Rob,
I recently modeled DCV successfully for the first time. (I showed
savings anyway.) You need to enter zone-level OA as OA-FLOW/PER and/or
OA-FLOW/AREA. The OA flow/per (person) is what will get you the savings,
based on your occupancy schedule(s). I also created a MIN-AIR-SCH,
coinciding with the fan schedule, set to zero when fan is off and -999
when fan is on.