[Equest-users] Demand Controlled Ventilation
R B
slv3sat at gmail.com
Wed Apr 28 11:35:55 PDT 2010
What I had ended up doing was to use both the numbers /person and
/sqft. but the per person number is slightly higher than the actual
per person number based on the area of the zone and the cfm/area. You
can use a equation in this cell to get the equivalent number.
So during the occupied time, if the occupancy is zero any hour, the
/sqft value gets used, and rest of the time /person value multiplied
with the actual number of people gets used. It is not exactly what you
want but it is better than one or the other.
I hope the equest team include sthe ASHRAE ventilation calcs in their
next version - the current version of calculating OA probably works
for Title 24?
-Rohini
On 4/28/10, Victor Yeung <Victor at invirosystems.ca> wrote:
> James,
>
>
>
> This is from the eQuest help file:
>
>
> OA-FLOW/AREA
>
>
> This keyword allows the specification of a minimum zone outside air (OA)
> flow rate per unit of zone floor area. The use of OUTSIDE-AIR-FLOW will
> over ride the value of this keyword. The maximum of values resulting
> from OA-FLOW/AREA, OA-FLOW/PER, and OA-CHANGES will be used unless an
> over-ride value for OUTSIDE-AIR-FLOW is specified.
>
> I've also tested this out by varying the OA-FLOW/PER in a model I've
> worked on. The total energy consumption didn't change, which suggested
> that my cfm/area rate was producing the larger cfm requirement and the
> program ignored my cfm/person rate.
>
>
>
> From: James Hansen [mailto:JHANSEN at ghtltd.com]
> Sent: April 28, 2010 2:08 PM
> To: Victor Yeung; Otto Schwieterman
> Cc: equest-users at lists.onebuilding.org
> Subject: RE: [Equest-users] Demand Controlled Ventilation
>
>
>
> "However, the way eQuest calculates min zone OA is by taking the higher
> value of either OA-FLOW/PER or OA-FLOW/AREA, not the combine total. To
> correctly model the OA requirement, I have to calculate the combine OA
> rate (i.e. {[cfm/per * max # of person] + [cfm/area * floor area] } /
> floor area) and input that value in OA-FLOW/AREA."
>
>
>
> Are you sure about that Victor? Last time I checked, when I input 5 CFM
> / person and 0.06 CFM / square foot, the minimum zone OA was the SUM of
> these two values. In which case you can model DCV without having to use
> that option in the system tab. eQuest will automatically size the 5 CFM
> / person portion of the outside air based on the occupancy diversity.
> Am I wrong here?
>
>
>
> GHT Limited
> James Hansen, PE, LEED AP
>
> Senior Associate
>
> 1010 N. Glebe Rd, Suite 200
>
> Arlington, VA 22201-4749
>
> 703-338-5754 (Cell)
>
> 703-243-1200 (Office)
>
> 703-276-1376 (Fax)
>
> www.ghtltd.com <http://www.ghtltd.com/>
>
>
>
>
>
>
>
> From: Victor Yeung [mailto:Victor at invirosystems.ca]
> Sent: Wednesday, April 28, 2010 12:30 PM
> To: Bishop, Bill; Rob Hudson
> Cc: equest-users at lists.onebuilding.org
> Subject: Re: [Equest-users] Demand Controlled Ventilation
>
>
>
> Hello all,
>
>
>
> I also have a similar question related to minimum OA settings for DCV,
> particularly with OA-FLOW/PER and OA-FLOW/AREA. Say I am using ASHRAE
> 62.1 for my OA rates, there are minimum requirements for cfm/person and
> cfm/area. However, the way eQuest calculates min zone OA is by taking
> the higher value of either OA-FLOW/PER or OA-FLOW/AREA, not the combine
> total. To correctly model the OA requirement, I have to calculate the
> combine OA rate (i.e. {[cfm/per * max # of person] + [cfm/area * floor
> area] } / floor area) and input that value in OA-FLOW/AREA. Now, the
> problem comes in when we include DCV into the model, at which eQuest
> cannot calculate the savings because the OA-FLOW/PER value is not
> entered. I would greatly appreciate it if anyone can clarify this.
>
>
>
> VICTOR YEUNG, BASc, LEED(r) AP
>
> EIT - LEED(r)/Sustainable Development
>
> victor at invirosystems.ca <mailto:victor at invirosystems...ca>
>
>
>
>
>
> From: Bishop, Bill [mailto:wbishop at pathfinder-ea.com]
> Sent: April 28, 2010 11:16 AM
> To: Rob Hudson
> Cc: equest-users at lists.onebuilding.org
> Subject: Re: [Equest-users] Demand Controlled Ventilation
>
>
>
> Rob,
>
>
>
> You need to set up an hourly report. See attached.
>
>
>
> Bill
>
>
>
> ________________________________
>
> From: Rob Hudson [mailto:rdh4176 at gmail.com]
> Sent: Wednesday, April 28, 2010 11:06 AM
> To: Bishop, Bill
> Cc: equest-users at lists.onebuilding.org
> Subject: Re: [Equest-users] Demand Controlled Ventilation
>
>
>
> How can i tell if the system is using a lower OA CFM during the less
> occupied times?
>
> On Wed, Apr 28, 2010 at 10:43 AM, Bishop, Bill
> <wbishop at pathfinder-ea.com> wrote:
>
> Rob,
>
>
>
> I recently modeled DCV successfully for the first time. (I showed
> savings anyway.) You need to enter zone-level OA as OA-FLOW/PER and/or
> OA-FLOW/AREA. The OA flow/per (person) is what will get you the savings,
> based on your occupancy schedule(s). I also created a MIN-AIR-SCH,
> coinciding with the fan schedule, set to zero when fan is off and -999
> when fan is on.
>
>
>
> Regards,
>
> Bill
>
>
>
> William Bishop, EIT, BEMP, LEED(r) AP | Pathfinder Engineers &
> Architects LLP
>
> Mechanical Engineer
>
>
>
> 134 South Fitzhugh Street
> Rochester, NY 14608
> T: (585) 325-6004 Ext. 114
> F: (585) 325-6005
>
> wbishop at pathfinder-ea.com
>
> www..pathfinder-ea.com <http://www.pathfinder-ea.com>
>
> P Please strive to live sustainably.
>
> ________________________________
>
> From: equest-users-bounces at lists.onebuilding.org
> [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Rob
> Hudson
> Sent: Wednesday, April 28, 2010 9:55 AM
> To: equest-users at lists.onebuilding.org
> Subject: [Equest-users] Demand Controlled Ventilation
>
>
>
> I am having some trouble with setting up DCV in my model. if i select
> DCV in Zone Sensors for the Min OA Control Method and a min outside Air
> Ratio, do i need any Zone level OA inputs?
> Any help or insight as to what inputs are necessary for DCV would be
> great!
>
> --
> Rob Hudson
>
>
>
>
> --
> Rob Hudson
>
> ________________________________________________________________________
> ________________
> Fanning/Howey Associates, Inc. intends to send this transmission
> (including any attachments) only to the
> designated individual or entity. If you received this message in
> error, please notify the sender by replying
> to the electronic mail (if electronic) or by telephone at the number
> indicated on this document.
> Fanning/Howey Associates, Inc. has taken reasonable precautions to
> ensure no viruses are present in the
> electronic mail. Fanning/Howey Associates, Inc., will not accept
> responsibility for any loss or damage arising
> from the use of this electronic mail or attachments. Use, disclosure,
> dissemination, distribution, or reproduction
> of this message by unintended recipients is not authorized and maybe
> unlawful. Any information included in
> this transmission that is not related to contracts with our
> authorization, verbal or written, by Fanning/Howey
> Associates, Inc. may not be covered by our professional liability
> insurance..
>
> ________________________________
>
>
> The information contained in this communication is confidential, may be
> privileged, and is intended only for the use of the addressee. It is
> the property of GHT Limited. Unauthorized use, disclosure or copying of
> this communication or any part thereof is strictly prohibited and may be
> unlawful. If you have received this communication in error, please
> notify me immediately by return e-mail or by e-mail to ght at ghtltd.com
> <mailto:ght at ghtltd.com> , and destroy this communication and all copies
> thereof, including all attachments. Thank you.
>
>
More information about the Equest-users
mailing list