[Equest-users] Energy recovery ventilation

Dakota Kelley dakotak at teliospc.com
Fri Apr 16 08:33:02 PDT 2010


Rob,

 

A DOAS won’t necessarily solve your problem because, while an ERV can be specified, it will only see the return air of its dummy zone.  You want to assign the ERV directly to the “real” zones’ parent systems so that the correct return air is simulated.  

 

You may want to try system types “multi-zone” or “variable air volume” and see which one you can tweak to match the fan coils.  You can assign one zone per system and get past the multi-zone part, and  you can adjust your minimum flow ratio if the fan coils are constant volume.  The biggest problem I see is making sure you’re not cooling and reheating; VAV won’t allow you to disable zone hot water coils.  If the fan coils are variable temp, maybe see if you can give yourself a wide berth on the cold deck leaving temp (possibly using a supply air reset schedule).    

 

Thanks,

 

                                

                         DAKOTA KELLEY                                                              

                                Project Designer

 

                                Office:      214-744-6199

                                Cell:         214-280-3825

                                Fax:         214-744-0770 

                

http://www.teliospc.com <http://www.teliospc.com/>           3535 Travis St. Suite 115 

dakotak at teliospc.com <mailto:dakotak at teliospc.com>              Dallas, TX 75204 

 

| MEP ENGINEERING · ENERGY MODELING · LEED CONSULTATION · COMMISSIONING |                         

 

 

CONFIDENTIALITY NOTICE: This email is intended only for the use of the individual or entity to which it is addressed, 

And may contain information that is privileged, confidential and exempt from disclosure under applicable law. If you 

are not the intended recipient, please email the sender immediately, and delete this email from all computers.  Any 

distribution or other use is strictly prohibited.  Copyright © 2010 Telios Corporation.

 

 

 

 

 

From: Rob Hudson [mailto:rdh4176 at gmail.com] 
Sent: Friday, April 16, 2010 7:39 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Energy recovery ventilation

 

I am modeling a school building with small "unit ventilators" that have hot water and chilled water coils, (i'm modeling as fan coil units in equest).  My problem is that these units have a small ERV and equest doesn't allow fan coils to have them.  If anyone has a bright solution or tips that would be great.  
my plan as of now is to create a dummy system that will feed OA to the fan coil units and put the ERV on this dummy system.  

Thanks,

-- 
Rob Hudson

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100416/c17d3d15/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 3170 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100416/c17d3d15/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 2327 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100416/c17d3d15/attachment.jpeg>


More information about the Equest-users mailing list