1.9 0.16
589.25 18.06 19.78 4.6 - - 16 19 - - 2.06 0.78
589.5 18.17 19.62 4.6 - - 16 19 - - 2.17 0.62
589.75 18.29 19.71 5.4 - - 16 19 - - 2.29 0.71
590 18.59 19.57 5.4 - - 16 19 - - 2.59 0.57
590.25 22.26 19.55 5.4 1 - 19 16 32 046.67 - 3.26 3.55
590.5 20.56 19.5 5.4 - - 19 16 - - 1.56 3.5
590.75 18.37 19.5 6.6 - - 19 16 - - -0.63 3.5
591 23 19.55 6.6 1 - 19 16 32 046.67 - 4 3.55
591.25 21.36 19.49 6.6 - - 19 16 - - 2.36 3.49
591.5 19.06 19.44 6.6 - - 19 16 - - 0.06 3.44
591.75 19.45 19.43 6.3 - - 19 16 - - 0.45 3.43
592 19.81 19.38 6.3 - - 19 16 - - 0.81 3.38
592.25 19.94 19.35 6.3 - - 19 16 - - 0.94 3.35
592.5 19.77 19.33 6.3 - - 19 16 - - 0.77 3.33
592.75 19.58 19.27 5.9 - - 19 16 - - 0.58 3.27
593 19.37 19.13 5.9 - - 19 16 - - 0.37 3.13
593.25 19.21 19.05 5.9 - - 19 16 - - 0.21 3.05
593.5 19.17 19.04 5.9 - - 19 16 - - 0.17 3.04
593.75 19.16 19.03 5.4 - - 19 16 - - 0.16 3.03
594 18.99 18.89 5.2 - - 19 16 - - -0.01 2.89
594.25 18.88 18.84 5.2 - - 16 16 - - 2.88 2.84
594.5 18.87 18.86 5.2 - - 16 16 - - 2.87 2.86
594.75 18.87 18.85 5.2 - - 16 16 - - 2.87 2.85
595 18.71 18.73 5.2 - - 16 16 - - 2.71 2.73
595.25 18.65 18.68 5.2 - - 16 16 - - 2.65 2.68
595.5 18.67 18.7 5.2 - - 16 16 - - 2.67 2.7
595.75 18.66 18.69 5 - - 16 16 - - 2.66 2.69
596 18.51 18.57 5 - - 16 16 - - 2.51 2.57
596.25 18.45 18.52 5 - - 16 16 - - 2.45 2.52
596.5 18.46 18.54 5 - - 16 16 - - 2.46 2.54
596.75 18.45 18.53 4.8 - - 16 16 - - 2.45 2.53
597 18.31 18.41 4.8 - - 16 16 - - 2.31 2.41
597.25 18.26 18.37 4.8 - - 16 16 - - 2.26 2.37
597.5 18.27 18.38 4.8 - - 16 16 - - 2.27 2.38
597.75 18.27 18.38 4.8 - - 16 16 - - 2.27 2.38
598 18.14 18.26 4.8 - - 16 16 - - 2.14 2.26
598.25 18.09 18.22 4.8 - - 16 16 - - 2.09 2.22
598.5 18.1 18.23 4.8 - - 16 16 - - 2.1 2.23
598.75 18.06 18.2 3.8 - - 16 16 - - 2.06 2.2
599 17.92 18.07 3.8 - - 16 16 - - 1.92 2.07
599.25 17.87 18.04 3.8 - - 16 16 - - 1.87 2.04
599.5 17.88 18.05 3.8 - - 16 16 - - 1.88 2.05
599.75 17.87 18.03 3.4 - - 16 16 - - 1.87 2.03
600 17.73 17.91 3.4 - - 16 16 - - 1.73 1.91
600.25 17.68 17.87 3.4 - - 16 16 - - 1.68 1.87
600.5 17.69 17.88 3.4 - - 16 16 - - 1.69 1.88
600.75 17.69 17.88 3.5 - - 16 16 - - 1.69 1.88
601 17.57 17.77 3.5 - - 16 16 - - 1.57 1.77
601.25 17.52 17.73 3.5 - - 16 16 - - 1.52 1.73
601.5 17.53 17.74 3.5 - - 16 16 - - 1.53 1.74
601.75 17.53 17.74 3.5 - - 16 16 - - 1.53 1.74
602 17.41 17.63 3.5 - - 16 16 - - 1.41 1.63
602.25 17.36 17.59 3.5 - - 16 16 - - 1.36 1.59
602.5 17.37 17.6 3.5 - - 16 16 - - 1.37 1.6
602.75 17.37 17.6 3.5 - - 16 16 - - 1.37 1.6
603 17.25 17.49 3.5 - - 16 16 - - 1.25 1.49
603.25 17.2 17.45 3.5 - - 16 16 - - 1.2 1.45
603.5 17.21 17.46 3.5 - - 16 16 - - 1.21 1.46
603.75 17.21 17.45 3.5 - - 16 16 - - 1.21 1.45
604 17.09 17.35 3.5 - - 16 16 - - 1.09 1.35
604.25 17.05 17.31 3.5 - - 16 16 - - 1.05 1.31
604.5 17.06 17.32 3.5 - - 16 16 - - 1.06 1.32
604.75 17.06 17.32 3.6 - - 16 16 - - 1.06 1.32
605 16.94 17.21 3.6 - - 16 16 - - 0.94 1.21
605.25 16.9 17.17 3.6 - - 16 16 - - 0.9 1.17
605.5 16.91 17.18 3.6 - - 16 16 - - 0.91 1.18
605.75 16.91 17.18 3.6 - - 16 16 - - 0.91 1.18
606 16.8 17.08 3.6 - - 16 16 - - 0.8 1.08
606.25 16.75 17.04 3.6 - - 16 16 - - 0.75 1.04
606.5 16.76 17.05 3.6 - - 16 16 - - 0.76 1.05
606.75 16.76 17.05 3.7 - - 16 16 - - 0.76 1.05
607 16.66 16.95 3.7 - - 16 16 - - 0.66 0.95
607.25 16.61 16.91 3.7 - - 16 16 - - 0.61 0.91
607.5 16.62 16.92 3.7 - - 16 16 - - 0.62 0.92
607.75 16.62 16.92 3.7 - - 16 16 - - 0.62 0.92
608 16.59 16.84 3.7 - - 16 16 - - 0.59 0.84
608.25 16.64 20.08 3.7 - 1 16 19 - 32 046.67 0.64 1.08
608.5 16.58 18.45 3.7 - - 16 19 - - 0.58 -0.55
608.75 16.62 19.69 3.8 - 1 16 19 - 32 046.67 0.62 0.69
609 16.56 19.13 3.8 - - 16 19 - - 0.56 0.13
609.25 16.52 17.21 3.8 - - 16 19 - - 0.52 -1.79
609.5 16.61 20.97 3.8 - 1 16 19 - 32 046.67 0.61 1.97
609.75 16.58 19.16 3.8 - - 16 19 - - 0.58 0.16
610 16.48 17.47 3.8 - - 16 19 - - 0.48 -1.53
610.25 16.55 21.3 3.8 - 1 16 19 - 32 046.67 0.55 2.3
610.5 16.52 19.47 3.8 - - 16 19 - - 0.52 0.47
610.75 16.48 17.55 3.9 - - 16 19 - - 0.48 -1.45
611 16.5 21.47 3.9 - 1 16 19 - 32 046.67 0.5 2.47
611.25 16.45 19.72 3.9 - - 16 19 - - 0.45 0.72
611.5 16.43 17.79 3.9 - - 16 19 - - 0.43 -1.21
611.75 16.52 21.55 4.1 - 1 16 19 - 32 046.67 0.52 2.55
612 16.46 20.21 4.1 - - 16 19 - - 0.46 1.21
612.25 16.41 18.46 4.1 - - 16 19 - - 0.41 -0.54
612.5 16.51 22.16 4.1 - 1 16 19 - 32 046.67 0.51 3.16
612.75 16.48 20.36 4.2 - - 16 19 - - 0.48 1.36
613 16.39 18.63 4.2 - - 16 19 - - 0.39 -0.37
613.25 16.44 22.44 4.2 - 1 16 19 - 32 046.67 0.44 3.44
613.5 16.4 20.6 4.2 - - 16 19 - - 0.4 1.6
613.75 16.35 18.67 4.2 - - 16 19 - - 0.35 -0.33
614 16.38 22.55 4.2 - 1 16 19 - 32 046.67 0.38 3.55
614.25 19.88 20.81 4.2 1 - 19 16 32 046.67 - 0.88 4.81
614.5 18.15 18.8 4.2 - - 19 16 - - -0.85 2.8
614.75 19.5 19.39 4.7 1 - 19 16 32 046.67 - 0.5 3.39
615 18.96 19.41 4.7 - - 19 16 - - -0.04 3.41
615.25 20.48 19.56 4.7 1 - 19 16 32 046.67 - 1.48 3.56
615.5 19.23 19.5 4.7 - - 19 16 - - 0.23 3.5
615.75 16.95 19.45 4.5 - - 19 16 - - -2.05 3.45
616 21.26 19.36 4.5 1 - 19 16 32 046.67 - 2.26 3.36
616.25 19.57 19.26 4.5 - - 19 16 - - 0.57 3.26
616.5 17.37 19.23 4.5 - - 19 16 - - -1.63 3.23
616.75 21.34 19.29 4.3 1 - 19 16 32 046.67 - 2.34 3.29
617 20.14 19.15 4.3 - - 19 16 - - 1.14 3.15
617.25 18.04 19.01 4.3 - - 19 16 - - -0.96 3.01
617.5 21.92 19.08 4.3 1 - 19 16 32 046.67 - 2.92 3.08
617.75 20.12 19.05 4.2 - - 19 16 - - 1.12 3.05
618 18.18 18.88 4.3 - - 19 16 - - -0.82 2.88
618.25 18.7 18.84 4.3 - - 16 16 - - 2.7 2.84
618.5 18.55 18.85 4.3 - - 16 16 - - 2.55 2.85
618.75 18.58 18.85 4.3 - - 16 16 - - 2.58 2.85
619 18.33 18.7 4.3 - - 16 16 - - 2.33 2.7
619.25 18.24 18.65 4.3 - - 16 16 - - 2.24 2.65
619.5 18.26 18.66 4.3 - - 16 16 - - 2.26 2.66
619.75 18.25 18.65 4.2 - - 16 16 - - 2.25 2.65
620 18.09 18.52 4.2 - - 16 16 - - 2.09 2.52
620.25 18.02 18.47 4.2 - - 16 16 - - 2.02 2.47
620.5 18.03 18.49 4.2 - - 16 16 - - 2.03 2.49
620.75 18.02 18.47 3.9 - - 16 16 - - 2.02 2.47
621 17.87 18.34 3.9 - - 16 16 - - 1.87 2.34
621.25 17.81 18.3 3.9 - - 16 16 - - 1.81 2.3
621.5 17.82 18.31 3.9 - - 16 16 - - 1.82 2.31
621.75 17.81 18.3 3.7 - - 16 16 - - 1.81 2.3
622 17.67 18.18 3.7 - - 16 16 - - 1.67 2.18
622.25 17.62 18.13 3.7 - - 16 16 - - 1.62 2.13
622.5 17.63 18.14 3.7 - - 16 16 - - 1.63 2.14
622.75 17.63 18.14 3.8 - - 16 16 - - 1.63 2.14
623 17.49 18.03 3.8 - - 16 16 - - 1.49 2.03
623.25 17.44 17.98 3.8 - - 16 16 - - 1.44 1.98
623.5 17.45 17.99 3.8 - - 16 16 - - 1.45 1.99
623.75 17.45 17.99 3.8 - - 16 16 - - 1.45 1.99
624 17.32 17.87 3.8 - - 16 16 - - 1.32 1.87
624.25 17.27 17.83 3.8 - - 16 16 - - 1.27 1.83
624.5 17.29 17.84 3.8 - - 16 16 - - 1.29 1.84
624.75 17.28 17.84 3.8 - - 16 16 - - 1.28 1.84
625 17.16 17.73 3.8 - - 16 16 - - 1.16 1.73
625.25 17.11 17.69 3.8 - - 16 16 - - 1.11 1.69
625.5 17.12 17.7 3.8 - - 16 16 - - 1.12 1.7
625.75 17.12 17.69 3.8 - - 16 16 - - 1.12 1.69
626 17 17.58 3.8 - - 16 16 - - 1 1.58
626.25 16.96 17.54 3.8 - - 16 16 - - 0.96 1.54
626.5 16.97 17.55 3.8 - - 16 16 - - 0.97 1.55
626.75 16.96 17.55 3.8 - - 16 16 - - 0.96 1.55
627 16.85 17.44 3.8 - - 16 16 - - 0.85 1.44
627.25 16.81 17.4 3.8 - - 16 16 - - 0.81 1.4
627.5 16.81 17.41 3.8 - - 16 16 - - 0.81 1.41
627.75 16.81 17.41 3.7 - - 16 16 - - 0.81 1.41
628 16.69 17.3 3.7 - - 16 16 - - 0.69 1.3
628.25 16.65 17.26 3.7 - - 16 16 - - 0.65 1.26
628.5 16.66 17.27 3.7 - - 16 16 - - 0.66 1.27
628.75 16.66 17.27 3.7 - - 16 16 - - 0.66 1.27
629 16.55 17.16 3.7 - - 16 16 - - 0.55 1.16
629.25 16.51 17.12 3.7 - - 16 16 - - 0.51 1.12
629.5 16.52 17.13 3.7 - - 16 16 - - 0.52 1.13
629.75 16.51 17.13 3.7 - - 16 16 - - 0.51 1.13
630 16.4 17.02 3.7 - - 16 16 - - 0.4 1.02
630.25 16.36 16.98 3.7 - - 16 16 - - 0.36 0.98
630.5 16.37 17 3.7 - - 16 16 - - 0.37 1
630.75 16.37 16.99 3.7 - - 16 16 - - 0.37 0.99
631 16.26 16.89 3.7 - - 16 16 - - 0.26 0.89
631.25 16.22 16.85 3.7 - - 16 16 - - 0.22 0.85
631.5 16.23 16.86 3.7 - - 16 16 - - 0.23 0.86
631.75 16.23 16.86 3.8 - - 16 16 - - 0.23 0.86
632 16.19 16.78 3.8 - - 16 16 - - 0.19 0.78
632.25 16.2 16.76 3.8 - - 16 16 - - 0.2 0.76
632.5 16.2 16.78 3.8 - - 16 16 - - 0.2 0.78
632.75 16.2 16.78 3.9 - - 16 16 - - 0.2 0.78
633 16.13 16.71 3.9 - - 16 16 - - 0.13 0.71
633.25 16.11 16.68 3.9 - - 16 16 - - 0.11 0.68
633.5 16.12 16.7 3.9 - - 16 16 - - 0.12 0.7
633.75 16.13 16.71 3.9 - - 16 16 - - 0.13 0.71
634 16.07 16.64 3.9 - - 16 16 - - 0.07 0.64
634.25 16.05 16.61 3.9 - - 16 16 - - 0.05 0.61
634.5 16.05 16.63 3.9 - - 16 16 - - 0.05 0.63
634.75 16.07 16.64 4.1 - - 16 16 - - 0.07 0.64
635 16.03 16.58 4.1 - - 16 16 - - 0.03 0.58
635.25 16.02 16.57 4.1 - - 16 16 - - 0.02 0.57
635.5 16.04 16.58 4.1 - - 16 16 - - 0.04 0.58
635.75 16.06 16.59 4.3 - - 16 16 - - 0.06 0.59
636 16.03 16.54 4.3 - - 16 16 - - 0.03 0.54
636.25 16.02 16.53 4.3 - - 16 16 - - 0.02 0.53
636.5 16.02 16.53 4.3 - - 16 16 - - 0.02 0.53
636.75 16.03 16.55 4.8 - - 16 16 - - 0.03 0.55
637 16.01 16.51 4.8 - - 16 16 - - 0.01 0.51
637.25 16 16.48 4.8 - - 16 16 - - 0 0.48
637.5 19.51 16.56 4.8 1 - 16 16 32 046.67 - 3.51 0.56
637.75 17.8 16.53 5 - - 16 16 - - 1.8 0.53
638 15.99 16.46 5 - - 16 16 - - -0.01 0.46
638.25 20.11 16.53 5 1 - 16 16 32 046.67 - 4.11 0.53
638.5 18.26 16.49 5 - - 16 16 - - 2.26 0.49
638.75 16.09 16.44 5.1 - - 16 16 - - 0.09 0.44
639 16.82 16.4 5.1 - - 16 16 - - 0.82 0.4
639.25 16.81 16.38 5.1 - - 16 16 - - 0.81 0.38
639.5 16.79 16.37 5.1 - - 16 16 - - 0.79 0.37
639.75 16.78 16.37 5.2 - - 16 16 - - 0.78 0.37
640 16.65 16.29 5.2 - - 16 16 - - 0.65 0.29
640.25 16.59 16.26 5.2 - - 16 16 - - 0.59 0.26
640.5 16.59 16.26 5.2 - - 16 16 - - 0.59 0.26
640.75 16.58 16.24 5 - - 16 16 - - 0.58 0.24
641 16.48 16.16 5 - - 16 16 - - 0.48 0.16
641.25 16.57 16.17 5 - - 16 16 - - 0.57 0.17
641.5 16.44 16.13 5 - - 16 16 - - 0.44 0.13
641.75 16.36 16.1 4.9 - - 16 16 - - 0.36 0.1
642 16.29 16.03 4.9 - - 16 16 - - 0.29 0.03
642.25 16.25 16 4.9 - - 16 16 - - 0.25 0
642.5 16.33 19.21 4.9 - 1 16 16 - 32 046.67 0.33 3.21
642.75 16.3 17.55 4.9 - - 16 16 - - 0.3 1.55
643 16.16 15.83 4.9 - - 16 16 - - 0.16 -0.17
643.25 16.21 19.68 4.9 - 1 16 16 - 32 046.67 0.21 3.68
643.5 16.18 17.84 4.9 - - 16 16 - - 0.18 1.84
643.75 16.13 15.91 4.7 - - 16 16 - - 0.13 -0.09
644 16.11 19.82 4.7 - 1 16 16 - 32 046.67 0.11 3.82
644.25 16.04 18.08 4.7 - - 16 16 - - 0.04 2.08
644.5 16.01 16.13 4.7 - - 16 16 - - 0.01 0.13
644.75 16 16.66 4.5 - - 16 16 - - 0 0.66
645 15.91 16.69 4.5 - - 16 16 - - -0.09 0.69
645.25 19.39 16.88 4.5 1 - 16 16 32 046.67 - 3.39 0.88
645.5 17.68 16.81 4.5 - - 16 16 - - 1.68 0.81
645.75 15.5 16.77 4.4 - - 16 16 - - -0.5 0.77
646 19.76 16.7 4.4 1 - 16 16 32 046.67 - 3.76 0.7
646.25 18.04 16.62 4.4 - - 16 16 - - 2.04 0.62
646.5 15.86 16.58 4.4 - - 16 16 - - -0.14 0.58
646.75 19.85 16.67 4.6 1 - 16 16 32 046.67 - 3.85 0.67
647 18.6 16.55 4.6 - - 16 16 - - 2.6 0.55
647.25 16.64 16.47 4.6 - - 16 16 - - 0.64 0.47
647.5 17.06 16.49 4.6 - - 16 16 - - 1.06 0.49
647.75 16.97 16.48 4.4 - - 16 16 - - 0.97 0.48
648 16.82 16.36 4.4 - - 16 16 - - 0.82 0.36
648.25 16.75 16.32 4.4 - - 16 16 - - 0.75 0.32
648.5 16.77 16.33 4.4 - - 16 16 - - 0.77 0.33
648.75 16.76 16.32 4.2 - - 16 16 - - 0.76 0.32
649 16.6 16.21 4.2 - - 16 16 - - 0.6 0.21
649.25 16.54 16.18 4.2 - - 16 16 - - 0.54 0.18
649.5 16.55 16.19 4.2 - - 16 16 - - 0.55 0.19
649.75 16.54 16.18 3.9 - - 16 16 - - 0.54 0.18
650 16.41 16.07 3.9 - - 16 16 - - 0.41 0.07
650.25 16.36 16.03 3.9 - - 16 16 - - 0.36 0.03
650.5 16.37 16.04 3.9 - - 16 16 - - 0.37 0.04
650.75 16.34 16.01 3 - - 16 16 - - 0.34 0.01
651 16.2 15.9 3 - - 16 16 - - 0.2 -0.1
651.25 16.23 19.07 3 - 1 16 16 - 32 046.67 0.23 3.07
651.5 16.2 17.42 3 - - 16 16 - - 0.2 1.42
651.75 16.13 15.42 2.1 - - 16 16 - - 0.13 -0.58
652 16.08 19.38 2.1 - 1 16 16 - 32 046.67 0.08 3.38
652.25 16.01 17.65 2.1 - - 16 16 - - 0.01 1.65
652.5 15.98 15.7 2.1 - - 16 16 - - -0.02 -0.3
652.75 19.55 19.5 1.4 1 1 16 16 32 046.67 32 046.67 3.55 3.5
653 18.02 18.12 1.4 - - 16 16 - - 2.02 2.12
653.25 15.88 16.33 1.4 - - 16 16 - - -0.12 0.33
653.5 19.85 16.89 1.4 1 - 16 16 32 046.67 - 3.85 0.89
653.75 18.02 16.71 0.8 - - 16 16 - - 2.02 0.71
654 16.12 16.53 0.8 - - 16 16 - - 0.12 0.53
654.25 16.69 16.47 0.8 - - 16 16 - - 0.69 0.47
654.5 16.57 16.49 0.8 - - 16 16 - - 0.57 0.49
654.75 16.59 16.48 0.5 - - 16 16 - - 0.59 0.48
655 16.35 16.31 0.5 - - 16 16 - - 0.35 0.31
655.25 16.27 16.25 0.5 - - 16 16 - - 0.27 0.25
655.5 16.29 16.27 0.5 - - 16 16 - - 0.29 0.27
655.75 16.28 16.25 0.3 - - 16 16 - - 0.28 0.25
656 16.22 16.14 0.3 - - 16 16 - - 0.22 0.14
656.25 16.17 16.1 0.3 - - 16 16 - - 0.17 0.1
656.5 16.16 16.12 0.3 - - 16 16 - - 0.16 0.12
656.75 16.15 16.12 0.3 - - 16 16 - - 0.15 0.12
657 16.03 16.01 0.3 - - 16 16 - - 0.03 0.01
657.25 16 15.97 0.3 - - 16 16 - - 0 -0.03
657.5 19.6 19.27 0.3 1 1 16 16 32 046.67 32 046.67 3.6 3.27
657.75 17.85 17.57 0.2 - - 16 16 - - 1.85 1.57
658 15.92 15.82 0.2 - - 16 16 - - -0.08 -0.18
658.25 20.09 19.75 0.2 1 1 16 16 32 046.67 32 046.67 4.09 3.75
658.5 18.21 17.87 0.2 - - 16 16 - - 2.21 1.87
658.75 16.03 15.92 0.7 - - 16 16 - - 0.03 -0.08
659 16.81 19.86 0.7 - 1 16 16 - 32 046.67 0.81 3.86
659.25 16.77 18.11 0.7 - - 16 16 - - 0.77 2.11
659.5 16.73 16.18 0.7 - - 16 16 - - 0.73 0.18
659.75 16.75 16.72 0.7 - - 16 16 - - 0.75 0.72
660 16.63 16.77 0.7 - - 16 16 - - 0.63 0.77
660.25 16.61 16.89 0.7 - - 16 16 - - 0.61 0.89
660.5 16.65 16.87 0.7 - - 16 16 - - 0.65 0.87
660.75 16.68 16.89 1.1 - - 16 16 - - 0.68 0.89
661 16.6 16.75 1.1 - - 16 16 - - 0.6 0.75
661.25 16.56 16.7 1.1 - - 16 16 - - 0.56 0.7
661.5 16.57 16.71 1.1 - - 16 16 - - 0.57 0.71
661.75 16.57 16.71 1.4 - - 16 16 - - 0.57 0.71
662 16.52 16.62 1.4 - - 16 16 - - 0.52 0.62
662.25 16.49 16.58 1.4 - - 16 16 - - 0.49 0.58
662.5 16.5 16.59 1.4 - - 16 16 - - 0.5 0.59
662.75 16.49 16.58 1.6 - - 16 16 - - 0.49 0.58
663 16.42 16.49 1.6 - - 16 16 - - 0.42 0.49
663.25 16.4 16.45 1.6 - - 16 16 - - 0.4 0.45
663.5 16.4 16.45 1.6 - - 16 16 - - 0.4 0.45
663.75 16.38 16.44 1.7 - - 16 16 - - 0.38 0.44
664 16.31 16.35 1.7 - - 16 16 - - 0.31 0.35
664.25 16.27 16.31 1.7 - - 16 16 - - 0.27 0.31
664.5 16.29 16.31 1.7 - - 16 16 - - 0.29 0.31
664.75 16.3 16.31 2 - - 16 16 - - 0.3 0.31
665 16.2 16.21 2 - - 16 16 - - 0.2 0.21
665.25 16.2 16.18 2 - - 16 16 - - 0.2 0.18
665.5 16.08 16.14 2 - - 16 16 - - 0.08 0.14
665.75 16.02 16.12 1.8 - - 16 16 - - 0.02 0.12
666 15.93 16.01 1.8 - - 16 16 - - -0.07 0.01
666.25 19.4 16.05 1.8 1 - 16 16 32 046.67 - 3.4 0.05
666.5 17.69 16.03 1.8 - - 16 16 - - 1.69 0.03
666.75 15.51 15.98 1.8 - - 16 16 - - -0.49 -0.02
667 19.82 19.17 1.8 1 1 16 16 32 046.67 32 046.67 3.82 3.17
667.25 18.07 17.44 1.8 - - 16 16 - - 2.07 1.44
667.5 15.84 15.43 1.8 - - 16 16 - - -0.16 -0.57
667.75 19.9 19.26 1.7 1 1 16 16 32 046.67 32 046.67 3.9 3.26
668 18.63 17.95 1.7 - - 16 16 - - 2.63 1.95
668.25 16.64 16.18 1.7 - - 16 16 - - 0.64 0.18
668.5 17.06 16.66 1.7 - - 16 16 - - 1.06 0.66
668.75 16.98 16.54 2 - - 16 16 - - 0.98 0.54
669 16.81 16.41 2 - - 16 16 - - 0.81 0.41
669.25 16.74 16.34 2 - - 16 16 - - 0.74 0.34
669.5 16.75 16.36 2 - - 16 16 - - 0.75 0.36
669.75 16.75 16.36 2.1 - - 16 16 - - 0.75 0.36
670 16.58 16.22 2.1 - - 16 16 - - 0.58 0.22
670.25 16.52 16.17 2.1 - - 16 16 - - 0.52 0.17
670.5 16.53 16.18 2.1 - - 16 16 - - 0.53 0.18
670.75 16.52 16.17 1.9 - - 16 16 - - 0.52 0.17
671 16.37 16.04 1.9 - - 16 16 - - 0.37 0.04
671.25 16.31 16 1.9 - - 16 16 - - 0.31 0
671.5 16.4 19.22 1.9 - 1 16 16 - 32 046.67 0.4 3.22
671.75 16.35 17.54 1.5 - - 16 16 - - 0.35 1.54
672 16.18 15.79 1.5 - - 16 16 - - 0.18 -0.21
672.25 16.22 19.62 1.5 - 1 16 16 - 32 046.67 0.22 3.62
672.5 16.19 17.78 1.5 - - 16 16 - - 0.19 1.78
672.75 16.11 15.83 0.5 - - 16 16 - - 0.11 -0.17
673 16.06 19.7 0.5 - 1 16 16 - 32 046.67 0.06 3.7
673.25 15.98 17.95 0.5 - - 16 16 - - -0.02 1.95
673.5 19.46 16.08 0.5 1 - 16 16 32 046.67 - 3.46 0.08
673.75 17.71 16.55 -0.5 - - 16 16 - - 1.71 0.55
674 15.79 16.51 -0.5 - - 16 16 - - -0.21 0.51
674.25 19.87 16.7 -0.5 1 - 16 16 32 046.67 - 3.87 0.7
674.5 18.04 16.64 -0.5 - - 16 16 - - 2.04 0.64
674.75 15.86 16.58 -1 - - 16 16 - - -0.14 0.58
675 20 16.47 -1 1 - 16 16 32 046.67 - 4 0.47
675.25 18.25 16.37 -1 - - 16 16 - - 2.25 0.37
675.5 16.07 16.34 -1 - - 16 16 - - 0.07 0.34
675.75 16.53 16.33 -1.5 - - 16 16 - - 0.53 0.33
676 16.59 16.18 -1.5 - - 16 16 - - 0.59 0.18
676.25 16.68 16.13 -1.5 - - 16 16 - - 0.68 0.13
676.5 16.66 16.14 -1.5 - - 16 16 - - 0.66 0.14
676.75 16.66 16.13 -1.7 - - 16 16 - - 0.66 0.13
677 16.43 15.98 -1.7 - - 16 16 - - 0.43 -0.02
677.25 16.42 19.12 -1.7 - 1 16 16 - 32 046.67 0.42 3.12
677.5 16.4 17.47 -1.7 - - 16 16 - - 0.4 1.47
677.75 16.37 15.52 -1.2 - - 16 16 - - 0.37 -0.48
678 16.3 19.46 -1.2 - 1 16 16 - 32 046.67 0.3 3.46
678.25 16.2 17.71 -1.2 - - 16 16 - - 0.2 1.71
678.5 16.17 15.77 -1.2 - - 16 16 - - 0.17 -0.23
678.75 16.26 19.53 -0.7 - 1 16 16 - 32 046.67 0.26 3.53
679 16.11 18.16 -0.7 - - 16 16 - - 0.11 2.16
679.25 16.02 16.39 -0.7 - - 16 16 - - 0.02 0.39
679.5 16.03 16.88 -0.7 - - 16 16 - - 0.03 0.88
679.75 16.04 16.76 -0.3 - - 16 16 - - 0.04 0.76
680 16.06 16.65 -0.3 - - 16 16 - - 0.06 0.65
680.25 16.12 19.84 -0.3 - 1 16 19 - 32 046.67 0.12 0.84
680.5 16.09 18.24 -0.3 - - 16 19 - - 0.09 -0.76
680.75 16.14 19.49 0.4 - 1 16 19 - 32 046.67 0.14 0.49
681 16.07 18.87 0.4 - - 16 19 - - 0.07 -0.13
681.25 16.08 20.13 0.4 - 1 16 19 - 32 046.67 0.08 1.13
681.5 16.06 19.02 0.4 - - 16 19 - - 0.06 0.02
681.75 16.03 16.93 1.2 - - 16 19 - - 0.03 -2.07
682 16.06 20.92 1.2 - 1 16 19 - 32 046.67 0.06 1.92
682.25 16 19.16 1.2 - - 16 19 - - 0 0.16
682.5 19.46 17.3 1.2 1 - 16 19 32 046.67 - 3.46 -1.7
682.75 17.84 21.03 1.9 - 1 16 19 - 32 046.67 1.84 2.03
683 15.99 19.66 1.9 - - 16 19 - - -0.01 0.66
683.25 20.06 17.98 1.9 1 - 16 19 32 046.67 - 4.06 -1.02
683.5 18.29 21.64 1.9 - 1 16 19 - 32 046.67 2.29 2.64
683.75 16.11 19.81 2.3 - - 16 19 - - 0.11 0.81
684 16.8 18.09 2.3 - - 16 19 - - 0.8 -0.91
684.25 16.87 21.9 2.3 - 1 16 19 - 32 046.67 0.87 2.9
684.5 16.84 20.06 2.3 - - 16 19 - - 0.84 1.06
684.75 16.79 18.14 2.3 - - 16 19 - - 0.79 -0.86
685 16.75 22.01 2.3 - 1 16 19 - 32 046.67 0.75 3.01
685.25 16.67 20.24 2.3 - - 16 19 - - 0.67 1.24
685.5 16.64 18.31 2.3 - - 16 19 - - 0.64 -0.69
685.75 16.72 22.05 2.3 - 1 16 19 - 32 046.67 0.72 3.05
686 16.63 20.69 2.3 - - 16 19 - - 0.63 1.69
686.25 20.11 18.94 2.3 1 - 19 16 32 046.67 - 1.11 2.94
686.5 18.43 19.36 2.3 - - 19 16 - - -0.57 3.36
686.75 19.75 19.26 2.3 1 - 19 16 32 046.67 - 0.75 3.26
687 19.15 19.11 2.3 - - 19 16 - - 0.15 3.11
687.25 17.1 18.99 2.3 - - 19 16 - - -1.9 2.99
687.5 21.05 19.09 2.3 1 - 19 16 32 046.67 - 2.05 3.09
687.75 19.22 19.03 1.9 - - 19 16 - - 0.22 3.03
688 17.33 18.82 1.9 - - 19 16 - - -1.67 2.82
688.25 21.41 18.84 1.9 1 - 19 16 32 046.67 - 2.41 2.84
688.5 19.56 18.81 1.9 - - 19 16 - - 0.56 2.81
688.75 17.38 18.74 1.5 - - 19 16 - - -1.62 2.74
689 21.55 18.67 1.5 1 - 19 16 32 046.67 - 2.55 2.67
689.25 19.82 18.58 1.5 - - 19 16 - - 0.82 2.58
689.5 17.55 18.52 1.5 - - 19 16 - - -1.45 2.52
689.75 21.48 18.57 1 1 - 19 16 32 046.67 - 2.48 2.57
690 20.19 18.41 1 - - 19 16 - - 1.19 2.41
690.25 18.17 18.31 0.8 - - 16 16 - - 2.17 2.31
690.5 18.57 18.33 0.8 - - 16 16 - - 2.57 2.33
690.75 18.48 18.33 0.8 - - 16 16 - - 2.48 2.33
691 18.27 18.17 0.8 - - 16 16 - - 2.27 2.17
691.25 18.18 18.11 0.8 - - 16 16 - - 2.18 2.11
691.5 18.2 18.12 0.8 - - 16 16 - - 2.2 2.12
691.75 18.18 18.11 0.4 - - 16 16 - - 2.18 2.11
692 17.97 17.95 0.4 - - 16 16 - - 1.97 1.95
692.25 17.89 17.9 0.4 - - 16 16 - - 1.89 1.9
692.5 17.91 17.91 0.4 - - 16 16 - - 1.91 1.91
692.75 17.9 17.9 0.2 - - 16 16 - - 1.9 1.9
693 17.71 17.75 0.2 - - 16 16 - - 1.71 1.75
693.25 17.64 17.7 0.2 - - 16 16 - - 1.64 1.7
693.5 17.66 17.72 0.2 - - 16 16 - - 1.66 1.72
693.75 17.66 17.72 0.3 - - 16 16 - - 1.66 1.72
694 17.49 17.58 0.3 - - 16 16 - - 1.49 1.58
694.25 17.43 17.53 0.3 - - 16 16 - - 1.43 1.53
694.5 17.44 17.54 0.3 - - 16 16 - - 1.44 1.54
694.75 17.44 17.54 0.5 - - 16 16 - - 1.44 1.54
695 17.29 17.41 0.5 - - 16 16 - - 1.29 1.41
695.25 17.23 17.36 0.5 - - 16 16 - - 1.23 1.36
695.5 17.24 17.37 0.5 - - 16 16 - - 1.24 1.37
695.75 17.24 17.37 0.6 - - 16 16 - - 1.24 1.37
696 17.09 17.24 0.6 - - 16 16 - - 1.09 1.24
696.25 17.04 17.2 0.6 - - 16 16 - - 1.04 1.2
696.5 17.05 17.21 0.6 - - 16 16 - - 1.05 1.21
696.75 17.05 17.21 0.6 - - 16 16 - - 1.05 1.21
697 16.9 17.08 0.6 - - 16 16 - - 0.9 1.08
697.25 16.85 17.03 0.6 - - 16 16 - - 0.85 1.03
697.5 16.86 17.04 0.6 - - 16 16 - - 0.86 1.04
697.75 16.86 17.04 0.6 - - 16 16 - - 0.86 1.04
698 16.72 16.91 0.6 - - 16 16 - - 0.72 0.91
698.25 16.67 16.87 0.6 - - 16 16 - - 0.67 0.87
698.5 16.68 16.88 0.6 - - 16 16 - - 0.68 0.88
698.75 16.68 16.88 0.7 - - 16 16 - - 0.68 0.88
699 16.55 16.76 0.7 - - 16 16 - - 0.55 0.76
699.25 16.5 16.71 0.7 - - 16 16 - - 0.5 0.71
699.5 16.51 16.73 0.7 - - 16 16 - - 0.51 0.73
699.75 16.51 16.73 0.8 - - 16 16 - - 0.51 0.73
700 16.38 16.61 0.8 - - 16 16 - - 0.38 0.61
700.25 16.33 16.56 0.8 - - 16 16 - - 0.33 0.56
700.5 16.34 16.57 0.8 - - 16 16 - - 0.34 0.57
700.75 16.33 16.56 0.6 - - 16 16 - - 0.33 0.56
701 16.2 16.44 0.6 - - 16 16 - - 0.2 0.44
701.25 16.16 16.4 0.6 - - 16 16 - - 0.16 0.4
701.5 16.17 16.41 0.6 - - 16 16 - - 0.17 0.41
701.75 16.16 16.41 0.6 - - 16 16 - - 0.16 0.41
702 16.04 16.29 0.6 - - 16 16 - - 0.04 0.29
702.25 15.99 16.25 0.6 - - 16 16 - - -0.01 0.25
702.5 19.51 16.33 0.6 1 - 16 16 32 046.67 - 3.51 0.33
702.75 17.79 16.29 0.4 - - 16 16 - - 1.79 0.29
703 15.88 16.14 0.4 - - 16 16 - - -0.12 0.14
703.25 19.96 16.19 0.4 1 - 16 16 32 046.67 - 3.96 0.19
703.5 18.12 16.17 0.4 - - 16 16 - - 2.12 0.17
703.75 15.97 16.12 0.3 - - 16 16 - - -0.03 0.12
704 20.22 16.13 0.3 1 - 16 16 32 046.67 - 4.22 0.13
704.25 18.62 19.34 0.3 - 1 16 19 - 32 046.67 2.62 0.34
704.5 16.39 17.67 0.3 - - 16 19 - - 0.39 -1.33
704.75 16.88 18.91 0.3 - 1 16 19 - 32 046.67 0.88 -0.09
705 17.12 21.55 0.3 - 1 16 19 - 32 046.67 1.12 2.55
705.25 17.17 17.97 0.3 - - 16 19 - - 1.17 -1.03
705.5 17.18 19.75 0.3 - 1 16 19 - 32 046.67 1.18 0.75
705.75 17.16 18.5 0.4 - - 16 19 - - 1.16 -0.5
706 17.08 20.18 0.4 - 1 16 19 - 32 046.67 1.08 1.18
706.25 17 19.3 0.4 - - 16 19 - - 1 0.3
706.5 16.97 17.13 0.4 - - 16 19 - - 0.97 -1.87
706.75 17.07 20.95 0.6 - 1 16 19 - 32 046.67 1.07 1.95
707 16.97 19.53 0.6 - - 16 19 - - 0.97 0.53
707.25 16.9 17.76 0.6 - - 16 19 - - 0.9 -1.24
707.5 17 21.46 0.6 - 1 16 19 - 32 046.67 1 2.46
707.75 17 19.69 1.3 - - 16 19 - - 1 0.69
708 16.92 17.96 1.3 - - 16 19 - - 0.92 -1.04
708.25 16.98 21.77 1.3 - 1 16 19 - 32 046.67 0.98 2.77
708.5 16.97 19.94 1.3 - - 16 19 - - 0.97 0.94
708.75 16.95 18.04 1.7 - - 16 19 - - 0.95 -0.96
709 17.06 21.94 1.7 - 1 16 19 - 32 046.67 1.06 2.94
709.25 17.06 20.18 1.7 - - 16 19 - - 1.06 1.18
709.5 17.07 18.25 1.7 - - 16 19 - - 1.07 -0.75
709.75 17.24 21.99 1.6 - 1 16 19 - 32 046.67 1.24 2.99
710 17.34 20.66 1.6 - - 16 19 - - 1.34 1.66
710.25 20.96 18.94 1.6 1 - 19 16 32 046.67 - 1.96 2.94
710.5 19.36 19.37 1.6 - - 19 16 - - 0.36 3.37
710.75 17.26 19.24 2.9 - - 19 16 - - -1.74 3.24
711 21.79 19.25 2.9 1 - 19 16 32 046.67 - 2.79 3.25
711.25 20.14 19.15 2.9 - - 19 16 - - 1.14 3.15
711.5 17.88 19.11 2.9 - - 19 16 - - -1.12 3.11
711.75 21.78 19.15 2.1 1 - 19 16 32 046.67 - 2.78 3.15
712 20.68 19.01 2.1 - - 19 16 - - 1.68 3.01
712.25 18.72 18.92 2.1 - - 19 16 - - -0.28 2.92
712.5 22.5 18.97 2.1 1 - 19 16 32 046.67 - 3.5 2.97
712.75 20.57 18.9 2 - - 19 16 - - 1.57 2.9
713 18.7 18.74 2 - - 19 16 - - -0.3 2.74
713.25 22.84 18.78 2 1 - 19 16 32 046.67 - 3.84 2.78
713.5 20.8 18.69 2 - - 19 16 - - 1.8 2.69
713.75 18.55 18.6 1.4 - - 19 16 - - -0.45 2.6
714 22.69 18.55 1.4 1 - 19 16 32 046.67 - 3.69 2.55
714.25 20.89 18.46 1.3 - - 16 16 - - 4.89 2.46
714.5 18.69 18.43 1.3 - - 16 16 - - 2.69 2.43
714.75 19.16 18.43 1.3 - - 16 16 - - 3.16 2.43
715 19.19 18.29 1.3 - - 16 16 - - 3.19 2.29
715.25 19.26 18.24 1.3 - - 16 16 - - 3.26 2.24
715.5 19.25 18.26 1.3 - - 16 16 - - 3.25 2.26
715.75 19.23 18.24 0.7 - - 16 16 - - 3.23 2.24
716 18.96 18.08 0.7 - - 16 16 - - 2.96 2.08
716.25 18.87 18.03 0.7 - - 16 16 - - 2.87 2.03
716.5 18.89 18.04 0.7 - - 16 16 - - 2.89 2.04
716.75 18.87 18.03 0.4 - - 16 16 - - 2.87 2.03
717 18.67 17.88 0.4 - - 16 16 - - 2.67 1.88
717.25 18.59 17.83 0.4 - - 16 16 - - 2.59 1.83
717.5 18.6 17.84 0.4 - - 16 16 - - 2.6 1.84
717.75 18.59 17.83 0.2 - - 16 16 - - 2.59 1.83
718 18.41 17.69 0.2 - - 16 16 - - 2.41 1.69
718.25 18.34 17.64 0.2 - - 16 16 - - 2.34 1.64
718.5 18.35 17.66 0.2 - - 16 16 - - 2.35 1.66
718.75 18.34 17.65 -0.1 - - 16 16 - - 2.34 1.65
719 18.16 17.51 -0.1 - - 16 16 - - 2.16 1.51
719.25 18.09 17.46 -0.1 - - 16 16 - - 2.09 1.46
719.5 18.11 17.47 -0.1 - - 16 16 - - 2.11 1.47
719.75 18.09 17.46 -0.4 - - 16 16 - - 2.09 1.46
720 17.92 17.32 -0.4 - - 16 16 - - 1.92 1.32
720.25 17.86 17.28 -0.4 - - 16 16 - - 1.86 1.28
720.5 17.87 17.29 -0.4 - - 16 16 - - 1.87 1.29
720.75 17.86 17.28 -0.5 - - 16 16 - - 1.86 1.28
721 17.7 17.15 -0.5 - - 16 16 - - 1.7 1.15
721.25 17.64 17.1 -0.5 - - 16 16 - - 1.64 1.1
721.5 17.65 17.11 -0.5 - - 16 16 - - 1.65 1.11
721.75 17.64 17.11 -0.6 - - 16 16 - - 1.64 1.11
722 17.48 16.98 -0.6 - - 16 16 - - 1.48 0.98
722.25 17.43 16.93 -0.6 - - 16 16 - - 1.43 0.93
722.5 17.44 16.94 -0.6 - - 16 16 - - 1.44 0.94
722.75 17.43 16.93 -0.8 - - 16 16 - - 1.43 0.93
723 17.27 16.8 -0.8 - - 16 16 - - 1.27 0.8
723.25 17.21 16.76 -0.8 - - 16 16 - - 1.21 0.76
723.5 17.23 16.77 -0.8 - - 16 16 - - 1.23 0.77
723.75 17.22 16.76 -1 - - 16 16 - - 1.22 0.76
724 17.06 16.63 -1 - - 16 16 - - 1.06 0.63
724.25 17.01 16.58 -1 - - 16 16 - - 1.01 0.58
724.5 17.02 16.6 -1 - - 16 16 - - 1.02 0.6
724.75 17.02 16.59 -1 - - 16 16 - - 1.02 0.59
725 16.87 16.47 -1 - - 16 16 - - 0.87 0.47
725.25 16.81 16.42 -1 - - 16 16 - - 0.81 0.42
725.5 16.82 16.43 -1 - - 16 16 - - 0.82 0.43
725.75 16.82 16.43 -1.1 - - 16 16 - - 0.82 0.43
726 16.67 16.3 -1.1 - - 16 16 - - 0.67 0.3
726.25 16.62 16.26 -1.1 - - 16 16 - - 0.62 0.26
726.5 16.63 16.27 -1.1 - - 16 16 - - 0.63 0.27
726.75 16.62 16.26 -1.1 - - 16 16 - - 0.62 0.26
727 16.48 16.14 -1.1 - - 16 16 - - 0.48 0.14
727.25 16.43 16.1 -1.1 - - 16 16 - - 0.43 0.1
727.5 16.44 16.11 -1.1 - - 16 16 - - 0.44 0.11
727.75 16.44 16.11 -1.1 - - 16 16 - - 0.44 0.11
728 16.5 16.04 -1.1 - - 16 16 - - 0.5 0.04
728.25 16.62 19.28 -1.1 - 1 16 19 - 32 046.67 0.62 0.28
728.5 16.54 17.66 -1.1 - - 16 19 - - 0.54 -1.34
728.75 16.53 18.88 -1.3 - 1 16 19 - 32 046.67 0.53 -0.12
729 16.56 21.5 -1.3 - 1 16 19 - 32 046.67 0.56 2.5
729.25 16.49 17.91 -1.3 - - 16 19 - - 0.49 -1.09
729.5 16.4 19.66 -1.3 - 1 16 19 - 32 046.67 0.4 0.66
729.75 16.29 18.34 -1.1 - - 16 19 - - 0.29 -0.66
730 16.25 20 -1.1 - 1 16 19 - 32 046.67 0.25 1