[Equest-users] Basic stuff - Infiltration
John Bixler
JBixler at Sebesta.com
Wed Aug 10 07:23:00 PDT 2011
My own personal opinion is that ASHRAE Fundamentals has not rescued us here.
As Nick mentioned, the data presented there is for residential houses and relies on incredibly vague and subjective judgment calls by the modeler.
Furthermore, the values presented are in the unit's of air changes per hour. To me, this is a terrible way to use the data. Your entries for infiltration then rely on the volume of the room to determine the amount of infiltration. The volume of the room (zone is probably a better term) has NOTHING to do with the infiltration. What if I have a gym that's 150'x100'x50' tall, but it only has 10' wide by 50' tall of exterior wall??? If I use the ASHRAE method and rely on air changes per hour, the zone will be modeled with a HUGE GIGANTIC REALLY REALLY LARGE amount of infiltration.
Yet this seems to be the only recourse we have that is grounded in any sort of defendable data.
I have looked and looked for a reliable report or other source for real world commercial/institutional construction infiltration values to no avail. It would be so incredibly useful.
I have, over the course of my energy modeling career, developed a set of seemingly practical infiltration values to use, using the units of "CFM per sq ft of gross external wall area" available in Trane Trace (I don't believe these units are an option in eQuest). These values were developed by taking a number of buildings with no infiltration and arbitrarily adding infiltration in, until I get a reasonable utility consumption value. Hardly scientific and no way could I defend these values if they came under scrutiny, other than to say "well, you got a better idea????"
Some may say "Eh, who cares about infiltration anyway?". Well, it makes a bigger difference then you'd think.
A novice user who relies on the ASHRAE air changes per hour is likely significantly oversizing their cooling equipment in large rooms (ie conference, assembly, gyms, etc) which is exactly where you don't want to be oversizing cooling equipment.
Think about the components of a heating load - envelope conduction losses, taking in cold OA...and infiltration. Envelope losses are generally small, the design community likes to temper their OA (rightfully so), so where is a major component of the heating (consumption) load coming from? Infiltration really adds up.
How do you justify replacing leaky, wood sash windows? How bout making a switch to spray foam insulation? How about modeling door seals?
I've rambled enough. Point being, we all are forced to use arbitrary numbers for something that is a significant component of both equipment sizing and energy modeling and it just makes me mad and embarrassed when I have to explain to a client or colleague "well those are really important, but completely imaginary, numbers..."
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Bruce Easterbrook
Sent: Tuesday, August 09, 2011 5:41 PM
To: John Bixler
Subject: Re: [Equest-users] Basic stuff - Infiltration
Since 1922!
Bruce Easterbrook P.Eng.
Abode Engineering
ASHRAE Member
On 09/08/2011 06:11 PM, lawrence Lile wrote:
Good ol ASHRAE Fundamentals! Why didn't I think of looking there? Thanks!
On Mon, Aug 8, 2011 at 11:36 AM, Nick Caton <ncaton at smithboucher.com<mailto:ncaton at smithboucher.com>> wrote:
Hi Lawrence,
My copy of ASHRAE Principles of HVAC includes a table (5-1) excerpted from ASHRAE Fundamentals, 2001 (Table 7, Ch 28). This table provides air change rates as a function of subjective envelope airtightness ("tight" / "medium" / "loose") and as a function of the outdoor design temperature. Upon reviewing the referenced Fundamentals chapter, I learned this table is built from research surveying residential homes of various vintages, so it helps to know that these are "tight" to "loose" residential constructions.
In any case, I've used and cited this resource before when modeling infiltration and calculating sizing loads for non-residential projects as well. I've searched, but have yet to come up with an equivalent table based on surveying and measuring commercial constructions from a subjective/objective standpoint... That might be handier, but in the meantime this is a good tool for "converting" your subjective observations into the right ballpark.
~Nick
[cid:489575314 at 22072009-0ABB]
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036<tel:913.344.0036>
fax 913.345.0617<tel:913.345.0617>
www.smithboucher.com<http://www.smithboucher.com>
From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org>] On Behalf Of lawrence Lile
Sent: Sunday, August 07, 2011 12:50 PM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] Basic stuff - Infiltration
In building modeling programs one always has to provide precise values for infiltration. In the real world, I will know one of two things: almost nothing (The building appears to be kinda leaky with old windows), or I will have a blower door test done at a specific pressure. How do I convert subjective ("kinda leaky") or objective (Blower door test) leakage into numbers that make sense in the program? Is there a guide one can use?
--Lawrence
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110810/41d431a4/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110810/41d431a4/attachment.jpg>
More information about the Equest-users
mailing list