[Equest-users] How to simulate a building with a unregular shape like pyramid?

Paul Brooks equestpaul at yahoo.com
Thu Mar 11 06:28:05 PST 2010


Cool, tso that is how you tilt the walls.  Thanks.  That helps on my project as well!




________________________________
From: John Aulbach <jra_sac at yahoo.com>
To: Lisa Zhang <lisazhangtj at gmail.com>; equest-users at lists.onebuilding.org
Sent: Thu, March 11, 2010 2:16:33 AM
Subject: Re: [Equest-users] How to simulate a building with a unregular shape like pyramid?


OK, LIsa:

Something "outside the box" from someone "outside the box."

An example:

Say you have a 4 story building. Create it in the DD Wizard. Say the walls have a 30° tilt (from vertical) and the actual wall is 12' in height along the wall face. That would mean the indent of the wall is 1/2 the wall length, or 6' (hope I can convey the math correctly - it's 11:15 PM at night). Create each floor with dimensions that shrinks each floor dimension by this much on each floor edge.

Then go to the Detailed Edit mode and put in a tilt of 60° (vertical wall is 90°).

I believe this will work.

Lisa, I will try to creat an example and send it to you.

John Aulbach 




________________________________
From: Lisa Zhang <lisazhangtj at gmail.com>
To: equest-users at lists.onebuilding.org
Sent: Wed, March 10, 2010 11:06:54 PM
Subject: [Equest-users] How to simulate a building with a unregular shape like pyramid?

Dear all,

      I met a project with the configulation quite unregular. It has
lean wall just like pyramid. How can I build it with equest? Have you
ever met with such problem?

      Thank you very much!


Lisa
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG


      
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100311/760f48b6/attachment.htm>


More information about the Equest-users mailing list