    My understanding (feel free to correct, those who know):<br>
    <br>
    - the water side economizer chiller is the newer, more correct way
    of modelling the system you describe -- where a plate frame heat
    exchanger is in parallel with the chiller with chilled water on 1
    side and condenser water on the other.  This is what I use.<br>
    <br>
    - the air-side, water-side economizer tab adds a new cooling coil
    connected to the condenser loop to precool your incoming air as well
    as pre-cooling the condenser water before it goes to the chiller. 
    Similar but this adds fan energy (static across the new chiller) and
    pumping energy and isn't really how a water-side economizer system
    that I am familiar with is implemented (at least around here).<br>
    <br>
    - in DOE-2.1e, you used to be able to set your cooling tower control
    to "strainer cycle" which would also give you a water-side
    economizer but I believe this was lost in going to DOE-2.2, with
    real loops etc.  Adding the water-side economizer chiller, restored
    this function.<br>
    <br>
    One more note -- I understand that you do not need a load management
    or equipment control to operate a water-side economizer chiller ...
    and further if you add them, they will be ignored anyway.  If there
    is sufficient cooling based on the outdoor air temperature for the
    water-side economizer chiller to carry the full cooling load, then
    it will operate (for that 1 hour timestep).  Otherwise, it will not
    operate and the chillers will carry the full cooling load.  There is
    no partial operating mode.<br>
    <br>
    Cheers,<br>
    <br>
    Brian<br>
    <br>
    <br>
    <br>
    On 6/6/2011 1:09 PM, Patrick Keeney wrote:
    <blockquote
      cite="mid:BANLkTim09a0RC7stvrEkU3DWuf4WfzoTkg@mail.gmail.com"
      type="cite">
      <div>Hi All,</div>
      <div> </div>
      <div>What is the difference between a "water side economizer
        chiller" and a "water side ecomizer," which you find under the
        air-side HVAC cooling subtab?  What does each do for their
        respective systems?</div>
      <div> </div>
      <div>I am trying to model a water-side economizer that runs in
        series with the other chiller, so I am pretty sure that I want
        the "water-side economizer chiller."  I just want to be sure
        because there is a substantial difference between the two in
        energy savings (water-side ecomizer chiller is more efficient).</div>
      <div> </div>
      <div>Thanks,</div>
      <div> </div>
      <div>Patrick<br clear="all">
      </div>
      <div> </div>
      <div>-- <br>
        Patrick J Keeney<br>
        MArch-MSSD Candidate<br>
        410-299-5627<br>
      </div>
      <pre wrap="">
<fieldset class="mimeAttachmentHeader"></fieldset>
_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <p class="avgcert" color="#000000" align="left">No virus found in
        this message.<br>
        Checked by AVG - <a moz-do-not-send="true"
          href="http://www.avg.com">www.avg.com</a><br>
        Version: 10.0.1382 / Virus Database: 1511/3684 - Release Date:
        06/06/11</p>
    </blockquote>
    <br>
  </body>
</html>