Rob,
Assuming you are looking at Table G3.1.1A in Standard 90 the key would be in
the use of the word AND: 3 stories or less AND less than 25,000 sf for PSZ
vs 5 stories or less AND between 25,000 and 100,000 sf for VAV. So I think
you should use VAV and that the below grade floor doesn't even come into
play.
Others?
Carol
On Mon, Mar 29, 2010 at 12:42 PM, Rob Hudson <rdh4176 at gmail.com> wrote:
> I have an office building that i am modeling that has 3 above ground floors
> and one below ground floor. the total square footage is 32,000. would this
> qualify as a VAV for the baseline or a single zone constant volume?
> The below ground floor is the part that is making me have second thoughts.
> my first thought was VAV, but i figured i would pose the question to get
> some healthy conversion.
>
> thanks,
>
> --
> Rob Hudson
>