My understanding (feel free to correct, those who know):
- the water side economizer chiller is the newer, more correct way of
modelling the system you describe -- where a plate frame heat exchanger
is in parallel with the chiller with chilled water on 1 side and
condenser water on the other. This is what I use.
- the air-side, water-side economizer tab adds a new cooling coil
connected to the condenser loop to precool your incoming air as well as
pre-cooling the condenser water before it goes to the chiller. Similar
but this adds fan energy (static across the new chiller) and pumping
energy and isn't really how a water-side economizer system that I am
familiar with is implemented (at least around here).
- in DOE-2.1e, you used to be able to set your cooling tower control to
"strainer cycle" which would also give you a water-side economizer but I
believe this was lost in going to DOE-2.2, with real loops etc. Adding
the water-side economizer chiller, restored this function.
One more note -- I understand that you do not need a load management or
equipment control to operate a water-side economizer chiller ... and
further if you add them, they will be ignored anyway. If there is
sufficient cooling based on the outdoor air temperature for the
water-side economizer chiller to carry the full cooling load, then it
will operate (for that 1 hour timestep). Otherwise, it will not operate
and the chillers will carry the full cooling load. There is no partial
operating mode.
Cheers,
Brian
On 6/6/2011 1:09 PM, Patrick Keeney wrote:
> Hi All,
> What is the difference between a "water side economizer chiller" and a
> "water side ecomizer," which you find under the air-side HVAC cooling
> subtab? What does each do for their respective systems?
> I am trying to model a water-side economizer that runs in series with
> the other chiller, so I am pretty sure that I want the "water-side
> economizer chiller." I just want to be sure because there is a
> substantial difference between the two in energy savings (water-side
> ecomizer chiller is more efficient).
> Thanks,
> Patrick
> --
> Patrick J Keeney
> MArch-MSSD Candidate
> 410-299-5627
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
> No virus found in this message.
> Checked by AVG - www.avg.com <http://www.avg.com>
> Version: 10.0.1382 / Virus Database: 1511/3684 - Release Date: 06/06/11
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110606/e6440822/attachment.htm>
More information about the Equest-users
mailing list