[Equest-users] Regarding error in modeling

Nick Caton ncaton at smithboucher.com
Wed Jun 1 08:12:05 PDT 2011


Hi Ashok,

Open your .BDL file (notepad), find the "ERROR" text and the adjacent
description of the problem, and that should help you resolve exactly
what the problem is. Alternatively, you may be able to use the dialog in
front of you to navigate to the source of the error within the eQuest
interface.

Looks on the surface and by your description that one or more zones is
referencing one or more spaces that don't exist anymore or have been
renamed.  You probably need to delete the offending zones & adjust
systems as necessary, or else recreate/rename/reassign the
offending/missing spaces.

~Nick



NICK CATON, E.I.T.
PROJECT ENGINEER
Smith & Boucher Engineers
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
www.smithboucher.com 


-----Original Message-----
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of ashok
singh
Sent: Wednesday, June 01, 2011 4:02 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Regarding error in modeling

Dear all,
             i am working on a mall, i have done zoning for this mall. 
but due to some changes in zoning , i have done rezoning of the mall.
now  this model is running and simulating, but further any change in
this model, shows error(Same as i attached) and not let it simulate.

 From last three days i am facing this problem, please gude me.
thanks in advance.

Regards
Ashok SIngh
M.Tech,
Energy Engg.
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Untitled.jpg
Type: image/jpeg
Size: 19700 bytes
Desc: Untitled.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110601/8be0b1e7/attachment.jpg>


More information about the Equest-users mailing list