How can i tell if the system is using a lower OA CFM during the less
occupied times?
On Wed, Apr 28, 2010 at 10:43 AM, Bishop, Bill <wbishop at pathfinder-ea.com>wrote:
>  Rob,
>
>
>
> I recently modeled DCV successfully for the first time. (I showed savings
> anyway.) You need to enter zone-level OA as OA-FLOW/PER and/or OA-FLOW/AREA.
> The OA flow/per (person) is what will get you the savings, based on your
> occupancy schedule(s). I also created a MIN-AIR-SCH, coinciding with the fan
> schedule, set to zero when fan is off and -999 when fan is on.
>
>
>
> Regards,
>
> Bill
>
>
>
> *William Bishop, EIT, BEMP, LEED® AP **|** **Pathfinder Engineers &
> Architects LLP***
>
> Mechanical Engineer
>
>
>
> 134 South Fitzhugh Street
> Rochester, NY 14608
> T: (585) 325-6004 Ext. 114
> F: (585) 325-6005
>
> wbishop at pathfinder-ea.com
>
> www.pathfinder-ea.com
>
> P Please strive to live sustainably.
>   ------------------------------
>
> *From:* equest-users-bounces at lists.onebuilding.org [mailto:
> equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Rob Hudson
> *Sent:* Wednesday, April 28, 2010 9:55 AM
> *To:* equest-users at lists.onebuilding.org
> *Subject:* [Equest-users] Demand Controlled Ventilation
>
>
>
> I am having some trouble with setting up DCV in my model.  if i select DCV
> in Zone Sensors for the Min OA Control Method and a min outside Air Ratio,
> do i need any Zone level OA inputs?
> Any help or insight as to what inputs are necessary for DCV would be great!
>
> --
> Rob Hudson
>
-- 