[Equest-users] Demand Controlled Ventilation
Victor Yeung
Victor at invirosystems.ca
Wed Apr 28 11:21:07 PDT 2010
James,
This is from the eQuest help file:
OA-FLOW/AREA
This keyword allows the specification of a minimum zone outside air (OA)
flow rate per unit of zone floor area. The use of OUTSIDE-AIR-FLOW will
over ride the value of this keyword. The maximum of values resulting
from OA-FLOW/AREA, OA-FLOW/PER, and OA-CHANGES will be used unless an
over-ride value for OUTSIDE-AIR-FLOW is specified.
I've also tested this out by varying the OA-FLOW/PER in a model I've
worked on. The total energy consumption didn't change, which suggested
that my cfm/area rate was producing the larger cfm requirement and the
program ignored my cfm/person rate.
From: James Hansen [mailto:JHANSEN at ghtltd.com]
Sent: April 28, 2010 2:08 PM
To: Victor Yeung; Otto Schwieterman
Cc: equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] Demand Controlled Ventilation
"However, the way eQuest calculates min zone OA is by taking the higher
value of either OA-FLOW/PER or OA-FLOW/AREA, not the combine total. To
correctly model the OA requirement, I have to calculate the combine OA
rate (i.e. {[cfm/per * max # of person] + [cfm/area * floor area] } /
floor area) and input that value in OA-FLOW/AREA."
Are you sure about that Victor? Last time I checked, when I input 5 CFM
/ person and 0.06 CFM / square foot, the minimum zone OA was the SUM of
these two values. In which case you can model DCV without having to use
that option in the system tab. eQuest will automatically size the 5 CFM
/ person portion of the outside air based on the occupancy diversity.
Am I wrong here?
GHT Limited
James Hansen, PE, LEED AP
Senior Associate
1010 N. Glebe Rd, Suite 200
Arlington, VA 22201-4749
703-338-5754 (Cell)
703-243-1200 (Office)
703-276-1376 (Fax)
www.ghtltd.com <http://www.ghtltd.com/>
From: Victor Yeung [mailto:Victor at invirosystems.ca]
Sent: Wednesday, April 28, 2010 12:30 PM
To: Bishop, Bill; Rob Hudson
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Demand Controlled Ventilation
Hello all,
I also have a similar question related to minimum OA settings for DCV,
particularly with OA-FLOW/PER and OA-FLOW/AREA. Say I am using ASHRAE
62.1 for my OA rates, there are minimum requirements for cfm/person and
cfm/area. However, the way eQuest calculates min zone OA is by taking
the higher value of either OA-FLOW/PER or OA-FLOW/AREA, not the combine
total. To correctly model the OA requirement, I have to calculate the
combine OA rate (i.e. {[cfm/per * max # of person] + [cfm/area * floor
area] } / floor area) and input that value in OA-FLOW/AREA. Now, the
problem comes in when we include DCV into the model, at which eQuest
cannot calculate the savings because the OA-FLOW/PER value is not
entered. I would greatly appreciate it if anyone can clarify this.
VICTOR YEUNG, BASc, LEED(r) AP
EIT - LEED(r)/Sustainable Development
victor at invirosystems.ca <mailto:victor at invirosystems...ca>
From: Bishop, Bill [mailto:wbishop at pathfinder-ea.com]
Sent: April 28, 2010 11:16 AM
To: Rob Hudson
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Demand Controlled Ventilation
Rob,
You need to set up an hourly report. See attached.
Bill
________________________________
From: Rob Hudson [mailto:rdh4176 at gmail.com]
Sent: Wednesday, April 28, 2010 11:06 AM
To: Bishop, Bill
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Demand Controlled Ventilation
How can i tell if the system is using a lower OA CFM during the less
occupied times?
On Wed, Apr 28, 2010 at 10:43 AM, Bishop, Bill
<wbishop at pathfinder-ea.com> wrote:
Rob,
I recently modeled DCV successfully for the first time. (I showed
savings anyway.) You need to enter zone-level OA as OA-FLOW/PER and/or
OA-FLOW/AREA. The OA flow/per (person) is what will get you the savings,
based on your occupancy schedule(s). I also created a MIN-AIR-SCH,
coinciding with the fan schedule, set to zero when fan is off and -999
when fan is on.
Regards,
Bill
William Bishop, EIT, BEMP, LEED(r) AP | Pathfinder Engineers &
Architects LLP
Mechanical Engineer
134 South Fitzhugh Street
Rochester, NY 14608
T: (585) 325-6004 Ext. 114
F: (585) 325-6005
wbishop at pathfinder-ea.com
www..pathfinder-ea.com <http://www.pathfinder-ea.com>
P Please strive to live sustainably.
________________________________
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Rob
Hudson
Sent: Wednesday, April 28, 2010 9:55 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Demand Controlled Ventilation
I am having some trouble with setting up DCV in my model. if i select
DCV in Zone Sensors for the Min OA Control Method and a min outside Air
Ratio, do i need any Zone level OA inputs?
Any help or insight as to what inputs are necessary for DCV would be
great!
--
Rob Hudson
--
Rob Hudson
________________________________________________________________________
________________
Fanning/Howey Associates, Inc. intends to send this transmission
(including any attachments) only to the
designated individual or entity. If you received this message in
error, please notify the sender by replying
to the electronic mail (if electronic) or by telephone at the number
indicated on this document.
Fanning/Howey Associates, Inc. has taken reasonable precautions to
ensure no viruses are present in the
electronic mail. Fanning/Howey Associates, Inc., will not accept
responsibility for any loss or damage arising
from the use of this electronic mail or attachments. Use, disclosure,
dissemination, distribution, or reproduction
of this message by unintended recipients is not authorized and maybe
unlawful. Any information included in
this transmission that is not related to contracts with our
authorization, verbal or written, by Fanning/Howey
Associates, Inc. may not be covered by our professional liability
insurance..
________________________________
The information contained in this communication is confidential, may be
privileged, and is intended only for the use of the addressee. It is
the property of GHT Limited. Unauthorized use, disclosure or copying of
this communication or any part thereof is strictly prohibited and may be
unlawful. If you have received this communication in error, please
notify me immediately by return e-mail or by e-mail to ght at ghtltd.com
<mailto:ght at ghtltd.com> , and destroy this communication and all copies
thereof, including all attachments. Thank you.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100428/1be68c93/attachment.htm>
More information about the Equest-users
mailing list