[Equest-users] windows on plenum walls
Hwakong Cheng
hwakong at hotmail.com
Thu Dec 2 15:25:19 PST 2010
I think that more than 1% of buildings will have times when the conditions in the plenums differ from the spaces below.
For example:
1) If you have recessed lights, some fraction of the heat gain from those lights will go straight to the plenum, rather than become a space load that needs to be cooled at the zone level. If you are economizer mode, this heat load could be directly exhausted, as opposed to needing to be cooled by the system or plant. If you are not in economizer mode, this heat load still contributes to the system load, but not to the zone load (i.e. less airflow required).
2) If you have a roof (as most buildings do), the condition in the plenum immediately below that roof is going to differ from the space below. In a high-rise bldg, this only impacts the top floor, but it surely has a non-negligible impact for low-rise buildings. With a plenum, the roof conduction load (whether it is a heat load when it is hot and sunny outside or the opposite when it is cold and dark) will go straight to the plenum air rather than become a space load. This could affect economizer performance, zone sizing, zone loads, system airflow, system loads, etc… in real life too, not just in the simulation world.
No doubt there are other impacts. Granted, ignoring the plenum won’t likely make or break an energy model, but I actually think it is very easy to make plenums in eQUEST (the program does it for you!) so why not just put them in?
Date: Thu, 2 Dec 2010 13:46:11 -0800
From: cmg750 at gmail.com
To: ncaton at smithboucher.com
CC: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] windows on plenum walls
My attitude, which comes from being older than dirt and using DOE2 in it's infancy, is why have plenums at all? In fact, I am sure that at one point in the dark ages it was suggested in the manuals that, since plenums are generally the same temperature and space condition as the space below them, that they need not be input. Of course there are instances when this "rule" will need to be broken, as when you are specifying underfloor plenums and maybe some other cases. But the 99% of the times when that's not the case, it sure saves a lot of time, bother and space to not have plenums.
Carol
On Thu, Dec 2, 2010 at 9:03 AM, Nick Caton <ncaton at smithboucher.com> wrote:
I’m not one to whine much, but I have run smack into this ‘feature’ enough times to issue a complaint “feature request” =).
Aside from losing custom window placements, many zones being lumped into one has caused me major headaches for other reasons… if you are in a proposed/baseline modeling situation, and don’t pick up on the problem until you are well into detailed edits (it may not be as obvious if you don’t see spandrel glass disappearing), it’s simply a daunting task to create/assign all the associated surfaces and spaces to make the models sync – something I wouldn’t wish on anyone.
Let it be on record that a very welcome feature in any future eQuest development would be an explicit option (radio button) to let the user decide whether individual plenums or cohesive 1-per-floor plenums are desired to be generated for the shell. This might logically show up in the wizard footprint/zone definition screen, immediately following the automatic/custom zone definition pull-down.
Does this seem feasible, or is there something fundamental to the way DOE2 operates that would get in the way?
~Nick
NICK CATON, E.I.T.
PROJECT ENGINEER
Smith & Boucher Engineers
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Pasha Korber-Gonzalez
Sent: Thursday, December 02, 2010 10:20 AM
To: Mehta, Gaurav
Cc: eQUEST Users List
Subject: Re: [Equest-users] windows on plenum walls
Ah-HA! Thank you Karen and Gaurav...I guess I didn't really pay attention to the system assignments in the wizard as I usually abandon the wizard after the custom windows anyway. I just like DDedit mode, better than wizard mode.
Thanks again, as always this list is the BEST to turn to for support.
pkg
On Thu, Dec 2, 2010 at 9:10 AM, Mehta, Gaurav <Gaurav.Mehta at stantec.com> wrote:
When in the wizard you select or by default:
- System by floor : it results in a single plenum for entire floor
- System per zone: it results in multiple plenums per zone.
Gaurav Mehta, LEED® AP BD+C
Sustainable Building Analyst
Stantec
1932 First Avenue Suite 307
Seattle WA 98101
Ph: (206) 770-7779
Fx: (206) 770-5941
Gaurav.Mehta at stantec.com
stantec.com
The content of this email is the confidential property of Stantec and should not be copied, modified, retransmitted, or used for any purpose except with Stantec's written authorization. If you are not the intended recipient, please delete all copies and notify us immediately.
ü Please consider the environment before printing this email.
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Pasha Korber-Gonzalez
Sent: Thursday, December 02, 2010 8:04 AM
To: eQUEST Users List
Subject: Re: [Equest-users] windows on plenum walls
So, I figured out where my plenum windows were going...Because eQuest set up a single plenum for my entire floor plan, as opposed to multilple plenum spaces for each Zoned space that I have.
My new question that I haven't been able to figure out is this:
When (or how to determine when) eQuest will create a single plenum for the entire floor plan, and when does it create a single plenum space for each space zoned in my floor plan?
Sometimes I'll set up a model and it will do one approach and then sometimes I'll set up a model and it will create a single space plenum??
Any hints anyone can give me are appreciated.
thanks,
Pasha
On Wed, Dec 1, 2010 at 3:35 PM, Pasha Korber-Gonzalez <pasha.pkconsulting at gmail.com> wrote:
Hi All,
I've always been able to do this before, but its not letting me do it today on a model I am working on...
I'm am trying to place some windows on the plenum walls. In real life these are actually a spandrel panel. I'm in the custom window placement and when I place the window on the plenum wall it shows up in the custom window screen, but when I go to check my 3D view, the window on the plenum wall is not displayed.
Has anyone had this problem before? I've always been able to place windows there before (I specifically remember being able to do it in the window wizard for 3.63b version. I know I can verify thier existance when I move to DDedit, but I'm just trying to be more efficient using my wizard tools first.
thanks,
pkg
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
--
Carol Gardner PE
_______________________________________________ Equest-users mailing list http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101202/72d3a4b4/attachment.htm>
More information about the Equest-users
mailing list