[Equest-users] Unmet Load Hours Calc

Carol Gardner cmg750 at gmail.com
Thu Jul 22 17:08:08 PDT 2010


You have a good nose, Dakota, so if you smell something fishy or otherwise,
I will probably agree with you.

Until you "kids" started talking about SS-R and SS-O reports I had never
even really looked at them. I always used the SS-F report to calculate my
hours. It reports hours underheated, hours undercooled, what the temperature
is (so you can see how far it goes out of range), and the time it occurs.
All of this information is very useful. For instance, you can quickly see if
you maybe just need to adjust your throttling range, from say 4 to 6, to
solve your problem, a frequently a reasonable and justifiable thing to do.
You can also see if your hours outside of throttling range happen to be
occurring on a Monday during the warm-up period during the winter or during
the late afternoon in a west facing zone during the summer, which might also
suggest an action to take. And, lastly, since you sometimes have hours in
both the heating and cooling columns, you have your coincident hours, too.
Then all you have to do is add them up. Granted that could be a chore if you
have 300 hours of unmet loads, but if I had 300 hours of unmet loads I'd
figure I hadn't modeled the building as well as I should have and I'd go
back and try to figure out why. I wouldn't be satisfied that the delta
between baseline and proposed didn't exceed the accepted 50 hours difference
until I had given it another shot to reduce the overall totals. And, like
many people have recently pointed out, and correctly I think, you've got to
know when to say "Enough".

That's MHO.

Carol



On Thu, Jul 22, 2010 at 4:34 PM, Dakota Kelley <dakotak at teliospc.com> wrote:

>  Brett,
>
>
>
> Let me state a few things, and then I’ll offer my interpretation of the
> comment:
>
>
>
> ·         The numbers in the SS-R report are the same numbers shown in the
> Air-Side Summary report.  These reports will yield inflated system totals,
> and therefore simulation totals, for multi-zone systems due to simultaneous
> counting of separate zones which belong to the same system.  Use them to
> determine the ratio of unmet heating and cooling hours relative to the two
> combined, but the sum of hours in these reports is not necessarily the same
> as multiplying the BEPS percentage by “hours fans on”.
>
> ·         Multiplying the BEPS percentage by the “hours fans on” in the
> SS-E report yields the correct sum of unmet heating and cooling hours,
> regardless of whether you are modeling multi- or single-zone systems.  Use
> the ratio obtained above to allocate this total between heating and cooling
> hours (I have posted previously<http://lists.onebuilding.org/htdig.cgi/equest-users-onebuilding.org/2010-July/005293.html>that there may be a more accurate method of allocating heating/cooling
> hours, but no one has corrected me).
>
> ·         The “hours fans on” includes hours the fans are *scheduled* *on*and the hours they are scheduled off but
> *cycle* *on*.  Refer to DOE2.2 Volume 4 (build 47), page 138 (SS-C report
> description), for the “hours fans on” definition.  This definition is echoed
> on page 142 (SS-E report description).  Therefore, for any system that
> cycles during off hours, all 8,760 hours have the potential to be counted as
> an unmet hour.
>
>
>
> Now for the review comment.  The “hours each zone exists” phrase doesn’t
> make sense on the first pass.  However, due to the last bullet point above
> and baseline requirement G3.1.2.4, “hours each zone exists” is practically
> the same thing as “hours the systems are on”.  All 8,760 hours have the
> potential to be counted as an unmet hour if the hourly T-stat setting &
> throttling range are not satisfied.  What if the proposed model doesn’t
> cycle over night?  I say that’s a bad idea; I would never design a system
> that way unless an owner wants mold, frozen pipes, etc.  Define a reasonable
> set back temperature, allow fans to cycle, and they will stay off if cycling
> is unnecessary.
>
>
>
> Where the comment is confusing/wrong is: “*SS-R reports have been
> used…does not take into account coincident hours*”.  Yes, it does.  It
> double-counts coincident hours on a multi-zone system, and because it is a
> system-level report, each system’s zones are counted separately.  It is as
> “coincident” as it gets.  I’m not sure how the reviewer rejects the SS-R
> report but then arrives at totals which are apparently greater than what was
> reported.  I have no .SIM file to review, but the smell of nonsense is
> strong.
>
>
>
>
>
>
>
> *DAKOTA KELLEY ***
>
> Project Designer | Energy Analyst
>
>
>
>                               Office: 214.744.6199
>
>                               Cell: 214.280.3825
>
>                               Fax: 214.744.0770
>
>
>
> http://www.teliospc.com          3535 Travis St. Suite 115
>
> dakotak at teliospc.com            Dallas, TX 75204
>
>
>
>
> | MEP ENGINEERING · ENERGY MODELING · LEED CONSULTATION · COMMISSIONING |
>
> * *
>
> CONFIDENTIALITY NOTICE: This email is intended only for the use of the
> individual or entity to which it is addressed,
>
> And may contain information that is privileged, confidential and exempt
> from disclosure under applicable law. If you
>
> are not the intended recipient, please email the sender immediately, and
> delete this email from all computers.  Any
>
> distribution or other use is strictly prohibited.  Copyright © 2009 Telios
> Corporation.
>
>
>
>
>
>
>
>
>
>
>
>
>
> *From:* Brett M. West [mailto:bwest at rmf.com]
> *Sent:* Thursday, July 22, 2010 8:01 AM
> *To:* equest-users at lists.onebuilding.org
> *Subject:* [Equest-users] Unmet Load Hours Calc
>
>
>
> I have a question regarding the way unmet load hours are calculated in
> eQuest. I have received the following comments from the USGBC reviewer after
> submitting my energy model.
>
>
>
> *1. The response narrative to preliminary comment 1 states that the SS-R
> reports have been used to determine the number of unmet load hours for each
> case however this method does not take into account coincident hours.
> Additionally, the number of hours any system outside of throttling range is
> not the number of hours the HVAC system is in operation but rather it is the
> number of hours each zone exists during the building simulation, or 8,760
> hours. Therefore the number of unmet load hours is 333 in the Baseline case
> and 508 in the Proposed case and the simulation does not meet the
> requirements of Section G3.1.2.2. If appealing this credit please revise
> both cases using the prescriptions of Section G3.1.2.2 until the number of
> unmet load hours is less than 300 for both cases and the number in the
> Proposed case does not exceed the number in the Baseline case by more than
> 50.*
>
>
>
> I thought the unmet load hours were calculated only during times when the
> fans are actually running in the simulation. This is why I always pull my
> unmet hours from the SS-R report, adding up the unmet hours for both cooling
> and heating for each individual unit. I can also go into the SS-E report and
> calculate the number of hours my fans are actually running and then
> calculate the total number of hours by using the percentage of hours outside
> the throttling range given in the BEPS report.
>
>
>
> If you calculate the hours in the manner the reviewer has outlined then
> there is no way to show which hours are heating and which are cooling and
> you have to provide that breakdown in the EAc1 template.
>
>
>
> Any input on this topic would be greatly appreciated.
>
>
>
> Thanks in advance.
>
>
>
>
>
> *BRETT M. WEST*
>
>
>
> RMF ENGINEERING**
>
> T: 843.971.9639 ext. 1499
>
> F: 843.971.9641
>
> bwest at rmf.com
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>


-- 
Carol Gardner PE
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100722/3570bcf6/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 2143 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100722/3570bcf6/attachment.jpeg>


More information about the Equest-users mailing list